    <p>OH!  I'm so glad I asked, because from the thread I got the
      impression that the mystery load was due to outside air introduced
      by the HVAC system!   So, your experience should be a warning to
      all eQUEST users that the LS-B, LS-D, etc. reports give only the
      heat flows from outdoor or indoor sources, and not heat flows from
      HVAC operations or the true interzone heat transfer from adjacent
      spaces.  The former is quite understandable since the HVAC
      simulation has not taken place yet, but latter needs a little bit
      of explanation.  In DOE-2 (underlying engine to eQUEST), the
      "Loads" loads are calculated based on the input temperatures for
      each space.  Since most runs are done using the same space
      temperatures, the LS-X reports would show no interzone heat
      transfer.  The subsequent System simulation solves for the true
      zone temperature, so that when zone temperatures are different
      between adjacent zones, there would be interzone heat transfer. 
      Unfortunately, this interzone heat transfer does not appear in any
      summary reports, although the hourly values can be obtained
      through the HOURLY-REPORT generator.</p>
    <p>Joe<br>
    </p>
    <div class="moz-cite-prefix">On 12/20/2018 1:19 PM, Chris Hadlock
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAFewGwfvCLkad5DMoYUYxK6erCdDKfKkJW7fzGnf4BqSapKiKA@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">right...although I had deleted all child components
        for my zone in question, there were interior walls (defined in
        adjacent zones) that were exchanging heat transfer with my zone.
        The adjacent zone just happened to be an unconditioned parking
        garage that was very cold...foolish that I missed it.</div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr">On Thu, Dec 20, 2018 at 4:00 PM Joe Huang via
          Equest-users <<a
            href="mailto:equest-users@lists.onebuilding.org"
            moz-do-not-send="true">equest-users@lists.onebuilding.org</a>>
          wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px
          0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div bgcolor="#FFFFFF">
            <p>And the cause for the mystery load is ??  Don't just
              leave us hanging!</p>
            <p>Joe<br>
            </p>
            <div class="gmail-m_-3904346340559647763moz-cite-prefix">On
              12/20/2018 12:47 PM, Chris Hadlock via Equest-users wrote:<br>
            </div>
            <blockquote type="cite">
              <div dir="ltr">
                <div>Thanks to all who responded...the problem has now
                  been solved. My faith in eQuest remains.<br>
                </div>
                <div><br>
                </div>
                <div>Chris</div>
              </div>
              <br>
              <div class="gmail_quote">
                <div dir="ltr">On Thu, Dec 20, 2018 at 2:33 PM David
                  Eldridge via Equest-users <<a
                    href="mailto:equest-users@lists.onebuilding.org"
                    target="_blank" moz-do-not-send="true">equest-users@lists.onebuilding.org</a>>
                  wrote:<br>
                </div>
                <blockquote class="gmail_quote" style="margin:0px 0px
                  0px 0.8ex;border-left:1px solid
                  rgb(204,204,204);padding-left:1ex">
                  <div lang="EN-US">
                    <div
class="gmail-m_-3904346340559647763gmail-m_7039130555017084751WordSection1">
                      <p class="MsoNormal"><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">That
                          last sentence is the issue â€“ the system is
                          providing some amount of air including return
                          and OA to the space, without a heating coil,
                          meanwhile the thermostat may be expecting 70F
                          all of the time.</span></p>
                      <p class="MsoNormal"><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p>
                      <p class="MsoNormal"><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">The
                          issue could be resolved by â€œupgrading” the
                          unit to heat, removing/reducing the OA
                          quantity, or by relaxing or removing the
                          thermostat schedules depending on what your
                          goals are for the project.</span></p>
                      <p class="MsoNormal"><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p>
                      <p class="MsoNormal"><span
                          style="font-size:11pt;font-family:Calibri,sans-serif">David</span></p>
                      <p class="MsoNormal"><span
                          style="font-size:11pt;font-family:Calibri,sans-serif"> </span></p>
                      <p class="MsoNormal"><span
                          style="font-size:11pt;font-family:Calibri,sans-serif"> </span></p>
                      <p class="MsoNormal"><b><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">David
                            S. Eldridge, Jr.</span></b><b><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">,
                            P</span></b><b><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">.</span></b><b><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">E</span></b><b><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">.</span></b><b><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">,
                            LEED AP BD+C, BEMP, BEAP, HBDP</span></b><span
style="font-size:11pt;font-family:Calibri,sans-serif"></span></p>
                      <p class="MsoNormal"><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Associate</span><span
style="font-size:11pt;font-family:Calibri,sans-serif"></span></p>
                      <p class="MsoNormal"><span
style="font-size:4pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span><span
style="font-size:11pt;font-family:Calibri,sans-serif"></span></p>
                      <p class="MsoNormal"><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">Direct:
                          (847) 316-92</span><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">24</span><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">
                          | Mobile: (</span><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">773</span><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">)
                        </span><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">490</span><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">-</span><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">5038</span><span
style="font-size:11pt;font-family:Calibri,sans-serif"></span></p>
                      <p class="MsoNormal"><span
style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span><span
style="font-size:11pt;font-family:Calibri,sans-serif"></span></p>
                      <p class="MsoNormal"><b><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">Grumman/Butkus
                            Associates</span></b><span
                          style="font-size:11pt;font-family:Calibri,sans-serif;color:gray">
                        </span><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(54,95,145)">|
                          820 Davis Street, Suite 300 | Evanston, IL
                          60201</span><span
                          style="font-size:11pt;font-family:Calibri,sans-serif"></span></p>
                      <p class="MsoNormal"><span
                          style="font-size:9pt;font-family:Calibri,sans-serif;color:gray">Energy
                          Efficiency Consultants and Sustainable Design
                          Engineers</span><span
                          style="font-size:11pt;font-family:Calibri,sans-serif"></span></p>
                      <p class="MsoNormal"><span
                          style="font-size:11pt;font-family:Calibri,sans-serif"> </span></p>
                      <p class="MsoNormal"><u><span
                            style="font-size:9pt;font-family:Calibri,sans-serif;color:gray"><a
                              href="http://grummanbutkus.com/"
                              target="_blank" moz-do-not-send="true"><span
                                style="color:gray">grummanbutkus.com</span></a></span></u><span
style="font-size:9pt;font-family:Calibri,sans-serif;color:gray"> | <u><a
                              href="http://grummanbutkus.com/blog"
                              target="_blank" moz-do-not-send="true"><span
                                style="color:gray">Blog</span></a></u> |
                          <u><a
href="https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526"
                              target="_blank" moz-do-not-send="true"><span
                                style="color:gray">Facebook</span></a></u>
                          | <u><a
                              href="https://twitter.com/grummanbutkus"
                              target="_blank" moz-do-not-send="true"><span
                                style="color:gray">Twitter</span></a></u></span><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:gray"></span></p>
                      <p class="MsoNormal"><span
style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p>
                      <p class="MsoNormal"><b><span
                            style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span
style="font-size:11pt;font-family:Calibri,sans-serif"> Equest-users
                          [mailto:<a
                            href="mailto:equest-users-bounces@lists.onebuilding.org"
                            target="_blank" moz-do-not-send="true">equest-users-bounces@lists.onebuilding.org</a>]
                          <b>On Behalf Of </b>Chris Hadlock via
                          Equest-users<br>
                          <b>Sent:</b> Thursday, December 20, 2018 1:05
                          PM<br>
                          <b>To:</b> <a
                            href="mailto:equest-users@lists.onebuilding.org"
                            target="_blank" moz-do-not-send="true">equest-users@lists.onebuilding.org</a><br>
                          <b>Subject:</b> Re: [Equest-users] mystery
                          heating load</span></p>
                      <p class="MsoNormal"> </p>
                      <div>
                        <div>
                          <p class="MsoNormal">I've had a few responses
                            requesting the modeling files so I've
                            attached the INP and PD2 file (weather file
                            is CWEC\Toronto.bin). The zone in question
                            is "L0 Elev Lobby S" and I've already
                            removed all exterior surfaces from this
                            space (i.e. there are no Child Components).
                            I've assigned this zone to it's own system
                            (it's the last system on the air-side tab)
                            called "Test System". I've already created
                            the hourly reports where you'll see all of
                            the underheated hours (which only occur in
                            the winter). The LS-B report shows no (zero)
                            htg load. I realize the system is not really
                            providing any heating to this zone the way
                            it's setup.</p>
                        </div>
                        <div>
                          <p class="MsoNormal"> </p>
                        </div>
                        <div>
                          <p class="MsoNormal">Thanks,</p>
                        </div>
                        <div>
                          <p class="MsoNormal">Chris</p>
                        </div>
                      </div>
                      <p class="MsoNormal"> </p>
                      <div>
                        <div>
                          <p class="MsoNormal">On Thu, Dec 20, 2018 at
                            1:26 PM Chris Hadlock <<a
                              href="mailto:cjhadlock@gmail.com"
                              target="_blank" moz-do-not-send="true">cjhadlock@gmail.com</a>>
                            wrote:</p>
                        </div>
                        <blockquote
style="border-top:none;border-right:none;border-bottom:none;border-left:1pt
                          solid rgb(204,204,204);padding:0in 0in 0in
                          6pt;margin-left:4.8pt;margin-right:0in">
                          <div>
                            <div>
                              <div>
                                <p class="MsoNormal">Hello,</p>
                                <div>
                                  <p class="MsoNormal"> </p>
                                </div>
                                <div>
                                  <p class="MsoNormal">I've created a
                                    model using eQuest 3.65 (DOE 2.2)
                                    build 7173 that is of a 20 storey
                                    multi-residential building located
                                    in Toronto, Ontario (Canada). There
                                    is a basement with a elevator lobby
                                    that is an interior space (no
                                    exterior walls). </p>
                                </div>
                                <div>
                                  <p class="MsoNormal"> </p>
                                </div>
                                <div>
                                  <p class="MsoNormal">My model keeps
                                    telling me I have underheated hours
                                    for this lobby. I'm trying to figure
                                    out why there is a heating load and
                                    I'm stumped. I have removed what I
                                    believe to be all potential sources
                                    of heat loss. I've deleted the
                                    underground floor (which was R-100
                                    anyway), I've deleted the interior
                                    walls (just to be thorough), there
                                    is no infiltration, and I've set the
                                    ventilation to zero. In my mind,
                                    there is no source of heat loss.
                                    I've even added a significant (10
                                    W/ft2) equipment load and yet there
                                    are still underheated hours (I've
                                    even reduced my Tstat setpoint to
                                    60F). </p>
                                </div>
                                <div>
                                  <p class="MsoNormal"> </p>
                                </div>
                                <div>
                                  <p class="MsoNormal">I've run an
                                    hourly report to help figure out the
                                    loads for both the space ("Sum of
                                    all weighted loads except infil and
                                    latent") and zone ("Load Calc'd
                                    SPACE Sensible load at const temp
                                    (Btu/hr)"). These reports all
                                    indicate a positive load (i.e. net
                                    heat gain) from my lights, plug
                                    loads and occupants. However through
                                    this process I'm also questioning
                                    these reports as the lighting,
                                    people and equipment load being
                                    reported don't exactly align with my
                                    modeled schedules for these
                                    loads....but I've put a pin in that.</p>
                                </div>
                                <div>
                                  <p class="MsoNormal"> </p>
                                </div>
                                <div>
                                  <p class="MsoNormal">Regardless, I
                                    have no idea how to figure out what
                                    may be resulting in net heat loss
                                    for this zone. To be thorough, I
                                    checked the elevator lobby on the
                                    ground level and the same thing is
                                    happening. Has anybody seen this
                                    before...any ideas what might be
                                    causing heat loss for a zone with no
                                    ventilation and no walls and no
                                    infiltration? It does seem to be
                                    seasonal (i.e no underheated hours
                                    in the summer) so it has some
                                    connection to weather file but does
                                    not correlate exactly.</p>
                                </div>
                                <div>
                                  <p class="MsoNormal"> </p>
                                </div>
                                <div>
                                  <p class="MsoNormal">If you do take
                                    the time to read this, a big thank
                                    you. If you provide the answer,
                                    you'll for sure be on Santa's "nice"
                                    list.</p>
                                </div>
                                <div>
                                  <p class="MsoNormal"> </p>
                                </div>
                                <div>
                                  <p class="MsoNormal">Chris </p>
                                </div>
                              </div>
                            </div>
                          </div>
                        </blockquote>
                      </div>
                    </div>
                  </div>
                  _______________________________________________<br>
                  Equest-users mailing list<br>
                  <a
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
                    rel="noreferrer" target="_blank"
                    moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                  To unsubscribe from this mailing list send  a blank
                  message to <a
                    href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG"
                    target="_blank" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                </blockquote>
              </div>
              <br>
              <fieldset
                class="gmail-m_-3904346340559647763mimeAttachmentHeader"></fieldset>
              <pre class="gmail-m_-3904346340559647763moz-quote-pre">_______________________________________________
Equest-users mailing list
<a class="gmail-m_-3904346340559647763moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="gmail-m_-3904346340559647763moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
            </blockquote>
          </div>
          _______________________________________________<br>
          Equest-users mailing list<br>
          <a
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
            rel="noreferrer" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>