<p dir="ltr">Hi Tejas,</p>
<p dir="ltr">As per me the space cooling goes to a higher value as VAV is meeting the set-point control of each and every zone.</p>
<p dir="ltr">Whereas the Single Zone Reheat meets the cooling requirement of the control zone. It does not meet the demand of slave zones. As per an exercise done by me I was able to find that the slave zones in the summary report in the Air-side tab are showing unmet load hours which is not in the case of VAV.</p>
<p dir="ltr">The heating requirement, the VAV can meet the zones requirement during winter season. We can also say that the VAV is also meeting the heating set-point requirement during winter and showing Heating consumption.</p>
<p dir="ltr">Thanks,<br>
Sharad. Kumar<br>
+91-9102906597<br>
Freelancer (Energy Simulation )<br>
India.</p>