<div dir="ltr"><font color="#073763">Hi Michael,</font><div><font color="#073763"><br></font></div><div><font color="#073763">The dehumidification process is the process to cool the air low-to dew point temperature and have the condensate.</font></div><div><font color="#073763">The dew point temperature is even below wet bulb temperature.</font></div><div><font color="#073763">Also the wet bulb temperature is a temperature below dry bulb or the normal air temperature.</font></div><div><font color="#073763">Hence if the air is having some condensate then the cooling coil is dehumidifying the air certainly below up-to dew point and then have the condensate.</font></div><div><font color="#073763">So may be the figure 60 F that you are looking is the below temperature low seeming to be dew point temperature or the low temperature seeming to be for having the possible condition to have water condensate and the condensate can be formed at low valued temperature.</font></div><div><font color="#073763"><br></font></div><div><font color="#073763">The low seeming value for having condensate temperature is possibly the dew point temperature.</font></div><div><font color="#073763"><br></font></div><div><font color="#073763">Then after the condensate formation then the latent heat of water of air (moisture plus air i.e the normal air in surrounding) is taken into the air (moisture left as condensate and left air) then that air aftermath the cooling and condensing process is heated up-to 74F in the room.The dummy room temperature is meeting the set points as the set-point is as per sensor and controllers in the HVAC to be met.</font></div><div><font color="#073763">I have read it before about the unmet load hours that it is the control issue.</font></div><div><font color="#073763">If the controllers and the HVAC design and the model is perfect then there can not be unmet load hour so possibly the air temperature is with-in the set-points and hence resulting less unmet load hour.</font></div><div><font color="#073763"><br></font></div><div><font color="#073763"><br></font></div><div><div style="font-size:12.8px"><div><p class="MsoNormal"><span style="color:rgb(12,52,61)">Thanks,</span><u></u><u></u></p></div><div><div><p class="MsoNormal"><span style="font-family:Georgia,serif;color:rgb(204,0,0)">Sharad.Kumar</span><span style="font-family:Georgia,serif;color:rgb(102,0,0)">|</span><span style="font-family:Georgia,serif;color:rgb(11,83,148)">Engineer.</span><u></u><u></u></p></div><div><p class="MsoNormal"><font color="#274e13"><span style="font-family:Georgia,serif">Green Horizon Consulting LLP.</span><u></u><u></u></font></p></div><div><p class="MsoNormal"><font color="#274e13"><span style="font-family:Georgia,serif">Gurgaon.</span><u></u><u></u></font></p></div><div><p class="MsoNormal"><span style="font-family:Georgia,serif"><font color="#274e13">India.</font></span><font color="#0000ff"><u></u><u></u></font></p></div></div></div><div style="font-size:12.8px"><p class="MsoNormal"><font color="#0000ff"><u></u> </font></p></div></div><div><div class="gmail_extra"><br></div><div class="gmail_extra">---------- Forwarded message ----------<br>From: Michael Campbell via Equest-users <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>><br>To: <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>Cc: <br>Date: Wed, 18 May 2016 08:36:42 -0400<br>Subject: [Equest-users] DOAS with dehumidification<br><div dir="ltr"><div><div><div><div>Hello,<br><br></div>I am trying to model a DOAS that supplies conditioned outside air to dwelling units.  It also has an ERV.  I have created a dummy zone with no loads and made the setpoints for the dummy zones my desired heating and cooling supply air temperatures (73F for heating and 75F for cooling).  However, the DOAS also has dehumidification in which it will operate in cooling mode to dehumidify at >60% RH.  There is no reheat coil, so when the system is dehumidifying, the supply air temperature should drop below the setpoint.  <br><br></div>Here is the issue I'm having.... when I look at my hourly reports, I can see that the air leaving the cooling coil will drop down to about 60F at times when the system is dehumidifying.  However, the dummy space is still showing a space temperature of ~74F.  How is this possible?  Does anyone have any ideas?<br><br></div>Thank you,<br></div>Mike C</div><div dir="ltr"><br></div></div></div></div>