<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns="http://www.w3.org/TR/REC-html40">
<head>
<meta http-equiv="Content-Type" content="text/html; charset=iso-8859-1">
<meta name="Generator" content="Microsoft Word 15 (filtered medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]--><style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
p.msonormal0, li.msonormal0, div.msonormal0
        {mso-style-name:msonormal;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
span.EmailStyle18
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle20
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
</head>
<body lang="EN-US" link="#0563C1" vlink="#954F72">
<div class="WordSection1">
<p class="MsoNormal">Dana,<o:p></o:p></p>
<p class="MsoNormal">The heating setpoint is 70° F. 90.1 says to size the system based on a 20° F delta T between space temperature setpoint and supply air temperature. Base on that, I revised the A1Sys Heating tab:<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><img width="699" height="442" style="width:7.2812in;height:4.6041in" id="Picture_x0020_1" src="cid:image001.jpg@01D42989.4E13B600"><o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">This reduces the total unmet heating hours for that system from 40348 to 3148.
<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I would then increase the minimum flow percentage and reheat delta T in the remaining problem zones. Q = 1.08 * (cfm * delta T). To meet the heating loads either the supply flow or delta T have to be increased.
<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial",sans-serif">Christopher R Jones, P.Eng.<o:p></o:p></span></b></p>
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial",sans-serif">T+ 1 416-644-0252<o:p></o:p></span></p>
<p class="MsoNormal"><span style="font-size:8.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><img width="60" height="29" style="width:.625in;height:.302in" id="_x0031_cc2331b-d8c3-424e-81de-2b17716d444e.png_x003f_ver_x003d_1495657656000" src="cid:image005.png@01D42989.4E13B600"><o:p></o:p></p>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<div style="border:none;border-top:solid #E1E1E1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [mailto:equest-users-bounces@lists.onebuilding.org]
<b>On Behalf Of </b>Dana M. Savage via Equest-users<br>
<b>Sent:</b> Monday, July 30, 2018 3:09 PM<br>
<b>To:</b> equest-users@lists.onebuilding.org<br>
<b>Subject:</b> [Equest-users] Crazy High Unmet Heating Hours on ASHRAE 90.1 Baseline Model<o:p></o:p></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Good afternoon everyone!<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I am working through the process of creating an ASHRAE 90.1-Appendix G baseline model and cannot understand where I’ve gone wrong in the design.  I have done a number of energy audits using eQuest but have never been through the LEED process
 and thus this is my first attempt at dealing with 90.1 directly.  Any help you may offer would be much appreciated and I am more than happy to compensate any time spent.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">The building is a System Type 7 – VAV with Reheat – and my cooling hours are 0.  However, I can’t seem to get my VAV terminal units to provide enough heat at any time during the year.  When I allow eQUEST to size the capacities on their
 own, not enough heat is added and temperatures throughout the winter and in all zones remain below 60F.  But when I specify a Maximum Heating Rate at the Zone Terminal the addition rate doesn’t change!  I’ve tired increasing the throttling range, which had
 some effect.  The only thing that had a significant effect on the unmet heating hours was increasing the Heating Design Temperature for each Zone.  But this also had the effect of dramatically increasing the cooling unmet hours!  Finally, and most confoundingly,
 my heating energy consumption in the winter is significant!  Where is it all going?? I am at a total loss.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I hope I was clear in articulating my issue and again appreciate your assistance.<o:p></o:p></p>
<p class="MsoNormal" style="line-height:110%"><b><span style="color:#323E4F"><o:p> </o:p></span></b></p>
<p class="MsoNormal" style="line-height:110%"><b><span style="color:#323E4F"><o:p> </o:p></span></b></p>
<p class="MsoNormal" style="line-height:110%"><b><span style="color:#323E4F">Dana M. Savage
</span><span style="color:#B6AF20">::</span></b> <span style="color:gray">Mechanical Engineer</span><span style="color:#A6A6A6"><o:p></o:p></span></p>
<p class="MsoNormal" style="line-height:120%"><span style="color:gray">CONTACT</span><b><span style="color:#BF8F00">
</span><span style="color:#B6AF20">::</span><span style="color:#BF8F00"> </span></b><span style="color:#323E4F"><a href="mailto:DSavage@cfrengineering.com">DSavage@cfrengineering.com</a><b><i>
</i></b></span><b><span style="color:#B6AF20">::</span><span style="color:#BF8F00">
</span></b><span style="color:#323E4F">C: 301.717.0003<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:gray">ADDRESS </span><b><span style="color:#D3B32B">::</span><span style="color:#BF8F00">
</span></b><span style="color:#323E4F">20251 Century Blvd. Suite 120 :: Germantown, MD 20874</span><span style="color:#1F497D"><o:p></o:p></span></p>
<p class="MsoNormal" style="margin-top:3.0pt;line-height:120%"><i><span style="color:#B6AF20"><a href="www.cfrengineering.com"><span style="color:#B6AF20">www.cfrengineering.com</span></a><o:p></o:p></span></i></p>
<p class="MsoNormal"><img border="0" width="159" height="79" style="width:1.6562in;height:.8229in" id="Picture_x0020_3" src="cid:image004.jpg@01D42989.4E0CFF40" alt="cfr"><span style="color:#44546A"><o:p></o:p></span></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<br>
<hr>
<font face="Arial" color="Gray" size="1"><br>
<br>
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s).
 Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify
 the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions
 regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at
<a href="http://www.wsp.com/casl">www.wsp.com/casl</a>. For any concern or if you believe you should not be receiving this message, please forward this message to
<a href="mailto:caslcompliance@wsp.com">caslcompliance@wsp.com</a> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
<br>
<br>
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif
 du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez
 en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques
 de WSP, veuillez consulter notre Engagement anti-pourriel au <a href="http://www.wsp.com/lcap">
www.wsp.com/lcap</a>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au
<a href="mailto:conformitelcap@wsp.com">conformitelcap@wsp.com</a> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
<br>
</font><br>
<font face="Arial" color="WhiteSmoke" size="0.10"><br>
<br>
-LAEmHhHzdJzBlTWfa4Hgs7pbKl </font>
</body>
</html>