    <p>Christopher,</p>
    <p>I think you are looking for<br>
    </p>
    <p>#SV(#L("TYPE"))==XX,</p>
    <p>Where XX corresponds to the integer symbol value assigned in
      BDL.  BDLKEY.OUT is where you can find what the symbol values are
      for a given keyword.</p>
    <p>Here is the section for the SYSTEM:TYPE command/keyword:</p>
    <p><tt>  1> TYPE                                Symbolic
        Defined    1  100 (CODE-WORD       )  TABLE =0    1         -9
        (* Required *    )</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        PSZ                              TYPE =  100 DEF/REF  -1/
        -1      VALUE =   19</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        PMZS                             TYPE =  100 DEF/REF  -1/
        -1      VALUE =   20</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        PVAVS                            TYPE =  100 DEF/REF  -1/
        -1      VALUE =   21</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        PVVT                             TYPE =  100 DEF/REF  -1/
        -1      VALUE =   28</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        PTAC                             TYPE =  100 DEF/REF  -1/
        -1      VALUE =   22</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        HP                               TYPE =  100 DEF/REF  -1/
        -1      VALUE =   15</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        SZRH                             TYPE =  100 DEF/REF  -1/
        -1      VALUE =    2</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        VAVS                             TYPE =  100 DEF/REF  -1/
        -1      VALUE =   13</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        RHFS                             TYPE =  100 DEF/REF  -1/
        -1      VALUE =   14</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        DDS                              TYPE =  100 DEF/REF  -1/
        -1      VALUE =    4</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        MZS                              TYPE =  100 DEF/REF  -1/
        -1      VALUE =    3</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        PIU                              TYPE =  100 DEF/REF  -1/
        -1      VALUE =   23</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        FC                               TYPE =  100 DEF/REF  -1/
        -1      VALUE =    9</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        IU                               TYPE =  100 DEF/REF  -1/
        -1      VALUE =   11</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        UVT                              TYPE =  100 DEF/REF  -1/
        -1      VALUE =    6</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        UHT                              TYPE =  100 DEF/REF  -1/
        -1      VALUE =    7</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        HVSYS                            TYPE =  100 DEF/REF  -1/
        -1      VALUE =   16</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        EVAP-COOL                        TYPE =  100 DEF/REF  -1/
        -1      VALUE =   26</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        RESYS2                           TYPE =  100 DEF/REF  -1/
        -1      VALUE =   29</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        RESVVT                           TYPE =  100 DEF/REF  -1/
        -1      VALUE =   27</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        RESYS                            TYPE =  100 DEF/REF  -1/
        -1      VALUE =   17</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        SZCI                             TYPE =  100 DEF/REF  -1/
        -1      VALUE =    5</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        CBVAV                            TYPE =  100 DEF/REF  -1/
        -1      VALUE =   18</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        FPH                              TYPE =  100 DEF/REF  -1/
        -1      VALUE =    8</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        PTGSD                            TYPE =  100 DEF/REF  -1/
        -1      VALUE =   25</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        SUM                              TYPE =  100 DEF/REF  -1/
        -1      VALUE =    1</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        FNSYS1                           TYPE =  100 DEF/REF  -1/
        -1      VALUE =   24</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        *UNUSED-TYPE1                    TYPE =  100 DEF/REF  -1/
        -1      VALUE =   10</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        *UNUSED-TYPE2                    TYPE =  100 DEF/REF  -1/
        -1      VALUE =   12</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        *SYS-30                          TYPE =  100 DEF/REF  -1/
        -1      VALUE =   30</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        *SYS-31                          TYPE =  100 DEF/REF  -1/
        -1      VALUE =   31</tt><tt><br>
      </tt><tt>                              SYMBOL TABLE ENTRY  
        *SYS-32                          TYPE =  100 DEF/REF  -1/
        -1      VALUE =   32</tt><br>
    </p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 3/16/2018 1:46 PM, Jones,
      Christopher via Equest-users wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:b1639732b9a445bb828546f7a494b84f@wsp.com">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Helvetica;
        panose-1:2 11 6 4 2 2 2 2 2 4;}
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Verdana;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
        {mso-style-priority:34;
        margin-top:0in;
        margin-right:0in;
        margin-bottom:0in;
        margin-left:.5in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
p.msonormal0, li.msonormal0, div.msonormal0
        {mso-style-name:msonormal;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
p.yiv1848449785msonormal, li.yiv1848449785msonormal, div.yiv1848449785msonormal
        {mso-style-name:yiv1848449785msonormal;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
p.yiv1848449785msochpdefault, li.yiv1848449785msochpdefault, div.yiv1848449785msochpdefault
        {mso-style-name:yiv1848449785msochpdefault;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
p.yiv1848449785msonormal1, li.yiv1848449785msonormal1, div.yiv1848449785msonormal1
        {mso-style-name:yiv1848449785msonormal1;
        margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
p.yiv1848449785msochpdefault1, li.yiv1848449785msochpdefault1, div.yiv1848449785msochpdefault1
        {mso-style-name:yiv1848449785msochpdefault1;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Calibri",sans-serif;}
span.yiv1848449785msohyperlink
        {mso-style-name:yiv1848449785msohyperlink;}
span.yiv1848449785msohyperlinkfollowed
        {mso-style-name:yiv1848449785msohyperlinkfollowed;}
span.yiv1848449785emailstyle17
        {mso-style-name:yiv1848449785emailstyle17;}
span.yiv1848449785msohyperlink1
        {mso-style-name:yiv1848449785msohyperlink1;
        color:#0563C1;
        text-decoration:underline;}
span.yiv1848449785msohyperlinkfollowed1
        {mso-style-name:yiv1848449785msohyperlinkfollowed1;
        color:#954F72;
        text-decoration:underline;}
span.yiv1848449785emailstyle171
        {mso-style-name:yiv1848449785emailstyle171;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle29
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle30
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle31
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle32
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle33
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle35
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
/* List Definitions */
@list l0
        {mso-list-id:257371401;
        mso-list-template-ids:-470127102;}
@list l0:level1
        {mso-level-start-at:2;
        mso-level-tab-stop:.5in;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1
        {mso-list-id:409161387;
        mso-list-type:hybrid;
        mso-list-template-ids:141954124 67698703 67698713 67698715 67698703 67698713 67698715 67698703 67698713 67698715;}
@list l1:level1
        {mso-level-start-at:0;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level2
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level3
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l1:level4
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level5
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level6
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l1:level7
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level8
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level9
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l2
        {mso-list-id:662273530;
        mso-list-template-ids:1491374902;}
@list l3
        {mso-list-id:1353457684;
        mso-list-template-ids:-1685570282;}
@list l3:level1
        {mso-level-start-at:3;
        mso-level-tab-stop:.5in;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l4
        {mso-list-id:1875728743;
        mso-list-template-ids:722252324;}
@list l4:level1
        {mso-level-start-at:4;
        mso-level-tab-stop:.5in;
        mso-level-number-position:left;
        text-indent:-.25in;}
ol
        {margin-bottom:0in;}
ul
        {margin-bottom:0in;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Hello
            Expressionistas,<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Is
            there a simpler way to achieve
            #L("TYPE")==#SI("PSZ","SYSTEM","TYPE")<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">I
            was thinking there would be a way to return the TYPE number,
            ie. PSZ = 19, PVAVS = 21, etc.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><b><span
style="font-size:6.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:FR"><o:p> </o:p></span></b></p>
          <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"
                lang="EN-GB">Christopher R. Jones</span></b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"
              lang="EN-GB">, P.Eng.<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"
              lang="EN-GB">Technical Specialist<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"
              lang="EN-GB">Sustainability & Energy<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif"><img
                style="width:.8125in;height:.3854in" id="_x0000_i1038"
                src="cid:part1.113F1EBD.1DBA5FF6@360-Analytics.com"
                class="" height="37" width="78"></span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR">T
              +1 416-644-0252<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR">2300
              Yonge Street, Suite 2300<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR">Toronto,
              ON M4P 1E4 Canada</span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"
              lang="EN-GB"><br>
              <br>
            </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:EN-CA"><a
                href="wsp.com" moz-do-not-send="true"><span
                  style="color:#0563C1">wsp.com</span></a><o:p></o:p></span></p>
          <p class="MsoNormal"><u><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:blue;mso-fareast-language:EN-CA"
                lang="EN-CA"><o:p><span style="text-decoration:none"> </span></o:p></span></u></p>
          <p class="MsoNormal" style="text-autospace:none"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#7F7F7F;mso-fareast-language:FR"><o:p> </o:p></span></b></p>
          <p class="MsoNormal" style="text-autospace:none"><i><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#6EA900;mso-fareast-language:FR">Please
                consider the environment before printing...<o:p></o:p></span></i></p>
          <p class="MsoNormal"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif"
              lang="EN-CA"><o:p> </o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Nicholas Caton
                [<a class="moz-txt-link-freetext" href="mailto:Nicholas.Caton@schneider-electric.com">mailto:Nicholas.Caton@schneider-electric.com</a>]
                <br>
                <b>Sent:</b> Thursday, March 15, 2018 3:13 PM<br>
                <b>To:</b> Nicholas Caton
                <a class="moz-txt-link-rfc2396E" href="mailto:Nicholas.Caton@schneider-electric.com"><Nicholas.Caton@schneider-electric.com></a>; Daric
                Adair <a class="moz-txt-link-rfc2396E" href="mailto:Daric.Adair@hendersonengineers.com"><Daric.Adair@hendersonengineers.com></a>; Jones,
                Christopher <a class="moz-txt-link-rfc2396E" href="mailto:Christopher.r.Jones@wsp.com"><Christopher.r.Jones@wsp.com></a>; John
                Aulbach <a class="moz-txt-link-rfc2396E" href="mailto:jra_sac@yahoo.com"><jra_sac@yahoo.com></a><br>
                <b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@onebuilding.org">equest-users@onebuilding.org</a><br>
                <b>Subject:</b> RE: [Equest-users] eQuest Generated EFLH<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Oh
            and hey, you can simplify the process I outlined by striking
            out Step #2 entirely… Custom reporting on the submeter isn’t
            necessary to generate the submeter PS-F report, but again
            may be necessary to cover FLEH for schedules and processes
            that aren’t related by a MULTIPLIER or FRACTION type
            schedule.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46"><img
                style="width:7.5625in;height:.0937in" id="_x0000_i1025"
                src="cid:part3.A085F25D.31608E58@360-Analytics.com"
                class="" height="9" width="726" border="0"><o:p></o:p></span></p>
          <p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46">Nick
                Caton, P.E., BEMP</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46"><o:p></o:p></span></p>
          <table class="MsoNormalTable"
            style="width:543.0pt;border-collapse:collapse"
            cellspacing="0" cellpadding="0" width="724" border="0">
            <tbody>
              <tr>
                <td style="width:172.3pt;padding:0in 0in 0in 0in"
                  valign="top" width="230">
                  <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Senior Energy Engineer</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Regional Energy Engineering Manager<o:p></o:p></span></p>
                  <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Energy and Sustainability Services</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Schneider Electric</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
                </td>
                <td style="width:218.3pt;padding:0in 0in 0in 0in"
                  valign="top" width="291">
                  <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">D  </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">913.564.6361
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">M  </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">785.410.3317
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">F  </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">913.564.6380</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">E  </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><a
href="mailto:nicholas.caton@schneider-electric.com"
                        moz-do-not-send="true"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">nicholas.caton@schneider-electric.com</span></a><o:p></o:p></span></p>
                </td>
                <td style="width:152.4pt;padding:0in 0in 0in 0in"
                  valign="top" width="203">
                  <p class="MsoNormal" style="text-align:right"
                    align="right"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">15200
                      Santa Fe Trail Drive<br>
                      Suite 204<br>
                      Lenexa, KS 66219<br>
                      United States</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:4.0pt">
                <td colspan="3" style="width:543.0pt;padding:0in 0in 0in
                  0in;height:4.0pt" valign="top" width="724">
                  <p class="MsoNormal" style="mso-line-height-alt:4.0pt"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46"><img
                        style="width:7.5208in;height:.5104in"
                        id="_x0000_i1026"
                        src="cid:part5.F2BBACB9.889C6C91@360-Analytics.com"
                        class="" height="49" width="722" border="0"><o:p></o:p></span></p>
                </td>
              </tr>
            </tbody>
          </table>
          <p class="MsoNormal"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Equest-users [<a
                  href="mailto:equest-users-bounces@lists.onebuilding.org"
                  moz-do-not-send="true">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Nicholas Caton via Equest-users<br>
                <b>Sent:</b> Thursday, March 15, 2018 2:01 PM<br>
                <b>To:</b> Daric Adair <<a
                  href="mailto:Daric.Adair@hendersonengineers.com"
                  moz-do-not-send="true">Daric.Adair@hendersonengineers.com</a>>;
                Jones, Christopher <<a
                  href="mailto:Christopher.r.Jones@wsp.com"
                  moz-do-not-send="true">Christopher.r.Jones@wsp.com</a>>;
                John Aulbach <<a href="mailto:jra_sac@yahoo.com"
                  moz-do-not-send="true">jra_sac@yahoo.com</a>><br>
                <b>Cc:</b> <a
                  href="mailto:equest-users@onebuilding.org"
                  moz-do-not-send="true">equest-users@onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] eQuest Generated EFLH<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Inserting
            a general caution on leveraging peaks with the suggested
            consumption/peak PS-F approach…<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">You
            would need at least one hour in every fractional schedule at
            1.0 to fully trust using the peak to derive FLEH from a
            meter report.  That has been the root source of many LEED
            comments making incorrect conclusions based on FLEH “margin
            math.”   You will also need to be mindful that each
            sub-meter is only covering the effects of a single schedule
            to ensure “coincident peaks” aren’t being conflated with
            actual peaks under a given end-use (like where you have 4
            lighting schedules), similarly messing with your math later.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">My
            concern with “tons of meters” vs. “tons of hourly reports”
            is that you’re kinda robbing Peter to pay Paul.  It’s a lot
            of extra reporting and time spent parsing the outputs either
            way.  My gut likes the *<b>idea</b>* of a custom hourly
            report approach more, as if you could construct a series of
            report blocks to replicate every schedule of interest, then
            you could do all the math in one output file, minimizing
            hours required for documentation and number-crunching.  My
            concern however is I don’t think there’s a report block
            option that lets you simply select the hourly schedule value
            for just any schedule…  You’ll need to do it indirectly…<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><br>
            So… here’s an idea that might combine the best potential of
            both approaches while minimizing error potential:<o:p></o:p></span></p>
        <ol style="margin-top:0in" start="0" type="1">
          <li class="MsoNormal" style="mso-list:l1 level1 lfo3"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif">Save
              a separate copy/fork of your model – you’ll want to retain
              this work for later but you won’t want it in your final
              model… unless you do some extra legwork to “toggle/flag”
              these dummy loads into activity.<o:p></o:p></span></li>
          <li class="MsoNormal" style="mso-list:l1 level1 lfo3"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif">Set
              up a dummy elec meter under EM1 with up to 12 schedules
              for which you need to document FLEH.  Give each schedule a
              1kW Load, and a unique enduse.<o:p></o:p></span></li>
        </ol>
        <p class="MsoListParagraph"><img
            style="width:6.1666in;height:4.5729in" id="Picture_x0020_3"
            src="cid:part11.B6875445.98D2169B@360-Analytics.com"
            class="" height="439" width="592" border="0"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p></o:p></span></p>
        <ol style="margin-top:0in" start="2" type="1">
          <li class="MsoNormal" style="mso-list:l1 level1 lfo3"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif">Copy
              the EM1 report block, and reassign it to your dummy
              meter.  You might actually untick “total end-use energy”
              as the 13<sup>th</sup> entry as that’ll be meaningless
              later.<o:p></o:p></span></li>
        </ol>
        <p class="MsoListParagraph"><img
            style="width:8.375in;height:4.5in" id="Picture_x0020_5"
            src="cid:part12.8955B6DC.CB3A8618@360-Analytics.com"
            class="" height="432" width="804" border="0"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p></o:p></span></p>
        <ol style="margin-top:0in" start="3" type="1">
          <li class="MsoNormal" style="mso-list:l1 level1 lfo3"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif">Now,
              if you sum annual kWh for each end-use of the meter
              (handily done for you within the SIM PS-F reports), it’s
              equivalently the FLEH (if rounded to the nearest integer):<o:p></o:p></span></li>
        </ol>
        <p class="MsoListParagraph"><img
            style="width:6.8854in;height:1.0416in" id="Picture_x0020_7"
            src="cid:part13.B55B6548.E35FCF7E@360-Analytics.com"
            class="" height="100" width="661" border="0"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p></o:p></span></p>
        <p class="MsoListParagraph"><img
            style="width:6.8333in;height:.75in" id="Picture_x0020_6"
            src="cid:part14.F1E1D4F8.F948E9A6@360-Analytics.com"
            class="" height="72" width="656" border="0"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p></o:p></span></p>
        <ol style="margin-top:0in" start="4" type="1">
          <li class="MsoNormal" style="mso-list:l1 level1 lfo3"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif">Set
              up additional sub-meters to cover schedules in multiples
              of 12 until you’ve covered every schedule for which you
              need to document FLEH.
              <o:p></o:p></span></li>
        </ol>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">This
            would only work for annual schedules of type FRACTION and
            MULTIPLIER.  If they’re asking for something like system
            runtime hours or snap temp loop operations you’ll need to be
            running custom hourlies, but those could be set up alongside
            this custom reporting structure as needed.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">For
            what it’s worth, I haven’t submitted a project for LEED v4
            review yet, and neither have I seen or reviewed the context
            under which they are asking for FLEH documentation, but I’d
            be inclined with my first project to instead take a minimal
            documentation0 approach on this front and have the reviewer
            ask in commentary specifically for what they really need. 
            Requiring FLEH for *everything* crosses the line of silly
            from a (this) reviewers’ perspective.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">~Nick<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46"><img
                style="width:7.5625in;height:.0937in"
                id="Picture_x0020_1"
                src="cid:part3.A085F25D.31608E58@360-Analytics.com"
                class="" height="9" width="726" border="0"><o:p></o:p></span></p>
          <p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46">Nick
                Caton, P.E., BEMP</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46"><o:p></o:p></span></p>
          <table class="MsoNormalTable"
            style="width:543.0pt;border-collapse:collapse"
            cellspacing="0" cellpadding="0" width="724" border="0">
            <tbody>
              <tr>
                <td style="width:172.3pt;padding:0in 0in 0in 0in"
                  valign="top" width="230">
                  <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Senior Energy Engineer</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Regional Energy Engineering Manager<o:p></o:p></span></p>
                  <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Energy and Sustainability Services</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Schneider Electric</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
                </td>
                <td style="width:218.3pt;padding:0in 0in 0in 0in"
                  valign="top" width="291">
                  <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">D  </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">913.564.6361
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">M  </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">785.410.3317
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">F  </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">913.564.6380</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">E  </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><a
href="mailto:nicholas.caton@schneider-electric.com"
                        moz-do-not-send="true"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">nicholas.caton@schneider-electric.com</span></a><o:p></o:p></span></p>
                </td>
                <td style="width:152.4pt;padding:0in 0in 0in 0in"
                  valign="top" width="203">
                  <p class="MsoNormal" style="text-align:right"
                    align="right"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">15200
                      Santa Fe Trail Drive<br>
                      Suite 204<br>
                      Lenexa, KS 66219<br>
                      United States</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:4.0pt">
                <td colspan="3" style="width:543.0pt;padding:0in 0in 0in
                  0in;height:4.0pt" valign="top" width="724">
                  <p class="MsoNormal" style="mso-line-height-alt:4.0pt"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46"><img
                        style="width:7.5208in;height:.5104in"
                        id="_x0000_i1032"
                        src="cid:part5.F2BBACB9.889C6C91@360-Analytics.com"
                        class="" height="49" width="722" border="0"><o:p></o:p></span></p>
                </td>
              </tr>
            </tbody>
          </table>
          <p class="MsoNormal"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Equest-users [<a
                  href="mailto:equest-users-bounces@lists.onebuilding.org"
                  moz-do-not-send="true">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Daric Adair via Equest-users<br>
                <b>Sent:</b> Thursday, March 15, 2018 9:27 AM<br>
                <b>To:</b> Jones, Christopher <<a
                  href="mailto:Christopher.r.Jones@wsp.com"
                  moz-do-not-send="true">Christopher.r.Jones@wsp.com</a>>;
                John Aulbach <<a href="mailto:jra_sac@yahoo.com"
                  moz-do-not-send="true">jra_sac@yahoo.com</a>><br>
                <b>Cc:</b> <a
                  href="mailto:equest-users@lists.onebuilding.org"
                  moz-do-not-send="true">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] eQuest Generated EFLH<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Oh,
            I agree, it’s screwy reporting requirements.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">The
            hard thing is its by annual schedule. Not necessarily by fan
            system or all lighting.
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">I
            means around thing might – might be to set the meters based
            on annual schedule. Then use the PS-F reports to take the
            consumption/peak to get the EFLH. That avoids a tons of
            hourly reports but uses potentially a lot of meters. Though,
            was hoping to avoid this.<o:p></o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A;text-transform:uppercase"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Thanks,<o:p></o:p></span></p>
          <p class="MsoNormal" style="background:white"><b><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">DARIC
                R ADAIR</span></b><span
style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">
              PE, CEM, BEMP </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383A35"><br>
              Mechanical Engineer, Energy Analyst <br>
              <br>
            </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#008C15;text-transform:uppercase">Henderson
                Engineers</span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383A35"><br>
              <b><span style="text-transform:uppercase">Tel</span></b>
              (913) 742-5530  <br>
              <a href="mailto:daric.adair@hendersonengineers.com"
                moz-do-not-send="true"><span style="color:#383A35">daric.adair@hendersonengineers.com</span></a><br>
              <br>
            </span><b><span
style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">Licensed
                in</span></b><span
style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">
              KS</span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383A35"><o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Jones, Christopher [<a
                  href="mailto:Christopher.r.Jones@wsp.com"
                  moz-do-not-send="true">mailto:Christopher.r.Jones@wsp.com</a>]
                <br>
                <b>Sent:</b> Thursday, March 15, 2018 9:11 AM<br>
                <b>To:</b> Daric Adair <<a
                  href="mailto:Daric.Adair@hendersonengineers.com"
                  moz-do-not-send="true">Daric.Adair@hendersonengineers.com</a>>;
                John Aulbach <<a href="mailto:jra_sac@yahoo.com"
                  moz-do-not-send="true">jra_sac@yahoo.com</a>><br>
                <b>Cc:</b> <a
                  href="mailto:equest-users@lists.onebuilding.org"
                  moz-do-not-send="true">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> RE: [Equest-users] eQuest Generated EFLH<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">What
            is the EFLH for lighting controlled by photo sensors? Fans
            that have VSDs? Etc.? To get accurate EFLH you would need
            hourly reports.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">LEED
            has some really goofy reporting requirements.
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><b><span
style="font-size:6.0pt;font-family:"Calibri",sans-serif;mso-fareast-language:FR"><o:p> </o:p></span></b></p>
          <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"
                lang="EN-GB">Christopher R. Jones</span></b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"
              lang="EN-GB">, P.Eng.<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"
              lang="EN-GB">Technical Specialist<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"
              lang="EN-GB">Sustainability & Energy<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif"><img
                style="width:.8125in;height:.3854in"
                id="Picture_x0020_15"
                src="cid:part1.113F1EBD.1DBA5FF6@360-Analytics.com"
                class="" height="37" width="78" border="0"></span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR">T
              +1 416-644-0252<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR">2300
              Yonge Street, Suite 2300<o:p></o:p></span></p>
          <p class="MsoNormal" style="margin-bottom:12.0pt"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:FR">Toronto,
              ON M4P 1E4 Canada<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;mso-fareast-language:EN-CA"><a
                href="wsp.com" moz-do-not-send="true"><span
                  style="color:#0563C1">wsp.com</span></a><o:p></o:p></span></p>
          <p class="MsoNormal"><u><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:blue;mso-fareast-language:EN-CA"
                lang="EN-CA"><o:p><span style="text-decoration:none"> </span></o:p></span></u></p>
          <p class="MsoNormal" style="text-autospace:none"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#7F7F7F;mso-fareast-language:FR"><o:p> </o:p></span></b></p>
          <p class="MsoNormal" style="text-autospace:none"><i><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#6EA900;mso-fareast-language:FR">Please
                consider the environment before printing...<o:p></o:p></span></i></p>
          <p class="MsoNormal"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif"
              lang="EN-CA"><o:p> </o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Equest-users [<a
                  href="mailto:equest-users-bounces@lists.onebuilding.org"
                  moz-do-not-send="true">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Daric Adair via Equest-users<br>
                <b>Sent:</b> Thursday, March 15, 2018 9:45 AM<br>
                <b>To:</b> John Aulbach <<a
                  href="mailto:jra_sac@yahoo.com" moz-do-not-send="true">jra_sac@yahoo.com</a>>;
                <a href="mailto:equest-users@lists.onebuilding.org"
                  moz-do-not-send="true">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] eQuest Generated EFLH<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">John
            & all;<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">That
            could work for the plant equipment, but LEEDv4 is requesting
            EFLH for all annual schedules. We have a project that has 4
            different main occupancy times/groups. Which cascades out to
            occupancy, lighting, fans, etc. Many, many schedules.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">I
            received a separate suggestion to check under
            File>Export, but none of the 3 options there had anything
            like the EFLH.<o:p></o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A">LEED
              has a ‘calculator’ in their documentation, but its built
              arround different days/week (which also don’t align in
              this project). Something could be built in excel to handle
              this – but I saw little need to recreate the wheel if
              eQuest/DOE2 does this automatically.<span
                style="text-transform:uppercase"><o:p></o:p></span></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A;text-transform:uppercase"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A;text-transform:uppercase"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Thanks,<o:p></o:p></span></p>
          <p class="MsoNormal" style="background:white"><b><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">DARIC
                R ADAIR</span></b><span
style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">
              PE, CEM, BEMP </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383A35"><br>
              Mechanical Engineer, Energy Analyst <br>
              <br>
            </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#008C15;text-transform:uppercase">Henderson
                Engineers</span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383A35"><br>
              <b><span style="text-transform:uppercase">Tel</span></b>
              (913) 742-5530  <br>
              <a href="mailto:daric.adair@hendersonengineers.com"
                moz-do-not-send="true"><span style="color:#383A35">daric.adair@hendersonengineers.com</span></a><br>
              <br>
            </span><b><span
style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">Licensed
                in</span></b><span
style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">
              KS</span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383A35"><o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                John Aulbach [<a href="mailto:jra_sac@yahoo.com"
                  moz-do-not-send="true">mailto:jra_sac@yahoo.com</a>]
                <br>
                <b>Sent:</b> Wednesday, March 14, 2018 7:52 PM<br>
                <b>To:</b> <a
                  href="mailto:equest-users@lists.onebuilding.org"
                  moz-do-not-send="true">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] eQuest Generated EFLH<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <div>
            <p class="MsoNormal"><span
                style="font-family:"Verdana",sans-serif">My
                best guess (assuming you want cooling for example) is to
                make a single chiller for your building (gotta be PLANT
                equipment). Figure out the peak cooling load from SS-D
                and size the chiller accordingly. Run the building. Look
                in PS-C, with 10% increments of load.<o:p></o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span
                style="font-family:"Verdana",sans-serif"><o:p> </o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span
                style="font-family:"Verdana",sans-serif">Multiply
                each 10% load increment (say chiller is 1000 ton, so 100
                tons for 10%, 200 tons for 20%, etc) by the number of
                hours shown for that increment. Take the total ton-hrs
                and divide by the 1000 ton (for this example).<o:p></o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span
                style="font-family:"Verdana",sans-serif"><o:p> </o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span
                style="font-family:"Verdana",sans-serif">That
                should give you equivalent load hours.<o:p></o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span
                style="font-family:"Verdana",sans-serif"><o:p> </o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span
                style="font-family:"Verdana",sans-serif">John
                Aulbach, PE<o:p></o:p></span></p>
          </div>
          <div>
            <p class="MsoNormal"><span
                style="font-family:"Verdana",sans-serif"><o:p> </o:p></span></p>
          </div>
          <div id="yahoo_quoted_1109733020">
            <div>
              <div>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">On
                    Wednesday, March 14, 2018, 2:27:48 PM PDT, Daric
                    Adair via Equest-users <<a
                      href="mailto:equest-users@lists.onebuilding.org"
                      moz-do-not-send="true">equest-users@lists.onebuilding.org</a>>
                    wrote: <o:p></o:p></span></p>
              </div>
              <div>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
              </div>
              <div>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
              </div>
              <div>
                <div id="yiv1848449785">
                  <div>
                    <div>
                      <p class="yiv1848449785msonormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Does
                          anyone know if there is a report or means from
                          eQuest to generate the EFLH (equivalent full
                          load hours) for each schedule?<o:p></o:p></span></p>
                      <p class="yiv1848449785msonormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Colleague
                          of mine believes VistualDOE was able to
                          complete and hoping there is a comparable
                          tool/report.<o:p></o:p></span></p>
                      <p class="yiv1848449785msonormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
                      <p class="yiv1848449785msonormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Thanks
                          in advance.<o:p></o:p></span></p>
                      <p class="yiv1848449785msonormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
                      <p class="yiv1848449785msonormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
                      <p class="yiv1848449785msonormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
                      <p class="yiv1848449785msonormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">Thanks,<o:p></o:p></span></p>
                      <p class="yiv1848449785msonormal"
                        style="background:white"><b><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#383A35;text-transform:uppercase">DARIC
                            R ADAIR</span></b><span
style="font-size:7.0pt;font-family:"Helvetica",sans-serif;color:#383A35;text-transform:uppercase"> PE,
                          CEM, BEMP </span><span
style="font-size:9.0pt;font-family:"Helvetica",sans-serif;color:#383A35"><br>
                          Mechanical Engineer, Energy Analyst <br>
                          <br>
                        </span><b><span
style="font-size:9.0pt;font-family:"Helvetica",sans-serif;color:#008C15;text-transform:uppercase">Henderson
                            Engineers</span></b><span
style="font-size:9.0pt;font-family:"Helvetica",sans-serif;color:#383A35"><br>
                          8345 Lenexa Drive, Suite 300  |  Lenexa, KS
                          66214<br>
                          <b><span style="text-transform:uppercase">Tel</span></b>
                          (913) 742-5530  <br>
                          <a
                            href="mailto:daric.adair@hendersonengineers.com"
                            target="_blank" moz-do-not-send="true"><span
                              style="color:#383A35">daric.adair@hendersonengineers.com</span></a><br>
                          <br>
                          <a href="http://www.hendersonengineers.com/"
                            target="_blank" moz-do-not-send="true"><span
style="font-size:8.0pt;color:#008C15;text-transform:uppercase">hendersonengineers.com</span></a><br>
                          <br>
                        </span><b><span
style="font-size:7.0pt;font-family:"Helvetica",sans-serif;color:#383A35;text-transform:uppercase">Licensed
                            in</span></b><span
style="font-size:7.0pt;font-family:"Helvetica",sans-serif;color:#383A35;text-transform:uppercase">
                          KS</span><span
style="font-size:9.0pt;font-family:"Helvetica",sans-serif;color:#383A35"><br>
                          <br>
                        </span><b><span
style="font-size:7.0pt;font-family:"Helvetica",sans-serif;color:#383A35;text-transform:uppercase">Sending
                            me large files? Please use
                            <a
href="https://apps.hendersonengineers.com/FileShare/Upload?to=daric.adair@hendersonengineers.com"
                              target="_blank" moz-do-not-send="true">
                              <span style="color:#008C15">Henderson File
                                Share</span></a> | TX ID #F-001236</span></b><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
                      <p class="yiv1848449785msonormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"> <o:p></o:p></span></p>
                    </div>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p> </o:p></span></p>
                    <div class="MsoNormal" style="text-align:center"
                      align="center"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">
                        <hr size="2" align="center" width="100%">
                      </span></div>
                    <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:gray"><br>
                        This email and any files transmitted with it are
                        confidential and are intended solely for the use
                        of the individual or entity to whom they are
                        addressed. This communication represents the
                        originator's personal views and opinions, which
                        do not necessarily reflect those of Henderson
                        Engineers, Inc. If you are not the original
                        recipient or the person responsible for
                        delivering the email to the intended recipient,
                        be advised that you have received this email in
                        error, and that any use, dissemination,
                        forwarding, printing, or copying of this email
                        is strictly prohibited. If you received this
                        email in error, please immediately notify
                        <a
                          href="mailto:administrator@hendersonengineers.com"
                          moz-do-not-send="true">administrator@hendersonengineers.com</a>.</span><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A"><o:p></o:p></span></p>
                  </div>
                </div>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Helvetica",sans-serif;color:#26282A">_______________________________________________<br>
                    Equest-users mailing list<br>
                    <a
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
                      target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                    To unsubscribe from this mailing list send  a blank
                    message to <a
                      href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG"
                      moz-do-not-send="true">
                      EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></span></p>
              </div>
            </div>
          </div>
        </div>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div class="MsoNormal" style="text-align:center" align="center"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
            <hr size="2" align="center" width="100%">
          </span></div>
        <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:gray"><br>
            This email and any files transmitted with it are
            confidential and are intended solely for the use of the
            individual or entity to whom they are addressed. This
            communication represents the originator's personal views and
            opinions, which do not necessarily reflect those of
            Henderson Engineers, Inc. If you are not the original
            recipient or the person responsible for delivering the email
            to the intended recipient, be advised that you have received
            this email in error, and that any use, dissemination,
            forwarding, printing, or copying of this email is strictly
            prohibited. If you received this email in error, please
            immediately notify
            <a href="mailto:administrator@hendersonengineers.com"
              moz-do-not-send="true">administrator@hendersonengineers.com</a>.</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div class="MsoNormal" style="text-align:center" align="center">
          <hr size="2" align="center" width="100%">
        </div>
        <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:gray"><br>
            <br>
            NOTICE: This communication and any attachments ("this
            message") may contain information which is privileged,
            confidential, proprietary or otherwise subject to restricted
            disclosure under applicable law. This message is for the
            sole use of the intended recipient(s). Any unauthorized use,
            disclosure, viewing, copying, alteration, dissemination or
            distribution of, or reliance on, this message is strictly
            prohibited. If you have received this message in error, or
            you are not an authorized or intended recipient, please
            notify the sender immediately by replying to this message,
            delete this message and all copies from your e-mail system
            and destroy any printed copies. You are receiving this
            communication because you are listed as a current WSP
            contact. Should you have any questions regarding WSP's
            electronic communications policy, please consult our
            Anti-Spam Commitment at
            <a href="http://www.wsp.com/casl" moz-do-not-send="true">www.wsp.com/casl</a>.
            For any concern or if you believe you should not be
            receiving this message, please forward this message to
            <a href="mailto:caslcompliance@wsp.com"
              moz-do-not-send="true">caslcompliance@wsp.com</a> so that
            we can promptly address your request. Note that not all
            messages sent by WSP qualify as commercial electronic
            messages.
            <br>
            <br>
            AVIS : Ce message, incluant tout fichier l'accompagnant («
            le message »), peut contenir des renseignements ou de
            l'information privilégiés, confidentiels, propriétaires ou à
            divulgation restreinte en vertu de la loi. Ce message est
            destiné à l'usage exclusif du/des destinataire(s) voulu(s).
            Toute utilisation non permise, divulgation, lecture,
            reproduction, modification, diffusion ou distribution est
            interdite. Si vous avez reçu ce message par erreur, ou que
            vous n'êtes pas un destinataire autorisé ou voulu, veuillez
            en aviser l'expéditeur immédiatement et détruire le message
            et toute copie électronique ou imprimée. Vous recevez cette
            communication car vous faites partie des contacts de WSP. Si
            vous avez des questions concernant la politique de
            communications électroniques de WSP, veuillez consulter
            notre Engagement anti-pourriel au <a
              href="http://www.wsp.com/lcap" moz-do-not-send="true">
              www.wsp.com/lcap</a>. Pour toute question ou si vous
            croyez que vous ne devriez pas recevoir ce message, prière
            de le transférer au
            <a href="mailto:conformitelcap@wsp.com"
              moz-do-not-send="true">conformitelcap@wsp.com</a> afin que
            nous puissions rapidement traiter votre demande. Notez que
            ce ne sont pas tous les messages transmis par WSP qui
            constituent des messages electroniques commerciaux.
            <br>
          </span><br>
          <span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:whitesmoke"><br>
            <br>
            -LAEmHhHzdJzBlTWfa4Hgs7pbKl </span><o:p></o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div class="MsoNormal" style="text-align:center" align="center"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
            <hr size="2" align="center" width="100%">
          </span></div>
        <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:gray"><br>
            This email and any files transmitted with it are
            confidential and are intended solely for the use of the
            individual or entity to whom they are addressed. This
            communication represents the originator's personal views and
            opinions, which do not necessarily reflect those of
            Henderson Engineers, Inc. If you are not the original
            recipient or the person responsible for delivering the email
            to the intended recipient, be advised that you have received
            this email in error, and that any use, dissemination,
            forwarding, printing, or copying of this email is strictly
            prohibited. If you received this email in error, please
            immediately notify
            <a href="mailto:administrator@hendersonengineers.com"
              moz-do-not-send="true">administrator@hendersonengineers.com</a>.<br>
          </span><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><br>
______________________________________________________________________<br>
            This email has been scanned by the Symantec Email
            Security.cloud service.<br>
______________________________________________________________________<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><br>
______________________________________________________________________<br>
            This email has been scanned by the Symantec Email
            Security.cloud service.<br>
______________________________________________________________________<o:p></o:p></span></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________