    <p>Here I am trying to keep the "chain letter" going :-)</p>
    <p>Nick has hit upon something that's a bit of a sore spot for me,
      i.e., modeling buildings by the intent or rationalization of a
      building policy, rather than documentation of how buildings
      actually behave.  I've always been skeptical of this
      "pressurization == no infiltration" claim that I've heard going
      all the way back to the early 1980s. I can see how pressurization
      might keep out infiltration, but wouldn't it then result in
      exfiltration, which would be a net loss of conditioned air that
      needs to be made up by the air handler? <br>
    </p>
    <p>The most rigid application of what I call "modeling by intent"
      was when I introduced the use of DOE-2 for a new residential
      building energy standard in China. When the topic got to be
      infiltration, I heard that should be set at 1.0 ACH, which was
      mandated as the amount of fresh air needed to an occupied space,
      although no equipment nor technology was mentioned for maintaining
      such a steady flow of air.  It must be "smart air". as one
      reviewer commented at a critique in Arizona upon seeing an
      architect's drawing with arrows bringing in natural ventilation
      horizontally into a building...</p>
    <p>Joe<br>
    </p>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 3/15/2017 3:23 PM, Nicholas Caton
      wrote:<br>
    </div>
    <blockquote
cite="mid:AMXPR04MB247A9BD10D1E432CCC7A3E0B6270@AMXPR04MB247.eurprd04.prod.outlook.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Wingdings;
        panose-1:5 0 0 0 0 0 0 0 0 0;}
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
@font-face
        {font-family:Verdana;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p
        {mso-style-priority:99;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma",sans-serif;}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
        {mso-style-priority:34;
        margin-top:0in;
        margin-right:0in;
        margin-bottom:0in;
        margin-left:.5in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:Consolas;}
p.msonormal0, li.msonormal0, div.msonormal0
        {mso-style-name:msonormal;
        mso-style-priority:99;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma",sans-serif;}
span.EmailStyle24
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle25
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle26
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle27
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle28
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle29
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle30
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
/* List Definitions */
@list l0
        {mso-list-id:497576584;
        mso-list-type:hybrid;
        mso-list-template-ids:-387932184 67698711 67698713 67698715 67698703 67698713 67698715 67698703 67698713 67698715;}
@list l0:level1
        {mso-level-number-format:alpha-lower;
        mso-level-text:"%1\)";
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l0:level2
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l0:level3
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l0:level4
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l0:level5
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l0:level6
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l0:level7
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l0:level8
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l0:level9
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l1
        {mso-list-id:836194086;
        mso-list-type:hybrid;
        mso-list-template-ids:-498945012 67698703 67698713 67698715 67698703 67698713 67698715 67698703 67698713 67698715;}
@list l1:level1
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level2
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level3
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l1:level4
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level5
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level6
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l1:level7
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level8
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l1:level9
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l2
        {mso-list-id:1001009814;
        mso-list-type:hybrid;
        mso-list-template-ids:-2072475348 67698703 67698713 67698715 67698703 67698713 67698715 67698703 67698713 67698715;}
@list l2:level1
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l2:level2
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l2:level3
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l2:level4
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l2:level5
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l2:level6
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l2:level7
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l2:level8
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l2:level9
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l3
        {mso-list-id:1645045461;
        mso-list-type:hybrid;
        mso-list-template-ids:1348376220 67698703 67698713 67698715 67698703 67698713 67698715 67698703 67698713 67698715;}
@list l3:level1
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l3:level2
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l3:level3
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l3:level4
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l3:level5
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l3:level6
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
@list l3:level7
        {mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l3:level8
        {mso-level-number-format:alpha-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;}
@list l3:level9
        {mso-level-number-format:roman-lower;
        mso-level-tab-stop:none;
        mso-level-number-position:right;
        text-indent:-9.0pt;}
ol
        {margin-bottom:0in;}
ul
        {margin-bottom:0in;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">I
            feel like expanding
            <s>just a little</s> (<i>who am I kidding?</i>) on Maria’s
            quote from the PNNL guidelines’ document regarding
            infiltration schedules: 
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><i><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif">“</span></i><i><span
              style="font-size:11.0pt">The total building infiltration
              schedule fraction will be 1.0 when all heating,
              ventilation and air-conditioning (HVAC) systems are off
              and 0.25 when the HVAC systems are in operation.”</span></i><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l2 level1 lfo3"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">1.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">For
            extra context:  That report details an exploration of
            options to constructively translate 90.1 envelope
            subcommittee advice concerning baseline overall air
            infiltration quantities (1.8 CFM/ft2 @ 75Pa) into a
            procedure and set of inputs appropriate for usage with
            energyplus 3.1+.  The above quote, if I am not mistaken,
            actually sources from the SSPC 90.1 Envelope Subcommittee…
            if not by direct citation.  I would not aim any specific
            concerns about this prescriptive language at those authors.<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l2 level1 lfo3"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">2.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">The
            <u>effects</u> of such a fractional schedule (uniformly for
            both energyplus and in doe-2, at least) would be to:
            <o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="margin-left:1.0in;text-indent:-.25in;mso-list:l2 level2
          lfo3">
          <!--[if !supportLists]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">a.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">reduce
            naturally driven infiltration (as determined each interval
            between wind /  temperature / stack effects) by 75% when
            HVAC = ON<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="margin-left:1.0in;text-indent:-.25in;mso-list:l2 level2
          lfo3">
          <!--[if !supportLists]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">b.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">not
            modify naturally driven infiltration when HVAC = OFF<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l2 level1 lfo3"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">3.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">The
            <u>purpose</u> of such a reduction is to (in broad strokes)
            represent the effects of aggregate building pressurization
            as is typically intended with new commercial HVAC design. 
            If my building interior is positively pressurized relative
            to the exterior, less air should infiltrate in.<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l2 level1 lfo3"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">4.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">This
            reduction as prescribed is intended to occur every hour that
            fans achieving building pressurization are in operation. 
            24/7 = correct for multifamily with centrally-driven
            ventilation/pressurization (typical multifamily design for
            some locales, but not in all markets).<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l2 level1 lfo3"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">5.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">To
            the best of my knowledge, 75%
            <u>is a dart on the wall</u>.  I’m not aware of any study
            that informed this directly, but it follows logic that
            generally infiltration still happens with pressurized
            buildings, sometimes, so any aggregate reduction should
            remain under 100%.  I’m personally convinced there is no
            single number that would be appropriately applied to all
            buildings/systems, however.  Indeed situations exist where
            the systems in operation actually de-pressurize the building
            interior and would therefore
            <u>amplify</u> infiltration (by design, coincidence, or
            accident).  <o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">This
            same schedule however is
            <u>also</u> the primary vector to factor in “higher than
            design state” naturally driven infiltration.  This occurs
            for example in scenarios where buildings that have doors
            that could open for people to enter and exit.  <o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">So
            what is this “design state?”  Depends on who you ask - I’d
            offer 2 perspectives:<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l1 level1 lfo5"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">1.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Open
            windows & doors are not normally considered by
            well-meaning mechanical engineers designing for building
            pressurization.  If I may reach a bit (I’m sure I cannot
            speak for everyone), the broad assumption is that doors,
            windows, and other openings are considered in an effectively
            closed state
            <u>most</u> of the time, and when they are open all bets are
            off.  While we can compartmentalize and try to mitigate the
            effects, we cannot generally design buildings to be
            effectively pressurized to combat infiltration on a macro
            level while many doors/windows are open, else those doors
            would never close and the windows would whistle all day.<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l1 level1 lfo5"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">2.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">From
            a prescriptive/compliance M+V perspective, leakage through
            windows and doors are for practical reasons deliberately
            excluded to ensure the air-tightness of the rest of the
            envelope assembly is what’s being measured in isolation (I’m
            sure this varies based on locally prescribed/normal
            protocol).  Such openings are taped/sealed off to ensure
            they do not impact blower door testing results. 
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">I
            suspect this phenomenon of building operation (operable
            doors/windows) was for justifications including the above
            <u>also</u> not a concern of the envelope committee when
            prescribing infiltration schedule factors no higher than 1.0
            during occupied/unoccupied hours.  …And that’s
            <u>totally fine</u> for those interested in setting an
            arbitrary bar for something like compliance
            modeling/testing: By the book, that reality has been pushed
            off the table for discussion and so shouldn’t be a concern
            or part of the conversation (unless someone with a big stick
            changes their mind on the matter).<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">The
            reality of operable doors/windows
            <u>can</u> however be a meaningful thing to miss if you are
            trying to calibrate and/or determine realistic savings
            potential for directly-affected ECM scope (including adding
            vestibules/compartmentalization to entryways, general
            envelope re-sealing packages, and addressing
            dysfunctional/non-existent building pressurization
            situations).<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Some
            suggestions for those concerned about getting infiltration
            schedules “right” for reasons beyond compliance:
            <o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l3 level1 lfo4"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">1.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Windows/doors/and
            other operable envelope openings are not always in closed
            state.  Consider increasing naturally driven infiltration
            rates above those expected/measured for “fully closed”
            states during hours where you can expect openings.  Typical
            elementary school should see values above 1.0 when school
            lets in & out (doors/vestibules are held open), and
            perhaps also seasonally during nice weather where windows
            are operable & actually used.  <o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l3 level1 lfo4"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">2.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Another
            dart on the wall to consider:  Depending on the occupancy
            type, eQUEST wizards seems to suggest hourly factors
            approaching 1.25 (25% increase in naturally driven
            infiltration) around hours where you’d typically expect
            heavier foot traffic around entries (at start/close of
            typical weekday occupancy patterns and around lunch hours,
            generally).  I call it a “dart on the wall” again because
            I’m not certain if this is based on any specific study.<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l3 level1 lfo4"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">3.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Working
            building pressurization systems can be rendered ineffective
            over time due to bad pressure sensors / controls / envelope
            degradation:  a 75% reduction may be too aggressive<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l3 level1 lfo4"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">4.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Building
            pressurization systems can be TOO effective for similar
            causes – ever notice doors blowing open or not shutting
            well?  75% may overly conservative in those cases<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l3 level1 lfo4"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">5.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">A
            fractional schedule appropriate for perimeter infiltration
            is probably not appropriate for core zones without vertical
            exterior exposures (if you presume any infiltration loads
            are seen there to begin with).<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l3 level1 lfo4"><!--[if !supportLists]--><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><span
              style="mso-list:Ignore">6.<span style="font:7.0pt
                "Times New Roman"">      
              </span></span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Accounting
            for the effects of adding vestibules, rotating doors, and
            similar compartmentalization ECM’s requires at least
            acknowledging naturally driven infiltration floats above
            “everything closed” or “design” levels of infiltration, so
            that you can make appropriate relative reductions.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">In
            closing, I guess I want to emphasis for tone: this is mostly
            just my opinion, man!  I am not a certified blower door
            technician, nor an energyplus developer, nor a
            standard/compliance language-crafter… Just a fellow with a
            few thoughts I feel others could benefit from considering. 
            My sincere hope is someone out there can benefit/grow from
            some of these perspectives and/or return the favor someday
            by setting me straight if/when I’m going down the wrong
            path.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">~Nick<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46"><img
                style="width:7.5625in;height:.0937in" id="_x0000_i1036"
src="cid:part1.D66D205E.38BA79A0@whiteboxtechnologies.com" height="9"
                width="726"><o:p></o:p></span></p>
          <p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46">Nick
                Caton, P.E., BEMP</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46"><o:p></o:p></span></p>
          <table class="MsoNormalTable"
            style="width:543.0pt;border-collapse:collapse" border="0"
            cellpadding="0" cellspacing="0" width="724">
            <tbody>
              <tr>
                <td style="width:172.3pt;padding:0in 0in 0in 0in"
                  valign="top" width="230">
                  <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Senior Energy Engineer</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Regional Energy Engineering Manager<o:p></o:p></span></p>
                  <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Energy and Sustainability Services</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469"> 
                      Schneider Electric</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
                </td>
                <td style="width:218.3pt;padding:0in 0in 0in 0in"
                  valign="top" width="291">
                  <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">D  </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">913.564.6361
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">M  </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">785.410.3317
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">F  </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">913.564.6380</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">E  </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><a
                        moz-do-not-send="true"
                        href="mailto:nicholas.caton@schneider-electric.com"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">nicholas.caton@schneider-electric.com</span></a><o:p></o:p></span></p>
                </td>
                <td style="width:152.4pt;padding:0in 0in 0in 0in"
                  valign="top" width="203">
                  <p class="MsoNormal" style="text-align:right"
                    align="right"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">15200
                      Santa Fe Trail Drive<br>
                      Suite 204<br>
                      Lenexa, KS 66219<br>
                      United States</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:4.0pt">
                <td colspan="3" style="width:543.0pt;padding:0in 0in 0in
                  0in;height:4.0pt" valign="top" width="724">
                  <p class="MsoNormal" style="mso-line-height-alt:4.0pt"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46"><img
                        style="width:7.5208in;height:.5104in"
                        id="_x0000_i1035"
                        src="cid:part3.F2A8F20C.A4CE1CD3@whiteboxtechnologies.com"
                        height="49" border="0" width="722"><!--[if gte mso 9]><xml>
<o:OLEObject Type="Embed" ProgID="PBrush" ShapeID="_x0000_i1035" DrawAspect="Content" ObjectID="_1551103779">
</o:OLEObject>
</xml><![endif]--><o:p></o:p></span></p>
                </td>
              </tr>
            </tbody>
          </table>
          <p class="MsoNormal"><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Equest-users
                [<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Maria Karpman via Equest-users<br>
                <b>Sent:</b> Tuesday, March 14, 2017 11:53 AM<br>
                <b>To:</b> Nathan Miller <a class="moz-txt-link-rfc2396E" href="mailto:nathanm@rushingco.com"><nathanm@rushingco.com></a>;
                Chris Jones <a class="moz-txt-link-rfc2396E" href="mailto:Christopher.Jones@rwdi.com"><Christopher.Jones@rwdi.com></a>; David
                Griffin II <a class="moz-txt-link-rfc2396E" href="mailto:DGriffin@archnexus.com"><DGriffin@archnexus.com></a>; Michael
                Campbell <a class="moz-txt-link-rfc2396E" href="mailto:mcamp1206@gmail.com"><mcamp1206@gmail.com></a>; Joe Huang
                <a class="moz-txt-link-rfc2396E" href="mailto:yjhuang@whiteboxtechnologies.com"><yjhuang@whiteboxtechnologies.com></a><br>
                <b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@onebuilding.org">equest-users@onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] Wall insulation in
                multifamily buildings<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">To
            David’s comment about infiltration (“<span
              style="color:#1F497D">Lower infiltration will save you
              more energy than any other envelope ECM.”),</span> there
            are a few caveats.
          </span><o:p></o:p></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l0 level1 lfo2"><!--[if !supportLists]--><span
            style="mso-list:Ignore">a)<span style="font:7.0pt
              "Times New Roman"">     
            </span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">To
            document infiltration-related savings in App G models (e.g.
            for LEED), the baseline air leakage would be modeled as 0.4
            CFM/SF
            <u>@ 75Pa</u> (90.1 2013 G3.1.1.4). 90.1 2013 Table G
            further requires that infiltration inputs in the simulation
            tool are adjusted to account for factors such as weather and
            “…. HVAC system operation….“. 90.1 leaves these adjustments
            to the modeler, but PNNL’s
            <a moz-do-not-send="true"
href="http://citeseerx.ist.psu.edu/viewdoc/download?doi=10.1.1.510.8703&rep=rep1&type=pdf">Infiltration
              Modeling Guidelines for Commercial Building Energy
              Analysis</a> mentions in passing (Note 2 on p.6) that “The
            total building infiltration schedule fraction will be 1.0
            when all heating, ventilation and air conditioning (HVAC)
            systems are off and 0.25 when the HVAC systems are in
            operation.”</span> <span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">
            (It’s good that they used Energy Plus for the study, so
            results must still be accurate in spite of this seemingly
            arbitrary assumption
          </span><span style="font-family:Wingdings">J</span><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">.)</span>
          <span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Since
            HVAC systems are operating 24/7 in multifamily, infiltration
            schedule in the baseline and proposed design would have to
            be set to 0.25 of the peak if we follow the PNNL study,
            which very significantly reduces infiltration-related
            heating load in the model. (The infiltration load is shown
            in LS-F report.)</span>
          <span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">As
            a side note, with LEED v3 and v4, infiltration-reduction
            credit can be claimed via exceptional calculation methods,
            or by using
            <a moz-do-not-send="true"
href="http://www.usgbc.org/credits/new-construction-core-and-shell-schools-new-construction-retail-new-construction-healthc-110">LEED
              pilot credit</a> which is based on 90.1 2016 Appendix G
            modeling rules with the appropriate adjustment to
            performance targets and point scale. (I recommend that you
            check out this credit, as it simplifies the baseline model.)</span><o:p></o:p></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l0 level1 lfo2"><!--[if !supportLists]--><span
            style="mso-list:Ignore">b)<span style="font:7.0pt
              "Times New Roman"">     
            </span></span><!--[endif]--><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Potential
            savings from infiltration reduction should be considered in
            conjunction with the specified ventilation strategy. In
            North East, it is overwhelmingly common to have 100% OA
            units serving multifamily corridors with no exhaust, and
            continuously running rooftop exhaust fans serving kitchens
            and bathrooms in apartments on one vertical stack with no
            make-up. Both supply and exhaust rates are often grossly
            oversized compared to the minimum CFM required by code, and
            since the relevant code (summarized <a
              moz-do-not-send="true"
href="https://buildingscience.com/sites/default/files/document/ba-1507_ventilation_guidance_final_measure_guideline.pdf">here</a>)
            requires that apartments are compartmentalized and envelope
            is air-tight, it creates an interesting conundrum for air
          </span><span style="font-family:Wingdings">J</span><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">.
            Balanced ventilation is still a rarity in NE even in high
            performance buildings. Old editions of ASHRAE Fundamentals
            had a way of taking into account this dynamics (see below),
            which was crude but better than “one size fits all” approach
            in the PNNL study.  So I’d use ASHRAE’s method in lieu of
            PNNL’s to model infiltration savings for LEED, and to decide
            whether tighter envelope should be pursued for a given
            project.</span><o:p></o:p></p>
        <p class="MsoListParagraph"><img
            style="width:9.0833in;height:5.8437in" id="_x0000_i1025"
            src="cid:part7.C78A6267.31E7E178@whiteboxtechnologies.com"
            height="561" border="0" width="872"><o:p></o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Nathan,
            thanks for clarifying your plug load observations. Your
            explanation makes total sense. On the related note, the
            latest LEED EAc1 template includes the following info (based
            on ASHRAE Applications handbook) for the impact of occupant
            demographics on HW usage. Perhaps you can reference this
            data (also used in EPA HRMF program) to justify modeling
            lower plug loads for certain projects. But I can also see
            that rating authorities may reject this logic and insist on
            using “typical” plug loads in the model, recognizing that
            occupant demographics may change over the life of the
            building.  </span><o:p></o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
        <p class="MsoNormal"><img
            style="width:13.3541in;height:1.1875in" id="Picture_x0020_2"
            src="cid:part8.86DFD154.7DB48E5C@whiteboxtechnologies.com"
            height="114" border="0" width="1282"><o:p></o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Nathan Miller [mailto:<a moz-do-not-send="true"
                  href="mailto:nathanm@rushingco.com">nathanm@rushingco.com</a>]
                <br>
                <b>Sent:</b> Tuesday, March 14, 2017 9:38 AM<br>
                <b>To:</b> Chris Jones <<a moz-do-not-send="true"
                  href="mailto:Christopher.Jones@RWDI.com">Christopher.Jones@RWDI.com</a>>;
                David Griffin II <<a moz-do-not-send="true"
                  href="mailto:DGriffin@archnexus.com">DGriffin@archnexus.com</a>>;
                Maria Karpman <<a moz-do-not-send="true"
                  href="mailto:maria.karpman@karpmanconsulting.net">maria.karpman@karpmanconsulting.net</a>>;
                Michael Campbell <<a moz-do-not-send="true"
                  href="mailto:mcamp1206@gmail.com">mcamp1206@gmail.com</a>>;
                Joe Huang <<a moz-do-not-send="true"
                  href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>><br>
                <b>Cc:</b> <a moz-do-not-send="true"
                  href="mailto:equest-users@onebuilding.org">equest-users@onebuilding.org</a><br>
                <b>Subject:</b> RE: [Equest-users] Wall insulation in
                multifamily buildings</span><o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"> <o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">I
            can’t think of the last high-rise project I worked on that
            stayed anywhere near 25% WWR. 40-50% is very much the norm
            in Seattle (climate where I do most of my modeling work).
            Owners want 60%+.  Mid-rise resi (and mixed use), I do tend
            to see 25-35% WWR as typical.
          </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">When
            we do the envelope sensitivity analysis on high rise
            multifamily projects, honestly the glazing percentage isn’t
            as bad a penalty as you’d think. Like on the order of
            0.1-0.25% energy penalty for each 1% increase in glazing
            when we are already in the 40%+ glazing band, meaning we are
            comparing extra glazing to opaque wall. This is with a WSHP
            system serving residences. If it is more of a traditional
            hydronic job, that penalty seems to go up a little, but
            still isn’t a killer. </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal" style="margin-bottom:12.0pt"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Using
            standard ESMFHRSG plug loads we see the conditioning load of
            the buildings driven by internal loads, ventilation, and
            infiltration, not envelope. Related to the previous comment
            in this thread from Maria:</span><o:p></o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">“I
            am curious about the reasoning behind Nathan’s comment that
            “… many of us in the Seattle market are starting to believe
            the standard plug/misc load assumptions from the Energy Star
            MF High Rise Sim Guidelines overestimate that energy use”.<span
              style="color:#1F497D">
            </span>EPA’s plug loads are 4 times lower than COMNET’s for
            Multifamily/Residential, and are also lower than the loads
            in PNNL High Rise Apartment prototype. Passive house
            protocols are the only two sources that I know off that
            prescribe lower in-unit loads - Passivehaus Institute (PHI)
            loads are less than half of EPA’s, and US passive house
            off-shoot (PHIUS) loads are 15% lower than EPA’s. In
            general, in-unit electricity consumption can vary
            significantly depending on occupant demographics (by factor
            of 10 based on some papers), so both COMNET and PHI may be
            correct for <u>some</u> apartments. We compared EPA
            assumptions to the in-unit electricity usage in several
            apartment complexes in NJ, and the numbers were in the right
            ballpark, so appear to represent reasonable averages.”  </span><o:p></o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Her
            comment made me realize I’m suffering a bit from
            selection-bias. The projects I tend to model are the newest
            multifamily projects to hit the market. These projects in
            Seattle are almost all studios and 1 BR, with a few 2 BR and
            penthouses sprinkled in. They aren’t serving as housing for
            families, but more professionally-employed individuals, who
            don’t cook much, who probably concentrate their electronics
            (laptop plus maybe a flat screen) more than the typical
            American family, and certainly do less laundry. Some of the
            trend on housing design seems to be minimal living space and
            more amenities. That is probably why the national averages
            for dwelling  unit plug loads seem high for THE TYPE OF
            PROJECTS I WORK ON. </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Hope
            that makes more sense (given some reflection).
          </span><o:p></o:p></p>
        <div>
          <p class="MsoNormal" style="margin-top:1.0pt"><b><span
style="font-size:10.0pt;font-family:"Verdana",sans-serif;color:#632423"> </span></b><o:p></o:p></p>
          <p class="MsoNormal" style="margin-bottom:4.0pt"><b><span
style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#6F1200">Nathan
                Miller, PE, LEED AP BD+C</span></b><b><span
style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#632423">
                –
              </span></b><i><span
style="font-size:8.0pt;font-family:"Verdana",sans-serif;color:black">Mechanical
                Engineer/Senior Energy Analyst</span></i><o:p></o:p></p>
          <p class="MsoNormal" style="margin-top:3.0pt;line-height:115%"><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200">RUSHING</span></b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#BFAB7F">
            </span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">|</span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#BFAB7F">
            </span><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200">O</span></b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#A50021">
            </span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">206-285-7100
              |</span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#BFAB7F"></span><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200">C</span></b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#A50021">
            </span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">207-650-3942</span><o:p></o:p></p>
          <p class="MsoNormal" style="line-height:115%"><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200"><a
                  moz-do-not-send="true"
                  href="http://www.rushingco.com/"><span
                    style="color:#6F1200">www.rushingco.com</span></a></span></b><o:p></o:p></p>
        </div>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Equest-users [mailto:<a moz-do-not-send="true"
                  href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Chris Jones via Equest-users<br>
                <b>Sent:</b> Tuesday, March 14, 2017 7:46 AM<br>
                <b>To:</b> David Griffin II <<a
                  moz-do-not-send="true"
                  href="mailto:DGriffin@archnexus.com">DGriffin@archnexus.com</a>>;
                Maria Karpman <<a moz-do-not-send="true"
                  href="mailto:maria.karpman@karpmanconsulting.net">maria.karpman@karpmanconsulting.net</a>>;
                Michael Campbell <<a moz-do-not-send="true"
                  href="mailto:mcamp1206@gmail.com">mcamp1206@gmail.com</a>>;
                Joe Huang <<a moz-do-not-send="true"
                  href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>><br>
                <b>Cc:</b> <a moz-do-not-send="true"
                  href="mailto:equest-users@onebuilding.org">equest-users@onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] Wall insulation in
                multifamily buildings</span><o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"> <o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">My
            only comment is that developers and contractors like curtain
            wall (window wall for high rise MURBS) because it is less
            expensive to install and can be installed in any weather.
            This may be the main reason we see glass towers north of the
            49<sup>th</sup>.</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <div>
          <p class="MsoNormal"><b><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"> </span></b><o:p></o:p></p>
          <table class="MsoNormalTable" style="width:6.25in" border="0"
            cellpadding="0" cellspacing="20" width="600">
            <tbody>
              <tr>
                <td style="width:52.5pt;padding:0in 0in 0in 0in"
                  valign="top" width="70">
                  <p class="MsoNormal"><a moz-do-not-send="true"
                      href="http://www.rwdi.com/assets/logos/RWDI-logo.gif"><span
                        style="color:#1F497D;text-decoration:none"><img
                          style="width:.7291in;height:.7291in"
                          id="Picture_x0020_1"
                          src="cid:part23.4698481B.04DFBD30@whiteboxtechnologies.com"
                          alt="Title: RWDI - Description: RWDI logo"
                          height="70" border="0" width="70"></span></a><o:p></o:p></p>
                </td>
                <td style="width:363.0pt;padding:0in 0in 0in 0in"
                  valign="top" width="484">
                  <p class="MsoNormal"
                    style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span
style="font-size:10.5pt;font-family:"Arial",sans-serif;color:#005EB8">Christopher
                        Jones, </span></b><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#005EB8">P.Eng.
                      </span></b><span
style="font-size:10.5pt;font-family:"Arial",sans-serif;color:#999999">|
                    </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:#999999">Senior
                      Energy Analyst</span><span
                      style="font-family:"Arial",sans-serif;color:#1F497D"><br>
                    </span><b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#999999">RWDI</span></b><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:#999999"><br>
                      901 King Street West, Suite 400, Toronto, ON M5V
                      3H5 Canada<br>
                      Tel: (519) 823-1311 ext 2052<br>
                      <a moz-do-not-send="true"
                        href="http://www.rwdi.com/"><span
                          style="color:#999999">rwdi.com</span></a></span><o:p></o:p></p>
                </td>
              </tr>
            </tbody>
          </table>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        </div>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:10.0pt;font-family:"Tahoma",sans-serif">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma",sans-serif">
                Equest-users [<a moz-do-not-send="true"
                  href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>David Griffin II via Equest-users<br>
                <b>Sent:</b> Monday, March 13, 2017 7:46 PM<br>
                <b>To:</b> Maria Karpman; Michael Campbell; Joe Huang<br>
                <b>Cc:</b> <a moz-do-not-send="true"
                  href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] Wall insulation in
                multifamily buildings</span><o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"> <o:p></o:p></p>
        <p class="MsoNormal"><a moz-do-not-send="true"
            name="_MailEndCompose"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">I
              thought I might chime in on this discussion as well to
              drive a few points home.</span></a><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">I
            have attached a file illustrating a graph to explain Joe’s
            comment below. It shows diminishing returns from increased
            insulation. When it comes to effective envelope ECMs for
            projects. I focus on two very important things:</span><o:p></o:p></p>
        <p class="MsoListParagraph" style="text-indent:-.25in"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">1)</span><span
            style="font-size:7.0pt;color:#1F497D">     
          </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Lower
            infiltration will save you more energy than any other
            envelope ECM. However, it is hard to get an owner to buy off
            on this and enforce the requirement with the contractor.
            Typically, an envelope consultant will be brought in to
            assist the architect with details, supervise the contractor
            during construction, and test the building (or a portion
            thereof) to verify performance. You can see how something
            like this is hard sell to an owner because it can be a
            costly process, and if the building fails the blower door
            test, the contractor has a $$ issue and the a lot of rework.</span><o:p></o:p></p>
        <p class="MsoListParagraph" style="text-indent:-.25in"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">2)</span><span
            style="font-size:7.0pt;color:#1F497D">     
          </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Window-to-Wall
            Ratio (WWR) reduction is great. On the curve illustrated in
            the attached file, you essentially replace an expensive
            window with a cheaper wall assembly and saving more energy!
            It’s a true win-win-win. However, windows exist for more
            reasons than daylight controls. Comfort and views are
            essential for occupants. Some architects may also argue they
            are essential for aesthetics as well, so you have to have a
            target in mind for the project you are willing to negotiate.
            On commercial projects, I generally shoot for 25% WWR.</span><o:p></o:p></p>
        <p class="MsoListParagraph" style="text-indent:-.25in"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">3)</span><span
            style="font-size:7.0pt;color:#1F497D">     
          </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Window
            upgrades are next since they have the most potential to save
            energy on the illustrated curve. Since you tried to minimize
            the WWR on #2, this ECM will be cheaper than it would have
            been otherwise – always saving the client $$ </span><span
            style="font-size:11.0pt;font-family:Wingdings;color:#1F497D">J</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">
            This includes glazing and frames.</span><o:p></o:p></p>
        <p class="MsoListParagraph" style="text-indent:-.25in"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">4)</span><span
            style="font-size:7.0pt;color:#1F497D">     
          </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">After
            all three of the above items are addressed, I start to talk
            about added insulation in the walls, roof, etc.</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Anyway,
            this is my approach on new construction. Is this what you
            guys see, or am I missing something?</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Let
            me know.</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <table class="MsoNormalTable" style="width:100.0%" border="0"
          cellpadding="0" cellspacing="0" width="100%">
          <tbody>
            <tr>
              <td style="width:60.0pt;padding:0in 9.75pt 0in 0in"
                valign="top" width="80">
                <p class="MsoNormal"><a moz-do-not-send="true"
                    href="http://www.archnexus.com"><span
                      style="border:solid windowtext
                      1.0pt;padding:0in;text-decoration:none"><img
                        style="width:.8333in;height:1.0312in"
                        id="_x0000_i1028"
                        src="cid:part29.D695D5A4.749EA079@whiteboxtechnologies.com"
                        alt="Image removed by sender. ARCH | NEXUS"
                        height="99" border="0" width="80"></span></a><o:p></o:p></p>
              </td>
              <td style="width:.75pt;border:none;border-left:solid
                #009AD9 1.0pt;padding:0in 0in 0in 0in" valign="top"
                width="1">
                <p class="MsoNormal">  <o:p></o:p></p>
              </td>
              <td style="padding:0in 0in 0in 6.75pt">
                <table class="MsoNormalTable" style="width:100.0%"
                  border="0" cellpadding="0" cellspacing="0"
                  width="100%">
                  <tbody>
                    <tr>
                      <td colspan="2" style="padding:0in 0in 0in 0in">
                        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Verdana",sans-serif;color:#52616E">DAVID
                            W. GRIFFIN II</span><o:p></o:p></p>
                      </td>
                    </tr>
                    <tr>
                      <td colspan="2" style="padding:4.5pt 0in 0in 0in">
                        <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Verdana",sans-serif;color:#52616E">BEMP<br>
                            ENERGY ANALYST</span><o:p></o:p></p>
                      </td>
                    </tr>
                    <tr>
                      <td colspan="2" style="padding:4.5pt 0in 4.5pt
                        0in">
                        <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Verdana",sans-serif;color:#52616E">2505
                            E Parleys Way<br>
                            Salt Lake City, UT 84109 </span><o:p></o:p></p>
                      </td>
                    </tr>
                    <tr>
                      <td style="width:100.0%;padding:0in 0in 0in
                        2.25pt" nowrap="nowrap" width="100%">
                        <p class="MsoNormal"><b><span
style="font-size:7.5pt;font-family:"Verdana",sans-serif;color:#52616E">Office</span></b><span
style="font-size:7.5pt;font-family:"Verdana",sans-serif;color:#52616E"> 801.924.5028
                          </span><o:p></o:p></p>
                      </td>
                      <td style="padding:0in 0in 0in 0in"><br>
                      </td>
                    </tr>
                    <tr>
                      <td colspan="2" style="padding:4.5pt 0in 0in 0in"
                        nowrap="nowrap">
                        <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Verdana",sans-serif;color:#52616E"><a
                              moz-do-not-send="true"
                              href="http://www.archnexus.com"><span
                                style="color:#52616E;text-decoration:none">archnexus.com</span></a></span><o:p></o:p></p>
                      </td>
                    </tr>
                    <tr>
                      <td colspan="2" style="padding:4.5pt 0in 0in 0in"
                        nowrap="nowrap">
                        <p class="MsoNormal"><a moz-do-not-send="true"
                            href="https://twitter.com/arch_nexus"><span
                              style="border:solid windowtext
                              1.0pt;padding:0in;text-decoration:none"><img
                                style="width:.3125in;height:.2291in"
                                id="_x0000_i1029"
                                src="cid:part32.B65E69E0.9D68B70E@whiteboxtechnologies.com"
                                alt="Image removed by sender. Twitter"
                                height="22" border="0" width="30"></span></a><a
                            moz-do-not-send="true"
href="https://www.facebook.com/pages/Architectural-Nexus/179588705397563?ref=ts&fref=ts"><span
                              style="border:solid windowtext
                              1.0pt;padding:0in;text-decoration:none"><img
                                style="width:.3125in;height:.2291in"
                                id="_x0000_i1030"
                                src="cid:part32.B65E69E0.9D68B70E@whiteboxtechnologies.com"
                                alt="Image removed by sender. Facebook"
                                height="22" border="0" width="30"></span></a><a
                            moz-do-not-send="true"
href="https://www.youtube.com/channel/UCYRPWKF-yp-AUiI8ia2XfKw?feature=mhee"><span
                              style="border:solid windowtext
                              1.0pt;padding:0in;text-decoration:none"><img
                                style="width:.3125in;height:.2291in"
                                id="_x0000_i1031"
                                src="cid:part32.B65E69E0.9D68B70E@whiteboxtechnologies.com"
                                alt="Image removed by sender. Youtube"
                                height="22" border="0" width="30"></span></a><a
                            moz-do-not-send="true"
                            href="https://www.linkedin.com/company/architectural-nexus"><span
                              style="border:solid windowtext
                              1.0pt;padding:0in;text-decoration:none"><img
                                style="width:.3125in;height:.2291in"
                                id="_x0000_i1032"
                                src="cid:part32.B65E69E0.9D68B70E@whiteboxtechnologies.com"
                                alt="Image removed by sender. LinkedIn"
                                height="22" border="0" width="30"></span></a><o:p></o:p></p>
                      </td>
                    </tr>
                  </tbody>
                </table>
              </td>
            </tr>
          </tbody>
        </table>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Maria Karpman via Equest-users [<a
                  moz-do-not-send="true"
                  href="mailto:equest-users@lists.onebuilding.org">mailto:equest-users@lists.onebuilding.org</a>]
                <br>
                <b>Sent:</b> Friday, March 10, 2017 9:24 PM<br>
                <b>To:</b> Michael Campbell; Joe Huang<br>
                <b>Cc:</b> <a moz-do-not-send="true"
                  href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] Wall insulation in
                multifamily buildings</span><o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"> <o:p></o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Few
            more thoughts on this:</span><o:p></o:p></p>
        <p class="MsoListParagraph" style="text-indent:-.25in">1)<span
            style="font-size:7.0pt">     
          </span><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">I
            agree with Joe and David that R-19 “…has already captured
            most of the energy losses (or savings) for the wall”. R-19
            is better than 90.1 2016 requirements for steel-framed wall
            in climate zone 4A, and since 90.1 requirements are set
            taking into account cost effectiveness, it is not surprising
            that further improvement does not often pay off.</span><o:p></o:p></p>
        <p class="MsoListParagraph" style="text-indent:-.25in">2)<span
            style="font-size:7.0pt">     
          </span><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Overwhelming
            majority of high performance multifamily projects have
            efficient heating systems, often condensing boilers or VRF
            HPs, which lowers heating costs and potential savings from
            envelope improvements.</span><o:p></o:p></p>
        <p class="MsoListParagraph" style="text-indent:-.25in">3)<span
            style="font-size:7.0pt">     
          </span><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">Most
            multifamily projects in North East have gas heating, and gas
            is cheap compared to electricity. For example EPA EStar MFHR
            projects in NY typically use $0.15/kWh and $1/Therm in
            performance rating calculations, which effectively makes BTU
            of electricity ~4.4 times more expensive than BTU of gas.
            This further shrinks contribution of heating toward the
            total building energy $, and reduces potential savings from
            envelope improvements. (Using source energy instead of $ in
            performance rating calculations makes envelope improvements
            more appealing, because with EPA PM site-to-source
            conversions BTU of electricity has only ~ 3 times greater
            weight than BTU of gas.)
          </span><o:p></o:p></p>
        <p class="MsoListParagraph" style="text-indent:-.25in">4)<span
            style="font-size:7.0pt">     
          </span><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif">I
            am curious about the reasoning behind Nathan’s comment that
            “… many of us in the Seattle market are starting to believe
            the standard plug/misc load assumptions from the Energy Star
            MF High Rise Sim Guidelines overestimate that energy use”.<span
              style="color:#1F497D">
            </span>EPA’s plug loads are 4 times lower than COMNET’s for
            Multifamily/Residential, and are also lower than the loads
            in PNNL High Rise Apartment prototype. Passive house
            protocols are the only two sources that I know off that
            prescribe lower in-unit loads - Passivehaus Institute (PHI)
            loads are less than half of EPA’s, and US passive house
            off-shoot (PHIUS) loads are 15% lower than EPA’s. In
            general, in-unit electricity consumption can vary
            significantly depending on occupant demographics (by factor
            of 10 based on some papers), so both COMNET and PHI may be
            correct for <u>some</u> apartments. We compared EPA
            assumptions to the in-unit electricity usage in several
            apartment complexes in NJ, and the numbers were in the right
            ballpark, so appear to represent reasonable averages.  </span><o:p></o:p></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;font-family:"Calibri",sans-serif"> </span><o:p></o:p></p>
        <p class="MsoNormal"><b><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
            Equest-users [mailto:<a moz-do-not-send="true"
              href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>]
            <b>On Behalf Of </b>Michael Campbell via Equest-users<br>
            <b>Sent:</b> Thursday, March 09, 2017 9:55 PM<br>
            <b>To:</b> Joe Huang <<a moz-do-not-send="true"
              href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>><br>
            <b>Cc:</b> equest-users <<a moz-do-not-send="true"
              href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>
            <b>Subject:</b> Re: [Equest-users] Wall insulation in
            multifamily buildings</span><o:p></o:p></p>
        <p class="MsoNormal"> <o:p></o:p></p>
        <div>
          <p class="MsoNormal">Wow, thank you everyone for the extremely
            helpful responses.  <o:p></o:p></p>
          <div>
            <p class="MsoNormal"> <o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal">To answer a few of the questions... the
              project is in NJ, Climate Zone 4A.<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal">I did account for the thermal bridging
              of the walls studs.  This project has some metals studs
              and some wood studs and I accounted for both using
              Appendix A of ASHRAE 90.1-2013.<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"> <o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal">Nathan, thanks for the input
              specifically regarding the Energy Star Multifamily High
              Rise inputs values.  This particular project is
              participating in the ESMFHR Program so I am using their
              guidelines for equipment/plug loads.<o:p></o:p></p>
          </div>
        </div>
        <div>
          <p class="MsoNormal"> <o:p></o:p></p>
          <div>
            <p class="MsoNormal">On Thu, Mar 9, 2017 at 6:32 PM, Joe
              Huang via Equest-users <<a moz-do-not-send="true"
                href="mailto:equest-users@lists.onebuilding.org"
                target="_blank">equest-users@lists.onebuilding.org</a>>
              wrote:<o:p></o:p></p>
            <blockquote style="border:none;border-left:solid #CCCCCC
              1.0pt;padding:0in 0in 0in
6.0pt;margin-left:4.8pt;margin-top:5.0pt;margin-right:0in;margin-bottom:5.0pt">
              <div>
                <p>I'd say the message is that R-19 wall insulation has
                  already "captured" most of the energy losses (or
                  savings) for the wall. 
                  <o:p></o:p></p>
                <p>(leaning heavily on my cane...) Back in 1986, I did a
                  project in support of ASHRAE and DOE residential
                  energy standards where I did what then seemed an
                  endless number of DOE-2 simulations (~ 20,000) for
                  five prototypical residences in 45 US climates, from
                  which using regression analyses I came up with the
                  component loads (KBtu/ft2) for various components of
                  the building (walls, roofs, internal loads, windows,
                  etc.).  Just picking out the wall component loads for
                  an apartment in Seattle, Miami, and DC, I get the
                  following:<o:p></o:p></p>
                <p class="MsoNormal" style="margin-bottom:12.0pt">   
                          Seattle             Miami           
                  Washington DC<br>
                              HL        CL        HL        CL       
                  HL        CL<br>
                  R-0     28.8     0.8       1.1       4.7       23.1  
                    1.5      <br>
                  R-11   10.9     0.4       0.3       1.5       
                  8.9      0.8<br>
                  R-19     7.1     0.3       0.2       0.9        5.9   
                    0.5<br>
                  R-34     3.9     0.2       0.1       0.5        3.2   
                    0.3<br>
                  <br>
                  So, by R-19, you're already on the flat part of the
                  curve and more insulation buys you very little.
                  <br>
                  <br>
                  Incidentally, this data base of component loads was
                  then turned into a PC program called PEAR (Program for
                  Energy Analysis of Residences) that then multiplied
                  the regression curves by the component scalar (ft2 of
                  wall, e.g.), and added them up to derive the heating
                  and cooling energy use of a house.<br>
                  PEAR is now so out-of-date technologically that the
                  display no longer functions, but I still think there's
                  some good basic information contained in the data
                  base.  David -  maybe something that could be updated
                  and maintained by IBPSA?  Or better yet, put it on the
                  Web ?<br>
                  <br>
                  source: "Technical documentation for a Residential
                  Energy Use Data Base Developed in Support of ASHRAE
                  Special Project 53", Huang, Ritschard, and Bull,<br>
                  LBL-24306,  November 1987.<o:p></o:p></p>
                <pre>Joe Huang<o:p></o:p></pre>
                <pre>White Box Technologies, Inc.<o:p></o:p></pre>
                <pre>346 Rheem Blvd., Suite 205A<o:p></o:p></pre>
                <pre>Moraga CA 94556<o:p></o:p></pre>
                <pre><a moz-do-not-send="true" href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
                <pre><a moz-do-not-send="true" href="http://weather.whiteboxtechnologies.com" target="_blank">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data<o:p></o:p></pre>
                <pre>(o) <a moz-do-not-send="true" href="tel:%28925%29%20388-0265" target="_blank">(925)388-0265</a><o:p></o:p></pre>
                <pre>(c) <a moz-do-not-send="true" href="tel:%28510%29%20928-2683" target="_blank">(510)928-2683</a><o:p></o:p></pre>
                <pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
                <div>
                  <div>
                    <div>
                      <p class="MsoNormal">On 3/9/2017 2:07 PM, David
                        Eldridge via Equest-users wrote:<o:p></o:p></p>
                    </div>
                  </div>
                </div>
                <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
                  <div>
                    <div>
                      <div>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">R-19
                            is not the worst starting point, I’d expect
                            diminishing returns going from good
                            insulation to great insulation, but a much
                            bigger jump in efficiency from poor to good
                            insulation levels.
                          </span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Make
                            sure you are modeling the cavity insulation
                            accurately including any equivalent assembly
                            resistance due to the studs. i.e. continuous
                            insulation requirements are there because
                            the cavity insulation is de-rated quite a
                            bit from the studs and which can be
                            important in colder climates.</span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">In
                            terms of an overall percentage difference
                            due to envelope changes you may also see
                            that window performance dominates if the WWR
                            is relatively high.</span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                        <div>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">David</span><o:p></o:p></p>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><u><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:black">                                                                                               
                              </span></u><o:p></o:p></p>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:8.0pt;font-family:"Calibri",sans-serif;color:black"> </span><o:p></o:p></p>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">David
                              S. Eldridge, Jr., P.E., LEED AP BD+C,
                              BEMP, BEAP, HBDP</span><o:p></o:p></p>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#244061">Grumman/Butkus
                                Associates</span></b><o:p></o:p></p>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><u><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:black">                                                                                               
                              </span></u><o:p></o:p></p>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:black"> </span><o:p></o:p></p>
                        </div>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                        <div>
                          <div style="border:none;border-top:solid
                            #E1E1E1 1.0pt;padding:3.0pt 0in 0in 0in">
                            <p class="MsoNormal"
                              style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                                Equest-users [<a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                                <b>On Behalf Of </b>Nathan Miller via
                                Equest-users<br>
                                <b>Sent:</b> Thursday, March 09, 2017
                                2:52 PM<br>
                                <b>To:</b> Michael Campbell <a
                                  moz-do-not-send="true"
                                  href="mailto:mcamp1206@gmail.com"
                                  target="_blank">
                                  <mcamp1206@gmail.com></a><br>
                                <b>Cc:</b> <a moz-do-not-send="true"
                                  href="mailto:equest-users@lists.onebuilding.org"
                                  target="_blank">equest-users@lists.onebuilding.org</a><br>
                                <b>Subject:</b> Re: [Equest-users] Wall
                                insulation in multifamily buildings</span><o:p></o:p></p>
                          </div>
                        </div>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Don’t
                            know where your building is located, but on
                            the Seattle area multifamily projects we
                            routinely model, envelope has very little
                            impact on building energy use. DHW and
                            ventilation seem to be the items we have the
                            most influence over that really can change
                            the energy consumption.
                          </span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">FWIW,
                            many of us in the Seattle market are
                            starting to believe the standard plug/misc
                            load assumptions from the Energy Star MF
                            High Rise Sim Guidelines (if you are using
                            them) overestimate that energy use, and
                            result in more “free heat” in the building
                            and thus less sensitivity to envelope
                            changes (among other implications).
                          </span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                        <p class="MsoNormal" style="margin-top:1.0pt"><b><span
style="font-size:10.0pt;font-family:"Verdana",sans-serif;color:#632423"> </span></b><o:p></o:p></p>
                        <p class="MsoNormal" style="margin-bottom:4.0pt"><b><span
style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#6F1200">Nathan
                              Miller, PE, LEED AP BD+C</span></b><b><span
style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#632423">
                              –
                            </span></b><i><span
style="font-size:8.0pt;font-family:"Verdana",sans-serif;color:black">Mechanical
                              Engineer/Senior Energy Analyst</span></i><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="margin-top:3.0pt;line-height:115%"><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200">RUSHING</span></b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#BFAB7F">
                          </span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">|</span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#BFAB7F">
                          </span><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200">O</span></b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#A50021">
                          </span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black"><a
                              moz-do-not-send="true"
                              href="tel:%28206%29%20285-7100"
                              target="_blank">206-285-7100</a> |</span><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200">C</span></b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#A50021">
                          </span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black"><a
                              moz-do-not-send="true"
                              href="tel:%28207%29%20650-3942"
                              target="_blank">207-650-3942</a></span><o:p></o:p></p>
                        <p class="MsoNormal" style="line-height:115%"><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200"><a
                                moz-do-not-send="true"
                                href="http://www.rushingco.com/"
                                target="_blank"><span
                                  style="color:#6F1200">www.rushingco.com</span></a></span></b><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"> </span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                            Equest-users [<a moz-do-not-send="true"
                              href="mailto:equest-users-bounces@lists.onebuilding.org"
                              target="_blank">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                            <b>On Behalf Of </b>Michael Campbell via
                            Equest-users<br>
                            <b>Sent:</b> Thursday, March 09, 2017 3:44
                            PM<br>
                            <b>To:</b> equest-users <<a
                              moz-do-not-send="true"
                              href="mailto:equest-users@lists.onebuilding.org"
                              target="_blank">equest-users@lists.onebuilding.org</a>><br>
                            <b>Subject:</b> [Equest-users] Wall
                            insulation in multifamily buildings</span><o:p></o:p></p>
                        <p class="MsoNormal"
                          style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto"> <o:p></o:p></p>
                        <div>
                          <div>
                            <div>
                              <div>
                                <div>
                                  <p class="MsoNormal"
                                    style="margin-bottom:12.0pt">Hello
                                    eQUEST Users,<o:p></o:p></p>
                                </div>
                                <p class="MsoNormal"
                                  style="margin-bottom:12.0pt">I've been
                                  working on a model for a multifamily
                                  building, 5 stories, approximately
                                  300,000 square feet.  I've been
                                  running a few iterations of the model
                                  to see how changes to the wall
                                  assembly affect the model results.  <br>
                                  <br>
                                  What I've found is that changes in the
                                  wall assembly seem to have a minimal
                                  impact on the model results.  I just
                                  did a comparison where I took an
                                  assembly with R-19 cavity insulation
                                  and 2" rigid insulation and compared
                                  that to the same assembly but without
                                  the rigid insulation.  This was
                                  applied to the entire building.  What
                                  I found was only a 0.4% increase in
                                  total energy cost after taking out the
                                  rigid insulation.  I'm wondering if
                                  others have found similar results in
                                  multifamily buildings?<o:p></o:p></p>
                              </div>
                              <p class="MsoNormal"
                                style="margin-bottom:12.0pt">Any input
                                is appreciated.<o:p></o:p></p>
                            </div>
                            <p class="MsoNormal"
                              style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Thank
                              you,<o:p></o:p></p>
                          </div>
                          <p class="MsoNormal"
                            style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto">Mike
                            Campbell<o:p></o:p></p>
                        </div>
                      </div>
                      <p class="MsoNormal" style="margin-bottom:12.0pt"> <o:p></o:p></p>
                    </div>
                  </div>
                  <pre>_______________________________________________<o:p></o:p></pre>
                  <pre>Equest-users mailing list<o:p></o:p></pre>
                  <pre><a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><o:p></o:p></pre>
                  <pre>To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></pre>
                </blockquote>
                <p class="MsoNormal"> <o:p></o:p></p>
              </div>
              <p class="MsoNormal" style="margin-bottom:12.0pt"><br>
                _______________________________________________<br>
                Equest-users mailing list<br>
                <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
                  target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                To unsubscribe from this mailing list send  a blank
                message to <a moz-do-not-send="true"
                  href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">
                  EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></p>
            </blockquote>
          </div>
          <p class="MsoNormal"> <o:p></o:p></p>
        </div>
        <div>
          <div class="MsoNormal" style="text-align:center"
            align="center"><span style="font-size:7.0pt">
              <hr align="center" size="2" width="100%">
            </span></div>
          <p class="MsoNormal"><b><span style="font-size:7.0pt">RWDI - A
                Platinum Member of Canada's 50 Best Managed Companies</span></b><span
              style="font-size:7.0pt">
              <br>
              This communication is intended for the sole use of the
              party to whom it was addressed and may contain information
              that is privileged and/or confidential. Any other
              distribution, copying or disclosure is strictly
              prohibited. If you received this email in error, please
              notify us immediately by replying to this email and delete
              the message without retaining any hard or electronic
              copies of same. Outgoing emails are scanned for viruses,
              but no warranty is made to their absence in this email or
              attachments. If you require any information supplied by
              RWDI in a different format to facilitate accessibility,
              contact the sender of the email, email
              <a moz-do-not-send="true" href="mailto:solutions@rwdi.com">solutions@rwdi.com</a>
              or call +1.519.823.1311.
            </span><o:p></o:p></p>
          <div class="MsoNormal" style="text-align:center"
            align="center"><span style="font-size:7.0pt">
              <hr align="center" size="2" width="100%">
            </span></div>
        </div>
        <p class="MsoNormal"><br>
______________________________________________________________________<br>
          This email has been scanned by the Symantec Email
          Security.cloud service.<br>
______________________________________________________________________<o:p></o:p></p>
      </div>
    </blockquote>
    <br>
  </body>
</html>