<html>
  <head>
    <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <p>I'd say the message is that R-19 wall insulation has already
      "captured" most of the energy losses (or savings) for the wall.  <br>
    </p>
    <p>(leaning heavily on my cane...) Back in 1986, I did a project in
      support of ASHRAE and DOE residential energy standards where I did
      what then seemed an endless number of DOE-2 simulations (~ 20,000)
      for five prototypical residences in 45 US climates, from which
      using regression analyses I came up with the component loads
      (KBtu/ft2) for various components of the building (walls, roofs,
      internal loads, windows, etc.).  Just picking out the wall
      component loads for an apartment in Seattle, Miami, and DC, I get
      the following:<br>
    </p>
                Seattle             Miami            Washington DC<br>
                HL        CL        HL        CL        HL        CL<br>
    R-0     28.8     0.8       1.1       4.7       23.1     1.5      <br>
    R-11   10.9     0.4       0.3       1.5        8.9      0.8<br>
    R-19     7.1     0.3       0.2       0.9        5.9      0.5<br>
    R-34     3.9     0.2       0.1       0.5        3.2      0.3<br>
    <br>
    So, by R-19, you're already on the flat part of the curve and more
    insulation buys you very little. <br>
    <br>
    Incidentally, this data base of component loads was then turned into
    a PC program called PEAR (Program for Energy Analysis of Residences)
    that then multiplied the regression curves by the component scalar
    (ft2 of wall, e.g.), and added them up to derive the heating and
    cooling energy use of a house.<br>
    PEAR is now so out-of-date technologically that the display no
    longer functions, but I still think there's some good basic
    information contained in the data base.  David -  maybe something
    that could be updated and maintained by IBPSA?  Or better yet, put
    it on the Web ?<br>
    <br>
    source: "Technical documentation for a Residential Energy Use Data
    Base Developed in Support of ASHRAE Special Project 53", Huang,
    Ritschard, and Bull,<br>
    LBL-24306,  November 1987.<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 3/9/2017 2:07 PM, David Eldridge via
      Equest-users wrote:<br>
    </div>
    <blockquote
cite="mid:MWHPR06MB2541FD56EF4B1145F4E9253AA0210@MWHPR06MB2541.namprd06.prod.outlook.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Wingdings;
        panose-1:5 0 0 0 0 0 0 0 0 0;}
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Verdana;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
        {mso-style-priority:34;
        margin-top:0in;
        margin-right:0in;
        margin-bottom:0in;
        margin-left:.5in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
span.EmailStyle17
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle18
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle19
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
/* List Definitions */
@list l0
        {mso-list-id:124006682;
        mso-list-type:hybrid;
        mso-list-template-ids:-173792100 67698689 67698691 67698693 67698689 67698691 67698693 67698689 67698691 67698693;}
@list l0:level1
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:Symbol;}
@list l0:level2
        {mso-level-number-format:bullet;
        mso-level-text:o;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:"Courier New";}
@list l0:level3
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:Wingdings;}
@list l0:level4
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:Symbol;}
@list l0:level5
        {mso-level-number-format:bullet;
        mso-level-text:o;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:"Courier New";}
@list l0:level6
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:Wingdings;}
@list l0:level7
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:Symbol;}
@list l0:level8
        {mso-level-number-format:bullet;
        mso-level-text:o;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:"Courier New";}
@list l0:level9
        {mso-level-number-format:bullet;
        mso-level-text:;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:Wingdings;}
ol
        {margin-bottom:0in;}
ul
        {margin-bottom:0in;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">R-19
            is not the worst starting point, I’d expect diminishing
            returns going from good insulation to great insulation, but
            a much bigger jump in efficiency from poor to good
            insulation levels. <o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Make
            sure you are modeling the cavity insulation accurately
            including any equivalent assembly resistance due to the
            studs. i.e. continuous insulation requirements are there
            because the cavity insulation is de-rated quite a bit from
            the studs and which can be important in colder climates.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">In
            terms of an overall percentage difference due to envelope
            changes you may also see that window performance dominates
            if the WWR is relatively high.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">David</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
          <p class="MsoNormal"><u><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:black">                                                                                               
              </span></u><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Calibri",sans-serif;color:black"> </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">David
              S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#244061">Grumman/Butkus
                Associates</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><u><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:black">                                                                                               
              </span></u><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:black"> </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
                Equest-users
                [<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Nathan Miller via Equest-users<br>
                <b>Sent:</b> Thursday, March 09, 2017 2:52 PM<br>
                <b>To:</b> Michael Campbell <a class="moz-txt-link-rfc2396E" href="mailto:mcamp1206@gmail.com"><mcamp1206@gmail.com></a><br>
                <b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> Re: [Equest-users] Wall insulation in
                multifamily buildings<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">Don’t
            know where your building is located, but on the Seattle area
            multifamily projects we routinely model, envelope has very
            little impact on building energy use. DHW and ventilation
            seem to be the items we have the most influence over that
            really can change the energy consumption.
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D">FWIW,
            many of us in the Seattle market are starting to believe the
            standard plug/misc load assumptions from the Energy Star MF
            High Rise Sim Guidelines (if you are using them)
            overestimate that energy use, and result in more “free heat”
            in the building and thus less sensitivity to envelope
            changes (among other implications).
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal" style="margin-top:1.0pt"><b><span
style="font-size:10.0pt;font-family:"Verdana",sans-serif;color:#632423"><o:p> </o:p></span></b></p>
        <p class="MsoNormal"
style="mso-margin-top-alt:1.0pt;margin-right:0in;margin-bottom:4.0pt;margin-left:0in"><b><span
style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#6F1200">Nathan
              Miller, PE, LEED AP BD+C</span></b><b><span
style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#632423">
              –
            </span></b><i><span
style="font-size:8.0pt;font-family:"Verdana",sans-serif;color:black">Mechanical
              Engineer/Senior Energy Analyst</span></i><b><span
style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#632423"><o:p></o:p></span></b></p>
        <p class="MsoNormal" style="margin-top:3.0pt;line-height:115%"><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200">RUSHING</span></b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#BFAB7F">
          </span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">|</span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#BFAB7F">
          </span><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200">O</span></b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#A50021">
          </span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">206-285-7100
            |</span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#BFAB7F"></span><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200">C</span></b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#A50021">
          </span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">207-650-3942</span><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#BFAB7F"><o:p></o:p></span></p>
        <p class="MsoNormal" style="line-height:115%"><b><span
style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200"><a
                moz-do-not-send="true" href="http://www.rushingco.com/"><span
                  style="color:#6F1200">www.rushingco.com</span></a></span></b><b><span
style="font-size:9.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6F1200"><o:p></o:p></span></b></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><b><span
              style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
            Equest-users [<a moz-do-not-send="true"
              href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
            <b>On Behalf Of </b>Michael Campbell via Equest-users<br>
            <b>Sent:</b> Thursday, March 09, 2017 3:44 PM<br>
            <b>To:</b> equest-users <<a moz-do-not-send="true"
              href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>
            <b>Subject:</b> [Equest-users] Wall insulation in
            multifamily buildings<o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <div>
            <div>
              <div>
                <div>
                  <p class="MsoNormal" style="margin-bottom:12.0pt">Hello
                    eQUEST Users,<o:p></o:p></p>
                </div>
                <p class="MsoNormal" style="margin-bottom:12.0pt">I've
                  been working on a model for a multifamily building, 5
                  stories, approximately 300,000 square feet.  I've been
                  running a few iterations of the model to see how
                  changes to the wall assembly affect the model
                  results.  <br>
                  <br>
                  What I've found is that changes in the wall assembly
                  seem to have a minimal impact on the model results.  I
                  just did a comparison where I took an assembly with
                  R-19 cavity insulation and 2" rigid insulation and
                  compared that to the same assembly but without the
                  rigid insulation.  This was applied to the entire
                  building.  What I found was only a 0.4% increase in
                  total energy cost after taking out the rigid
                  insulation.  I'm wondering if others have found
                  similar results in multifamily buildings?<o:p></o:p></p>
              </div>
              <p class="MsoNormal" style="margin-bottom:12.0pt">Any
                input is appreciated.<o:p></o:p></p>
            </div>
            <p class="MsoNormal">Thank you,<o:p></o:p></p>
          </div>
          <p class="MsoNormal">Mike Campbell<o:p></o:p></p>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>