<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    The power of the user group comes to bear.<br>
    Thanks Daric for running some numbers for everyone.<br>
    As Joe mentioned the area in question is actually the floor area. 
    My solution on this part of the project was in the end not solved by
    the model.  As my time was bid limited and I was already getting
    push back on my modelling hours I concentrated my time on designing
    the seal between the buildings.  They were 6" apart and the curing
    room was using 15 psi steam to heat the space.  Needless to say a
    60' x 6" crack was the elephant in this building and I was required
    to drop my model evaluation of the infiltration in this instance. 
    It would have proved fruitless anyway as my assumption on the
    reference square footage was incorrect.<br>
    I sometimes worry about posts and getting the dunce cap.  lol  I
    suppose age and a thicker skin helps.  I rationalize it away with
    these exercises being a learning experience that benefit me as much
    as the group.  The knowledge and experience this group brings to
    bear is impressive.<br>
    This discussion is illuminating and an old dog is still learning new
    tricks.<br>
    Bruce<br>
    <br>
    <div class="moz-cite-prefix">On 3/2/2018 10:33 AM, Daric Adair
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:20180302153306.MXRJ2981.toroondcmxzimta03-srv.bellnexxia.net@tordcvbicmrk02">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Wingdings;
        panose-1:5 0 0 0 0 0 0 0 0 0;}
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
@font-face
        {font-family:Corbel;
        panose-1:2 11 5 3 2 2 4 2 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;
        color:black;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
p
        {mso-style-priority:99;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;
        color:black;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
        {mso-style-priority:34;
        margin-top:0in;
        margin-right:0in;
        margin-bottom:0in;
        margin-left:.5in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;
        color:black;}
p.msonormal0, li.msonormal0, div.msonormal0
        {mso-style-name:msonormal;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;
        color:black;}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:"Consolas",serif;
        color:black;}
span.EmailStyle21
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle22
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
/* List Definitions */
@list l0
        {mso-list-id:118107625;
        mso-list-type:hybrid;
        mso-list-template-ids:2043950596 51445406 67698691 67698693 67698689 67698691 67698693 67698689 67698691 67698693;}
@list l0:level1
        {mso-level-start-at:0;
        mso-level-number-format:bullet;
        mso-level-text:-;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        margin-left:.75in;
        text-indent:-.25in;
        font-family:"Calibri",sans-serif;
        mso-fareast-font-family:Calibri;}
@list l0:level2
        {mso-level-number-format:bullet;
        mso-level-text:o;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        margin-left:1.25in;
        text-indent:-.25in;
        font-family:"Courier New";}
@list l0:level3
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        margin-left:1.75in;
        text-indent:-.25in;
        font-family:Wingdings;}
@list l0:level4
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        margin-left:2.25in;
        text-indent:-.25in;
        font-family:Symbol;}
@list l0:level5
        {mso-level-number-format:bullet;
        mso-level-text:o;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        margin-left:2.75in;
        text-indent:-.25in;
        font-family:"Courier New";}
@list l0:level6
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        margin-left:3.25in;
        text-indent:-.25in;
        font-family:Wingdings;}
@list l0:level7
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        margin-left:3.75in;
        text-indent:-.25in;
        font-family:Symbol;}
@list l0:level8
        {mso-level-number-format:bullet;
        mso-level-text:o;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        margin-left:4.25in;
        text-indent:-.25in;
        font-family:"Courier New";}
@list l0:level9
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        margin-left:4.75in;
        text-indent:-.25in;
        font-family:Wingdings;}
ol
        {margin-bottom:0in;}
ul
        {margin-bottom:0in;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span style="color:#1F497D">All;<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Confused as to
            how Bruce’s answer isn’t directly applicable. What he
            detailed in the first instance is directly in line with my
            experiences. eQuest wizard modes doesn’t realize that two
            abutting/touching shells should have interior walls. If a
            space wall touches a shell wall, an exterior wall is
            created.<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="margin-left:.75in;text-indent:-.25in;mso-list:l0 level1
          lfo1">
          <!--[if !supportLists]--><span style="color:#1F497D"><span
              style="mso-list:Ignore">-<span style="font:7.0pt
                "Times New Roman"">         
              </span></span></span><!--[endif]--><span
            style="color:#1F497D">If a zone boarders a shell, eQuest
            creates an exterior wall.
            <o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="margin-left:.75in;text-indent:-.25in;mso-list:l0 level1
          lfo1">
          <!--[if !supportLists]--><span style="color:#1F497D"><span
              style="mso-list:Ignore">-<span style="font:7.0pt
                "Times New Roman"">         
              </span></span></span><!--[endif]--><span
            style="color:#1F497D">If a zone does not touch a shell edge,
            eQuest makes an adiabatic interior wall.
            <o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="margin-left:.75in;text-indent:-.25in;mso-list:l0 level1
          lfo1">
          <!--[if !supportLists]--><span style="color:#1F497D"><span
              style="mso-list:Ignore">-<span style="font:7.0pt
                "Times New Roman"">         
              </span></span></span><!--[endif]--><span
            style="color:#1F497D">If two shells are touching and each
            have zones touching the common wall, two exterior walls are
            created; one in each zone. Wizard eQuest doesn’t distinguish
            if two shells are 0 feet apart/touching or if they are 25
            feet apart.  (example described below)<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">If eQuest uses
            exterior wall area to calculate a floor area normalized
            infiltration rate, and there are ‘extra’ exterior walls
            which are actually interior walls where shells touch, then
            the infiltration rate will be  calculated as though the two
            shells were never touching. This will increase the
            calculated infiltration rate since these are not actually
            interior walls.
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Bruce’s
            solution only neglected to mention that the infiltration
            rate will either need to be corrected for this condition, or
            ignored/neglected. The second option is not to say
            infiltration is not important – it is important – but
            requires modeler judgement and some math. The length/area of
            the touching walls is also a factor to consider. If project
            is a large industrial setting as described in thread, yes,
            probably should check/revise. If a small connecting
            corridor, probably minor and can be ignored. <o:p></o:p></span></p>
        <div>
          <p class="MsoNormal"><span style="color:#44546A"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A">Did a quick
              (very simplified ) example. All examples have: 10ft high.
              No plenum. Set Perimeter infiltration to 0.05 CFM/sf. 0.0
              core infiltration.<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A">- Made two
              shells, 50ft x 50ft each. 2 spaces per shell, spliting
              shell equally.  Placed the shells touching. The calculated
              infiltration is 0.0400 cfm/ft<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A">- Made two
              shells, 50ft x 50ft each. 2 spaces per shell, spliting
              shell equally.  Placed the shells 50 feet apart. The
              calculated infiltration is 0.0400 cfm/ft<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A">- Made one
              shell, 100ft x 50ft each. 4 spaces per shell, spliting
              vertically,such that the zones are the same
              area/dimensions as the previous examples. The calculated
              infiltration is 0.0400 cfm/ft in the end cap spaces, and
              0.0200 CFM/sf in the middle spaces. This is due to less
              exterior wall area (as expected).<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A">- Made two
              shells, 50ft x 50ft each. 2 spaces per shell, same spaces
              as above.  But – offset the edge of the shells when
              drawing in wizard mode such that the edge of the spaces
              were not the edge of the shell(s) (refer to image). Placed
              the shells such that the two zones were touching. The
              calculated infiltration is 0.0400 cfm/ft in the end cap
              spaces, and 0.0200 CFM/sf in the middle spaces; matching
              as if done in a single shell.<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A">The last
              example allows the user to change the wall from adiabatic
              to a heat transfer surface easily. Can also modify the
              infiltration rate as needed & detailed ablve. PNNL has
              published several reports on infilatration rates which can
              be references as well for good information.<o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A">Let me (and
              all of us) know if this seems at odd with previous
              experiences or overlooked a detail. Thanks in advance.<o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="color:#44546A;text-transform:uppercase"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span style="color:#44546A"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span style="color:#1F497D">Thanks,<o:p></o:p></span></p>
          <p class="MsoNormal" style="background:white"><b><span
style="font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">DARIC
                R ADAIR</span></b><span
style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">
              PE, CEM, BEMP </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383A35"><br>
              Mechanical Engineer, Energy Analyst <br>
              <br>
            </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#008C15;text-transform:uppercase">Henderson
                Engineers</span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383A35"><br>
              <b><span style="text-transform:uppercase">Tel</span></b>
              (913) 742-5530  <br>
              <a href="mailto:daric.adair@hendersonengineers.com"
                moz-do-not-send="true"><span style="color:#383A35">daric.adair@hendersonengineers.com</span></a><br>
              <br>
            </span><b><span
style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">Licensed
                in</span></b><span
style="font-size:7.0pt;font-family:"Arial",sans-serif;color:#383A35;text-transform:uppercase">
              KS</span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#383A35"><o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span style="color:windowtext">From:</span></b><span
                style="color:windowtext"> Bruce Easterbrook
                [<a class="moz-txt-link-freetext" href="mailto:bruce5@bellnet.ca">mailto:bruce5@bellnet.ca</a>]
                <br>
                <b>Sent:</b> Thursday, March 1, 2018 11:19 PM<br>
                <b>To:</b> Joe Huang
                <a class="moz-txt-link-rfc2396E" href="mailto:yjhuang@whiteboxtechnologies.com"><yjhuang@whiteboxtechnologies.com></a>;
                <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] Infiltration issues
                whith more than one shell<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal" style="margin-bottom:12.0pt">Thank's Joe, I
          didn't realize that.  There are many quirks with DOE2 and
          eQuest.  I haven't looked at that part of the fine print
          recently.  Leakage does depend on the wall area and not the
          floor area in real terms.  Buildings have many different wall
          heights, plenums or not, ducted or not, etc.  I would guess
          after normalization that one would have to be careful with how
          manipulations in geometry are done to achieve other effects in
          the model.  Infiltration can have a serious effect on a model.<br>
          I can remember a past model where I used this technique for an
          actual butting of 2 industrial spaces/buildings.  The one area
          was a cable casing thermal setting zone, 1/2 height of the
          warehouse/machinery high bay zone that was adjacent to it.  I
          was more concerned with the door and seal between the 2
          buildings.  I possibly missed the infiltration difference
          seeing it was based on floor area and not wall area.   I will
          have to re-read the fine print.<br>
          Bruce<span style="font-size:12.0pt"><o:p></o:p></span></p>
        <div>
          <p class="MsoNormal">On 3/1/2018 10:32 PM, Joe Huang via
            Equest-users wrote:<o:p></o:p></p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <p>I don't think Bruce's comment is germaine to the problem
            posed by Menush, since Menush is asking about infiltration
            and not heat transfer through interior walls.  As far as I
            know from DOE-2 (always have to add that caveat because I
            don't work much in eQUEST), infiltration rates are
            normalized per floor area, rather than external wall area,
            mainly because that's how the infiltration models have been
            developed, i.e., effective leakage areas have always been
            defined as per floor area.  If you don't think that's right,
            you can always adjust the input values by the ratio of the
            external wall area to the floor area, as you've described,
            but then you're on your own in coming up with the
            correlation,
            <o:p></o:p></p>
          <p>Joe<o:p></o:p></p>
          <pre>Joe Huang<o:p></o:p></pre>
          <pre>White Box Technologies, Inc.<o:p></o:p></pre>
          <pre>346 Rheem Blvd., Suite 205A<o:p></o:p></pre>
          <pre>Moraga CA 94556<o:p></o:p></pre>
          <pre><a href="mailto:yjhuang@whiteboxtechnologies.com" moz-do-not-send="true">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
          <pre><a href="http://weather.whiteboxtechnologies.com" moz-do-not-send="true">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data<o:p></o:p></pre>
          <pre>(o) (925)388-0265<o:p></o:p></pre>
          <pre>(c) (510)928-2683<o:p></o:p></pre>
          <pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
          <div>
            <p class="MsoNormal">On 3/1/2018 6:44 PM, Bruce Easterbrook
              via Equest-users wrote:<o:p></o:p></p>
          </div>
          <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
            <p class="MsoNormal" style="margin-bottom:12.0pt">Hi Menush,<br>
              I don't think you have the same thing.  eQuest will treat
              2 shells butted to each other differently than a single
              interior wall separating 2 zones in a shell.  It treats
              the 2 butted walls as exterior walls with a tiny space
              between.  They are the same wall in your thinking but they
              are not.  You can delete one of them and make the
              remaining wall an interior wall and assign the proper
              butting spaces on each side of the wall as sharing the
              wall and transferring heating and cooling through the
              wall.  Or you can add an interior wall to the original
              space and separate it into 2 zones.  As you have noticed
              there is a difference in the way eQuest treats your 2
              solutions.  It is particular.  Now you need to pick the
              configuration that matches what you are trying to model in
              such a way that eQuest does/treats the wall in the way you
              want it to work.<br>
              Bruce Easterbrook P.Eng.<br>
              Abode Engineering<o:p></o:p></p>
            <div>
              <p class="MsoNormal">On 3/1/2018 5:23 PM, Menush Akbari
                via Equest-users wrote:<o:p></o:p></p>
            </div>
            <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
              <p class="MsoNormal">Hi all,<o:p></o:p></p>
              <p class="MsoNormal"> <o:p></o:p></p>
              <p class="MsoNormal">I’m having an issue with infiltration
                and wondering if anyone else has noticed this. When I’m
                in wizard mode, I build a very simple rectangular shell
                and I change the infiltration rate for perimeter zones
                to 0.05cfm/ft2. I leave the core zone infiltration rate
                to the eQuest default value (0.001cfm/ft2). From my
                understanding, the perimeter zone entered value in
                wizard mode is based on exterior gross wall area. When I
                move on to detail mode, eQuest changes the value to an
                infiltration value per floor area instead of exterior
                wall area. The values so far make sense and I can do the
                math and get the same numbers eQuest calculates in
                detail mode. No problems here.<o:p></o:p></p>
              <p class="MsoNormal"> <o:p></o:p></p>
              <p class="MsoNormal">The problem however happens when I
                create different shells. For example, let’s say I have
                the same rectangular building as mentioned above, but I
                split this up into two different shells next to each
                other (two square shells), therefore one of the walls of
                each square shell is an interior wall, which means I
                should not see an infiltration of 0.05 cfm/ft2 of the
                gross wall area. However when I finish building these
                two shells in detail mode (which would be identical to
                one rectangular shell), the infiltration value is not
                accurate anymore. Instead of the same numbers as my
                first model (one rectangular shell), the second model
                calculates an exterior wall infiltration value for the
                interior walls that are budded up against each other.<o:p></o:p></p>
              <p class="MsoNormal"> <o:p></o:p></p>
              <p class="MsoNormal">Has anyone come across this? Is this
                a quirk with eQuest and just needs to be changed
                manually in detail mode, or am I doing something wrong
                here?<o:p></o:p></p>
              <p class="MsoNormal"> <o:p></o:p></p>
              <p class="MsoNormal">Thanks for the help.<o:p></o:p></p>
              <p class="MsoNormal"> <o:p></o:p></p>
              <p class="MsoNormal">Cheers,<o:p></o:p></p>
              <p class="MsoNormal"> <o:p></o:p></p>
              <p class="MsoNormal"><b><span
style="font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                    lang="EN-CA">Menush Akbari</span></b><o:p></o:p></p>
              <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                  lang="EN-CA">BEng, PEng, BEMP, CMVP</span><o:p></o:p></p>
              <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                  lang="EN-CA">Senior Energy Engineer</span><o:p></o:p></p>
              <p class="MsoNormal"><span
style="font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                  lang="EN-CA">Mission Green Buildings</span><o:p></o:p></p>
              <p class="MsoNormal"><i><span
style="font-size:9.0pt;font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                    lang="EN-CA">(Mission Green Buildings is the trading
                    name of Mission Green Limited)</span></i><o:p></o:p></p>
              <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                  lang="EN-CA"> </span><o:p></o:p></p>
              <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                  lang="EN-CA">t. 250 777 3380</span><o:p></o:p></p>
              <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                  lang="EN-CA"><a
                    href="mailto:makbari@missiongreenbuildings.com"
                    moz-do-not-send="true">makbari@missiongreenbuildings.com</a></span><o:p></o:p></p>
              <p class="MsoNormal"><u><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                    lang="EN-CA"><a
                      href="http://missiongreenbuildings.com/"
                      moz-do-not-send="true">http://missiongreenbuildings.com</a></span></u><o:p></o:p></p>
              <p class="MsoNormal"><span
style="font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                  lang="EN-CA"> </span><o:p></o:p></p>
              <p class="MsoNormal"><span
style="font-family:"Corbel",sans-serif;mso-fareast-language:EN-CA"
                  lang="EN-CA"><img
                    style="width:3.3645in;height:.8854in"
                    id="Picture_x0020_1"
                    src="cid:part6.50FF6E2F.B62C8457@bellnet.ca"
                    alt="MGB 5 Years 2" class="" height="85" width="323"
                    border="0"></span><o:p></o:p></p>
              <p class="MsoNormal"> <o:p></o:p></p>
              <p class="MsoNormal"><span
                  style="font-size:12.0pt;font-family:"Times New
                  Roman",serif"><br>
                  <br>
                  <br>
                  <o:p></o:p></span></p>
              <pre>_______________________________________________<o:p></o:p></pre>
              <pre>Equest-users mailing list<o:p></o:p></pre>
              <pre><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><o:p></o:p></pre>
              <pre>To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></pre>
            </blockquote>
            <p class="MsoNormal"><span
                style="font-size:12.0pt;font-family:"Times New
                Roman",serif"><br>
                <br>
                <br>
                <br>
                <o:p></o:p></span></p>
            <pre>_______________________________________________<o:p></o:p></pre>
            <pre>Equest-users mailing list<o:p></o:p></pre>
            <pre><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><o:p></o:p></pre>
            <pre>To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></pre>
          </blockquote>
          <p class="MsoNormal"><span
              style="font-size:12.0pt;font-family:"Times New
              Roman",serif"><br>
              <br>
              <br>
              <br>
              <o:p></o:p></span></p>
          <pre>_______________________________________________<o:p></o:p></pre>
          <pre>Equest-users mailing list<o:p></o:p></pre>
          <pre><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><o:p></o:p></pre>
          <pre>To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></pre>
        </blockquote>
        <p class="MsoNormal"><span
            style="font-size:12.0pt;font-family:"Times New
            Roman",serif"><o:p> </o:p></span></p>
      </div>
      <br>
      <hr>
      <font size="1" face="Arial" color="Gray"><br>
        This email and any files transmitted with it are confidential
        and are intended solely for the use of the individual or entity
        to whom they are addressed. This communication represents the
        originator's personal views and opinions, which do not
        necessarily reflect those of Henderson Engineers, Inc. If you
        are not the original recipient or the person responsible for
        delivering the email to the intended recipient, be advised that
        you have received this email in error, and that any use,
        dissemination, forwarding, printing, or copying of this email is
        strictly prohibited. If you received this email in error, please
        immediately notify <a class="moz-txt-link-abbreviated" href="mailto:administrator@hendersonengineers.com">administrator@hendersonengineers.com</a>.<br>
      </font>
    </blockquote>
    <br>
  </body>
</html>