<div dir="ltr"><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px">Hi All,</div><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px"><br></div><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px">I'm using eQuest version 3.65 and am having trouble with sequencing my chillers - I've combed through the archives but haven't found anything that has helped.</div><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px"><br></div><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px">I have 3 chillers in my model, a water-side economizing chiller and two air-cooled scroll chillers. I would like to control them such that my WS economizing chiller runs up to a certain capacity only (175 Tons = 2.1 MBtu/h). Without any controls, eQuest is ignoring the capacity I have entered, and is meeting my building's entire cooling load. Beyond the 2.1 MBtu/h, I would like my 2 other chillers to run to meet the remaining load. </div><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px"><br></div><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px">I've created an Equipment Control (and selected it on my CHW loop) that has my WS Econo Chiller as sequence no. 1 with a max load of 2.1 (I believe units of MBtu/h). Then I have my other chillers as sequence 2/3 and left max loads as "999". I've played around with the "Max Load" values and also the "Loads Through" value and nothing I do changes the outcome. Is anyone able to help me figure out why eQuest is not capping my WS Econo Chiller at the 2.1 MBtu/h and why it continues to meet the entire cooling load (with a peak approaching 4 MBtu/h)?</div><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px"><br></div><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px">Thank you in advance. </div><div style="color:rgb(0,0,0);font-family:Tahoma;font-size:13.3333px"><br></div><div style="color:rgb(0,0,0);font-size:13.3333px;font-family:tahoma,arial,helvetica,sans-serif">---<br>Chris Hadlock, <span style="font-size:8pt"><a target="_blank" href="http://m.a.sc/" style="color:rgb(0,0,255)">M.A.Sc</a>., P.Eng, LEED AP BD+C</span><br>Founder & Senior Energy Consultant<br><br><span style="color:rgb(136,136,136)">HADLOCK</span> CONSULTING<br>201 Candlewood Cr<br>Waterloo, ON N2L5T3<br>tel: (519) 804-1223</div><div style="color:rgb(0,0,0);font-size:13.3333px;font-family:tahoma,arial,helvetica,sans-serif">cel: (226) 343-5599<br><a target="_blank" href="http://www.hadlockconsulting.ca/" style="color:rgb(0,0,255)">www.hadlockconsulting.ca</a></div></div>