    Jing, I think the mistake is making the zone unconditioned.  You are
    trying to keep it under control with ventilation, therefore it is
    conditioned, no active heating or cooling but it is conditioned. 
    You also need the temperature profile of what is going on in that
    space so you can understand what is happening.  Buildings aren't
    always intuitive depending what is going on and where it is
    located.  You have a fully walled and windowed zone I presume.  For
    unconditioned I would think a space like a parking garage that is
    more than half open on 3 sides.<br>
    You also have the impacts of the floor below and the floor above
    which probably have larger boundary surfaces with your second floor
    space than that space has exterior wall.  It may not be energy
    efficient to let the second floor stay near exterior temperatures
    because of it's impact on the floors above and below.  By making it
    conditioned and giving it to a system will give you the information
    you need to evaluate whether you want to treat it with just
    ventilation.  Open up your heating and cooling set points so there
    really isn't going to be a call for heating and cooling and see what
    the temperatures in the space do.   Then start tinkering with the
    exhaust cfm and zone cooling set point to see if this is practical
    from an energy consumption point of view.  Also watch what is
    happening in the floor above and the floor below.  You can advantage
    of auto-sizing too.<br>
    Bruce Easterbook P.Eng.<br>
    Abode Engineering<br>
    <br>
    <div class="moz-cite-prefix">On 11/15/2017 2:33 PM, Jones,
      Christopher via Equest-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:20171115193401.RBFR9331.toroondcmxzimta02-srv.bellnexxia.net@tordcvbicmrk03">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri",sans-serif;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">SUM
            system type. The DOE2.2 manuals do not explain the SUM
            system type very well. From the DOE2.1e manual:<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">4.
            System Descriptions<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">a.
            Summation of LOADS to PLANT (SUM)<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">This
            is actually not a secondary HVAC distribution system, but
            rather a diagnostic tool, which is used to 1) pass the
            hourly LOADS program output to the PLANT program without
            simulating a system, 2) adjust the constant zone
            temperatures specified in LOADS, 3) simulate the thermostat
            schedules (but not the equipment), and 4) tabulate energy
            consumption by ZONE (or group of ZONEs). SUM is not a
            miscellaneous SYSTEM-TYPE for UNCONDITIONED zones.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">UNCONDITIONEO
            ZONEs should be assigned to another SYSTEM.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><b><span
style="font-size:6.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:FR"><o:p> </o:p></span></b></p>
        <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
              lang="EN-GB">Christopher R. Jones</span></b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
            lang="EN-GB">, P.Eng.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
            lang="EN-GB">Technical Specialist<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
            lang="EN-GB">Sustainability & Energy<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><img
              id="Picture_x0020_15"
              src="cid:part1.AF146470.2C48BDF5@bellnet.ca" class=""
              height="37" width="78"></span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"><o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">T
            +1 416-644-0252<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">2300
            Yonge Street, Suite 2300<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">Toronto,
            ON M4P 1E4 Canada</span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
            lang="EN-GB"><br>
            <br>
          </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"><o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:EN-CA"><a
              href="wsp.com" moz-do-not-send="true"><span
                style="color:#0563C1">wsp.com</span></a><o:p></o:p></span></p>
        <p class="MsoNormal"><u><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:blue;mso-fareast-language:EN-CA"
              lang="EN-CA"><o:p><span style="text-decoration:none"> </span></o:p></span></u></p>
        <p class="MsoNormal" style="text-autospace:none"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#7F7F7F;mso-fareast-language:FR"><o:p> </o:p></span></b></p>
        <p class="MsoNormal" style="text-autospace:none"><i><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#6EA900;mso-fareast-language:FR">Please
              consider the environment before printing...<o:p></o:p></span></i></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"
            lang="EN-CA"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><b><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
            Equest-users
            [<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
            <b>On Behalf Of </b>Jing Hong via Equest-users<br>
            <b>Sent:</b> Wednesday, November 15, 2017 2:13 PM<br>
            <b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
            <b>Subject:</b> [Equest-users] Zones with different HVAC
            systems<o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <p class="MsoNormal">Dear All,<o:p></o:p></p>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">I have a building with more than one
              kind HVAC system. I have the first floor with VAV system,
              and the second floor only has ventilation fans running. So
              I made all the zones on Second Floor unconditioned, and
              choose SUM as air-side HVAC system for second floor.
              However, the Space Cool of no VAV for second floor is even
              higher than that of the whole VAV, which does not make
              sense to me. <br clear="all">
              <o:p></o:p></p>
            <div>
              <p class="MsoNormal">Do you know how the eQuest calculate
                Space Cool? Should The VAV energy consumption be Space
                Cool+Vent. Fans shown on the simulation output?<o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal">Thank you,<o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal">Jing<o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal"><o:p> </o:p></p>
            </div>
            <p class="MsoNormal">-- <o:p></o:p></p>
            <div>
              <div>
                <div>
                  <div>
                    <div>
                      <div>
                        <p class="MsoNormal">PhD Candidate, LEED AP BD+C<o:p></o:p></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><o:p> </o:p></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-size:9.5pt">School of
                            Architecture and Urban Planning</span><o:p></o:p></p>
                      </div>
                      <div>
                        <p class="MsoNormal">University of
                          Wisconsin-Milwaukee<o:p></o:p></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><o:p> </o:p></p>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <hr>
      <font size="1" face="Arial" color="Gray"><br>
        <br>
        NOTICE: This communication and any attachments ("this message")
        may contain information which is privileged, confidential,
        proprietary or otherwise subject to restricted disclosure under
        applicable law. This message is for the sole use of the intended
        recipient(s). Any unauthorized use, disclosure, viewing,
        copying, alteration, dissemination or distribution of, or
        reliance on, this message is strictly prohibited. If you have
        received this message in error, or you are not an authorized or
        intended recipient, please notify the sender immediately by
        replying to this message, delete this message and all copies
        from your e-mail system and destroy any printed copies. You are
        receiving this communication because you are listed as a current
        WSP contact. Should you have any questions regarding WSP's
        electronic communications policy, please consult our Anti-Spam
        Commitment at
        <a href="http://www.wsp.com/casl" moz-do-not-send="true">www.wsp.com/casl</a>.
        For any concern or if you believe you should not be receiving
        this message, please forward this message to
        <a href="mailto:caslcompliance@wsp.com" moz-do-not-send="true">caslcompliance@wsp.com</a>
        so that we can promptly address your request. Note that not all
        messages sent by WSP qualify as commercial electronic messages.
        <br>
        <br>
        AVIS : Ce message, incluant tout fichier l'accompagnant (« le
        message »), peut contenir des renseignements ou de l'information
        privilégiés, confidentiels, propriétaires ou à divulgation
        restreinte en vertu de la loi. Ce message est destiné à l'usage
        exclusif du/des destinataire(s) voulu(s). Toute utilisation non
        permise, divulgation, lecture, reproduction, modification,
        diffusion ou distribution est interdite. Si vous avez reçu ce
        message par erreur, ou que vous n'êtes pas un destinataire
        autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement
        et détruire le message et toute copie électronique ou imprimée.
        Vous recevez cette communication car vous faites partie des
        contacts de WSP. Si vous avez des questions concernant la
        politique de communications électroniques de WSP, veuillez
        consulter notre Engagement anti-pourriel au <a
          href="http://www.wsp.com/lcap" moz-do-not-send="true">
          www.wsp.com/lcap</a>. Pour toute question ou si vous croyez
        que vous ne devriez pas recevoir ce message, prière de le
        transférer au
        <a href="mailto:conformitelcap@wsp.com" moz-do-not-send="true">conformitelcap@wsp.com</a>
        afin que nous puissions rapidement traiter votre demande. Notez
        que ce ne sont pas tous les messages transmis par WSP qui
        constituent des messages electroniques commerciaux.
        <br>
      </font><br>
      <font size="0.10" face="Arial" color="WhiteSmoke"><br>
        <br>
        -LAEmHhHzdJzBlTWfa4Hgs7pbKl </font>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>