<div dir="auto"><div style="font-family:sans-serif;font-size:13.696px" dir="auto">Thank you very much Mr. Joe for your response to my questions. I have taken note of all that you have recommended. </div><div dir="auto" style="font-family:sans-serif;font-size:13.696px"><br></div><div dir="auto" style="font-family:sans-serif;font-size:13.696px">I am grateful and will work with that.</div><div dir="auto" style="font-family:sans-serif;font-size:13.696px"><br></div><div dir="auto" style="font-family:sans-serif;font-size:13.696px">Please I will like to ask further if there's a document or anything that can give me the comprehensive information I will need to get from the church buildings in order to successfully carry out the energy simulation on eQUEST? </div><div dir="auto" style="font-family:sans-serif;font-size:13.696px"><br></div><div dir="auto" style="font-family:sans-serif;font-size:13.696px">I have a questionnaire already prepared for the survey of the chosen church buildings but I want to make sure I am not leaving any information out so I don't have to start going back to the churches a second time. I will really appreciate your help with this. </div><div dir="auto" style="font-family:sans-serif;font-size:13.696px"><br></div><div dir="auto" style="font-family:sans-serif;font-size:13.696px">If I have further questions or encounter any difficulty while using the software, I will let you know. </div><div dir="auto" style="font-family:sans-serif;font-size:13.696px"><br></div><div dir="auto" style="font-family:sans-serif;font-size:13.696px">Thank you again. </div><font color="#888888" style="font-family:sans-serif;font-size:13.696px"><div dir="auto"><br></div><div dir="auto">Effiong Edentekhe </div><div dir="auto">+2348032327091</div></font></div><div class="gmail_extra"><br><div class="gmail_quote">On Jan 16, 2018 2:24 AM, "Joe Huang via Equest-users" <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.<wbr>onebuilding.org</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    <p>Effiong,</p>
    <p>Here is my reaction to your questions:</p>
    <p>1) While it's true you might not need simulations to determine
      the energy usage of church buildings in Nigeria, simulations are
      very helpful in understanding the reasons behind that energy
      usage.  For example, if you just wanted to know  how much energy
      church buildings in Nigeria used, you can simply survey a number
      of them and get their energy bills. But then what?  However, if
      you used simulations you can determine the factors for that energy
      use and, understand how much energy can be saved with changes in
      operations and building construction, normalize for building size
      and climate to get an EEI, etc.<br>
    </p>
    <p>2)  I would recommend using eQUEST because it has the most easy
      to use Graphical User Interface of all the programs I've seen, and
      of course, is free of charge. However, be aware that eQUEST works
      only in Inch-Pound (IP) units rather than metric SI, so be
      prepared to do a lot of conversions in creating your building
      model. <br>
    </p>
    <p>3) I'm not aware of any purpose-built software for calculating
      carbon footprint, but you should be able to do that with the
      hourly reports from eQUEST for energy usage by fuel type, and
      figuring out the fuel-to-electricity conversion in your area.</p>
    <p>Joe<br>
    </p>
    <pre class="m_-3877111661070172471moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="m_-3877111661070172471moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.<wbr>com</a>
<a class="m_-3877111661070172471moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com" target="_blank">http://weather.<wbr>whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="m_-3877111661070172471moz-cite-prefix">On 1/12/2018 10:32 AM, Effiong
      Edentekhe via Equest-users wrote:<br>
    </div>
    <blockquote type="cite">
      <div dir="auto">
        <div dir="auto">Compliments
          everyone,</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">Please
          I am currently working on a Masters degree project titled
          "Energy Performance and Carbon Footprint of Church Buildings
          in Nigeria."</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">The
          objectives of the project are:</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">1.
          Assess the energy consumption of major church buildings.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">2.
          Determine the factors responsible for their current energy
          performance.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">3.
          Estimate some of the energy performance indices in church
          buildings (e.g. EEI, EPI, etc.).</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">4.
          Determine the quantities of energy usage and their consumption
          patterns within the location of the churches (e.g. unit energy
          for lighting, cooling, etc.).</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">5.
          Evaluate the carbon footprint of the church buildings.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">I
          initially picked eQUEST thinking the project requires energy
          simulation but one of the energy consultants here said it may
          not require that. </div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">I
          am currently not familiar with any building software but I can
          learn really fast if the project requires that I use one by
          your assessment of the above objectives.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">I
          will appreciate if there are other more suitable softwares for
          this kind of project you can recommend, especially simpler and
          purpose-built options. </div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">Also,
          I will appreciate if you can recommend a simple software for
          calculating carbon footprint outside online carbon footprint
          calculators. </div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">I
          will really appreciate your input. </div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">Thank
          you very much.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">Effiong
          Edentekhe</div>
      </div>
      <br>
      <fieldset class="m_-3877111661070172471mimeAttachmentHeader"></fieldset>
      <br>
      <pre>______________________________<wbr>_________________
Equest-users mailing list
<a class="m_-3877111661070172471moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/equest-users-<wbr>onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="m_-3877111661070172471moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@<wbr>ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </div>

<br>______________________________<wbr>_________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/equest-users-<wbr>onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@<wbr>ONEBUILDING.ORG</a><br>
<br></blockquote></div></div>