    Hi Menush,<br>
    I don't think you have the same thing.  eQuest will treat 2 shells
    butted to each other differently than a single interior wall
    separating 2 zones in a shell.  It treats the 2 butted walls as
    exterior walls with a tiny space between.  They are the same wall in
    your thinking but they are not.  You can delete one of them and make
    the remaining wall an interior wall and assign the proper butting
    spaces on each side of the wall as sharing the wall and transferring
    heating and cooling through the wall.  Or you can add an interior
    wall to the original space and separate it into 2 zones.  As you
    have noticed there is a difference in the way eQuest treats your 2
    solutions.  It is particular.  Now you need to pick the
    configuration that matches what you are trying to model in such a
    way that eQuest does/treats the wall in the way you want it to work.<br>
    Bruce Easterbrook P.Eng.<br>
    Abode Engineering<br>
    <br>
    <div class="moz-cite-prefix">On 3/1/2018 5:23 PM, Menush Akbari via
      Equest-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:20180301222331.DDCX20225.toroondcmxzimta01-srv.bellnexxia.net@tordcvbicmrk03">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Corbel;
        panose-1:2 11 5 3 2 2 4 2 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri",sans-serif;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">Hi all,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">I’m having an issue with infiltration and
          wondering if anyone else has noticed this. When I’m in wizard
          mode, I build a very simple rectangular shell and I change the
          infiltration rate for perimeter zones to 0.05cfm/ft2. I leave
          the core zone infiltration rate to the eQuest default value
          (0.001cfm/ft2). From my understanding, the perimeter zone
          entered value in wizard mode is based on exterior gross wall
          area. When I move on to detail mode, eQuest changes the value
          to an infiltration value per floor area instead of exterior
          wall area. The values so far make sense and I can do the math
          and get the same numbers eQuest calculates in detail mode. No
          problems here.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">The problem however happens when I create
          different shells. For example, let’s say I have the same
          rectangular building as mentioned above, but I split this up
          into two different shells next to each other (two square
          shells), therefore one of the walls of each square shell is an
          interior wall, which means I should not see an infiltration of
          0.05 cfm/ft2 of the gross wall area. However when I finish
          building these two shells in detail mode (which would be
          identical to one rectangular shell), the infiltration value is
          not accurate anymore. Instead of the same numbers as my first
          model (one rectangular shell), the second model calculates an
          exterior wall infiltration value for the interior walls that
          are budded up against each other.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Has anyone come across this? Is this a
          quirk with eQuest and just needs to be changed manually in
          detail mode, or am I doing something wrong here?<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Thanks for the help.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Cheers,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><b><span
style="font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA">Menush Akbari<o:p></o:p></span></b></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
            lang="EN-CA">BEng, PEng, BEMP, CMVP<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
            lang="EN-CA">Senior Energy Engineer<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
            lang="EN-CA">Mission Green Buildings<o:p></o:p></span></p>
        <p class="MsoNormal"><i><span
style="font-size:9.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA">(Mission Green Buildings is the trading name
              of Mission Green Limited)<o:p></o:p></span></i></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
            lang="EN-CA"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
            lang="EN-CA">t. 250 777 3380<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
            lang="EN-CA"><a
              href="mailto:makbari@missiongreenbuildings.com"
              moz-do-not-send="true">makbari@missiongreenbuildings.com</a><o:p></o:p></span></p>
        <p class="MsoNormal"><u><span
style="font-size:10.0pt;font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
              lang="EN-CA"><a href="http://missiongreenbuildings.com/"
                moz-do-not-send="true">http://missiongreenbuildings.com</a><o:p></o:p></span></u></p>
        <p class="MsoNormal"><span
style="font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
            lang="EN-CA"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-family:"Corbel",sans-serif;color:black;mso-fareast-language:EN-CA"
            lang="EN-CA"><img style="width:3.3666in;height:.8833in"
              id="Picture_x0020_1"
              src="cid:part3.2B971050.9EAC3C9C@bellnet.ca" alt="MGB 5
              Years 2" class="" height="85" width="323" border="0"></span><span
            style="color:black;mso-fareast-language:EN-CA" lang="EN-CA"><o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>