<div dir="ltr">Hi Paul,<div><br></div><div>Thanks for your reply. It is very helpful. Yes, we have an exhaust fan in the kitchen, I wonder if there is an equation to estimate the cooling load for a kitchen like this. </div><div><br></div><div>Jing</div></div><br><div class="gmail_quote"><div dir="ltr">On Tue, Dec 18, 2018 at 6:38 AM Paul Diglio <<a href="mailto:paul.diglio@sbcglobal.net">paul.diglio@sbcglobal.net</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">Jing:<br>
<br>
Usually there is an exhaust hood with makeup air in the kitchen.  If this is true, then you need to estimate how much heat is actually transmitted to the space compared to how much heat is expelled through the hood.  This should lower your cooling load.<br>
<br>
Paul Diglio<br>
87 Fairmont Avenue <br>
New Haven, CT  06513 <br>
<br>
<br>
--------------------------------------------<br>
On Mon, 12/17/18, Jing Hong via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>> wrote:<br>
<br>
 Subject: [Equest-users] Equipment Load<br>
 To: <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>, <a href="mailto:equest-users@onebuilding.org" target="_blank">equest-users@onebuilding.org</a>, <a href="mailto:equestuser00@gmail.com" target="_blank">equestuser00@gmail.com</a><br>
 Date: Monday, December 17, 2018, 7:37 PM<br>
<br>
 Dear<br>
 All,<br>
 I have a question regarding<br>
 the internal load.<br>
 Under the Equipment tab of<br>
 the internal load, there are two tables. One is Equipment<br>
 and another is Internal Energy Sources. For my project with<br>
 a kitchen serving 5 hours daily, how to input the power?<br>
 For example, based on the specification sheets, we have<br>
 26.5 W/sqft input power density for electricity, and<br>
 474,000 Btu/hr for gas equipment. However, it will make the<br>
 cooling load so huge for cooling<br>
 systems. Does anyone know<br>
 how eQuest convert energy input to cooling load? Did I fill<br>
 the tables right?<br>
<br>
<br>
<br>
 Thank you!Jing_______________________________________________<br>
 Equest-users mailing list<br>
 <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
 To unsubscribe from this mailing list send  a blank<br>
 message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>
 -----Inline Attachment Follows-----<br>
<br>
<br>
</blockquote></div>