<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    Hi Jing,<br>
    It is a little difficult to tell from your explanation of what you
    are doing but it doesn't seem like the correct approach to me. 
    eQuest will allow you to have different zones for the
    conductive/thermal model and then different zone configurations for
    the HVAC model.  Differing constructions I do as separate zones.  It
    makes putting all the boxes together.  All surfaces have to be
    accounted for.  Everything has to conduct to another zone or to the
    exterior.  Even if you miss a 1" strip the model will throw errors. 
    When you build your model I find it better to err on the side of too
    many zones.  Your picks of areas for zones need to initially reflect
    how the building is constructed but also thinking of how the
    building is going to be heated and cooled.<br>
    I would split that zone you are working on into 2.  Each portion
    will cover the different ceiling height.  Give each zone a plenum
    and make it the height of the difference in the zone heights.  That
    will allow you to split the wall into 2 different sections and give
    each one different properties.  It also gives you 2 ceilings.  Make
    the one with the higher ceiling an air wall type boundary.  Adjust
    the plenum wall construction to reflect what is actually happening
    at the boundary.  Adjust the ceiling construction of the room/plenum
    of the lower zone, delete what you don't need.  Later when doing the
    HVAC you can put both of these zones on the same unit.  So you don't
    necessarily zone a building according to the proposed HVAC system. 
    You have to take the discontinuities into account and add zones to
    make it easier to model.  Every thermal box has to be perfectly
    closed or eQuest will stall on you.  You are lucky it tossed warning
    messages, these are clues to what you have missed.  You are close. 
    It is really bad when you crash and don't get clues.<br>
    Good luck.  You seem to be coming along fine.  One other tip, stay
    in the detailed wizard as long as possible.  Ignore windows and just
    leave them as general areas until you get everything else worked
    out.  Save files lots so you can go back if something happens.  They
    are like restore points.  The closer you are to the crash the less
    work you lose.  Plus, projects change once everyone starts looking
    at the modelling results, you find more efficient ways and need to
    be able to adjust your model.<br>
    Bruce Easterbrook P.Eng.<br>
    Abode Engineering<br>
    <br>
    <div class="moz-cite-prefix">On 11/9/2017 9:17 AM, Jing Hong via
      Equest-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:20171109141831.HHOY19211.toroondcmxzimta03-srv.bellnexxia.net@tordcvbicmrk02">
      <div dir="ltr">Dear All,
        <div><br>
        </div>
        <div>I built up two shells for a room with two different ceiling
          heights. And then deleted the exterior walls. Now the BDL Load
          File Log shows some warnings of no delayed wall, no delay
          ceiling for those spaces. Should I ignore those warnings? Or
          try to fix them? Am I doing correctly to deal with a zone with
          different heights in this way?</div>
        <div><br>
        </div>
        <div>Thanks,</div>
        <div><br>
        </div>
        <div>Jing<br clear="all">
          <div><br>
          </div>
          -- <br>
          <div class="gmail_signature" data-smartmail="gmail_signature">
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div dir="ltr">
                    <div>PhD Candidate, LEED AP BD+C</div>
                    <div><span style="font-size:12.8px"><br>
                      </span></div>
                    <div><span style="font-size:12.8px">School of
                        Architecture and Urban Planning</span></div>
                    <div>University of Wisconsin-Milwaukee</div>
                    <div><br>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>