<div dir="ltr"><font color="#073763">Hi Chris,</font><div><font color="#073763"><br></font></div><div><font color="#073763">CO2 sensor based control can be called as DCV. </font><span style="color:rgb(7,55,99)">Minimum-cfm-schedules and minimum-oa-fraction based OA control is for the outside air being partially served for sometime to the zones.</span></div><div><font color="#073763">If you have to model DCV at the system level then you will be required to use that DCV CO2 based option in the outside air tab of the system.</font></div><div><font color="#073763">DCV is used for the areas with more than 50 square meter area  and more than 40 occupancy in 100 square meter floor area. This is mentioned in the ASHRAE 90.1-2007.</font></div><div><font color="#073763">I have done DCV for some projects by the DCV CO2 sensor based option for areas especially like classrooms and canteens.</font></div><div><font color="#073763">So if in a small area there is higher transit occupancy then we are required to have DCV as per ASHRAE-90.1.</font></div><div><font color="#073763"><br></font></div><div><font color="#073763"><br></font></div><div><font color="#660000"><b>Thanks,</b></font></div><div><b><font color="#0c343d">Sharad.Kumar</font></b></div><div><font color="#073763"><br></font></div><div><br>---------- Forwarded message ----------<br>From: "Jones, Christopher via Equest-users" <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>To: "<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>" <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>Cc: <br>Bcc: <br>Date: Mon, 3 Apr 2017 15:05:28 +0000<br>Subject: [Equest-users] 100% OA VAV system control question<br><div lang="EN-US"><div class="gmail-m_-52828658511889719WordSection1"><p class="MsoNormal">The school project I am working on has a 100% outdoor air VAV system. The VAV box flow is controlled by CO2 sensors. I am not sure if this can be directly modeled in eQuest?  In the past I have modeled this kind of system by specifying min-cfm-schedules in each zone and specifying a min-oa-fraction of 1 at the system. I have never tried using the CO2 DCV option.<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><span lang="EN-CA"><u></u> <u></u></span></p><p class="MsoNormal"><img width="108" height="34" id="gmail-m_-52828658511889719Picture_x0020_2" src="cid:image001.jpg@01D2AC66.74684D80" alt="cid:image001.jpg@01D2A6E9.840756F0"><u></u><u></u></p><p class="MsoNormal"><b><span style="font-size:6pt"><u></u> <u></u></span></b></p><p class="MsoNormal"><b><span lang="EN-GB" style="font-size:10pt;font-family:arial,sans-serif">Christopher R. Jones</span></b><span lang="EN-GB" style="font-size:10pt;font-family:arial,sans-serif">, P.Eng.<u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-GB" style="font-size:10pt;font-family:arial,sans-serif">Technical Specialist</span><span style="font-size:10pt;font-family:arial,sans-serif"><u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:arial,sans-serif"><u></u> <u></u></span></p><p class="MsoNormal"><b><span lang="EN-GB" style="font-size:10pt;font-family:arial,sans-serif">WSP Canada Inc.</span></b><span lang="EN-GB" style="font-size:10pt;font-family:arial,sans-serif"><br></span><span style="font-size:10pt;font-family:arial,sans-serif">2300 Yonge Street, Suite 2300<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:arial,sans-serif">Toronto, ON M4P 1E4 Canada</span><span lang="EN-GB" style="font-size:10pt;font-family:arial,sans-serif"><br></span><span style="font-size:10pt;font-family:arial,sans-serif">T +1 416-644-0252<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:arial,sans-serif"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:arial,sans-serif"><a href="http://www.wspgroup.ca/" target="_blank"><span style="color:blue">www.wspgroup.ca</span></a></span><u><span lang="EN-CA" style="color:blue"><u></u><u></u></span></u></p><p class="MsoNormal"><b><span style="color:rgb(127,127,127)"><u></u> <u></u></span></b></p><p class="MsoNormal"><i><span style="font-size:10pt;font-family:arial,sans-serif;color:rgb(110,169,0)">Please consider the environment before printing...</span></i></p></div></div></div></div>