<div dir="ltr"><div>Thanks to all who responded...the problem has now been solved. My faith in eQuest remains.<br></div><div><br></div><div>Chris</div></div><br><div class="gmail_quote"><div dir="ltr">On Thu, Dec 20, 2018 at 2:33 PM David Eldridge via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">





<div lang="EN-US">
<div class="gmail-m_7039130555017084751WordSection1">
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">That last sentence is the issue – the system is providing some amount of air including return and OA to the space, without a heating coil, meanwhile the thermostat
 may be expecting 70F all of the time.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">The issue could be resolved by “upgrading” the unit to heat, removing/reducing the OA quantity, or by relaxing or removing the thermostat schedules depending
 on what your goals are for the project.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif">David<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">David S. Eldridge, Jr.</span></b><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">, P</span></b><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">.</span></b><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">E</span></b><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">.</span></b><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">,
 LEED AP BD+C, BEMP, BEAP, HBDP</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Associate</span><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:4pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">Direct: (847) 316-92</span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">24</span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">
 | Mobile: (</span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">773</span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">)
</span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">490</span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">-</span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">5038</span><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">Grumman/Butkus Associates</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:gray">
</span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">| 820 Davis Street, Suite 300 | Evanston, IL 60201</span><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9pt;font-family:Calibri,sans-serif;color:gray">Energy Efficiency Consultants and Sustainable Design Engineers</span><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal"><u><span style="font-size:9pt;font-family:Calibri,sans-serif;color:gray"><a href="http://grummanbutkus.com/" target="_blank"><span style="color:gray">grummanbutkus.com</span></a></span></u><span style="font-size:9pt;font-family:Calibri,sans-serif;color:gray">
 | <u><a href="http://grummanbutkus.com/blog" target="_blank"><span style="color:gray">Blog</span></a></u> |
<u><a href="https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526" target="_blank"><span style="color:gray">Facebook</span></a></u> |
<u><a href="https://twitter.com/grummanbutkus" target="_blank"><span style="color:gray">Twitter</span></a></u></span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:gray"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> Equest-users [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Chris Hadlock via Equest-users<br>
<b>Sent:</b> Thursday, December 20, 2018 1:05 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] mystery heating load<u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal">I've had a few responses requesting the modeling files so I've attached the INP and PD2 file (weather file is CWEC\Toronto.bin). The zone in question is "L0 Elev Lobby S" and I've already removed all exterior surfaces from this space (i.e.
 there are no Child Components). I've assigned this zone to it's own system (it's the last system on the air-side tab) called "Test System". I've already created the hourly reports where you'll see all of the underheated hours (which only occur in the winter).
 The LS-B report shows no (zero) htg load. I realize the system is not really providing any heating to this zone the way it's setup.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Thanks,<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">Chris<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal">On Thu, Dec 20, 2018 at 1:26 PM Chris Hadlock <<a href="mailto:cjhadlock@gmail.com" target="_blank">cjhadlock@gmail.com</a>> wrote:<u></u><u></u></p>
</div>
<blockquote style="border-top:none;border-right:none;border-bottom:none;border-left:1pt solid rgb(204,204,204);padding:0in 0in 0in 6pt;margin-left:4.8pt;margin-right:0in">
<div>
<div>
<div>
<p class="MsoNormal">Hello,<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">I've created a model using eQuest 3.65 (DOE 2.2) build 7173 that is of a 20 storey multi-residential building located in Toronto, Ontario (Canada). There is a basement with a elevator lobby that is an interior space (no exterior walls). <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">My model keeps telling me I have underheated hours for this lobby. I'm trying to figure out why there is a heating load and I'm stumped. I have removed what I believe to be all potential sources of heat loss. I've deleted the underground
 floor (which was R-100 anyway), I've deleted the interior walls (just to be thorough), there is no infiltration, and I've set the ventilation to zero. In my mind, there is no source of heat loss. I've even added a significant (10 W/ft2) equipment load and
 yet there are still underheated hours (I've even reduced my Tstat setpoint to 60F). <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">I've run an hourly report to help figure out the loads for both the space ("Sum of all weighted loads except infil and latent") and zone ("Load Calc'd SPACE Sensible load at const temp (Btu/hr)"). These reports all indicate a positive load
 (i.e. net heat gain) from my lights, plug loads and occupants. However through this process I'm also questioning these reports as the lighting, people and equipment load being reported don't exactly align with my modeled schedules for these loads....but I've
 put a pin in that.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Regardless, I have no idea how to figure out what may be resulting in net heat loss for this zone. To be thorough, I checked the elevator lobby on the ground level and the same thing is happening. Has anybody seen this before...any ideas
 what might be causing heat loss for a zone with no ventilation and no walls and no infiltration? It does seem to be seasonal (i.e no underheated hours in the summer) so it has some connection to weather file but does not correlate exactly.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">If you do take the time to read this, a big thank you. If you provide the answer, you'll for sure be on Santa's "nice" list.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Chris <u></u><u></u></p>
</div>
</div>
</div>
</div>
</blockquote>
</div>
</div>
</div>

_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div>