A long time ago (like 1993-2005), I was marketing a program DrawBDL
to display DOE-2 building models. Following is how DrawBDL would
display a similar 5-zone/floor building model:<br>
<p><img title="unnamed_1.png"
src="cid:part1.FD0A0F91.C28CC5C3@whiteboxtechnologies.com"
alt="" height="1024" width="936"></p>
<p>At that time, I was toying around with the idea of using the
FLOOR-MULTIPLIER number to create the missing floors, but that
would require the user to specify an appropriate Z of the
representative floor, whether it's at the lowest, the middle, or
maybe even the top of the floors.</p>
<p>The building model would then be displayed as this (done using
cut-and-paste of the DrawBDL drawing, which uses Microsoft
primitive drawing tools):<br>
</p>
<p><img src="cid:part2.E2DFB5A3.35BD9B78@whiteboxtechnologies.com"
alt=""><br>
</p>
<pre class="moz-signature" cols="90">
<font size="+1">I also thought of adding an option for the user to display the duplicated floors with a lighter shade to indicate their prevenance.
But alas, these were all just ideas, and since DrawBDL sales tanked after 2004, and my graphics programmer got a real job,
I never did anything to DrawBDL except to add an EnergyPlus import, which was actually quite easy to do because the EnergyPlus
idf is completely explicit, with no shortcuts like LIKE, SET DEFAULT, etc. In fact, doing DrawBDL for DOE-2.1E was probably the
harder thing to do than for eQUEST or EnergyPlus :-)
By the way, I'm still passively marketing DrawBDL, but have to caution that it works only with DOE-2.1E and EnergyPlus-3.0,
see Web site at <a class="moz-txt-link-abbreviated" href="http://www.drawbdl.com">www.drawbdl.com</a> .
Joe </font>
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<div class="moz-cite-prefix">On 3/7/2017 2:35 PM, Keith Swartz via
Equest-users wrote:<br>
</div>
<blockquote
cite="mid:CY4PR1201MB0216493B994C8741ED2F4EC6AE2F0@CY4PR1201MB0216.namprd12.prod.outlook.com"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=windows-1252">
<meta name="Generator" content="Microsoft Word 15 (filtered
medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
<style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Verdana;
panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman",serif;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p.msonormal0, li.msonormal0, div.msonormal0
{mso-style-name:msonormal;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman",serif;}
p.yiv5601753002msonormal, li.yiv5601753002msonormal, div.yiv5601753002msonormal
{mso-style-name:yiv5601753002msonormal;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman",serif;}
p.yiv5601753002msochpdefault, li.yiv5601753002msochpdefault, div.yiv5601753002msochpdefault
{mso-style-name:yiv5601753002msochpdefault;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Times New Roman",serif;}
p.yiv5601753002msonormal1, li.yiv5601753002msonormal1, div.yiv5601753002msonormal1
{mso-style-name:yiv5601753002msonormal1;
margin-top:0in;
margin-right:0in;
margin-bottom:8.0pt;
margin-left:0in;
line-height:105%;
font-size:11.0pt;
font-family:"Calibri",sans-serif;}
p.yiv5601753002msochpdefault1, li.yiv5601753002msochpdefault1, div.yiv5601753002msochpdefault1
{mso-style-name:yiv5601753002msochpdefault1;
mso-margin-top-alt:auto;
margin-right:0in;
mso-margin-bottom-alt:auto;
margin-left:0in;
font-size:12.0pt;
font-family:"Calibri",sans-serif;}
span.yiv5601753002msohyperlink
{mso-style-name:yiv5601753002msohyperlink;}
span.yiv5601753002msohyperlinkfollowed
{mso-style-name:yiv5601753002msohyperlinkfollowed;}
span.yiv5601753002emailstyle17
{mso-style-name:yiv5601753002emailstyle17;}
span.yiv5601753002msohyperlink1
{mso-style-name:yiv5601753002msohyperlink1;
color:#0563C1;
text-decoration:underline;}
span.yiv5601753002msohyperlinkfollowed1
{mso-style-name:yiv5601753002msohyperlinkfollowed1;
color:#954F72;
text-decoration:underline;}
span.yiv5601753002emailstyle171
{mso-style-name:yiv5601753002emailstyle171;
font-family:"Calibri",sans-serif;
color:windowtext;}
span.EmailStyle28
{mso-style-type:personal;
font-family:"Calibri",sans-serif;
color:windowtext;}
span.EmailStyle29
{mso-style-type:personal-reply;
font-family:"Arial",sans-serif;
color:windowtext;
font-weight:normal;
font-style:normal;
text-decoration:none none;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif">Another
trick to get intermediate floors to show up in the graphic
is to make one of the zones an “atrium.” Be careful with the
zone selection for this if you need the floor area, but an
elevator or chase could be a good choice. Doing this truly
creates separate floors in the model, which might be a
problem with run time and file size, but maybe not.
<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif">If
there is no useful zone for this, then I suggest doing a
“save as…” and using this “atrium” file just for the pretty
picture.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><img style="width:3.7708in;height:3.6979in"
id="_x0000_i1030"
src="cid:part3.4D8D6EE2.6BDEC62D@whiteboxtechnologies.com"
height="355" width="362"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif">In
the DD wizard, Screen 2 for the shell, click on the “Zone
Names and Characteristics” button.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><img style="width:4.1145in;height:3.0625in"
id="Picture_x0020_2"
src="cid:part4.62020485.1607787B@whiteboxtechnologies.com"
height="294" width="395"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif">Click
on the desired zone, then check the box in the upper right
for “Multi-Level Space (atrium).<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><img style="width:4.7187in;height:3.5937in"
id="Picture_x0020_3"
src="cid:part5.F68B84BC.78356260@whiteboxtechnologies.com"
height="345" width="453"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif">The
intermediate floors show on the 3-D image!<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><img style="width:3.3541in;height:3.1458in"
id="Picture_x0020_4"
src="cid:part6.8267B28C.0BB3CB4E@whiteboxtechnologies.com"
height="302" width="322"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Keith
Swartz, PE
</span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:gray">|
</span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Senior
Energy Engineer<o:p></o:p></span></p>
<p class="MsoNormal" style="line-height:110%"><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">Seventhwave</span></b><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:gray"><o:p></o:p></span></b></p>
<p class="MsoNormal" style="line-height:110%"><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">608.210.7123
seventhwave.org<o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
Nicholas Caton via Equest-users
[<a class="moz-txt-link-freetext" href="mailto:equest-users@lists.onebuilding.org">mailto:equest-users@lists.onebuilding.org</a>]
<br>
<b>Sent:</b> Tuesday, March 07, 2017 11:09 AM<br>
<b>To:</b> John Aulbach <a class="moz-txt-link-rfc2396E" href="mailto:jra_sac@yahoo.com"><jra_sac@yahoo.com></a>;
Sunayana Jain
<a class="moz-txt-link-rfc2396E" href="mailto:sunayana@sustainablesolutionscorporation.com"><sunayana@sustainablesolutionscorporation.com></a><br>
<b>Cc:</b> equest-users
<a class="moz-txt-link-rfc2396E" href="mailto:equest-users@lists.onebuilding.org"><equest-users@lists.onebuilding.org></a><br>
<b>Subject:</b> Re: [Equest-users] Floor Multiplier in
Detailed Edit Mode<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">This
is the easiest solution if the end-goal is “I need a pretty
picture” and you haven’t made substantial/visible geometry
edits post-wizards.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">Otherwise,
I’ve used photoshop/paint to manipulate the image where it
really matters to someone.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">~Nick<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46"><img
style="width:7.5625in;height:.0937in"
id="Picture_x0020_1"
src="cid:part7.AEDEBD4A.AD4990B6@whiteboxtechnologies.com"
height="9" width="726"><o:p></o:p></span></p>
<p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Arial",sans-serif;color:#3A7A46">Nick
Caton, P.E., BEMP</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46"><o:p></o:p></span></p>
<table class="MsoNormalTable"
style="width:543.0pt;border-collapse:collapse" border="0"
cellpadding="0" cellspacing="0" width="724">
<tbody>
<tr>
<td style="width:172.3pt;padding:0in 0in 0in 0in"
valign="top" width="230">
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">
Senior Energy Engineer</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">
Regional Energy Engineering Manager<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">
Energy and Sustainability Services</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">
Schneider Electric</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
</td>
<td style="width:218.3pt;padding:0in 0in 0in 0in"
valign="top" width="291">
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">D </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">913.564.6361
</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">M </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">785.410.3317
</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">F </span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">913.564.6380</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#1F497D"><br>
</span><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#57B069">E </span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><a
moz-do-not-send="true"
href="mailto:nicholas.caton@schneider-electric.com"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">nicholas.caton@schneider-electric.com</span></a><o:p></o:p></span></p>
</td>
<td style="width:152.4pt;padding:0in 0in 0in 0in"
valign="top" width="203">
<p class="MsoNormal" style="text-align:right"
align="right"><span
style="font-size:8.0pt;font-family:"Arial",sans-serif;color:#626469">15200
Santa Fe Trail Drive<br>
Suite 204<br>
Lenexa, KS 66219<br>
United States</span><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1F497D"><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:4.0pt">
<td colspan="3" style="width:543.0pt;padding:0in 0in 0in
0in;height:4.0pt" valign="top" width="724">
<p class="MsoNormal" style="mso-line-height-alt:4.0pt"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#3A7A46"><img
style="width:7.5208in;height:.5104in"
id="_x0000_i1026"
src="cid:part9.3E3947FE.1A8B6D28@whiteboxtechnologies.com"
height="49" border="0" width="722"><o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
</div>
<p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri",sans-serif">
Equest-users [<a moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>John Aulbach via Equest-users<br>
<b>Sent:</b> Tuesday, March 07, 2017 10:41 AM<br>
<b>To:</b> Sunayana Jain <<a moz-do-not-send="true"
href="mailto:sunayana@sustainablesolutionscorporation.com">sunayana@sustainablesolutionscorporation.com</a>>;
<a moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Floor Multiplier in
Detailed Edit Mode<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<div>
<div>
<p class="MsoNormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif">Hi:<o:p></o:p></span></p>
</div>
</div>
<div>
<p class="MsoNormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif">I
believe if you make another copy and call it "Full
Building" or something, then uncheck the Floor
multipliers checkbox Screen 1), all floors will appear.<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif"><o:p> </o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif">John
Aulbach<o:p></o:p></span></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif"><o:p> </o:p></span></p>
</div>
<div id="yahoo_quoted_9424675771">
<div>
<p class="MsoNormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif">On
Tuesday, March 7, 2017, 6:54:31 AM PST, Sunayana Jain
via Equest-users <<a moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>>
wrote:<o:p></o:p></span></p>
</div>
<div>
<div id="yiv5601753002">
<div>
<div>
<p class="yiv5601753002msonormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif">Hi,<o:p></o:p></span></p>
<p class="yiv5601753002msonormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif">I
am working on a multi-story identical floor
plans building. I am using floor multiplier in
wizard mode for simplicity of the model and to
keep shorter simulation time. In the model,
equest is showing the bottom floor and top floor
for the identical floors. However, I was
wondering if I can have all the floors
<b><u>visible</u></b> at the later stage of the
project in detailed edit mode?<o:p></o:p></span></p>
<p class="yiv5601753002msonormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif">Thanks,<o:p></o:p></span></p>
<p class="yiv5601753002msonormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif">Sunayana
<o:p></o:p></span></p>
<p class="yiv5601753002msonormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif"> <o:p></o:p></span></p>
</div>
</div>
</div>
<p class="MsoNormal"><span
style="font-size:13.5pt;font-family:"Verdana",sans-serif">_______________________________________________<br>
Equest-users mailing list<br>
<a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank
message to <a moz-do-not-send="true"
href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></span></p>
</div>
</div>
</div>
<p class="MsoNormal"><br>
______________________________________________________________________<br>
This email has been scanned by the Symantec Email
Security.cloud service.<br>
______________________________________________________________________<o:p></o:p></p>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</body>
</html>