    With the speed this field is moving several of the main standards
    are under continuous review and have a very large list of addenda. 
    Many times something that was a problem in application or thought
    process or intent in an earlier version of the standard is debated
    as an addendum, if approved it is accepted.  All these adjustments
    and fixes are wrapped into the next version.  So you could find the
    answer to your question in a much later version where the have
    really pinned down the wording so everything is clear.   In my
    humble opinion this new clarity would apply to all previous versions
    because it is logic and application.  It doesn't always apply to
    moving the bar higher which is what you are concerned with because
    your project is 2007.  There also might be even more clarification
    in a even newer version because as these standards get applied by
    more modeller's over an increasing array of buildings and projects
    cracks will show and they get fixed.  Also the previous projects are
    now built and everyone can see how they are working in the field. 
    What works, what doesn't and why and more addenda.<br>
    The small experiments done on the differences in technique show
    there is very little difference in the effect of the approaches. 
    Maybe a discussion with the reviewer might show some illumination to
    the issue.  It is a rapidly evolving standard and that makes it hard
    to stay current with all the nuances.<br>
    Bruce Easterbrook P.Eng.<br>
    Abode Engineering<br>
    <br>
    <div class="moz-cite-prefix">On 4/24/2017 3:43 AM, Pasha
      Korber-Gonzalez wrote:<br>
    </div>
    <blockquote
cite="mid:20170424074508.BWPI7399.toroondcmxzimta03-srv.bellnexxia.net@tordcvbicmrk03"
      type="cite">
      <div dir="ltr">Hi All-- Thank you for this in depth discussion and
        taking time to go over all of this.  (I was away from work for a
        few days, thus my delayed response.)
        <div><br>
        </div>
        <div>I agree with the commentary regarding how REAL LIFE
          operations happen in VAV systems, and yes modulating airflow
          is the first approach.  However, i did always find it odd that
          temp first was stated in Appendix G, but who am I to question
          Appendix G, right?<br>
          <br>
          As for the discussion of direction from the PNNL User's
          Manual-- that is interesting, and I hadn't seen that document
          prior to now because I am still only working on projects that
          reference ASHRAE 90.1-2007.  Therefore I have had no need or
          time to look at the 2010 version or any supporting
          docs...which brings us to the next debate:</div>
        <div><br>
        </div>
        <div>Why should anyone be referencing a 2010 version document
          for guidance for a 2007 version compliance model/project? 
          Therefore it seems prudent to stand firm to follow exactly
          what the governed/reference standard states-explicitly which
          is "temperature reset."  </div>
        <div><br>
        </div>
        <div>But then-  Thank you Daric for confirming that the 2007
          version User's Manual doesn't specifically guide us on how to
          meet the criteria of that section.  AND thank you Daric for
          also conducting a minor experiment on your model.  (I will do
          the same with a couple of mine this week.) </div>
        <div><br>
        </div>
        <div>So based on what I have learned from this awesome
          discussion/debate, I will assume that my third party reviewer
          (non GBCI group) was indeed referencing the PNNL User's Manual
          for the 2010 version, possibly out of habit, and/or not even
          aware that the LEED guided project they were contracted for
          reviewing (my model, which I was contracted to produce by the
          Architect & owner) is in fact registered as a LEED 2009
          project that is referencing and following ASHRAE 90.1-2007
          version.</div>
        <div><br>
        </div>
        <div>Hmm, I'm in a quandary of how to take action for my model
          based on this questionable review comment- who is not the
          actual LEED reviewer.  This seems like a weird situation to be
          in...</div>
        <div><br>
        </div>
        <div>Thanks again for all your input on this topic!</div>
        <div><br>
        </div>
        <div>Pasha Korber</div>
        <div>Ph 308-763-1593</div>
        <div><br>
        </div>
        <div><a moz-do-not-send="true"
            href="http://www.korberenergy.com">www.korberenergy.com</a></div>
        <div><br>
        </div>
        <div class="gmail_extra"><br>
          <div class="gmail_quote">On Fri, Apr 21, 2017 at 8:49 AM,
            Daric Adair <span dir="ltr"><<a moz-do-not-send="true"
                href="mailto:Daric.Adair@hei-eng.com" target="_blank">Daric.Adair@hei-eng.com</a>></span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin:0 0 0
              .8ex;border-left:1px #ccc solid;padding-left:1ex">
              <div bgcolor="white" link="#0563C1" vlink="#954F72"
                lang="EN-US">
                <div class="m_5603468327082964812WordSection1">
                  <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Agreed
                      on ventilation. But 90.1 Appendix G addresses the
                      VAV box minimums for Baseline models in
                      G3.1.3.13/G3.1.3.14. The box minimums must take
                      ventilation into account.</span></p>
                  <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Fan
                      energy is a major element. Several of my more
                      recent models have had fan energy on par with
                      heating and cooling energy. Both for baseline and
                      proposed models. Fans unload nicely…which is a
                      blessing and a curse.</span></p>
                  <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                  <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Running
                      some quick diagnostic tests on a couple of my most
                      recent models, the difference in the two control
                      strategies didn’t yield a massive difference. But
                      one test does not a trend make….in any sense, the
                      Temperature Frist reset set was 0.29% lower on a
                      cost basis…</span></p>
                  <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                  <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Another
                      factor specific to eQuest, when using Airflow
                      first control, is the ‘</span>MIN-RESET-FLOW’
                    <span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">variable.
                      This defaults to 0.66. Which from the help files
                      seems to indicate that the it will only allow the
                      fan to reset to this level (0.66 in this case/by
                      default) before starting temperature reset.
                      Modifying this value  impacts when the system will
                      start to modify the DAT. This did have an impact
                      on the results, but not very underwhelming at best
                      from my very limited testing pool….</span></p>
                  <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                  <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">In
                      short, it gets back to which element should unload
                      first – fans vs chiller/boiler. Fan curves are
                      dictated for Appendix G (and Fan laws). Chiller
                      curves are not provided/dictated for Appendix G,
                      but performance is. Similar for boilers. In a
                      ‘real’ system with actual equipment curves, it
                      would be a balance between savings from the fan
                      slowing vs savings from central plant equipment
                      unloadng (which has more complex relationships).</span></p>
                  <span class="">
                    <div>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546a;text-transform:uppercase"> </span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546a;text-transform:uppercase"> </span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546a;text-transform:uppercase"> </span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546a;text-transform:uppercase"> </span></p>
                      <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Thanks,</span></p>
                      <p class="MsoNormal"><span
                          style="font-size:10.0pt;font-family:"Arial
Black",sans-serif;text-transform:uppercase">DARIC R. ADAIR</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1f497d">
                        </span><span
                          style="font-size:8.0pt;font-family:"Arial
Black",sans-serif;text-transform:uppercase"> PE, C.E.M.</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1f497d">
                          <br>
                        </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#566c11">Henderson
                            Engineers, Inc. | </span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#566c11">Mechanical
                          Engineer, Energy Analyst</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1f497d"><br>
                        </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;font-variant:small-caps">dir</span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif"> <a
                            moz-do-not-send="true"
                            href="tel:%28913%29%20742-5530"
                            value="+19137425530" target="_blank">913 742
                            5530</a> 
                          <b><span style="font-variant:small-caps">tel</span></b>
                          <a moz-do-not-send="true"
                            href="tel:%28913%29%20742-5000"
                            value="+19137425000" target="_blank">913 742
                            5000</a>  <b><span
                              style="font-variant:small-caps">fax</span></b>
                          <a moz-do-not-send="true"
                            href="tel:%28913%29%20742-5001"
                            value="+19137425001" target="_blank">913 742
                            5001</a> 
                          <b><span style="font-variant:small-caps">tx id</span></b>
                          #F-001236  <b><span
                              style="font-variant:small-caps">email</span></b>
                          <a moz-do-not-send="true"
                            href="mailto:daric.adair@hei-eng.com"
                            target="_blank">daric.adair@hei-eng.com</a></span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1f497d"> 
                          <a moz-do-not-send="true"
                            href="http://www.hei-eng.com/"
                            target="_blank"><b><span
                                style="font-size:8.0pt;color:#566c11">www.hei-eng.com</span></b></a>
                          <br>
                        </span><span
                          style="font-size:7.5pt;font-family:"Arial",sans-serif">Licensed
                          in KS.</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1f497d"> </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"></span></p>
                    </div>
                    <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                  </span>
                  <div>
                    <div style="border:none;border-top:solid #e1e1e1
                      1.0pt;padding:3.0pt 0in 0in 0in">
                      <p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:windowtext">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:windowtext">
                          Bruce Easterbrook [mailto:<a
                            moz-do-not-send="true"
                            href="mailto:bruce5@bellnet.ca"
                            target="_blank">bruce5@bellnet.ca</a>]
                          <br>
                          <b>Sent:</b> Thursday, April 20, 2017 10:24 PM<br>
                          <b>To:</b> Daric Adair <<a
                            moz-do-not-send="true"
                            href="mailto:Daric.Adair@hei-eng.com"
                            target="_blank">Daric.Adair@hei-eng.com</a>>;
                          Jennings, Coles <Coles.Jennings@<wbr>MasonandHanger.com>;
                          PKConsulting <<a moz-do-not-send="true"
                            href="mailto:pasha.pkconsulting@gmail.com"
                            target="_blank">pasha.pkconsulting@gmail.com</a>><wbr>;
                          Shaun Martin <<a moz-do-not-send="true"
                            href="mailto:smartin@shaunmartinconsulting.com"
                            target="_blank">smartin@<wbr>shaunmartinconsulting.com</a>></span></p>
                      <div>
                        <div class="h5"><br>
                          <b>Cc:</b> <a moz-do-not-send="true"
                            href="mailto:equest-users@onebuilding.org"
                            target="_blank">equest-users@onebuilding.org</a><br>
                          <b>Subject:</b> Re: [Equest-users] Supply Air
                          Temp Reset Interpretation Please...?</div>
                      </div>
                    </div>
                  </div>
                  <div>
                    <div class="h5">
                      <p class="MsoNormal"> </p>
                      <p class="MsoNormal" style="margin-bottom:12.0pt">I
                        may be all wet here but one other consideration
                        is OA.  If there is no DOAS then the VAV system
                        is supplying the OA to the zones.  A drop in
                        flow could reduce the OA below minimum
                        requirements for the zones.  A temp first reset
                        would maintain airflow and the OA air portion. 
                        With energy consumption, cooling and heating are
                        the most expensive components of the flow and
                        then the fan energy.  This is why economizers
                        are very energy efficient in the right
                        conditions.<br>
                        So ultimately you have to meet ASHRAE 90.1 and
                        also 62.1.  These are also baseline systems,
                        just setting the low bar before we start to
                        tinker.  All points and justification come from
                        the magnitude you can exceed the baseline.  The
                        baseline has been ratcheting up, things are not
                        as easy now and almost all the low hanging fruit
                        is gone.<br>
                        I was reading an article in the online Journal
                        this morning from 2014.  Part of it concerned
                        fan efficiency, FC, AF and plenum with direct
                        and belt drive.  Now that efficiency is getting
                        right down to belt slippage you know there isn't
                        much left to play with.<br>
                        Bruce Easterbrook P.Eng.<br>
                        Abode Engineering</p>
                      <div>
                        <p class="MsoNormal">On 4/20/2017 6:54 PM, Daric
                          Adair via Equest-users wrote:</p>
                      </div>
                      <blockquote
                        style="margin-top:5.0pt;margin-bottom:5.0pt">
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">All;</span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Great
                            discussion.</span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">For
                            context, the text of G3.1.3.12 is: “Supply
                            Air Temperature Reset (System 5 through8).
                            The air temperature for cooling shall be
                            reset higher by 5F under the minimum cooling
                            load conditions.”</span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Stepping
                            back, the reset is said to occur at ‘the
                            minimum cooling load condition.’ Thinking
                            through how a typlica/real VAV system will
                            control, the terminal box dampers will close
                            towards their minimum as the cooling load in
                            a zone decreases. In a ‘real’ building this
                            should cause the Supply fan to see a
                            pressure increase and slow down to get back
                            to its static pressure setpoint. At some
                            point if all of the boxes are at a minimum
                            position (aka, minimum cooling demand), the
                            Supply Air Temperature should/can be
                            increased.</span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Looking
                            through the above, this would indicate an
                            Air Flow first reset, before increasing the
                            discharge temperature.</span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Per
                            the eQuest help file, it would seem to
                            indicate that a ‘Temp-First’ approach
                            attempts to reset the temperature, without
                            modulating the fan down.  This seems fairly
                            odd in a ‘real’ system since in that if any
                            single zone calls for cooling, no reset
                            occurs, no energy saved. Even if it is a
                            Baseline, it should have some sort of gut
                            check to it. If it were a ‘real’ system and
                            going Prescriptive path, it would be subject
                            to Section 6.5.2. I didn’t see any
                            requirement (Mandatory or Prescriptive) for
                            DAT reset….(but I may be missing it….)</span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Therefore,
                            I’d think in a VAV system the Air-Flow first
                            modulation, then allow the DAT to reset
                            would be the intended path.</span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Another
                            minor bit of confusion here: The 90.1 ASHREA
                            User’s Manual does not offer much guidance
                            here. There is new guide from PNNL for the
                            90.1-2010 standard, which is what is also
                            mentioned below. Just want to clarify for
                            readers that these are two separate (and
                            both are useful) guides.</span></p>
                        <div>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546a;text-transform:uppercase"> </span></p>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546a;text-transform:uppercase"> </span></p>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546a;text-transform:uppercase"> </span></p>
                          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Thanks,</span></p>
                          <p class="MsoNormal"><span
                              style="font-size:10.0pt">DARIC R. ADAIR</span><span
                              style="font-size:8.0pt"> PE, C.E.M.</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1f497d"><br>
                            </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#566c11">Henderson
                                Engineers, Inc. | </span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#566c11">Mechanical
                              Engineer, Energy Analyst</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1f497d"><br>
                            </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;font-variant:small-caps">dir</span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif"> <a
                                moz-do-not-send="true"
                                href="tel:%28913%29%20742-5530"
                                value="+19137425530" target="_blank">913
                                742 5530</a> 
                              <b><span style="font-variant:small-caps">tel</span></b>
                              <a moz-do-not-send="true"
                                href="tel:%28913%29%20742-5000"
                                value="+19137425000" target="_blank">913
                                742 5000</a>  <b><span
                                  style="font-variant:small-caps">fax</span></b>
                              <a moz-do-not-send="true"
                                href="tel:%28913%29%20742-5001"
                                value="+19137425001" target="_blank">913
                                742 5001</a> 
                              <b><span style="font-variant:small-caps">tx
                                  id</span></b> #F-001236  <b><span
                                  style="font-variant:small-caps">email</span></b>
                              <a moz-do-not-send="true"
                                href="mailto:daric.adair@hei-eng.com"
                                target="_blank">daric.adair@hei-eng.com</a></span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1f497d"> 
                              <a moz-do-not-send="true"
                                href="http://www.hei-eng.com/"
                                target="_blank"><b><span
                                    style="font-size:8.0pt;color:#566c11">www.hei-eng.com</span></b></a>
                              <br>
                            </span><span
                              style="font-size:7.5pt;font-family:"Arial",sans-serif">Licensed
                              in KS.</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1f497d"> </span></p>
                        </div>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <div>
                          <div style="border:none;border-top:solid
                            #e1e1e1 1.0pt;padding:3.0pt 0in 0in 0in">
                            <p class="MsoNormal"><b><span
                                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                                Jennings, Coles via Equest-users [<a
                                  moz-do-not-send="true"
                                  href="mailto:equest-users@lists.onebuilding.org"
                                  target="_blank">mailto:equest-users@lists.<wbr>onebuilding.org</a>]
                                <br>
                                <b>Sent:</b> Thursday, April 20, 2017
                                10:38 AM<br>
                                <b>To:</b> PKConsulting <a
                                  moz-do-not-send="true"
                                  href="mailto:pasha.pkconsulting@gmail.com"
                                  target="_blank"><pasha.pkconsulting@gmail.com></a><wbr>;
                                Shaun Martin
                                <a moz-do-not-send="true"
                                  href="mailto:smartin@shaunmartinconsulting.com"
                                  target="_blank"><smartin@<wbr>shaunmartinconsulting.com></a><br>
                                <b>Cc:</b> <a moz-do-not-send="true"
                                  href="mailto:equest-users@onebuilding.org"
                                  target="_blank">equest-users@onebuilding.org</a><br>
                                <b>Subject:</b> Re: [Equest-users]
                                Supply Air Temp Reset Interpretation
                                Please...?</span></p>
                          </div>
                        </div>
                        <p class="MsoNormal"> </p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">I
                            wanted to chime in quickly, because this is
                            an interesting question that we’ve gone back
                            and forth on in my office as well.</span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">I
                            don’t agree with the stance that, because
                            the section is labelled supply air
                            temperature reset, therefore temperature
                            first is the correct input. Airflow
                            modulation is a given for VAV systems
                            (baseline systems 5 through 8), so the
                            question is not whether airflow modulates,
                            but what takes precedence between the
                            airflow modulation inherent in a VAV system
                            and the temperature modulation also required
                            by 90.1. The three possible combinations are
                            reflected in the available eQUEST inputs:
                            “temperature first,” “airflow first,” or
                            “simultaneous.”</span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">In
                            my view, the correct order of priority
                            between temperature and airflow modulation
                            is not something the standard directly
                            addresses. Absent clear direction in the
                            standard, I would then look for any <a
                              moz-do-not-send="true"
href="https://www.ashrae.org/standards-research--technology/standards-interpretations/interpretation-for-standard-90-1-2010https:/www.ashrae.org/standards-research--technology/standards-interpretations/interpretation-for-standard-90-1-2010"
                              target="_blank">
                              formal interpretations</a> of the standard
                            issued by ASHRAE, and if that still doesn’t
                            clear it up, then a user’s manual may be the
                            next best thing. A user’s manual such as the
                            PNNL manual at least provides specific
                            direction by a neutral third party, which is
                            often a great way to make a case to the
                            reviewing authority (GBCI reviewer, code
                            official, etc...).</span></p>
                        <p class="MsoNormal"><span
                            style="font-size:9.0pt;font-family:"Arial",sans-serif"><br>
                            <br>
                          </span><b><span
                              style="font-size:11.0pt;font-family:"Arial",sans-serif">Coles
                              Jennings</span></b><span
                            style="font-size:9.0pt;font-family:"Arial",sans-serif">
                            PE, BEMP, LEED AP BD+C
                            <br>
                            Sr. Energy Engineer, Building Sciences
                            Manager </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#ba0c2f">|
                          </span><span
                            style="font-size:9.0pt;font-family:"Arial",sans-serif">Mason
                            & Hanger
                            <br>
                            A Day & Zimmermann Company <br>
                            <b>D </b><a moz-do-not-send="true"
                              href="tel:%28804%29%20521-7045"
                              value="+18045217045" target="_blank">804.521.7045</a>
                          </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#ba0c2f">|
                          </span><b><span
                              style="font-size:9.0pt;font-family:"Arial",sans-serif">O
                            </span></b><span
                            style="font-size:9.0pt;font-family:"Arial",sans-serif"><a
                              moz-do-not-send="true"
                              href="tel:%28804%29%20285-4171"
                              value="+18042854171" target="_blank">804.285.4171</a>
                          </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#ba0c2f">|
                          </span><b><span
                              style="font-size:9.0pt;font-family:"Arial",sans-serif">F
                            </span></b><span
                            style="font-size:9.0pt;font-family:"Arial",sans-serif"><a
                              moz-do-not-send="true"
                              href="tel:%28804%29%20217-8520"
                              value="+18042178520" target="_blank">804.217.8520</a>
                            <br>
                            4880 Sadler Road, Suite 300 </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#ba0c2f">|
                          </span><span
                            style="font-size:9.0pt;font-family:"Arial",sans-serif">Glen
                            Allen, VA 23060
                            <br>
                            <a moz-do-not-send="true"
                              href="http://www.masonandhanger.com/"
                              target="_blank"><span
                                style="color:#224bf1;text-decoration:none">Mason
                                & Hanger</span></a>
                            <br>
                          </span><b><i><span
                                style="font-size:11.0pt;font-family:"Adobe
                                Garamond ;color:#BA0C2F",serif">We
                                do what we say.®</span></i></b><span
                            style="font-size:9.0pt;font-family:"Arial",sans-serif">
                            <br>
                            <br>
                              </span></p>
                        <div>
                          <div style="border:none;border-top:solid
                            #e1e1e1 1.0pt;padding:3.0pt 0in 0in 0in">
                            <p class="MsoNormal"><b><span
                                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                                Equest-users [<a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">mailto:equest-users-bounces@<wbr>lists.onebuilding.org</a>]
                                <b>On Behalf Of </b>PKConsulting via
                                Equest-users<br>
                                <b>Sent:</b> Thursday, April 20, 2017
                                11:19 AM<br>
                                <b>To:</b> Shaun Martin <<a
                                  moz-do-not-send="true"
                                  href="mailto:smartin@shaunmartinconsulting.com"
                                  target="_blank">smartin@<wbr>shaunmartinconsulting.com</a>><br>
                                <b>Cc:</b> <a moz-do-not-send="true"
                                  href="mailto:equest-users@lists.onebuilding.org"
                                  target="_blank">equest-users@lists.<wbr>onebuilding.org</a><br>
                                <b>Subject:</b> Re: [Equest-users]
                                Supply Air Temp Reset Interpretation
                                Please...?</span></p>
                          </div>
                        </div>
                        <p class="MsoNormal"> </p>
                        <div>
                          <p class="MsoNormal">Yes!  Thanks Shaun- even
                            one count of validation makes me feel not so
                            crazy
                            <span style="font-family:"Segoe UI
                              Symbol",sans-serif">😜</span>,
                             especially from an old colleague.  Thank
                            you- thank you.  Why is there too much room
                            for interpretation on these things?  I
                            accept that the User Manual is helpful in
                            most scenarios- but this is one instance
                            that just seems backwards.  If it is
                            supposed to airflow reset controls,  then
                            why is the section written with "Supply Air
                            Temperature Reset"?</p>
                        </div>
                        <div
                          id="m_5603468327082964812AppleMailSignature">
                          <p class="MsoNormal"> </p>
                        </div>
                        <div
                          id="m_5603468327082964812AppleMailSignature">
                          <p class="MsoNormal">I appreciate your
                            validation of my interpretation.</p>
                        </div>
                        <div
                          id="m_5603468327082964812AppleMailSignature">
                          <p class="MsoNormal"><br>
                            Pasha</p>
                          <div>
                            <p class="MsoNormal">Ph: <a
                                moz-do-not-send="true"
                                href="tel:%28308%29%20763-1593"
                                value="+13087631593" target="_blank">308-763-1593</a></p>
                          </div>
                        </div>
                        <div>
                          <p class="MsoNormal"
                            style="margin-bottom:12.0pt"><br>
                            On Apr 20, 2017, at 8:29 AM, Shaun Martin
                            <<a moz-do-not-send="true"
                              href="mailto:smartin@shaunmartinconsulting.com"
                              target="_blank">smartin@<wbr>shaunmartinconsulting.com</a>>
                            wrote:</p>
                        </div>
                        <blockquote
                          style="margin-top:5.0pt;margin-bottom:5.0pt">
                          <div>
                            <p class="MsoNormal"><span
                                style="font-size:11.0pt;font-family:"Calibri",sans-serif">Hi,</span></p>
                            <p class="MsoNormal"><span
                                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span></p>
                            <p class="MsoNormal"><span
                                style="font-size:11.0pt;font-family:"Calibri",sans-serif">I
                                think the Standard is quite clear about
                                resetting temperature, and says nothing
                                about modulating airflow.  The user
                                manual seems to be wrong.</span></p>
                            <p class="MsoNormal"><span
                                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span></p>
                            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Shaun
                                Martin LEED-AP, BEMP</span></p>
                            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Principal</span></p>
                            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Shaun
                                Martin Consulting</span></p>
                            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">#90
                                – 425 Carrall Street</span></p>
                            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Vancouver,
                                BC  V6B 6E3</span></p>
                            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">p.
                                <a moz-do-not-send="true"
                                  href="tel:%28604%29%20789-1095"
                                  value="+16047891095" target="_blank">604-789-1095</a></span></p>
                            <p class="MsoNormal"><span
                                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span></p>
                            <p class="MsoNormal"><span
                                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span></p>
                            <p class="MsoNormal"><span
                                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span></p>
                            <p class="MsoNormal"><a
                                moz-do-not-send="true"
                                name="m_5603468327082964812__MailEndCompose"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span></a></p>
                            <div>
                              <div style="border:none;border-top:solid
                                #e1e1e1 1.0pt;padding:3.0pt 0in 0in 0in">
                                <p class="MsoNormal"><b><span
                                      style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                                    Equest-users [<a
                                      moz-do-not-send="true"
                                      href="mailto:equest-users-bounces@lists.onebuilding.org"
                                      target="_blank">mailto:equest-users-bounces@<wbr>lists.onebuilding.org</a>]
                                    <b>On Behalf Of </b>PKConsulting
                                    via Equest-users<br>
                                    <b>Sent:</b> Thursday, April 20,
                                    2017 7:12 AM<br>
                                    <b>To:</b> Jones, Christopher <<a
                                      moz-do-not-send="true"
                                      href="mailto:Christopher.r.Jones@wspgroup.com"
                                      target="_blank">Christopher.r.Jones@wspgroup.<wbr>com</a>><br>
                                    <b>Cc:</b> <a
                                      moz-do-not-send="true"
                                      href="mailto:equest-users@lists.onebuilding.org"
                                      target="_blank">equest-users@lists.<wbr>onebuilding.org</a><br>
                                    <b>Subject:</b> Re: [Equest-users]
                                    Supply Air Temp Reset Interpretation
                                    Please...?</span></p>
                              </div>
                            </div>
                            <p class="MsoNormal"> </p>
                            <div>
                              <p class="MsoNormal">Thanks for the
                                feedback-  so if the justification for
                                the approach is solely based on the user
                                manual explanation- I can accept that. 
                                I'll cross reference it for the 2007
                                user manual to put it in my notes.</p>
                            </div>
                            <div>
                              <p class="MsoNormal"> </p>
                            </div>
                            <div>
                              <p class="MsoNormal">I've always used
                                air-flow first as a standard reset for
                                all my design energy models, What is
                                counter-intuitive here is that the title
                                of the Appendix G section specifically
                                states 'reset-temp', so why should we
                                not take the section text literally? 
                                I've always humbly assumed that the
                                ASHRAE standard writers know more than
                                me.  After all these years of creating
                                Baseline conforming models (or so I
                                thought),  this makes me feel lost all
                                over again.  AND is it not possible to
                                apply code standard requirements without
                                the use of the User Manual?   </p>
                            </div>
                            <div>
                              <p class="MsoNormal"> </p>
                            </div>
                            <div>
                              <p class="MsoNormal"
                                style="margin-bottom:12.0pt">Thankful-
                                but-frustrated,</p>
                              <div>
                                <p class="MsoNormal">Pasha</p>
                                <div>
                                  <p class="MsoNormal">Ph: <a
                                      moz-do-not-send="true"
                                      href="tel:%28308%29%20763-1593"
                                      value="+13087631593"
                                      target="_blank">308-763-1593</a></p>
                                </div>
                              </div>
                            </div>
                            <div>
                              <p class="MsoNormal"
                                style="margin-bottom:12.0pt"><br>
                                On Apr 20, 2017, at 6:48 AM, Jones,
                                Christopher <<a
                                  moz-do-not-send="true"
                                  href="mailto:Christopher.r.Jones@wspgroup.com"
                                  target="_blank">Christopher.r.Jones@wspgroup.<wbr>com</a>>
                                wrote:</p>
                            </div>
                            <blockquote
                              style="margin-top:5.0pt;margin-bottom:5.0pt">
                              <div>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">I
                                    had always assumed temperature first
                                    but reading the PNNL 90.1-2010
                                    Performance Rating Method Reference
                                    Manual, 3.121 (pdf page 151), it
                                    states “For systems 5 through 8, the
                                    air temperature for cooling shall be
                                    reset higher by 5°F under the
                                    minimum cooling load conditions
                                    using a reset by warmest zone,
                                    airflow first strategy.”</span></p>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">The
                                    manual states that the airflow first
                                    strategy minimizes zone reheat coil
                                    energy ( or overcooling) and central
                                    chiller energy consumption at the
                                    cost of possible increased fan
                                    energy. </span></p>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Unfortunately,
                                    the reviewer may have a case.
                                  </span></p>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"
                                    lang="EN-CA"> </span></p>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"><image001.jpg></span></p>
                                <p class="MsoNormal"><b><span
style="font-size:6.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></b></p>
                                <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d"
                                      lang="EN-GB">Christopher R. Jones</span></b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d"
                                    lang="EN-GB">, P.Eng.</span></p>
                                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d"
                                    lang="EN-GB">Technical Specialist</span></p>
                                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d"> </span></p>
                                <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d"
                                      lang="EN-GB">WSP Canada Inc.</span></b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d"
                                    lang="EN-GB"><br>
                                  </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d">2300
                                    Yonge Street, Suite 2300</span></p>
                                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d">Toronto,
                                    ON M4P 1E4 Canada</span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d"
                                    lang="EN-GB"><br>
                                  </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d">T
                                    <a moz-do-not-send="true"
                                      href="tel:%28416%29%20644-0252"
                                      value="+14166440252"
                                      target="_blank">+1 416-644-0252</a></span></p>
                                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d"> </span></p>
                                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1f497d"><a
                                      moz-do-not-send="true"
href="https://urldefense.proofpoint.com/v2/url?u=http-3A__www.wspgroup.ca_&d=DwMFaQ&c=xB5UQg5qXm2axe_t44neldV-XNditz6D2ZXZLA0vHlE&r=JrIPsTq2z-_669uhqn51VqSZFL7dpX6NqxKBTKpeQZ9m5XksAJHnQhCI_rEcbMFG&m=TUl4CO4lm0_JnjocmrzLbupzOeFu-9zJ4Wttnq-IxpY&s=wcUq0_D9t-Xi40LrszT5MooY6bxaUqaU8_S_1WcmUOY&e="
                                      target="_blank"><span
                                        style="color:blue">www.wspgroup.ca</span></a></span></p>
                                <p class="MsoNormal"
                                  style="text-autospace:none"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#7f7f7f"> </span></b></p>
                                <p class="MsoNormal"
                                  style="text-autospace:none"><i><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#6ea900">Please
                                      consider the environment before
                                      printing...</span></i></p>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"
                                    lang="EN-CA"> </span></p>
                                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"> </span></p>
                                <p class="MsoNormal"><b><span
                                      style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                                    Equest-users [<a
                                      moz-do-not-send="true"
                                      href="mailto:equest-users-bounces@lists.onebuilding.org"
                                      target="_blank">mailto:equest-users-bounces@<wbr>lists.onebuilding.org</a>]
                                    <b>On Behalf Of </b>Pasha
                                    Korber-Gonzalez via Equest-users<br>
                                    <b>Sent:</b> Thursday, April 20,
                                    2017 3:59 AM<br>
                                    <b>To:</b> eQUEST Users List <<a
                                      moz-do-not-send="true"
                                      href="mailto:equest-users@lists.onebuilding.org"
                                      target="_blank">equest-users@lists.<wbr>onebuilding.org</a>><br>
                                    <b>Subject:</b> [Equest-users]
                                    Supply Air Temp Reset Interpretation
                                    Please...?</span></p>
                                <p class="MsoNormal"> </p>
                                <div>
                                  <p class="MsoNormal">Hello--- I
                                    received this note from a fellow
                                    energy model reviewer (non-LEED
                                    review comment) regarding my
                                    Baseline energy model that is
                                    supposed to be compliant with
                                    Appendix G.  I disagree with what
                                    they are saying.  I appreciate your
                                    feedback please and verification if
                                    in fact I am wrong in how I am
                                    interpreting Section G3.1.3.12.</p>
                                  <div>
                                    <p class="MsoNormal"> </p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"> </p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal">"We believe
                                      TEMP-FIRST supply air reset
                                      control strategy is not the
                                      correct interpretation of
                                      G3.1.3.12 – rather, AIRFLOW-FIRST
                                      should be used."</p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"> </p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"> </p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal">Thanks!</p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal"> </p>
                                  </div>
                                  <div>
                                    <p class="MsoNormal">Pasha</p>
                                  </div>
                                </div>
                              </div>
                            </blockquote>
                          </div>
                        </blockquote>
                        <p class="MsoNormal"> </p>
                        <div class="MsoNormal" style="text-align:center"
                          align="center">
                          <hr align="center" size="2" width="100%">
                        </div>
                        <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:gray"><br>
                            This email and any files transmitted with it
                            are confidential and are intended solely for
                            the use of the individual or entity to whom
                            they are addressed. This communication
                            represents the originator's personal views
                            and opinions, which do not necessarily
                            reflect those of Henderson Engineers, Inc.
                            If you are not the original recipient or the
                            person responsible for delivering the email
                            to the intended recipient, be advised that
                            you have received this email in error, and
                            that any use, dissemination, forwarding,
                            printing, or copying of this email is
                            strictly prohibited. If you received this
                            email in error, please immediately notify
                            <a moz-do-not-send="true"
                              href="mailto:administrator@hei-eng.com"
                              target="_blank">administrator@hei-eng.com</a>.</span></p>
                        <div
                          id="m_5603468327082964812DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2">
                          <p class="MsoNormal"> </p>
                          <table
                            class="m_5603468327082964812MsoNormalTable"
                            style="border:none;border-top:solid #d3d4de
                            1.0pt" border="1" cellpadding="0">
                            <tbody>
                              <tr>
                                <td
                                  style="width:41.25pt;border:none;padding:9.75pt
                                  .75pt .75pt .75pt" width="55">
                                  <p class="MsoNormal"><a
                                      moz-do-not-send="true"
href="http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient"
                                      target="_blank"><span
                                        style="text-decoration:none"><img
                                          moz-do-not-send="true"
                                          style="width:.4791in;height:.302in"
id="m_5603468327082964812_x0000_i1026"
src="https://ipmcdn.avast.com/images/icons/icon-envelope-tick-green-avg-v1.png"
                                          height="29" border="0"
                                          width="46"></span></a></p>
                                </td>
                                <td
                                  style="width:352.5pt;border:none;padding:9.0pt
                                  .75pt .75pt .75pt" width="470">
                                  <p class="MsoNormal"
                                    style="line-height:13.5pt"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#41424e">Virus-free.
                                      <a moz-do-not-send="true"
href="http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient"
                                        target="_blank">
                                        <span style="color:#4453ea">www.avg.com</span></a>
                                    </span></p>
                                </td>
                              </tr>
                            </tbody>
                          </table>
                        </div>
                        <p class="MsoNormal"><br>
                          <br>
                          <br>
                        </p>
                        <pre>______________________________<wbr>_________________</pre>
<pre>Equest-users mailing list</pre>
<pre><a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/equest-users-<wbr>onebuilding.org</a></pre>
<pre>To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@<wbr>ONEBUILDING.ORG</a></pre>
</blockquote>
<p class="MsoNormal"> </p>
</div></div></div><div><div class="h5">


<hr>
<font face="Arial" color="Gray" size="1">

This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect
 those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing,
 or copying of this email is strictly prohibited. If you received this email in error, please immediately notify <a moz-do-not-send="true" href="mailto:administrator@hei-eng.com" target="_blank">administrator@hei-eng.com</a>.

</font>
</div></div></div>

</blockquote></div>
</div></div>



</blockquote>
</body></html>