One other thing to remember with this check is one error can
generate many flags, dozens even. So reading through the stream of
flags will give you clues as to what the error is. This stream is a
record of how the error propagates through the DOE program. You are
looking for the head. Start at #1 not #100. Make<u> a</u> change
and rerun everything, unless of course you come across a couple of
totally obvious mistakes. Sometimes you can't get rid of all the
flags, unmet hours can do this.<br>
Bruce Easterbrook P.Eng.<br>
Abode Engineering<br>
<br>
<div class="moz-cite-prefix">On 7/27/2016 4:39 AM, Sharad Kumar via
Equest-users wrote:<br>
</div>
<blockquote
cite="mid:CABgTvi84sDWdD=pJdrnhPsHZ5D+BfD+9ByPGb0kD4zaP-FAxMg@mail.gmail.com"
type="cite">
<div dir="ltr"><font color="#073763">Hi Darryl,</font>
<div><font color="#073763"><br>
</font></div>
<div><font color="#073763">I think this is some other software
than equest.</font></div>
<div><font color="#073763">But as far as my understanding is
concerned Nick is correct.</font></div>
<div><font color="#073763">I also think that you have assigned
two three components to wall or glazing.</font></div>
<div><font color="#073763">The component can be the default or
make of the assignments.</font></div>
<div><font color="#073763">The assignments can be the properties
having components or assignments.</font></div>
<div><font color="#073763">So kindly assign or link the proper
assignments to the building envelope so that the proper U
valued or property having assignments can be singly linked
to proper building envelope.</font></div>
<div><font color="#073763"><br>
</font></div>
<div><font color="#073763">For this you will have to have a look
at the make or sectional drawings of building envelope and
then have the make to assign it to the proper surface or
building envelope. These construction can be singly linked
to the envelope in equest. There can not be two building
envelope assignments at one time. This is not the means.</font></div>
<div><font color="#073763"><br>
</font></div>
<div><b><font color="#0c343d">Thanks</font><font color="#073763">,</font></b></div>
<div>
<div style="font-size:12.8px">
<p><span style="font-family:georgia,serif"><b><font
color="#b45f06">Sharad.Kumar.</font></b></span><span
style="font-family:georgia,serif"><font
style="font-weight:bold" color="#660000"> </font><font
color="#0c343d">(<a moz-do-not-send="true"
href="mailto:sharadcapricious@gmail.com"
target="_blank">sharadcapricious@gmail.com</a>)</font></span></p>
<p><span style="font-family:georgia,serif"><font
color="#783f04">B. Tech (Vellore Institute of
Technology)</font></span></p>
<p><span style="font-family:georgia,serif"><font
color="#660000">India.</font></span></p>
</div>
</div>
<div>.............................................................................................................</div>
<div>---------- Forwarded message ----------<br>
From: Darryl Kasun via Equest-users <<a
moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org"
target="_blank">equest-users@lists.onebuilding.org</a>><br>
To: <a moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org"
target="_blank">equest-users@lists.onebuilding.org</a><br>
Cc: <br>
Date: Mon, 25 Jul 2016 13:43:23 -0700<br>
Subject: Re: [Equest-users] Construction Assignment Error<br>
<div dir="ltr"><span style="font-size:12.8px">Hello everyone -
I posted this a couple days back but didn't get a response
so going to repost it!</span>
<div style="font-size:12.8px"><br>
</div>
<div style="font-size:12.8px">Whilst doing some quality
control reporting, the following popped up:</div>
<div style="font-size:12.8px"><br>
</div>
<div style="font-size:12.8px"><img
src="cid:part4.03C6221A.94CFA956@bellnet.ca" alt="Inline
image 1" height="166" width="408"><br>
</div>
<div style="font-size:12.8px"><br>
</div>
<div style="font-size:12.8px">To put this image into words,
the Quality Control Reports that many of the constructions
have multiple component types assigned to them.</div>
<div style="font-size:12.8px"><br>
</div>
<div style="font-size:12.8px">Do you know what this possible
error means?</div>
<div style="font-size:12.8px"><br>
</div>
<div style="font-size:12.8px">Thanks</div>
<div style="font-size:12.8px">Darryl Kasun</div>
</div>
<div class="gmail_extra"><br>
</div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<p class="" avgcert""="" color="#000000" align="left">No virus
found in this message.<br>
Checked by AVG - <a moz-do-not-send="true"
href="http://www.avg.com">www.avg.com</a><br>
Version: 2016.0.7690 / Virus Database: 4627/12693 - Release
Date: 07/27/16</p>
</blockquote>
<br>
</body>
</html>