    <p>This might be true in the real world, but not in eQUEST (nor any
      other simulation program that I know) because it would require CFD
      modeling of the spaces.</p>
    <p>Joe <br>
    </p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 12/20/2018 11:44 AM, Bruce
      Easterbrook via Equest-users wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:bd92194b-1d0e-974f-649d-61a8468e63ac@bellnet.ca">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      Hi Chris,<br>
      I'm thinking it could be due to infiltration.  You have a 22 story
      elevator shaft that probably has a machine room on the roof.  You
      also have stack effect.  Any exterior air from the machine room
      getting in from this drive is going to be cold and move down to
      the bottom of the shaft and pool there.  That would be the
      basement.  It would also affect levels above this explaining your
      load in on the first floor.  It should decline as you get higher
      in the building.<br>
      Bruce Easterbrook P.Eng.<br>
      Abode Engineering<br>
      <br>
      <div class="moz-cite-prefix">On 12/20/2018 2:05 PM, Chris Hadlock
        via Equest-users wrote:<br>
      </div>
      <blockquote type="cite"
cite="mid:20181220190537.KSWF29026.toroondcmxzimta01-srv.bellnexxia.net@tordcvbicmrk03">
        <meta http-equiv="content-type" content="text/html;
          charset=UTF-8">
        <div dir="ltr">
          <div>I've had a few responses requesting the modeling files so
            I've attached the INP and PD2 file (weather file is
            CWEC\Toronto.bin). The zone in question is "L0 Elev Lobby S"
            and I've already removed all exterior surfaces from this
            space (i.e. there are no Child Components). I've assigned
            this zone to it's own system (it's the last system on the
            air-side tab) called "Test System". I've already created the
            hourly reports where you'll see all of the underheated hours
            (which only occur in the winter). The LS-B report shows no
            (zero) htg load. I realize the system is not really
            providing any heating to this zone the way it's setup.</div>
          <div><br>
          </div>
          <div>Thanks,</div>
          <div>Chris</div>
        </div>
        <br>
        <div class="gmail_quote">
          <div dir="ltr">On Thu, Dec 20, 2018 at 1:26 PM Chris Hadlock
            <<a href="mailto:cjhadlock@gmail.com"
              moz-do-not-send="true">cjhadlock@gmail.com</a>> wrote:<br>
          </div>
          <blockquote class="gmail_quote" style="margin:0px 0px 0px
            0.8ex;border-left:1px solid
            rgb(204,204,204);padding-left:1ex">
            <div dir="ltr">
              <div dir="ltr">
                <div dir="ltr">Hello,
                  <div><br>
                  </div>
                  <div>I've created a model using eQuest 3.65 (DOE 2.2)
                    build 7173 that is of a 20 storey multi-residential
                    building located in Toronto, Ontario (Canada). There
                    is a basement with a elevator lobby that is an
                    interior space (no exterior walls). </div>
                  <div><br>
                  </div>
                  <div>My model keeps telling me I have underheated
                    hours for this lobby. I'm trying to figure out why
                    there is a heating load and I'm stumped. I have
                    removed what I believe to be all potential sources
                    of heat loss. I've deleted the underground floor
                    (which was R-100 anyway), I've deleted the interior
                    walls (just to be thorough), there is no
                    infiltration, and I've set the ventilation to zero.
                    In my mind, there is no source of heat loss. I've
                    even added a significant (10 W/ft2) equipment load
                    and yet there are still underheated hours (I've even
                    reduced my Tstat setpoint to 60F). </div>
                  <div><br>
                  </div>
                  <div>I've run an hourly report to help figure out the
                    loads for both the space ("Sum of all weighted loads
                    except infil and latent") and zone ("Load Calc'd
                    SPACE Sensible load at const temp (Btu/hr)"). These
                    reports all indicate a positive load (i.e. net heat
                    gain) from my lights, plug loads and occupants.
                    However through this process I'm also questioning
                    these reports as the lighting, people and equipment
                    load being reported don't exactly align with my
                    modeled schedules for these loads....but I've put a
                    pin in that.</div>
                  <div><br>
                  </div>
                  <div>Regardless, I have no idea how to figure out what
                    may be resulting in net heat loss for this zone. To
                    be thorough, I checked the elevator lobby on the
                    ground level and the same thing is happening. Has
                    anybody seen this before...any ideas what might be
                    causing heat loss for a zone with no ventilation and
                    no walls and no infiltration? It does seem to be
                    seasonal (i.e no underheated hours in the summer) so
                    it has some connection to weather file but does not
                    correlate exactly.</div>
                  <div><br>
                  </div>
                  <div>If you do take the time to read this, a big thank
                    you. If you provide the answer, you'll for sure be
                    on Santa's "nice" list.</div>
                  <div><br>
                  </div>
                  <div>Chris </div>
                </div>
              </div>
            </div>
          </blockquote>
        </div>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <pre class="moz-quote-pre" wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
      </blockquote>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>