<div dir="ltr"><div dir="ltr">Dear Vishal,<br></div><div><br></div><div>There is a methodology in <strong>Appendix C</strong><span><span> for calculation of average efficiency for Proposed Case for option 2 of "Treatment of district or campus thermal energy in LEED v2 and LEED 2009- Design & Construction" document.. Appendix C describes two methods for virtual plant average efficiencies <span><span>a). Monitoring b) Modelling.</span></span></span></span></div><div><span><span><span><span><br></span></span></span></span></div><div>To avoid complexity in modeling and if you are not seeking more than 10 or 12 points as per project type, you can also go for Option 1 which does not require to model any plant side system (Chilled water meter is sufficient). </div><div><br></div><div>Hope this helps :)</div><div><span><span> <br></span></span></div>
<p dir="ltr">Regards,</p>
<p dir="ltr">Mayank Bhatnagar<br>
Sr. Energy Analyst,<br>
Environmental Design Solutions Pvt Ltd.<br>
New Delhi.</p>
<div class="gmail_quote">On Aug 25, 2016 7:27 PM, "Vishal Jagdale via Equest-users" <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.<wbr>onebuilding.org</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid"><div dir="ltr"><p class="MsoNormal"><b>Hi,</b></p><p class="MsoNormal"><br></p>
<p class="MsoNormal">Our working project has One (1) central chiller plant (4
nos. of chiller + 4 nos. primary & secondary pump + 4 Cooling Tower) which
is serving to the both phase 1 & phase 2 area…whereas currently we are
working on the phase2 model.</p>
<p class="MsoNormal"><br></p><p class="MsoNormal">Hence our question is-<b>What capacity & efficiency to be
consider for modelling phase2 chillers, pump & cooling tower in E-quest?</b></p><p class="MsoNormal"><br></p>
<p class="MsoNormal">As per the USGBC guidelines for the <b>treatment of district
cooling</b>, we need to calculate average efficiency. So can anyone guide us on <b>how
to calculate the average efficiency? </b></p><p class="MsoNormal"><b><br></b></p>
<p class="MsoNormal">However the same guidelines suggest to consider the <b>default
efficiencies</b> in case of unavailability of average <a href="http://efficiency.it" target="_blank">efficiency.it</a> says COP of 4.4
for the total cooling plant average efficiency (including cooling towers &
primary pumps).<b>Can anyone guide us on how to take it (default efficiency) into account for all the
system while modelling in Equest?</b></p><p class="MsoNormal"><b><br></b></p><p class="MsoNormal"><b><br></b></p><p class="MsoNormal"><b>Regards,</b></p><p class="MsoNormal"><b>Vishal</b></p><p class="MsoNormal"></p></div>
<br>______________________________<wbr>_________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank" rel="noreferrer">http://lists.onebuilding.org/l<wbr>istinfo.cgi/equest-users-onebu<wbr>ilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBU<wbr>ILDING.ORG</a><br>
<br></blockquote></div>
</div>