<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <p>I don't think Bruce's comment is germaine to the problem posed by
      Menush, since Menush is asking about infiltration and not heat
      transfer through interior walls.  As far as I know from DOE-2
      (always have to add that caveat because I don't work much in
      eQUEST), infiltration rates are normalized per floor area, rather
      than external wall area, mainly because that's how the
      infiltration models have been developed, i.e., effective leakage
      areas have always been defined as per floor area.  If you don't
      think that's right, you can always adjust the input values by the
      ratio of the external wall area to the floor area, as you've
      described, but then you're on your own in coming up with the
      correlation, <br>
    </p>
    <p>Joe<br>
    </p>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 3/1/2018 6:44 PM, Bruce Easterbrook
      via Equest-users wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:5669491f-8e14-0dce-e943-4b7f2f5dfa09@bellnet.ca">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      Hi Menush,<br>
      I don't think you have the same thing.  eQuest will treat 2 shells
      butted to each other differently than a single interior wall
      separating 2 zones in a shell.  It treats the 2 butted walls as
      exterior walls with a tiny space between.  They are the same wall
      in your thinking but they are not.  You can delete one of them and
      make the remaining wall an interior wall and assign the proper
      butting spaces on each side of the wall as sharing the wall and
      transferring heating and cooling through the wall.  Or you can add
      an interior wall to the original space and separate it into 2
      zones.  As you have noticed there is a difference in the way
      eQuest treats your 2 solutions.  It is particular.  Now you need
      to pick the configuration that matches what you are trying to
      model in such a way that eQuest does/treats the wall in the way
      you want it to work.<br>
      Bruce Easterbrook P.Eng.<br>
      Abode Engineering<br>
      <br>
      <div class="moz-cite-prefix">On 3/1/2018 5:23 PM, Menush Akbari
        via Equest-users wrote:<br>
      </div>
      <blockquote type="cite"
cite="mid:20180301222331.DDCX20225.toroondcmxzimta01-srv.bellnexxia.net@tordcvbicmrk03">
        <meta http-equiv="Content-Type" content="text/html;
          charset=utf-8">
        <meta name="Generator" content="Microsoft Word 15 (filtered
          medium)">
        <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
        <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Corbel;
        panose-1:2 11 5 3 2 2 4 2 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri",sans-serif;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
        <div class="WordSection1">
          <p class="MsoNormal">Hi all,<o:p></o:p></p>
          <p class="MsoNormal"><o:p> </o:p></p>
          <p class="MsoNormal">I’m having an issue with infiltration and
            wondering if anyone else has noticed this. When I’m in
            wizard mode, I build a very simple rectangular shell and I
            change the infiltration rate for perimeter zones to
            0.05cfm/ft2. I leave the core zone infiltration rate to the
            eQuest default value (0.001cfm/ft2). From my understanding,
            the perimeter zone entered value in wizard mode is based on
            exterior gross wall area. When I move on to detail mode,
            eQuest changes the value to an infiltration value per floor
            area instead of exterior wall area. The values so far make
            sense and I can do the math and get the same numbers eQuest
            calculates in detail mode. No problems here.<o:p></o:p></p>
          <p class="MsoNormal"><o:p> </o:p></p>
          <p class="MsoNormal">The problem however happens when I create
            different shells. For example, let’s say I have the same
            rectangular building as mentioned above, but I split this up
            into two different shells next to each other (two square
            shells), therefore one of the walls of each square shell is
            an interior wall, which means I should not see an
            infiltration of 0.05 cfm/ft2 of the gross wall area. However
            when I finish building these two shells in detail mode
            (which would be identical to one rectangular shell), the
            infiltration value is not accurate anymore. Instead of the
            same numbers as my first model (one rectangular shell), the
            second model calculates an exterior wall infiltration value
            for the interior walls that are budded up against each
            other.<o:p></o:p></p>
          <p class="MsoNormal"><o:p> </o:p></p>
          <p class="MsoNormal">Has anyone come across this? Is this a
            quirk with eQuest and just needs to be changed manually in
            detail mode, or am I doing something wrong here?<o:p></o:p></p>
          <p class="MsoNormal"><o:p> </o:p></p>
          <p class="MsoNormal">Thanks for the help.<o:p></o:p></p>
          <p class="MsoNormal"><o:p> </o:p></p>
          <p class="MsoNormal">Cheers,<o:p></o:p></p>
          <p class="MsoNormal"><o:p> </o:p></p>
          <p class="MsoNormal"><b><span
style="font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
                lang="EN-CA">Menush Akbari<o:p></o:p></span></b></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA">BEng, PEng, BEMP, CMVP<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA">Senior Energy Engineer<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA">Mission Green Buildings<o:p></o:p></span></p>
          <p class="MsoNormal"><i><span
style="font-size:9.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
                lang="EN-CA">(Mission Green Buildings is the trading
                name of Mission Green Limited)<o:p></o:p></span></i></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA">t. 250 777 3380<o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA"><a
                href="mailto:makbari@missiongreenbuildings.com"
                moz-do-not-send="true">makbari@missiongreenbuildings.com</a><o:p></o:p></span></p>
          <p class="MsoNormal"><u><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
                lang="EN-CA"><a href="http://missiongreenbuildings.com/"
                  moz-do-not-send="true">http://missiongreenbuildings.com</a><o:p></o:p></span></u></p>
          <p class="MsoNormal"><span
style="font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA"><img style="width:3.3666in;height:.8833in"
                id="Picture_x0020_1"
                src="cid:part3.CE9FC407.DC6FCA4D@whiteboxtechnologies.com"
                alt="MGB 5 Years 2" class="" height="85" width="323"
                border="0"></span><span
              style="color:black;mso-fareast-language:EN-CA"
              lang="EN-CA"><o:p></o:p></span></p>
          <p class="MsoNormal"><o:p> </o:p></p>
        </div>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <br>
        <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
      </blockquote>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>