<div dir="ltr">thank you Bill & Michael for some insights.<div><br></div><div>The Baseline model is Pkg VAV units with hot water heating</div><div>The Proposed model is VAV with heat recovery chilled water and hot water heating with condensing boilers.</div><div><br></div><div>When I read the SS-L reports I can see some differences in the run hours of the fans, but I don't really know what to explain about the differences that I'm seeing from the Proposed & Baseline models.  All the eQuest related info doesn't really tell me where these values in the SS-L reports are generated from.  Below is the Proposed SS-L for AHU-1 and the Baseline SS-L for one of the Baseline systems.  One thing at the bottom of the report shows that the fan elec kWh is noticeably smaller for the proposed system versus the baseline system.</div><div><br></div><div><img src="cid:ii_15b211564c68b63a" alt="Inline image 1" width="495" height="337"><br></div><div><br></div><div><img src="cid:ii_15b21182d1b95f7c" alt="Inline image 2" width="495" height="355"><br></div></div><div class="gmail_extra"><br><div class="gmail_quote">On Thu, Mar 30, 2017 at 2:23 PM, Michael Mantai <span dir="ltr"><<a href="mailto:mmantai@systemworcx.com" target="_blank">mmantai@systemworcx.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div bgcolor="white" lang="EN-US" link="#0563C1" vlink="#954F72"><div class="m_5012537085294881038WordSection1"><p class="MsoNormal"><span style="font-size:11.0pt;font-family:Calibri">What type of HVAC systems do you have in the baseline vs. proposed?  As noted in the comment, the baseline system fans should run continuous during occupied hours and cycle at night.  If your proposed case system has dedicated outside air systems, those fans would run continuously during occupied hours but other fans could cycle on temperature.  I’ve done schools that use a DOAS unit coupled with fan coils or heat pumps.  In the proposed case I set the DOAS to run continuous and set the fan coils/heat pump fans to cycle on temperature, which would result in less fan hours.  I’m also surprised your proposed fan kW is that much higher than baseline, so you might check that.<u></u><u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:Calibri"><u></u> <u></u></span></p><div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0in 0in 0in"><p class="MsoNormal"><b><span style="font-family:Calibri;color:black">From: </span></b><span style="font-family:Calibri;color:black">Equest-users <<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.<wbr>onebuilding.org</a>> on behalf of Pasha Korber-Gonzalez via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.<wbr>onebuilding.org</a>><br><b>Reply-To: </b>Pasha Korber-Gonzalez <<a href="mailto:pasha.pkconsulting@gmail.com" target="_blank">pasha.pkconsulting@gmail.com</a>><br><b>Date: </b>Thursday, March 30, 2017 at 3:51 PM<span class=""><br><b>To: </b>eQUEST Users List <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.<wbr>onebuilding.org</a>><br><b>Subject: </b>[Equest-users] LEED Comment for FAN EFLH--help please<u></u><u></u></span></span></p></div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">Hello fellow eQuesters,<u></u><u></u></p><div><div class="h5"><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">I'm sure we all get the standard LEED review comment regarding Fan equivalent full load hours (EFHL).<u></u><u></u></p></div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">I received this one on my current project (elementary school in Ohio with heat recovery units.)  I have confirmed that my fan schedules for both models are exactly the same.  But I do have drastically different EFLH values for the baseline (over 3,000) and proposed (less than 1,500).<br><br>I have made changes in my models, but I cannot seem to get the proposed hours over 1,600 of run time.  <u></u><u></u></p></div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">QUESTION:  Do any of you have any experience of suggesting to the LEED Reviewer that it is possible to have this significant of difference between the two models hvac systems AND how can I show justification for these run hours??  Any advice & suggestions are welcomed at this time.<u></u><u></u></p></div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><p class="MsoNormal">Here is the LEED comment I received with highlighted notes:<u></u><u></u></p></div><div><p class="MsoNormal"><span style="color:#444444">. Table EAp2-5 of the form indicates that the <span style="background:yellow">equivalent full load hours for interior fans in the Proposed and Baseline model are 1,200 hours (57,951 kWh/48.31 kW) and 3,702 hours (130,702 kWh/35.31 kW), respectively; however, it is unclear if the HVAC fans are modeled as cycling to meet the cooling and heating loads of the building during unoccupied hours.</span> Table G3.1.4 in the Proposed building column requires that HVAC fans that provide ventilation air in the Proposed model must be modeled as operating continuously during occupied hours <span style="background:yellow">and cycled to meet the cooling and heating loads of the building during unoccupied hours, unless one of the exceptions of Table G3.1.4 are met. In addition, Section G3.1.2.4 requires that supply and return fans reflected in the Baseline model must be modeled as operating continuously during occupied hours and cycled to meet the cooling and heating loads of the building during unoccupied hours,</span> </span><u></u><u></u></p></div></div></div></div><p class="MsoNormal">______________________________<wbr>_________________ Equest-users mailing list <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/equest-users-<wbr>onebuilding.org</a> To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@<wbr>ONEBUILDING.ORG</a> <u></u><u></u></p></div></div>
</blockquote></div><br></div>