    I may be all wet here but one other consideration is OA.  If there
    is no DOAS then the VAV system is supplying the OA to the zones.  A
    drop in flow could reduce the OA below minimum requirements for the
    zones.  A temp first reset would maintain airflow and the OA air
    portion.  With energy consumption, cooling and heating are the most
    expensive components of the flow and then the fan energy.  This is
    why economizers are very energy efficient in the right conditions.<br>
    So ultimately you have to meet ASHRAE 90.1 and also 62.1.  These are
    also baseline systems, just setting the low bar before we start to
    tinker.  All points and justification come from the magnitude you
    can exceed the baseline.  The baseline has been ratcheting up,
    things are not as easy now and almost all the low hanging fruit is
    gone.<br>
    I was reading an article in the online Journal this morning from
    2014.  Part of it concerned fan efficiency, FC, AF and plenum with
    direct and belt drive.  Now that efficiency is getting right down to
    belt slippage you know there isn't much left to play with.<br>
    Bruce Easterbrook P.Eng.<br>
    Abode Engineering<br>
    <br>
    <div class="moz-cite-prefix">On 4/20/2017 6:54 PM, Daric Adair via
      Equest-users wrote:<br>
    </div>
    <blockquote
cite="mid:20170420225428.TOSD27085.toroondcmxzimta01-srv.bellnexxia.net@tordcvbicmrk03"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:"Arial Black";
        panose-1:2 11 10 4 2 1 2 2 2 4;}
@font-face
        {font-family:"Segoe UI Symbol";
        panose-1:2 11 5 2 4 2 4 2 2 3;}
@font-face
        {font-family:"Adobe Garamond";}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
p.msonormal0, li.msonormal0, div.msonormal0
        {mso-style-name:msonormal;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
span.EmailStyle18
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle19
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle20
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle21
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">All;<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Great
            discussion.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">For
            context, the text of G3.1.3.12 is: “Supply Air Temperature
            Reset (System 5 through8). The air temperature for cooling
            shall be reset higher by 5F under the minimum cooling load
            conditions.”<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Stepping
            back, the reset is said to occur at ‘the minimum cooling
            load condition.’ Thinking through how a typlica/real VAV
            system will control, the terminal box dampers will close
            towards their minimum as the cooling load in a zone
            decreases. In a ‘real’ building this should cause the Supply
            fan to see a pressure increase and slow down to get back to
            its static pressure setpoint. At some point if all of the
            boxes are at a minimum position (aka, minimum cooling
            demand), the Supply Air Temperature should/can be increased.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Looking
            through the above, this would indicate an Air Flow first
            reset, before increasing the discharge temperature.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Per
            the eQuest help file, it would seem to indicate that a
            ‘Temp-First’ approach attempts to reset the temperature,
            without modulating the fan down.  This seems fairly odd in a
            ‘real’ system since in that if any single zone calls for
            cooling, no reset occurs, no energy saved. Even if it is a
            Baseline, it should have some sort of gut check to it. If it
            were a ‘real’ system and going Prescriptive path, it would
            be subject to Section 6.5.2. I didn’t see any requirement
            (Mandatory or Prescriptive) for DAT reset….(but I may be
            missing it….)<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Therefore,
            I’d think in a VAV system the Air-Flow first modulation,
            then allow the DAT to reset would be the intended path.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Another
            minor bit of confusion here: The 90.1 ASHREA User’s Manual
            does not offer much guidance here. There is new guide from
            PNNL for the 90.1-2010 standard, which is what is also
            mentioned below. Just want to clarify for readers that these
            are two separate (and both are useful) guides.<o:p></o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A;text-transform:uppercase"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A;text-transform:uppercase"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#44546A;text-transform:uppercase"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Thanks,<o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:10.0pt;font-family:"Arial
              Black",sans-serif;color:black;text-transform:uppercase">DARIC
              R. ADAIR</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1F497D"></span><span
              style="font-size:8.0pt;font-family:"Arial
              Black",sans-serif;color:black;text-transform:uppercase"> PE,
              C.E.M.</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
            </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#566C11">Henderson
                Engineers, Inc. | </span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#566C11">Mechanical
              Engineer, Energy Analyst</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
            </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;font-variant:small-caps;color:black">dir</span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">
              913 742 5530 
              <b><span style="font-variant:small-caps">tel</span></b>
              913 742 5000  <b><span style="font-variant:small-caps">fax</span></b>
              913 742 5001 
              <b><span style="font-variant:small-caps">tx id</span></b>
              #F-001236  <b><span style="font-variant:small-caps">email</span></b>
              <a class="moz-txt-link-abbreviated" href="mailto:daric.adair@hei-eng.com">daric.adair@hei-eng.com</a></span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1F497D"> 
              <a moz-do-not-send="true" href="http://www.hei-eng.com/"><b><span
                    style="font-size:8.0pt;color:#566C11">www.hei-eng.com</span></b></a>
              <br>
            </span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:black">Licensed
              in KS.</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:#1F497D"> </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Jennings, Coles via Equest-users
                [<a class="moz-txt-link-freetext" href="mailto:equest-users@lists.onebuilding.org">mailto:equest-users@lists.onebuilding.org</a>]
                <br>
                <b>Sent:</b> Thursday, April 20, 2017 10:38 AM<br>
                <b>To:</b> PKConsulting
                <a class="moz-txt-link-rfc2396E" href="mailto:pasha.pkconsulting@gmail.com"><pasha.pkconsulting@gmail.com></a>; Shaun Martin
                <a class="moz-txt-link-rfc2396E" href="mailto:smartin@shaunmartinconsulting.com"><smartin@shaunmartinconsulting.com></a><br>
                <b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@onebuilding.org">equest-users@onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] Supply Air Temp Reset
                Interpretation Please...?<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">I
            wanted to chime in quickly, because this is an interesting
            question that we’ve gone back and forth on in my office as
            well.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">I
            don’t agree with the stance that, because the section is
            labelled supply air temperature reset, therefore temperature
            first is the correct input. Airflow modulation is a given
            for VAV systems (baseline systems 5 through 8), so the
            question is not whether airflow modulates, but what takes
            precedence between the airflow modulation inherent in a VAV
            system and the temperature modulation also required by 90.1.
            The three possible combinations are reflected in the
            available eQUEST inputs: “temperature first,” “airflow
            first,” or “simultaneous.”<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">In
            my view, the correct order of priority between temperature
            and airflow modulation is not something the standard
            directly addresses. Absent clear direction in the standard,
            I would then look for any <a moz-do-not-send="true"
href="https://www.ashrae.org/standards-research--technology/standards-interpretations/interpretation-for-standard-90-1-2010https:/www.ashrae.org/standards-research--technology/standards-interpretations/interpretation-for-standard-90-1-2010">formal
              interpretations</a> of the standard issued by ASHRAE, and
            if that still doesn’t clear it up, then a user’s manual may
            be the next best thing. A user’s manual such as the PNNL
            manual at least provides specific direction by a neutral
            third party, which is often a great way to make a case to
            the reviewing authority (GBCI reviewer, code official,
            etc...).<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black"><br>
            <br>
          </span><b><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:black">Coles
              Jennings</span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">
            PE, BEMP, LEED AP BD+C
            <br>
            Sr. Energy Engineer, Building Sciences Manager </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#BA0C2F">|
          </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">Mason
            & Hanger
            <br>
            A Day & Zimmermann Company <br>
            <b>D </b>804.521.7045 </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#BA0C2F">|
          </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">O
            </span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">804.285.4171
          </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#BA0C2F">|
          </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">F
            </span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">804.217.8520
            <br>
            4880 Sadler Road, Suite 300 </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#BA0C2F">|
          </span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">Glen
            Allen, VA 23060
            <br>
            <a moz-do-not-send="true"
              href="http://www.masonandhanger.com/"><span
                style="color:#224BF1;text-decoration:none">Mason &
                Hanger</span></a>
            <br>
          </span><b><i><span
                style="font-size:11.0pt;font-family:"Adobe
                Garamond";color:#BA0C2F">We do what we say.®</span></i></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">
            <br>
            <br>
              </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Equest-users [<a moz-do-not-send="true"
                  href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>PKConsulting via Equest-users<br>
                <b>Sent:</b> Thursday, April 20, 2017 11:19 AM<br>
                <b>To:</b> Shaun Martin <<a moz-do-not-send="true"
                  href="mailto:smartin@shaunmartinconsulting.com">smartin@shaunmartinconsulting.com</a>><br>
                <b>Cc:</b> <a moz-do-not-send="true"
                  href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] Supply Air Temp Reset
                Interpretation Please...?<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <p class="MsoNormal">Yes!  Thanks Shaun- even one count of
            validation makes me feel not so crazy
            <span style="font-family:"Segoe UI
              Symbol",sans-serif">😜</span>,  especially from an
            old colleague.  Thank you- thank you.  Why is there too much
            room for interpretation on these things?  I accept that the
            User Manual is helpful in most scenarios- but this is one
            instance that just seems backwards.  If it is supposed to
            airflow reset controls,  then why is the section written
            with "Supply Air Temperature Reset"?<o:p></o:p></p>
        </div>
        <div id="AppleMailSignature">
          <p class="MsoNormal"><o:p> </o:p></p>
        </div>
        <div id="AppleMailSignature">
          <p class="MsoNormal">I appreciate your validation of my
            interpretation.<o:p></o:p></p>
        </div>
        <div id="AppleMailSignature">
          <p class="MsoNormal"><br>
            Pasha<o:p></o:p></p>
          <div>
            <p class="MsoNormal">Ph: 308-763-1593<o:p></o:p></p>
          </div>
        </div>
        <div>
          <p class="MsoNormal" style="margin-bottom:12.0pt"><br>
            On Apr 20, 2017, at 8:29 AM, Shaun Martin <<a
              moz-do-not-send="true"
              href="mailto:smartin@shaunmartinconsulting.com">smartin@shaunmartinconsulting.com</a>>
            wrote:<o:p></o:p></p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <div>
            <p class="MsoNormal"><span
                style="font-size:11.0pt;font-family:"Calibri",sans-serif">Hi,</span><o:p></o:p></p>
            <p class="MsoNormal"><span
                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
            <p class="MsoNormal"><span
                style="font-size:11.0pt;font-family:"Calibri",sans-serif">I
                think the Standard is quite clear about resetting
                temperature, and says nothing about modulating airflow. 
                The user manual seems to be wrong.</span><o:p></o:p></p>
            <p class="MsoNormal"><span
                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Shaun
                Martin LEED-AP, BEMP</span><o:p></o:p></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Principal</span><o:p></o:p></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Shaun
                Martin Consulting</span><o:p></o:p></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">#90
                – 425 Carrall Street</span><o:p></o:p></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Vancouver,
                BC  V6B 6E3</span><o:p></o:p></p>
            <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">p.
                604-789-1095</span><o:p></o:p></p>
            <p class="MsoNormal"><span
                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
            <p class="MsoNormal"><span
                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
            <p class="MsoNormal"><span
                style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
            <p class="MsoNormal"><a moz-do-not-send="true"
                name="_MailEndCompose"><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span></a><o:p></o:p></p>
            <div>
              <div style="border:none;border-top:solid #E1E1E1
                1.0pt;padding:3.0pt 0in 0in 0in">
                <p class="MsoNormal"><b><span
                      style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                    Equest-users [<a moz-do-not-send="true"
                      href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                    <b>On Behalf Of </b>PKConsulting via Equest-users<br>
                    <b>Sent:</b> Thursday, April 20, 2017 7:12 AM<br>
                    <b>To:</b> Jones, Christopher <<a
                      moz-do-not-send="true"
                      href="mailto:Christopher.r.Jones@wspgroup.com">Christopher.r.Jones@wspgroup.com</a>><br>
                    <b>Cc:</b> <a moz-do-not-send="true"
                      href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                    <b>Subject:</b> Re: [Equest-users] Supply Air Temp
                    Reset Interpretation Please...?</span><o:p></o:p></p>
              </div>
            </div>
            <p class="MsoNormal"> <o:p></o:p></p>
            <div>
              <p class="MsoNormal">Thanks for the feedback-  so if the
                justification for the approach is solely based on the
                user manual explanation- I can accept that.  I'll cross
                reference it for the 2007 user manual to put it in my
                notes.<o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal"> <o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal">I've always used air-flow first as a
                standard reset for all my design energy models, What is
                counter-intuitive here is that the title of the Appendix
                G section specifically states 'reset-temp', so why
                should we not take the section text literally?  I've
                always humbly assumed that the ASHRAE standard writers
                know more than me.  After all these years of creating
                Baseline conforming models (or so I thought),  this
                makes me feel lost all over again.  AND is it not
                possible to apply code standard requirements without the
                use of the User Manual?   <o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal"> <o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal" style="margin-bottom:12.0pt">Thankful-
                but-frustrated,<o:p></o:p></p>
              <div>
                <p class="MsoNormal">Pasha<o:p></o:p></p>
                <div>
                  <p class="MsoNormal">Ph: 308-763-1593<o:p></o:p></p>
                </div>
              </div>
            </div>
            <div>
              <p class="MsoNormal" style="margin-bottom:12.0pt"><br>
                On Apr 20, 2017, at 6:48 AM, Jones, Christopher <<a
                  moz-do-not-send="true"
                  href="mailto:Christopher.r.Jones@wspgroup.com">Christopher.r.Jones@wspgroup.com</a>>
                wrote:<o:p></o:p></p>
            </div>
            <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
              <div>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">I
                    had always assumed temperature first but reading the
                    PNNL 90.1-2010 Performance Rating Method Reference
                    Manual, 3.121 (pdf page 151), it states “For systems
                    5 through 8, the air temperature for cooling shall
                    be reset higher by 5°F under the minimum cooling
                    load conditions using a reset by warmest zone,
                    airflow first strategy.”</span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">The
                    manual states that the airflow first strategy
                    minimizes zone reheat coil energy ( or overcooling)
                    and central chiller energy consumption at the cost
                    of possible increased fan energy. </span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Unfortunately,
                    the reviewer may have a case.
                  </span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:EN-CA"
                    lang="EN-CA"> </span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><image001.jpg></span><o:p></o:p></p>
                <p class="MsoNormal"><b><span
style="font-size:6.0pt;font-family:"Calibri",sans-serif;color:#1F497D;mso-fareast-language:FR"> </span></b><o:p></o:p></p>
                <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
                      lang="EN-GB">Christopher R. Jones</span></b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
                    lang="EN-GB">, P.Eng.</span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
                    lang="EN-GB">Technical Specialist</span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"> </span><o:p></o:p></p>
                <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
                      lang="EN-GB">WSP Canada Inc.</span></b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
                    lang="EN-GB"><br>
                  </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">2300
                    Yonge Street, Suite 2300</span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">Toronto,
                    ON M4P 1E4 Canada</span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"
                    lang="EN-GB"><br>
                  </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR">T
                    +1 416-644-0252</span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:FR"> </span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#1F497D;mso-fareast-language:EN-CA"><a
                      moz-do-not-send="true"
href="https://urldefense.proofpoint.com/v2/url?u=http-3A__www.wspgroup.ca_&d=DwMFaQ&c=xB5UQg5qXm2axe_t44neldV-XNditz6D2ZXZLA0vHlE&r=JrIPsTq2z-_669uhqn51VqSZFL7dpX6NqxKBTKpeQZ9m5XksAJHnQhCI_rEcbMFG&m=TUl4CO4lm0_JnjocmrzLbupzOeFu-9zJ4Wttnq-IxpY&s=wcUq0_D9t-Xi40LrszT5MooY6bxaUqaU8_S_1WcmUOY&e="><span
                        style="color:blue">www.wspgroup.ca</span></a></span><o:p></o:p></p>
                <p class="MsoNormal" style="text-autospace:none"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#7F7F7F;mso-fareast-language:FR"> </span></b><o:p></o:p></p>
                <p class="MsoNormal" style="text-autospace:none"><i><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#6EA900;mso-fareast-language:FR">Please
                      consider the environment before printing...</span></i><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"
                    lang="EN-CA"> </span><o:p></o:p></p>
                <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                <p class="MsoNormal"><b><span
                      style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                    Equest-users [<a moz-do-not-send="true"
                      href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                    <b>On Behalf Of </b>Pasha Korber-Gonzalez via
                    Equest-users<br>
                    <b>Sent:</b> Thursday, April 20, 2017 3:59 AM<br>
                    <b>To:</b> eQUEST Users List <<a
                      moz-do-not-send="true"
                      href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>
                    <b>Subject:</b> [Equest-users] Supply Air Temp Reset
                    Interpretation Please...?</span><o:p></o:p></p>
                <p class="MsoNormal"> <o:p></o:p></p>
                <div>
                  <p class="MsoNormal">Hello--- I received this note
                    from a fellow energy model reviewer (non-LEED review
                    comment) regarding my Baseline energy model that is
                    supposed to be compliant with Appendix G.  I
                    disagree with what they are saying.  I appreciate
                    your feedback please and verification if in fact I
                    am wrong in how I am interpreting Section G3.1.3.12.<o:p></o:p></p>
                  <div>
                    <p class="MsoNormal"> <o:p></o:p></p>
                  </div>
                  <div>
                    <p class="MsoNormal"> <o:p></o:p></p>
                  </div>
                  <div>
                    <p class="MsoNormal">"We believe TEMP-FIRST supply
                      air reset control strategy is not the correct
                      interpretation of G3.1.3.12 – rather,
                      AIRFLOW-FIRST should be used."<o:p></o:p></p>
                  </div>
                  <div>
                    <p class="MsoNormal"> <o:p></o:p></p>
                  </div>
                  <div>
                    <p class="MsoNormal"> <o:p></o:p></p>
                  </div>
                  <div>
                    <p class="MsoNormal">Thanks!<o:p></o:p></p>
                  </div>
                  <div>
                    <p class="MsoNormal"> <o:p></o:p></p>
                  </div>
                  <div>
                    <p class="MsoNormal">Pasha<o:p></o:p></p>
                  </div>
                </div>
              </div>
            </blockquote>
          </div>
        </blockquote>
      </div>
      <br>
      <hr>
      <font face="Arial" color="Gray" size="1"><br>
        This email and any files transmitted with it are confidential
        and are intended solely for the use of the individual or entity
        to whom they are addressed. This communication represents the
        originator's personal views and opinions, which do not
        necessarily reflect those of Henderson Engineers, Inc. If you
        are not the original recipient or the person responsible for
        delivering the email to the intended recipient, be advised that
        you have received this email in error, and that any use,
        dissemination, forwarding, printing, or copying of this email is
        strictly prohibited. If you received this email in error, please
        immediately notify <a class="moz-txt-link-abbreviated" href="mailto:administrator@hei-eng.com">administrator@hei-eng.com</a>.<br>
      </font>
      <div id="DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2"><br>
        <table style="border-top: 1px solid #D3D4DE;">
          <tbody>
            <tr>
              <td style="width: 55px; padding-top: 13px;"><a
                  moz-do-not-send="true"
href="http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient"
                  target="_blank"><img moz-do-not-send="true"
src="https://ipmcdn.avast.com/images/icons/icon-envelope-tick-green-avg-v1.png"
                    style="width: 46px; height: 29px;" height="29"
                    width="46"></a></td>
              <td style="width: 470px; padding-top: 12px; color:
                #41424e; font-size: 13px; font-family: Arial, Helvetica,
                sans-serif; line-height: 18px;">Virus-free. <a
                  moz-do-not-send="true"
href="http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient"
                  target="_blank" style="color: #4453ea;">www.avg.com</a>
              </td>
            </tr>
          </tbody>
        </table>
        <a moz-do-not-send="true"
          href="#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2" width="1"
          height="1"> </a></div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>