<div dir="ltr"><font color="#0000ff">Hi Marcus,</font><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">I will like to mention the auto-sizing formula for various loops which is 500 X GPM X delta T.</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">For primary and secondary loops the delta T is 12 degree Fahrenheit and based on auto-sizing the loop flow is 1370.6 GPM and  Cooling capacity (500 X GPM X delta T) is 8.300 MBtuh.(500 X 1370.6 X 12 ).</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">The design delta T input is provided in the CHW and CW loops.In your case the design delta T is 12 and 10 degree Fahrenheit for CHW and CW loop respectively.</font></div><div><font color="#0000ff">This delta T is nothing but the loop design temperature differences. You can have a look at the inputs in various loops.There is design temperature and loop design delta T.</font></div><div><font color="#0000ff">Also, as per my understanding the water side is as a result of the auto-sizing of air-side and both are dependent up-to certain extent.</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">............................................................................................................................</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">The pumps have mainly pump curves to design and help operate the flow as per efficiencies and heads. Head is nothing but the height or the pressure due to friction above which the Pump power should help to surpass.</font></div><div><font color="#0000ff">There are various pump curves available for various makers and design.</font></div><div><font color="#0000ff">Pump curves are helpful in designing of the flow, head and other things of various pumps.</font></div><div><font color="#0000ff">...........................................................................................................................</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">Lastly i think there have been two chillers having being distributed equally in the Loop water flow.So the CHW and CW loops are equally distributed in the parallel primary equipment.I think both the equipments are parallel.</font></div><div><span style="color:rgb(0,0,255)">I have tried to help from my side.</span></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">Thanks,</font></div><div><font color="#0000ff">Sharad.Kumar.</font></div><div><font color="#0000ff">Green Horizon Consulting LLP</font></div><div><font color="#0000ff">Gurgaon</font></div><div><font color="#0000ff">India.</font></div><div><font color="#0000ff"><a href="https://www.linkedin.com/profile/view?id=AAIAAAkDQT8BnMb3JcQGaRqKkHto3EoNbFcu_FY&trk=nav_responsive_tab_profile">Linked-In</a> <br></font></div><div><font color="#0000ff"><br></font></div><div>1. PV-A Report Differences (Marcus Eliason)<br><br><br>---------- Forwarded message ----------<br>From: Marcus Eliason <<a href="mailto:meliason@apollobbc.com" target="_blank">meliason@apollobbc.com</a>><br>To: <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>Cc: <br>Date: Tue, 15 Dec 2015 14:36:56 -0600<br>Subject: [Equest-users] PV-A Report Differences<br><div style="word-wrap:break-word">Hello,<div><br></div><div>Can anyone explain why the flow rates expressed in the PV-A reports do not agree between the “Circulation Loop”, “Pumps”, and “Primary Equipment” headings.</div><div><br></div><div>I have a baseline model for LEED in which all of the flows would be autosized, but the flow under each heading is different.  I have attached the PV-A report of the model run for reference.</div><div><br></div><div>Thanks in advance,</div><div><br></div><div><br><div><div style="word-wrap:break-word">Marcus T Eliason, PE, LEED AP<br>Consultant<br><br><b>Apollo BBC</b><br>Better Building Consultants<br><br>O: 713.869.0000</div><div style="word-wrap:break-word">M: 832.228.6293</div><div style="word-wrap:break-word">611 West 22nd Street, No. 207<br>Houston, Texas 77008<br><a href="http://www.apollobbc.com/" target="_blank">www.apollobbc.com</a></div></div></div></div></div></div>