    <p>Yongqing is correct.  This kind of information is not available
      in any of the hourly reports, but it can be calculated although
      depending on the complexity of the building it might almost feel
      like you're writing a small loads calculation program :-)  <br>
    </p>
    <p>I worked with a Research Associate (Ellen Franconi, now at the
      Rocky Mountain Institute) to do this using FUNCTIONs in DOE-2.1E,
      but since FUNCTIONS are not invoked in DOE-2.2/eQUEST, you'd have
      to write out hourly reports for the LOADS loads for each exterior
      surface and then adjust the loads for the difference between the
      constant LOADS temperature and the actual zone temperature in
      SYSTEMS using a simple UA delta T correction, i.e., Loads
      Correction = (UA of surface)*(Tsystem - Tloads).  You can get the
      U-value and area of each surface from the LDS verification
      report.  For infiltration, instead of a UA use the air volume
      times its specific heat.  Once you've done all this, you will have
      the actual heat flows to the building, but these will not
      correspond to the SYSTEM Loads because of the temperature
      deadband. After trying various approaches, Ellen and I found the
      best to be aggregating the heat flows when the system is off, and
      then dumping it to either heating or cooling depending on the
      system mode when it starts up again.  Don't expect complete
      correspondence with the System Load, but generally we were getting
      within 5-10%.<br>
    </p>
    <p>This <a moz-do-not-send="false"
        href="cid:part1.EE65E257.20A3318C@whiteboxtechnologies.com">paper<u><font
            color="#000000"> (the first report) describes th<u>e FUNCTION-based
              method that Ellen and I used.</u></font></u></a></p>
    <p><a moz-do-not-send="false"
        href="cid:part1.EE65E257.20A3318C@whiteboxtechnologies.com"><u><font
            color="#000000"><u>Joe</u></font></u><font color="#000000"></font></a><br>
    </p>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 11/18/2016 8:14 AM, zhaoyongqing1987
      via Equest-users wrote:<br>
    </div>
    <blockquote
      cite="mid:20e45ccc.149c6.158783822dd.Coremail.zhaoyongqing1987@126.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <div id="contentDescription"
        style="line-height:1.5;text-align:justify;text-justify:inter-ideograph">
        <div>No hourly report can provide these information!</div>
        <div class="NETEASEMAILMASTERLOCALSIGNATURE">
          <div id="imail_signature"><br>
          </div>
        </div>
        <div class="borderFixWidth iMailDoNotReScale"
style="background-color:#f2f2f2;color:black;padding-top:6px;padding-bottom:6px;border-radius:3px;-moz-border-radius:3px;-webkit-border-radius:3px;margin-top:45px;margin-bottom:20px;">
          <div
style="font-size:14px;line-height:1.5;word-break:break-all;margin-left:10px;margin-right:10px">On
            11/18/2016 23:48, <a moz-do-not-send="true"
              style="text-decoration:none;color:#2a97ff;"
              href="mailto:smartin@shaunmartinconsulting.com">Shaun
              Martin</a> wrote:</div>
        </div>
        <blockquote id="ntes-iosmail-quote" style="margin:0">
          <p dir="ltr">Hi,</p>
          <p dir="ltr">You'll have to use hourly reports to get at that
            data. The procedure is fairly well laid out in the doe2
            manuals and it's under the project tab on the equest screen.</p>
          <p dir="ltr">Shaun<br>
          </p>
          <div class="gmail_extra"><br>
            <div class="gmail_quote">On Nov 17, 2016 11:58 PM,
              zhaoyongqing1987 via Equest-users <<a
                moz-do-not-send="true"
                href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>>
              wrote:<br type="attribution">
              <blockquote class="quote" style="margin:0 0 0
                .8ex;border-left:1px #ccc solid;padding-left:1ex">
                <div
                  style="line-height:1.7;color:#000000;font-size:14px;font-family:'arial'">
                  <div
                    style="line-height:1.7;color:#000000;font-size:14px;font-family:'arial'"><br>
                    Hi,Saurabh <br>
                    <br>
                    <div>Sorry,maybe I don't make my question clear. </div>
                    <div><br>
                    </div>
                    <div>the procedure of the building loads's
                      calculation in eQUEST is shown as following:</div>
                    <div>
                      <p><span
                          style="font-family:'verdana';font-size:11pt"> In
                          Loads,  all the heat flows are calculated at
                          the reference temperature (TLOADS) and counted
                          as Cooling if the net space load that hour is
                          positive or Heating if it's negative.  In
                          Systems, these loads are corrected to the
                          actual zone temperature and the load from OA
                          and interzone heat transfer added, while
                          solving for the zone temperature. If the zone
                          temperature is outside the thermostat
                          deadband, a deficit would be considered a
                          heating load and an excess as a cooling  load
                          on the HVAC system.(posted by Joe huang)</span><span
                          style="font-family:'verdana';font-size:11pt"><br>
                        </span></p>
                    </div>
                    <div><b>And monthly building load components(such as
                        building load from roof,building load from wall
                        and building load from window conduction etc.)
                        are listed in LS-F report. But all these results
                        in LS-F report are calculated based on the
                        reference temperature(TLOADS),which is a fixed
                        value assumed by user,not the actual zone
                        temperature.My question is how to get the
                        building components that are calculated based on
                        actual zone temperature!</b></div>
                    <div><b><br>
                      </b></div>
                    <div><b>Yongqing</b></div>
                    <br>
                    At 2016-11-18 15:15:42, "Saurabh Kumar Srivastava"
                    <<a moz-do-not-send="true"
                      href="mailto:SASV@cowi.com">SASV@cowi.com</a>>
                    wrote:<br>
                    <blockquote style="padding-left:1ex;margin:0px 0px
                      0px 0.8ex;border-left:#ccc 1px solid">
                      <div>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d">Hi Yongqing,</span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d"> </span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d">I believe what
                            you're looking for is:
                            <br>
                            If you have a room which is conditioned, you
                            would like to know the building energy
                            consumption without specifying the Room
                            set-point temperature?</span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d"> </span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d">To calculate the
                            Energy consumption a Delta T(temp) value
                            would be required by eQuest, so it uses 1
                            temp from the weather file and other is the
                            set point you have defined in the zone.<br>
                            Until now </span><span
                            style="font-family:'calibri' ,
                            sans-serif;color:#1f497d">I guess</span><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d"> it not possible
                            to model Free Cooling/Passive cooling for
                            Rooms in a building, where in you let the
                            room achieve various temperature when
                            unconditioned and calculate fan power etc.
                            etc.</span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d"> </span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d">But the crude
                            way out of all this is you can input various
                            Set point temperatures for a room in a given
                            range say from 20°C to 30°C and take a
                            median values obtained post simulation and
                            evaluate the building load component.</span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d">The software
                            does give hourly outputs for a fixed room
                            set point temperate in Report SS-G. Scroll
                            down in the .sim file  to see additional
                            hourly data for a zone. <br>
                            <br>
                          </span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d">Feel free to
                            ask, if any more doubt
                          </span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d"> </span></p>
                        <p><span
                            style="font-size:8pt;font-family:'verdana' ,
                            sans-serif;color:#7f7f7f">Best Regards</span><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d"></span></p>
                        <p><span
                            style="font-size:8pt;font-family:'verdana' ,
                            sans-serif;color:#7f7f7f"> </span><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d"></span></p>
                        <p style="margin-bottom:12pt"><b><span
                              style="font-size:8pt;font-family:'verdana'
                              , sans-serif;color:#f04e23">Saurabh
                              <br>
                              <br>
                            </span></b><span
                            style="font-size:8pt;font-family:'verdana' ,
                            sans-serif;color:black"></span></p>
                        <p><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif;color:#1f497d"> </span></p>
                        <p><b><span
                              style="font-size:11pt;font-family:'calibri'
                              , sans-serif">From:</span></b><span
                            style="font-size:11pt;font-family:'calibri'
                            , sans-serif"> Equest-users [mailto:<a
                              moz-do-not-send="true"
                              href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>]
                            <b>On Behalf Of </b>zhaoyongqing1987 via
                            Equest-users<br>
                            <b>Sent:</b> Friday, November 18, 2016 11:22
                            AM<br>
                            <b>To:</b> equest-users <<a
                              moz-do-not-send="true"
                              href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>
                            <b>Subject:</b> [Equest-users] How to get
                            accurate building load component using
                            eQUEST</span></p>
                        <p> </p>
                        <div>
                          <div>
                            <p><span
                                style="font-size:10.5pt;font-family:'arial'
                                , sans-serif;color:black">Dear eQUEST
                                user,</span></p>
                          </div>
                          <div>
                            <p><span
                                style="font-size:10.5pt;font-family:'arial'
                                , sans-serif;color:black"> </span></p>
                          </div>
                          <div>
                            <p><span
                                style="font-size:10.5pt;font-family:'arial'
                                , sans-serif;color:black">In eQUEST,LS-F
                                is the building load component
                                report,but the load in this report is
                                calculated based on fixed indoor
                                temperature.</span></p>
                          </div>
                          <div>
                            <p><span
                                style="font-size:10.5pt;font-family:'arial'
                                , sans-serif;color:black">And it is not
                                 precise.My question is if there is
                                anyway to get the accurate building load
                                component,which is calculated based on </span></p>
                          </div>
                          <div>
                            <p><span
                                style="font-size:10.5pt;font-family:'arial'
                                , sans-serif;color:black">hourly changed
                                indoor temperature.</span></p>
                          </div>
                          <div>
                            <p><span
                                style="font-size:10.5pt;font-family:'arial'
                                , sans-serif;color:black"> </span></p>
                          </div>
                          <div>
                            <p><span
                                style="font-size:10.5pt;font-family:'arial'
                                , sans-serif;color:black"> </span></p>
                          </div>
                          <div>
                            <p><span
                                style="font-size:10.5pt;font-family:'arial'
                                , sans-serif;color:black"> </span></p>
                          </div>
                          <div>
                            <p><span
                                style="font-size:10.5pt;font-family:'arial'
                                , sans-serif;color:black">Yongqing</span></p>
                          </div>
                        </div>
                        <p style="margin-bottom:12pt"> </p>
                        <p> </p>
                      </div>
                    </blockquote>
                  </div>
                  <br>
                  <br>
                  <p> </p>
                </div>
                <br>
                <br>
                <p> </p>
              </blockquote>
            </div>
            <br>
          </div>
        </blockquote>
      </div>
      <br>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>