<div dir="ltr"><div><font color="#0000ff">Dear Sambhav,</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">I am post-scripting the snapshot of the eQUEST help.</font></div><div><br></div><div><img src="cid:ii_153c0fdeb81d6f85" alt="Inline image 1" width="278" height="408"><br></div><div><br></div><div><font color="#0000ff">You are getting the cooling capacity in Kbtu/h to be more in draw through fan.</font></div><div><font color="#0000ff">As mentioned above the draw through fans are placed after the cooling coils and hence it's heating is not included in the cooling coil's cooling job.</font></div><div><font color="#0000ff">I mean the cooling coil is not able to take away the heating of the fan in draw through placement.</font></div><div><font color="#0000ff">In blow through the fan's heating can be removed by the cooling coil.</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">As mentioned the draw through fans adds heat to the down stream air, hence increasing the zone's load.</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">The added heat of the fan results in increasing the cooling load of the room or zone.</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">I believe the cooling capacity in the SV-A report is the cooling load in the zone. Also the system sizing is as per the cooling load of the zone so i believe that the zone report in SV-A is the cooling load of the zone.</font></div><div><font color="#0000ff">The cooling capacity is the cooling coil's cooling capacity and the ability to do the cooling. Also if input it will over run the cooling capacity of the of the zone.</font></div><div><font color="#0000ff">Hope this may help.</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">Thanks,</font></div><div><font color="#0000ff">Sharad.Kumar.</font></div><div><font color="#0000ff">Green Horizon Consulting LLP</font></div><div><font color="#0000ff">Gurgaon</font></div><div><font color="#0000ff"><br></font></div><div><br></div><div><br></div>Today's Topics:<br><br>   1. Fan placement (Sambhav Tiwari)<br>   2. Re: Simulation of a Steel Deck + concrete for an office<br>      building in eQuest 3.65 (Sharad Kumar)<br>   3. Re: Hot Water for Boilers with LP Gas for office building in<br>      Mexico City using eQuest 3.65 (Sharad Kumar)<br>   4. Re: Outdoor swimming pool and heater (Sunayana Jain)<br>   5. Mechanical Engineer/Energy Modeler - Job Opportunity      -<br>      Dallas, TX (Mary Mabel)<br>   6. Output of Space cool consumption comes in negative (Nitin Harjai)<br>   7. Re: Outdoor swimming pool and heater (Christian Kaltreider)<br>   8. Re: Outdoor swimming pool and heater (Elizabeth Gillmor)<br>   9. Re: Outdoor swimming pool and heater (Jayant Patil)<br>  10. Output of Space cool consumption comes in negative (Nitin Harjai)<br>  11. Re: Output of Space cool consumption comes in     negative<br>      (Javed Iqbal)<br><br><br>---------- Forwarded message ----------<br>From: Sambhav Tiwari <<a href="mailto:tiwari.sambhav@gmail.com" target="_blank">tiwari.sambhav@gmail.com</a>><br>To: <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>Cc: <br>Date: Mon, 28 Mar 2016 13:56:51 +0530<br>Subject: [Equest-users] Fan placement<br><br>Dear All,<br><br>I m changing my fan placement from draw through to blow through and when I see Output report SVA I found that system cooling capacity is increasing in draw through placement     But actually cooling capacity much increase in blow through as fan heat will add up in cooling cool load.<br><br>Can anyone explain this . Also want to know if the system cooling capacity mentioned in SV-A report in Kbtu/hr is the load or capacity of cooling coil?<br><br>Any response shall be highly appreciable<br><br>Warm Regards<br>Sambhav Tiwari<br><br>Sent from my iPhone<div><br></div><div>.............................................................................................................</div></div>