<div dir="ltr"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Below is the summary of a discussion regarding Chilled Water Modeling; specifically secondary condenser water loops.  This topic was discussed between Aug 16 2016 and Aug 18 2016.  It is organized in reverse chronologically.</span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><br></span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><br></span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><br></span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="color:rgb(85,85,85);font-family:arial,sans-serif;font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Darryl,</span><br></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">I think Coles is leading you in the right direction. I did not really look through your schematics, etc., but this sounds like the right work around. Just check the plant equipment reports to make sure your “virtual” CW loop pump and cooler don’t use energy when they shouldn’t, and that the annual COP of the chillers is reasonable. (Look at PS-C  and the sum of equipment cooling load and sum of electric use.)<u></u><u></u></span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Fred</span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="color:rgb(85,85,85);font-family:arial,sans-serif;font-size:12.8px"><a href="mailto:fporter@noresco.com" target="_blank">fporter@noresco.com</a></span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><br></span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="color:rgb(85,85,85);font-family:arial,sans-serif;font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span></p><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Darryl,</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">I agree the dry coolers will provide the function of condenser relief, though I haven’t seen condenser relief accomplished this way before. I’m used to seeing either a completely separate condenser water loop, or an air-cooled condenser for relief. As such, I can’t speak from direct experience as to the best modeling approach. My initial thought is that you would still model a water-cooled HRC, which requires a separate condenser water loop, and assign the dry-coolers to the condenser water loop. This is an approximation, but the closest readily available that I can think of.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Thanks,</span><br><font color="#000000" face="Arial, sans-serif"><span style="font-size:14.6667px"><br></span></font><b style="font-family:"Times New Roman",serif;font-size:12pt;color:rgb(80,0,80)"><span style="font-size:13pt;font-family:Arial,sans-serif;color:black">Coles Jennings,</span></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"> PE, BEMP, LEED AP BD+C </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">Sr. Energy Engineer, Building Sciences Manager </span><br><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">Sr. Energy Engineer, Building Sciences Manager </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">Mason & Hanger<i>(formerly Hankins & Anderson) </i></span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">A Day & Zimmermann Company </span><br><b style="color:black;font-family:Arial,sans-serif;font-size:11pt">D </b><a href="tel:804.521.7045" value="+18045217045" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank">804.521.7045</a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">A Day & Zimmermann Company </span><br><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"><b>D </b><a href="tel:804.521.7045" value="+18045217045" target="_blank">804.521.7045</a> </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><b style="font-family:"Times New Roman",serif;font-size:12pt;color:rgb(80,0,80)"><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">O </span></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"><a href="tel:804.285.4171" value="+18042854171" target="_blank">804.285.<wbr>4171</a> </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><b style="font-family:"Times New Roman",serif;font-size:12pt;color:rgb(80,0,80)"><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">F </span></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"><a href="tel:804.217.8520" value="+18042178520" target="_blank">804.217.8520</a> </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">4880 Sadler Road, Suite 300 </span><br><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">4880 Sadler Road, Suite 300 </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">Glen Allen, VA 23060 </span><br><a href="http://www.ha-inc.com/" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank"><span style="color:rgb(186,12,47);text-decoration:none">ha-inc.com</span></a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><i style="color:black;font-family:Arial,sans-serif;font-size:11pt">(soon to be <a href="http://masonandhanger.com/" target="_blank">masonandhanger.com</a>) </i><br><a href="http://www.ha-inc.com/" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank"><span style="color:rgb(186,12,47);text-decoration:none">ha-inc.com</span></a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><i style="color:black;font-family:Arial,sans-serif;font-size:11pt">(soon to be <a href="http://masonandhanger.com/" target="_blank">masonandhanger.com</a>) </i><br><b style="font-family:"Times New Roman",serif;font-size:12pt;color:rgb(80,0,80)"><i><span style="font-size:11pt;font-family:"Adobe Garamond";color:rgb(186,12,47)">We do what we say.®</span></i></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"> </span><br><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="color:rgb(85,85,85);font-family:arial,sans-serif;font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span></p><br></div><span style="font-size:12.8px">Hi Coles,</span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">So I'm good on the Max Recover T now.  </span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">I have not found anything yet that would indicate that the HRCs have condenser relief.  There are dry coolers on the condenser side of the HRCs that operate when entering condenser water temperature is above 100 degF (design entering water temps of the HRC).  The dry coolers would take provide the function of a condenser relief correct?  </span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">Thanks</span><br><span style="font-size:12.8px">Darryl</span><br><font color="#1f497d" face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Darryl,</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Max Recovery T is the maximum temperature at which the HRC can contribute heat to the system. In the situation you described below, you can set this to 110 and rest assured that all available heat from the HRC can be recovered to the HWS loop.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Condenser relief indicates how the balance of heat is handled. For the majority of the year there will be an imbalance between the heating load and cooling load in the building, so the load needs to be balanced (either via air-cooled or water-cooled condenser). Let’s say on a mild day, you have 2x building cooling load as compared to the heating load. If you only have an HRC supplying chilled water for the cooling load, it’s going to be generating more than twice the heat you need to meet your heating load (</span><u style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">more</u><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> than twice because the compressor heat is also contributing to the heat available to the condenser). So you need somewhere for this extra heat to go, which is what condenser relief accomplishes. Multi-stack makes HRCs that have air-cooled condenser relief, or water-cooled condenser relief which would have six piping connections (two for chilled water, two for hot water, and two for condenser water to relieve the balance of heat).</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">If you don’t have any other chillers attached to this cooling system, my strong hunch is that you do have condenser relief. I would check the equipment schedules to confirm, or best case if you have a cut-sheet it should be clearly indicated.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Luckily eQUEST models condenser relief fairly readily. It’s when you don’t have it that things get tricky.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Thanks,</span><br><font color="#000000" face="Arial, sans-serif"><span style="font-size:14.6667px"><br></span></font><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><b style="font-family:"Times New Roman",serif;font-size:12pt;color:rgb(80,0,80)"><span style="font-size:13pt;font-family:Arial,sans-serif;color:black">Coles Jennings,</span></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"> PE, BEMP, LEED AP BD+C </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">Sr. Energy Engineer, Building Sciences Manager </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">Sr. Energy Engineer, Building Sciences Manager </span><br><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">Sr. Energy Engineer, Building Sciences Manager </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">Mason & Hanger<i>(formerly Hankins & Anderson) </i></span><br><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">A Day & Zimmermann Company </span><br><b style="color:black;font-family:Arial,sans-serif;font-size:11pt">D </b><a href="tel:804.521.7045" value="+18045217045" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank">804.521.7045</a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">A Day & Zimmermann Company </span><br><b style="color:black;font-family:Arial,sans-serif;font-size:11pt">D </b><a href="tel:804.521.7045" value="+18045217045" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank">804.521.7045</a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">A Day & Zimmermann Company </span><br><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"><b>D </b><a href="tel:804.521.7045" value="+18045217045" target="_blank">804.521.7045</a> </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><b style="font-family:"Times New Roman",serif;font-size:12pt;color:rgb(80,0,80)"><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">O </span></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"><a href="tel:804.285.4171" value="+18042854171" target="_blank">804.285.<wbr>4171</a> </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><b style="font-family:"Times New Roman",serif;font-size:12pt;color:rgb(80,0,80)"><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">F </span></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"><a href="tel:804.217.8520" value="+18042178520" target="_blank">804.217.8520</a> </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">4880 Sadler Road, Suite 300 </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">4880 Sadler Road, Suite 300 </span><br><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">4880 Sadler Road, Suite 300 </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">Glen Allen, VA 23060 </span><br><a href="http://www.ha-inc.com/" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank"><span style="color:rgb(186,12,47);text-decoration:none">ha-inc.com</span></a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><i style="color:black;font-family:Arial,sans-serif;font-size:11pt">(soon to be <a href="http://masonandhanger.com/" target="_blank">masonandhanger.com</a>) </i><br><a href="http://www.ha-inc.com/" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank"><span style="color:rgb(186,12,47);text-decoration:none">ha-inc.com</span></a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><i style="color:black;font-family:Arial,sans-serif;font-size:11pt">(soon to be <a href="http://masonandhanger.com/" target="_blank">masonandhanger.com</a>) </i><br><a href="http://www.ha-inc.com/" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank"><span style="color:rgb(186,12,47);text-decoration:none">ha-inc.com</span></a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><i style="color:black;font-family:Arial,sans-serif;font-size:11pt">(soon to be <a href="http://masonandhanger.com/" target="_blank">masonandhanger.com</a>) </i><br><b style="font-family:"Times New Roman",serif;font-size:12pt;color:rgb(80,0,80)"><i><span style="font-size:11pt;font-family:"Adobe Garamond";color:rgb(186,12,47)">We do what we say.®</span></i></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"> </span><br><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">Coles,</span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">Thanks for your input.</span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">Couple questions:</span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">What is Max Recovery T.?  I know the design condenser leaving temp. is 110 degF which is also the design HWS temp. of the heat recovery loop.  </span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">There are non-heat recovery chillers but they are separate from this cooling system.</span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">Regarding condenser relief - how does this affect operation and/or energy use? </span><div><span style="font-size:12.8px"><br>I'll start working on this configuration and will almost likely come back with some questions.</span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">Thanks</span><br><span style="font-size:12.8px">Darryl</span><br><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Darryl,</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">I’ve been following this thread and the configuration described by your colleague makes a lot more sense to me. I can understand the initial confusion because the heat rejection side of the heat recovery chiller acts as the condenser, but also as the heating source for the terminal  unit reheat.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">We do a lot of HRC models, so I just wanted to throw in a few words of advice:</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="font-size:11pt;font-family:Symbol;color:rgb(31,73,125)">·<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">         </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Make sure that the Max Recovery T is compatible with the supply temperature of your hot water loop. For example, if the max recovery T is only 100°F, but your hot water loop is configured to supply 180°F water with a 40°F delta, you will never recover any heat from the HRC in the model. We’ve done multi-stack projects with recovery temps up to 140°F, have not gone higher than this. The hot water system needs to be designed to be able to make use of this heat. It’s especially beneficial in this case to have a hot water reset schedule that lowers the supply temp during milder outdoor temperatures, as the HRC will get more efficient the lower the recovery temp is.</span><br><span style="font-size:11pt;font-family:Symbol;color:rgb(31,73,125)">·<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">         </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Do you have standard, non-heat-recovering chillers on this project as well? If so, you’ll need to pay special attention to the equipment control (EQUIP-CTRL) sequences in your model, to make sure you prioritize the HRCs when there is a heating load.</span><br><span style="font-size:11pt;font-family:Symbol;color:rgb(31,73,125)">·<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">         </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Do you have condenser relief on the HRCs? This is an option on multi-stacks. If  you don’t have condenser relief, you’ll need to pay even more attention to the EQUIP-CTRL sequences. To my knowledge, eQUEST can’t model HRCs without condenser relief, but you can make more detailed control sequences to limit relief in the model.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Thanks,</span><br><font color="#000000" face="Arial, sans-serif"><br><span style="font-size:14.6667px"><br></span></font><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:13pt;font-family:Arial,sans-serif;color:black">Coles Jennings,</span></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"> PE, BEMP, LEED AP BD+C </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">Sr. Energy Engineer, Building Sciences Manager </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">Sr. Energy Engineer, Building Sciences Manager </span><br><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">Sr. Energy Engineer, Building Sciences Manager </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">Mason & Hanger<i>(formerly Hankins & Anderson) </i></span><br><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">A Day & Zimmermann Company </span><br><b style="color:black;font-family:Arial,sans-serif;font-size:11pt">D </b><a href="tel:804.521.7045" value="+18045217045" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank">804.521.7045</a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">A Day & Zimmermann Company </span><br><b style="color:black;font-family:Arial,sans-serif;font-size:11pt">D </b><a href="tel:804.521.7045" value="+18045217045" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank">804.521.7045</a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">A Day & Zimmermann Company </span><br><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"><b>D </b><a href="tel:804.521.7045" value="+18045217045" target="_blank">804.521.7045</a> </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">O </span></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"><a href="tel:804.285.4171" value="+18042854171" target="_blank">804.285.<wbr>4171</a> </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">F </span></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"><a href="tel:804.217.8520" value="+18042178520" target="_blank">804.217.8520</a> </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">4880 Sadler Road, Suite 300 </span><br><span style="color:black;font-family:Arial,sans-serif;font-size:11pt">4880 Sadler Road, Suite 300 </span><br><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">4880 Sadler Road, Suite 300 </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:rgb(186,12,47)">| </span><span style="font-size:11pt;font-family:Arial,sans-serif;color:black">Glen Allen, VA 23060 </span><br><a href="http://www.ha-inc.com/" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank"><span style="color:rgb(186,12,47);text-decoration:none">ha-inc.com</span></a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><i style="color:black;font-family:Arial,sans-serif;font-size:11pt">(soon to be <a href="http://masonandhanger.com/" target="_blank">masonandhanger.com</a>) </i><br><a href="http://www.ha-inc.com/" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank"><span style="color:rgb(186,12,47);text-decoration:none">ha-inc.com</span></a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><i style="color:black;font-family:Arial,sans-serif;font-size:11pt">(soon to be <a href="http://masonandhanger.com/" target="_blank">masonandhanger.com</a>) </i><br><a href="http://www.ha-inc.com/" style="font-family:Arial,sans-serif;font-size:11pt" target="_blank"><span style="color:rgb(186,12,47);text-decoration:none">ha-inc.com</span></a><span style="color:black;font-family:Arial,sans-serif;font-size:11pt"> </span><i style="color:black;font-family:Arial,sans-serif;font-size:11pt">(soon to be <a href="http://masonandhanger.com/" target="_blank">masonandhanger.com</a>) </i><br><b style="font-family:"Times New Roman",serif;font-size:12pt"><i><span style="font-size:11pt;font-family:"Adobe Garamond";color:rgb(186,12,47)">We do what we say.®</span></i></b><span style="font-size:11pt;font-family:Arial,sans-serif;color:black"> </span><br><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">If this approach is reasonable, the CW loop can perhaps be defined as a WWHP loop, and then it will accept a scheduled process “heating” load.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">A “virtual” boiler might need to be added to that loop make it work, but if your loads are reasonable then it shouldn’t activate, or maybe you want it to activate to “simulate” this series or seasonal steam heat.  I’m not sure if there would be other “side effects.”</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">And then there is also the heat-recovery chiller option. The CW and HW loops won’t be the same, but perhaps it might better represent the action better, and will certainly allow supplementary heating of the reheat/etc. loop based on some criteria, though perhaps not the exact criteria in the real building.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Good Luck,</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Fred</span><br><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black">Fred Porter, BEMP, LEED</span></b><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">©</span></b><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black"> AP</span></b><br><span style="color:rgb(127,127,127);font-family:Calibri,sans-serif;font-size:11pt">Principal Engineer</span><br><span style="color:rgb(127,127,127);font-family:Calibri,sans-serif;font-size:11pt">Sustainability Services</span><br><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(0,93,170)">NORESCO</span></b><br><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Part of the issue is that it can’t be a condenser loop to perform this function. I was originally hoping to load the condenser loop in this way as well.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">How about if the load is modeled as a WSHP on a dummy zone? Then it can both add or subtract heat from a condenser loop?</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">My other question though would be what proportion of load these have on the overall system and they might be modeled as “negligible” in the scheme of the overall capacity of the condenser system.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">I also may have missed the part where it describes what is using 100F reheat, which isn’t a lot for most reheat applications.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Darryl, for your benefit – the more typical approach for this type of heat recovery in parts “South” of your location would be to size one of the modular chillers for the heat recovery application and reject even warmer water, while the rest of the chillers can operate at a more efficient ECWT through the towers or dry-coolers.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">To make the whole plant run at 100F means that the designer may be expecting a large amount of heat recovery load in proportion to the cooling plant capacity.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">David</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><u style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black">                                                          <wbr>                              <wbr>       </span></u><br><span style="color:black;font-family:Calibri,sans-serif;font-size:8pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP</span><br><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">Grumman/Butkus Associates</span></b><br><u style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black">                                                          <wbr>                              <wbr>       </span></u><br><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><br><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Well, I guess from a logical point of vue, a negative load on the condenser water loop doesn’t make much sense.. can’t really blame eQUEST on this I guess.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">At this point the only way I see left is to post-process all that’s happening on the condenser water side.. which is not really ideal.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><table border="0" cellspacing="0" cellpadding="0" width="100%" style="width:740px;border-collapse:collapse"><tbody><tr><td width="35" style="width:26.25pt;padding:0cm"><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><a href="http://www.bpa.ca/" target="_blank"><span style="text-decoration:none"><img border="0" width="31" height="34" src="cid:image001.jpg@01D1F934.C6A82920" alt="Bouthillette Parizeau"></span></a><span lang="EN-US" style="color:rgb(31,73,125)"><u></u><u></u></span></p></td><td valign="top" style="padding:0cm"><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><b><span lang="EN-US" style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(63,63,63)">Patrick</span></b><b><span lang="EN-US" style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(31,73,125)"> </span></b><b><span lang="EN-US" style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(63,63,63)">Lapierre</span></b><b><span lang="EN-US" style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(125,125,125)">_ing.</span></b><b><span lang="EN-US" style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></b></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span lang="EN-US" style="font-size:7.5pt;font-family:Arial,sans-serif;color:rgb(165,165,165)"><a href="mailto:plapierre@bpa.ca" target="_blank">plapierre@bpa.ca</a></span></p></td></tr></tbody></table><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><br><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">I also did a test. Add a positive process load to the condenser loop increases the heat rejection energy – the process load itself is not reported as misc. energy – as expected. In the case of the condenser loop serving the reheat coil loop, you would need to enter a negative process load to reduce the cooling tower load/energy. Unfortunately, Equest/DOE22 thinks it is smarter than you so it changes the sign of the load to positive if you enter a negative load. Therefore, this idea won’t fly.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"> </span></b><br><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">Christopher Jones, P. Eng.</span></b><br><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">Rowan Williams Davies & Irwin Inc.</span></b><br><i style="color:rgb(31,73,125);font-family:Arial,sans-serif;font-size:8pt">Consulting Engineers & Scientists</i><br><span style="color:rgb(31,73,125);font-family:Arial,sans-serif;font-size:8pt">901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5</span><br><b style="color:rgb(31,73,125);font-family:Arial,sans-serif;font-size:8pt">T:</b><span style="color:rgb(31,73,125);font-family:Arial,sans-serif;font-size:8pt"> </span><a href="tel:%28519%29%20823-1311%20ext%202052" value="+15198231311" style="font-family:Arial,sans-serif;font-size:8pt" target="_blank">(519) 823-1311 ext 2052</a><br><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">M:</span></b><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"> <a href="tel:%28416%29%20697-0056" value="+14166970056" target="_blank">(416) 697-0056</a></span><br><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Darryl, I made a quick test to figure out about how the process load on the condenser loop reports as a endues and it seems like it does not report at all.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">I’m quite surprised but it’s the result I got… In any case, just double check to make sure the artificial process load (C) doesn’t get counted in your results.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><table border="0" cellspacing="0" cellpadding="0" width="100%" style="width:452px;border-collapse:collapse"><tbody><tr><td width="35" style="width:26.25pt;padding:0cm"><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><a href="http://www.bpa.ca/" target="_blank"><span style="text-decoration:none"><img border="0" width="31" height="34" src="cid:image001.jpg@01D1F92B.656B3610" alt="Bouthillette Parizeau"></span></a><span style="color:rgb(31,73,125)"><u></u><u></u></span></p></td><td valign="top" style="padding:0cm"><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><b><span style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(63,63,63)">Patrick</span></b><b><span style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(31,73,125)"> </span></b><b><span style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(63,63,63)">Lapierre</span></b><b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(125,125,125)">_ing.</span></b><b><span style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></b></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:7.5pt;font-family:Arial,sans-serif;color:rgb(165,165,165)"><a href="mailto:plapierre@bpa.ca" target="_blank">plapierre@bpa.ca</a></span></p></td></tr></tbody></table><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">It’s a pleasure to help. I’m always greatful when the community solves one of my problems so it’s only natural to help out in turn.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">The idea with the load (C) as I described it below is that once you plug it as a process load on the condenser water loop, it will change the condenser water loop temperature entering the dry coolers.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">What you want to calculate is Qc = 500*GPMscnd1/2*(T3-T1) and add that load to the condenser water loop.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">In other words, you want the condenser leaving temperature calculated by eQUEST to become T3 instead of T1. For that to happen, you plug Qc on the condenser water loop. That way, the flow going to the dry coolers heat exchanger will be at the right temperature.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">As Nick mentioned also, be mindful that plugging a load on a loop as process load will be reported as an endues (in the misc equip category I believe.. not 100% sure on this). You’ll need to manually subtract it from your results.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Don’t hesitate if something’s still fuzzy.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><table border="0" cellspacing="0" cellpadding="0" width="100%" style="color:rgb(80,0,80);font-size:12.8px;width:452px;border-collapse:collapse"><tbody><tr><td width="35" style="width:26.25pt;padding:0cm"><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><a href="http://www.bpa.ca/" target="_blank"><span style="text-decoration:none"><img border="0" width="31" height="34" src="cid:image001.jpg@01D1F924.BF5E9240" alt="Bouthillette Parizeau"></span></a><span style="color:rgb(31,73,125)"><u></u><u></u></span></p></td><td valign="top" style="padding:0cm"><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><b><span style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(63,63,63)">Patrick</span></b><b><span style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(31,73,125)"> </span></b><b><span style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(63,63,63)">Lapierre</span></b><b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(125,125,125)">_ing.</span></b><b><span style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></b></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:7.5pt;font-family:Arial,sans-serif;color:rgb(165,165,165)"><a href="mailto:plapierre@bpa.ca" target="_blank">plapierre@bpa.ca</a></span></p></td></tr></tbody></table><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><br>Thank you very much Nick and Patrick for your responses!<br><br>So I've gone thru the steps suggested by Pat. <br><br>I am good with formulas (A) & (B) but am having a tougher time with (C).    <br><br>Pat you wrote "<span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:14.6667px">Calculate the energy required to bring the actual condenser leaving temperature to the calculated (A) global return temperature of the loop after the reheat coils. (C)".  </span><br><br>Is it possible that instead of actual condenser <i>leaving</i> temperature you meant actual condenser <i>entering</i> <wbr>temperature?  That seems to make sense to me, but again I could be missing something.</div><div><br>Thanks again for your help everyone!<br><span style="font-size:12.8px">Darryl Kasun</span><br><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, Arial, Helvetica, sans-serif"><br><span style="font-size:16px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,Arial,Helvetica,sans-serif;font-size:16px">Clever!  I really like the idea of dumping a process load onto the CW loop, and am curious how this might report as an enduse.  This would result in appropriate loop temps for the coolers and chillers, but be mindful in output post processing to not double count the artificial "process" energies.</span><br><font color="#1f497d" face="Calibri, Arial, Helvetica, sans-serif"><span style="font-size:16px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,Arial,Helvetica,sans-serif;font-size:16px">Also I could see your intermediate processing growing more complex if considering reheat temperature resets and/or seasonal HX bypass...  I would want to quiz the designer(s) thoroughly to ensure nothing like this that would affect my calculations is missed.  </span><br><font color="#1f497d" face="Calibri, Arial, Helvetica, sans-serif"><span style="font-size:16px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,Arial,Helvetica,sans-serif;font-size:16px">Keep us posted - you might yet be covering new ground with this project!</span><br><font color="#1f497d" face="Calibri, Arial, Helvetica, sans-serif"><span style="font-size:16px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,Arial,Helvetica,sans-serif;font-size:16px">~Nick</span><br><br><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">As Nick pointed out, I don’t think eQUEST can model this particular case without some intermediate processing or post-processing.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">My first idea would be to try to model loads on the condenser water loop to simulate the real terminal reheat return temperature (right before it goes to the dry cooler exchangers). That way the dry cooler would see the real load.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">Here’s my take on the problem:</span><br><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">1-<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">     </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Model the reheat coils on its own hot water loop and plus a steam meter to it, along with a dummy pump. Now I’m not sure if the flow going into the coils is variable or constant.. the loop’s pumps have VFD but it seems like the reheat coils have a bypass with a 3-way valve (so constant gpm flow?). Either way can be modelled but it’s important to model to right case.</span><br><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">2-<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">     </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Look up the supply temperature of the steam heat exchanger feeding the terminal reheat coils (i.e. 120 F).</span><br><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">3-<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">     </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Here’s the intermediate processing step (on an hourly basis):</span><br><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">a.<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">      </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Using the terminal reheat load (1), the actual loop’s flow and the steam exchanger supply temperature (2), calculate the global return temperature of the loop after the reheat coils. (A)</span><br><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">b.<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">      </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Using the actual condenser leaving temperature and the actual flow, calculate the energy required to increase the condenser leaving temperature to the steam exchanger supply temperature (2). (B)</span><br><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">c.<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">      </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Calculate the energy required to bring the actual condenser leaving temperature to the calculated (A) global return temperature of the loop after the reheat coils. (C)</span><br><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">d.<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">      </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Using EMIT, create an hourly load schedule for (B) and (C).</span><br><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">4-<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">     </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Plug the load schedule (C) on the condenser water loop as process load.</span><br><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">5-<span style="font-stretch:normal;font-size:7pt;font-family:"Times New Roman"">     </span></span><u style="font-family:"Times New Roman",serif;font-size:12pt"></u><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Plug the load schedule (B) on the steam loop.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">If all goes well, step (4) should simulate the real terminal reheat return temperature so that the dry coolers see the real load and step (5) should get you your real steam demand for the terminal reheat.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">All in all this strategy requires intermediate processing but no post-processing. It’s not too complicated either but you’ll need to update the 2 hourly schedules every time you make a change to the model.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt">That is unless I missed something.. it happens to all of us sometimes! Don’t hesitate to comment/edit the strategy if that’s the case.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><table border="0" cellspacing="0" cellpadding="0" width="100%" style="font-size:12.8px;width:452px;border-collapse:collapse"><tbody><tr><td width="44" style="width:26.25pt;padding:0cm"><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><a href="http://www.bpa.ca/" target="_blank"><span style="text-decoration:none"><img border="0" width="31" height="34" src="cid:image001.jpg@01D1F857.60111330" alt="Bouthillette Parizeau"></span></a><span lang="EN-US" style="color:rgb(31,73,125)"><u></u><u></u></span></p></td><td valign="top" style="padding:0cm"><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><b><span lang="EN-US" style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(63,63,63)">Patrick</span></b><b><span lang="EN-US" style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(31,73,125)"> </span></b><b><span lang="EN-US" style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(63,63,63)">Lapierre</span></b><b><span lang="EN-US" style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(125,125,125)">_ing.</span></b><b><span lang="EN-US" style="font-size:10pt;font-family:"Arial Black",sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></b></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span lang="EN-US" style="font-size:7.5pt;font-family:Arial,sans-serif;color:rgb(165,165,165)"><a href="mailto:plapierre@bpa.ca" target="_blank">plapierre@bpa.ca</a></span></p></td></tr></tbody></table><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#1f497d" face="Calibri, sans-serif"><span style="font-size:16px"><i><br></i></span></font><i style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-family:Calibri,sans-serif;color:rgb(31,73,125)">Fun stuff</span></i><span style="font-size:12pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> - You didn’t even mention the snow melt!</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">What novel/nifty/weird here is that the CW loop is </span><u style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">also</u><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> the terminal reheat heating loop (</span><b style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"><u>Note: condenser temps are boosted up with steam HX’s – critical point</u></b><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">), before coming back to hit the dry coolers tasked with bringing things down to within reason for the chillers’ ECT.  To my own terminology… I might consider your chillers “preheat” for your steam HHW reheat loop.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">As an aside, this is NOT common to my personal design experience and I wouldn’t feel shy about sharing that with the designers to open up a conversation and be sure everyone is on the same page.  Even if this is standard practice in your region/company, it never hurts to review the intent and function of the mechanical design with those putting it together & simulating performance.  You might both learn something!</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">There are a number of hard stops bounding this problem for doe2/eQUEST.  Airside reheat coils can only be assigned to circulation loops of type HW and PIPE-2.  From context and a few more clues in the diagram, I suspect you have a bunch of simultaneous heating/cooling to deal with, so 2-pipe is probably out of the running (can only deliver heating or cooling any given hour, and has lots of other attachment limitations regardless). </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">I toyed in a dummy model with a possibility for re-purposing a GLHX of type “Lake/Well” to force-feed a “return from the reheat” temperature profile to the dry coolers on a CW loop – but some piece of that Frankenstein’s monster (when I gave it a temperature schedule of straight 140’s) resulted in negative cooling consumption in the outputs…  Here’s a picture if anyone is interested in carrying that ball further – it might actually work if you built this from scratch:</span><br><img width="500" height="348" src="cid:image002.jpg@01D1F7E3.0793D220" style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">Now I’m going to do something VERY WEIRD from my typical contributions here on [eQUEST-users]: Frankly, this may be a case where </span><u style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">eQUEST/doe2 simply isn’t a workable platform</u><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">.  I’m </span><i style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">really</i><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> stretching my brain here and having trouble coming up with something that wouldn’t involve a very complex set of intermediate and post-simulation output processing assumptions…</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">How bad would it be to suggest no simultaneous heating/cooling?  That could open up some doors for specific circulation loops & plant equipment…  I gather however you probably have a bunch of cooling+heating happening from clues in the shared sequencing.</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">The only other hypothetical path I might consider is some odd approximation using LOOP-TO-LOOP-HP chillers… but then my brain starts to hurt…</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">I’d be very interested to hear if anyone else would come to a different conclusion!</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt">~Nick</span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:12pt"> </span><br><span style="color:rgb(31,73,125);font-family:Calibri,sans-serif;font-size:11pt"> </span><br><img width="722" height="9" src="cid:image003.png@01D1F7E2.7AE14BF0" style="color:rgb(58,122,70);font-family:Arial,sans-serif;font-size:12pt"><br><b style="font-family:"Times New Roman",serif;font-size:12pt"><span style="font-family:Arial,sans-serif;color:rgb(58,122,70)">Nick Caton, P.E.</span></b><br><table border="0" cellspacing="0" cellpadding="0" width="724" style="font-size:12.8px;width:543pt;border-collapse:collapse"><tbody><tr><td width="230" valign="top" style="width:172.3pt;padding:0in"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(98,100,105)">  Senior Energy Engineer</span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><br></span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(98,100,105)">  Energy and Sustainability Services</span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><br></span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(98,100,105)">  Schneider Electric</span><span style="color:rgb(31,73,125)"><u></u><u></u></span></p></td><td width="291" valign="top" style="width:218.3pt;padding:0in"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(87,176,105)">D  </span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(98,100,105)"><a href="tel:913.564.6361" value="+19135646361" target="_blank">913.564.6361</a> </span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><br></span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(87,176,105)">M  </span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(98,100,105)"><a href="tel:785.410.3317" value="+17854103317" target="_blank">785.410.3317</a> </span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><br></span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(87,176,105)">E  </span><span style="color:rgb(31,73,125)"><a href="mailto:nicholas.caton@schneider-electric.com" target="_blank"><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(98,100,105)">nicholas.caton@schneider-el<wbr>ectric.com</span></a></span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><br></span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(87,176,105)">F  </span><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(98,100,105)"><a href="tel:913.564.6380" value="+19135646380" target="_blank">913.564.6380</a></span><span style="color:rgb(31,73,125)"><u></u><u></u></span></p></td><td width="203" valign="top" style="width:152.4pt;padding:0in"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-size:8pt;font-family:Arial,sans-serif;color:rgb(98,100,105)">15200 Santa Fe Trail Drive<br>Suite 204<br>Lenexa, KS 66219<br>United States</span><span style="color:rgb(31,73,125)"><u></u><u></u></span></p></td></tr><tr style="height:4pt"><td width="724" colspan="3" valign="top" style="width:543pt;padding:0in;height:4pt"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="color:rgb(58,122,70)"><img border="0" width="722" height="49" src="cid:image004.png@01D1F7E2.7AE14BF0" alt="cid:image001.png@01D189AB.58634A10"></span></p></td></tr></tbody></table><span style="font-size:12.8px"><br></span><blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px"></blockquote><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><span style="font-size:12.8px"><br></span><div><span style="font-size:12.8px">Hi David - thank you for the reply!  </span></div><div><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">I went through the heating schematic and there are a lot of reheat coils this loop serves.  I don't know how to hook up this heating demand to the condenser water loop and maybe that's not directly possible in eQuest??  If I add up the heating load, I guess I'll have to make some assumption as to what that load will be and what it's schedule would be.  Is that what you meant?</span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">Now regarding the dry cooler, looks like that loop doesn't activate until entering condenser water temp hits 100 degF.  Any thoughts on how to model this?</span><br><span style="font-size:12.8px"><br></span><p style="margin-top:0px;margin-bottom:0px"><span style="font-size:12.8px">Darryl</span></p><span style="font-size:12.8px"><a href="mailto:darryl.kasun@gmail.com" target="_blank">darryl.kasun@gmail.com</a></span><br><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><font color="#000000" face="Calibri, Arial, Helvetica, sans-serif"><span style="font-size:16px"><br></span></font><span style="color:rgb(0,0,0);font-family:Calibri,Arial,Helvetica,sans-serif;font-size:16px">What information do you have about these reheat coils that are using the 100F secondary condenser water? These might need to be modeled as a load on the loop rather than explicitly as heating coils.</span><br><font color="#000000" face="Calibri, Arial, Helvetica, sans-serif"><span style="font-size:16px"><br></span></font><span style="color:rgb(0,0,0);font-family:Calibri,Arial,Helvetica,sans-serif;font-size:16px">Setup-wise you may need to take some liberty with the primary/secondary classification of the condenser water loops in model space to allow the needed connections. It would help to know what proportion of the load the designers envision going to the heating coils, and what proportion will go to the dry-coolers.</span><br><font color="#000000" face="Calibri, Arial, Helvetica, sans-serif"><span style="font-size:16px"><br></span></font><span style="color:rgb(0,0,0);font-family:Calibri,Arial,Helvetica,sans-serif;font-size:16px">David</span><br><a href="mailto:DEldridge@grummanbutkus.com" style="font-size:12.8px" target="_blank">DEldridge@grummanbutkus.com</a><br><font face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><span style="color:rgb(85,85,85);font-size:12.8px">______________________________<wbr>______________________________<wbr>____________________</span><br><font face="Calibri, sans-serif"><span style="font-size:14.6667px"><br></span></font><span style="font-family:Calibri,sans-serif;font-size:11pt">Hi Everyone,</span><br><span style="font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="font-family:Calibri,sans-serif;font-size:11pt">I am having difficulty setting up this part of my model & looking for some direction. </span><br><span style="font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="font-family:Calibri,sans-serif;font-size:11pt">The project has a modular chiller (CH-1,2,3) that serves the bldg’s cooling needs with the exception of the AHUs.  I’m good on that side of things.</span><br><span style="font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="font-family:Calibri,sans-serif;font-size:11pt">On the condenser side, a secondary condenser loop serves terminal reheat and there are also dry coolers that serve the condenser loop.  First off, just want to confirm I know how this system works.  Please correct me if I’m wrong.</span><br><span style="font-family:Calibri,sans-serif;font-size:11pt"> </span><br><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:11pt;font-family:Calibri,sans-serif">So the chiller is working to provide cooling to the bldg.  On the condenser side, one secondary loop provides reheat as required.  The dry coolers provide additional cooling to this loop as required.  Is it as simple as this?  Please provide any or all insight that you can! </p><span style="font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="font-family:Calibri,sans-serif;font-size:11pt">If I am correct on how this system works – if so, any suggestions on how do I model it? </span><br><span style="font-family:Calibri,sans-serif;font-size:11pt"> </span><br><span style="font-family:Calibri,sans-serif;font-size:11pt">Thanks!</span><br><span style="font-size:12.8px"><br></span><span style="font-size:12.8px">Darryl Kasun</span><br><div style="margin:2px 0px 0px;font-size:12.8px"><div><a href="mailto:darryl.kasun@gmail.com" target="_blank">darryl.kasun@gmail.com</a></div></div><div><p style="margin-right:0in;margin-left:0in;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0in;margin-left:0in;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0in;margin-left:0in;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span style="font-family:arial,sans-serif;font-size:12.8px"></span></p></div><div><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"></span></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><span style="font-family:arial,sans-serif;font-size:12.8px"></span></span></p></div><div><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:12pt;font-family:"Times New Roman",serif"><span lang="EN-US" style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"></span></p><p style="margin-right:0cm;margin-left:0cm;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0cm;margin-left:0cm;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0cm;margin-left:0cm;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0cm;margin-left:72pt;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0cm;margin-left:72pt;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0cm;margin-left:72pt;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0cm;margin-left:72pt;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0cm;margin-left:0cm;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p><p style="margin-right:0cm;margin-left:0cm;font-size:12pt;font-family:"Times New Roman",serif"><u></u></p></div><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></p><p class="MsoNormal" style="margin:0cm 0cm 0.0001pt;font-size:11pt;font-family:Calibri,sans-serif"><u></u><u></u></p></div></div></div>