    <p>Effiong,</p>
    <p>Here is my reaction to your questions:</p>
    <p>1) While it's true you might not need simulations to determine
      the energy usage of church buildings in Nigeria, simulations are
      very helpful in understanding the reasons behind that energy
      usage.  For example, if you just wanted to know  how much energy
      church buildings in Nigeria used, you can simply survey a number
      of them and get their energy bills. But then what?  However, if
      you used simulations you can determine the factors for that energy
      use and, understand how much energy can be saved with changes in
      operations and building construction, normalize for building size
      and climate to get an EEI, etc.<br>
    </p>
    <p>2)  I would recommend using eQUEST because it has the most easy
      to use Graphical User Interface of all the programs I've seen, and
      of course, is free of charge. However, be aware that eQUEST works
      only in Inch-Pound (IP) units rather than metric SI, so be
      prepared to do a lot of conversions in creating your building
      model. <br>
    </p>
    <p>3) I'm not aware of any purpose-built software for calculating
      carbon footprint, but you should be able to do that with the
      hourly reports from eQUEST for energy usage by fuel type, and
      figuring out the fuel-to-electricity conversion in your area.</p>
    <p>Joe<br>
    </p>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 1/12/2018 10:32 AM, Effiong
      Edentekhe via Equest-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAKdEw5JRM2cL7-MPG_DycWGG4_dk+bs8R=meGFtJQa95L6Y-YA@mail.gmail.com">
      <div dir="auto">
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">Compliments
          everyone,</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">Please
          I am currently working on a Masters degree project titled
          "Energy Performance and Carbon Footprint of Church Buildings
          in Nigeria."</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">The
          objectives of the project are:</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">1.
          Assess the energy consumption of major church buildings.</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">2.
          Determine the factors responsible for their current energy
          performance.</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">3.
          Estimate some of the energy performance indices in church
          buildings (e.g. EEI, EPI, etc.).</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">4.
          Determine the quantities of energy usage and their consumption
          patterns within the location of the churches (e.g. unit energy
          for lighting, cooling, etc.).</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">5.
          Evaluate the carbon footprint of the church buildings.</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">I
          initially picked eQUEST thinking the project requires energy
          simulation but one of the energy consultants here said it may
          not require that. </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">I
          am currently not familiar with any building software but I can
          learn really fast if the project requires that I use one by
          your assessment of the above objectives.</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">I
          will appreciate if there are other more suitable softwares for
          this kind of project you can recommend, especially simpler and
          purpose-built options. </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">Also,
          I will appreciate if you can recommend a simple software for
          calculating carbon footprint outside online carbon footprint
          calculators. </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">I
          will really appreciate your input. </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">Thank
          you very much.</div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto"><br>
        </div>
        <div style="font-family:'helvetica
          neue','arial','sans',sans-serif;font-size:16px" dir="auto">Effiong
          Edentekhe</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>