    You shouldn't have overlapping walls.  There should be a wall
    between the 2 zones that is common and in 2 areas if you used the
    plenum setup to deal with the height differences.  It will be an
    interior wall initially but can be changed to exterior if you delete
    exterior walls in the second zone.  You will also need to make the
    ceiling below a roof which means what you need to reflect the zones
    in the floor above and the floor below.  I assume you are dealing
    with a portion of the floor with the different foot prints from a
    week or so ago.<br>
    Normally I don't use the 2 shell method but sometimes it was the
    only way forward and have.  It seemed to me you wouldn't have to do
    that in this case.  Having the 2 zones allows you to have them at
    the same conditions or different.  By adding in the plenum spaces
    gives you 4 zones.  What you are doing is trying to is mimic the
    constructions and boundary conditions.  By that I meant is the
    surface adjacent to another zone or to the exterior.  That is the
    only condition you need to worry about at this time.<br>
    A few things are coming back but it has been a while since I have
    done this.  To eQuest a wall is just a line, typically taken as the
    centre line of the wall.  It has no thickness.  This can trip you up
    if you are using 2 shells.  They have to occupy the same space
    before you delete one.  I know I had to play with the wireframe to
    make sure I was deleting the right wall.  I also remember sometimes
    having to adjust the polygons as they have a direction.  That may
    present itself when changing an interior wall to exterior.<br>
    In short I'm not exactly sure what you are trying to do.  A picture
    or sketch might help.  Some of these work arounds are tricky and my
    time is short.  I'm working from memory to sketch the concept for
    you.  So there might be a few details that have escaped me.<br>
    Bruce<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 11/9/2017 11:47 AM, Jing Hong wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:20171109164751.OABR22643.toroondcmxzimta02-srv.bellnexxia.net@tordcvbicmrk01">
      <div dir="ltr">Hi Bruce,
        <div><br>
        </div>
        <div>Thanks for your patient explanation. Yes, I did split a
          room into two zones (and also two shells). And then deleted
          the overlapping exterior walls, which should not exist.  When
          you said "<span style="font-size:12.8px">reflect what is
            actually happening at the boundary</span>". Does that mean
          you make the adjacent two zones the same condition and work as
          one zone?  Could you please clarify how to set that up? I
          really appreciate. </div>
        <div><br>
        </div>
        <div>Jing</div>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Thu, Nov 9, 2017 at 9:21 AM, Bruce
          Easterbrook <span dir="ltr"><<a
              href="mailto:bruce5@bellnet.ca" target="_blank"
              moz-do-not-send="true">bruce5@bellnet.ca</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div text="#000000" bgcolor="#FFFFFF"> Hi Jing,<br>
              It is a little difficult to tell from your explanation of
              what you are doing but it doesn't seem like the correct
              approach to me.  eQuest will allow you to have different
              zones for the conductive/thermal model and then different
              zone configurations for the HVAC model.  Differing
              constructions I do as separate zones.  It makes putting
              all the boxes together.  All surfaces have to be accounted
              for.  Everything has to conduct to another zone or to the
              exterior.  Even if you miss a 1" strip the model will
              throw errors.  When you build your model I find it better
              to err on the side of too many zones.  Your picks of areas
              for zones need to initially reflect how the building is
              constructed but also thinking of how the building is going
              to be heated and cooled.<br>
              I would split that zone you are working on into 2.  Each
              portion will cover the different ceiling height.  Give
              each zone a plenum and make it the height of the
              difference in the zone heights.  That will allow you to
              split the wall into 2 different sections and give each one
              different properties.  It also gives you 2 ceilings.  Make
              the one with the higher ceiling an air wall type
              boundary.  Adjust the plenum wall construction to reflect
              what is actually happening at the boundary.  Adjust the
              ceiling construction of the room/plenum of the lower zone,
              delete what you don't need.  Later when doing the HVAC you
              can put both of these zones on the same unit.  So you
              don't necessarily zone a building according to the
              proposed HVAC system.  You have to take the
              discontinuities into account and add zones to make it
              easier to model.  Every thermal box has to be perfectly
              closed or eQuest will stall on you.  You are lucky it
              tossed warning messages, these are clues to what you have
              missed.  You are close.  It is really bad when you crash
              and don't get clues.<br>
              Good luck.  You seem to be coming along fine.  One other
              tip, stay in the detailed wizard as long as possible. 
              Ignore windows and just leave them as general areas until
              you get everything else worked out.  Save files lots so
              you can go back if something happens.  They are like
              restore points.  The closer you are to the crash the less
              work you lose.  Plus, projects change once everyone starts
              looking at the modelling results, you find more efficient
              ways and need to be able to adjust your model.<br>
              Bruce Easterbrook P.Eng.<br>
              Abode Engineering
              <div>
                <div class="h5"><br>
                  <br>
                  <div class="m_7637244212381738145moz-cite-prefix">On
                    11/9/2017 9:17 AM, Jing Hong via Equest-users wrote:<br>
                  </div>
                </div>
              </div>
              <blockquote type="cite">
                <div>
                  <div class="h5">
                    <div dir="ltr">Dear All,
                      <div><br>
                      </div>
                      <div>I built up two shells for a room with two
                        different ceiling heights. And then deleted the
                        exterior walls. Now the BDL Load File Log shows
                        some warnings of no delayed wall, no delay
                        ceiling for those spaces. Should I ignore those
                        warnings? Or try to fix them? Am I doing
                        correctly to deal with a zone with different
                        heights in this way?</div>
                      <div><br>
                      </div>
                      <div>Thanks,</div>
                      <div><br>
                      </div>
                      <div>Jing<br clear="all">
                        <div><br>
                        </div>
                        -- <br>
                        <div
                          class="m_7637244212381738145gmail_signature"
                          data-smartmail="gmail_signature">
                          <div dir="ltr">
                            <div>
                              <div dir="ltr">
                                <div dir="ltr">
                                  <div>PhD Candidate, LEED AP BD+C</div>
                                  <div><span style="font-size:12.8px"><br>
                                    </span></div>
                                  <div><span style="font-size:12.8px">School
                                      of Architecture and Urban Planning</span></div>
                                  <div>University of Wisconsin-Milwaukee</div>
                                  <div><br>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                    <br>
                    <fieldset
                      class="m_7637244212381738145mimeAttachmentHeader"></fieldset>
                    <br>
                  </div>
                </div>
                <pre>______________________________<wbr>_________________
Equest-users mailing list
<a class="m_7637244212381738145moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/<wbr>listinfo.cgi/equest-users-<wbr>onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="m_7637244212381738145moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank" moz-do-not-send="true">EQUEST-USERS-UNSUBSCRIBE@<wbr>ONEBUILDING.ORG</a>
</pre>
              </blockquote>
              <br>
            </div>
          </blockquote>
        </div>
        <br>
        <br clear="all">
        <div><br>
        </div>
        -- <br>
        <div class="gmail_signature" data-smartmail="gmail_signature">
          <div dir="ltr">
            <div>
              <div dir="ltr">
                <div dir="ltr">
                  <div>PhD Candidate, LEED AP BD+C</div>
                  <div><span style="font-size:12.8px"><br>
                    </span></div>
                  <div><span style="font-size:12.8px">School of
                      Architecture and Urban Planning</span></div>
                  <div>University of Wisconsin-Milwaukee</div>
                  <div><br>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
    </blockquote>
    <br>
  </body>
</html>