<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    I am not clear whether the supply fan volume is also too high or
    just the return volume.<br>
    <br>
    If supply volume:<br>
    - Check the SV-A to see if the altitude correction factor is 1.0. 
    If not, set your altitude to 0 on Project & Site -> Site
    Data.<br>
    - Check your system sizing ratio -- if you specify a supply flow and
    a sizing ratio, the flow entered will be multiplied by the sizing
    ratio.<br>
    <br>
    If just return volume -- you can specify a return fan volume on the
    flow parameters tab of Air-Side HVAC -> Fans <br>
    <br>
    <img src="cid:part1.04050602.09030807@greensim.com" alt=""><br>
    <br>
    <div class="moz-cite-prefix">On 11/02/2016 10:41 AM, shilpa surana
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAOXv2e5+vNkTCRUf5Xhb=hQD3+aWRG6H3EXt=OeZZynKXCUXUA@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>Simulation Community,</div>
        <div><br>
        </div>
        <div>I have a question regarding the EMIT Baseline fan power
          calculator, a tool provided to the energy modelers by RMI. I
          have used the calculator to determine the baseline fan power.
          I have entered the supply airflow from the autosized baseline
          model, exhaust air flow as the outside air flow and the
          appropriate supply fan ratio and return fan ratio in the
          calculator. I used the inputs in kW/cfm provided by the
          calculator in the Baseline model. However, the SVA report is
          reporting higher return fan power as the model is auto sizing
          the return flows higher than what the EMIT tool is using for
          calculations. EMIT tool determines the return airflow by
          subtracting exhaust airflow from the supply airflow. As a
          result when I fill out the Section 1.4 table inputs, the
          calculated total fan power from the software is higher than
          the Baseline allowance. </div>
        <div><br>
        </div>
        <div>Has anyone faced similar issues when calculating the
          baseline fan power allowances?</div>
        <div><br>
        </div>
        <div>Thanks,</div>
        <div><br>
        </div>
        <div class="gmail_signature">
          <div><strong><em>Shilpa Surana</em></strong></div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>