<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    One thing you could try is putting a electric baseboard in the
    bathroom.  Unmet hours can be real dubious.  The baseboard will
    quantify it and give you more information about when it is
    happening.  That could allow you to zero in on the cause easier.  It
    will also let you have an idea about the actual impact.  You could
    be chasing smoke.  A minute out of spec could be registered as an
    unmet hour.<br>
    Bruce Easterbrook P.Eng.<br>
    Abode Engineering<br>
    <br>
    <div class="moz-cite-prefix">On 28/10/2015 4:17 PM, Michael Campbell
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAGcWTbgJmoD=JD=qxxEr-VCBzPdFhPtSuNyHyEL+3FPFLd0O6A@mail.gmail.com"
      type="cite">
      <div dir="ltr">I've tried different values for the degree day
        multipliers, into the hundreds.  I'm trying out different
        scenarios now to see what works, but I'm still getting unmet
        heating hours in the bathroom.<br>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Wed, Oct 28, 2015 at 3:57 PM, Julien
          Marrec <span dir="ltr"><<a moz-do-not-send="true"
              href="mailto:julien.marrec@gmail.com" target="_blank">julien.marrec@gmail.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div dir="auto">
              <div>Mike,</div>
              <div><br>
              </div>
              <div>You have set a zonal exhaust with make up air defined
                as infiltration? And your space linked to the thermal
                zone has an infiltration defined as ACH with a higher
                value for design days? How much higher?</div>
              <div>Your HVAC is autosized for the zone?</div>
              <div>Do you still have unmet hours for the bathroom?</div>
              <div><br>
              </div>
              <div>If this is not doing anything, your HVAC system might
                be already autosized to a greater value due to another
                parameter such as sizing factor so that the added
                infiltration does nothing.</div>
              <div>Or maybe your zonal fan doesn't actually run? Try and
                request some hourly variables to understand what is
                going on.</div>
              <div><br>
              </div>
              <div>Julien<br>
                Envoyé de mon iPhone</div>
              <div>
                <div class="h5">
                  <div><br>
                    Le 28 oct. 2015 à 20:27, Michael Campbell <<a
                      moz-do-not-send="true"
                      href="mailto:mcamp1206@gmail.com" target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:mcamp1206@gmail.com">mcamp1206@gmail.com</a></a>>
                    a écrit :<br>
                    <br>
                  </div>
                  <blockquote type="cite">
                    <div>
                      <div dir="ltr">
                        <div>
                          <div>
                            <div>Julien,<br>
                              <br>
                            </div>
                            Regarding the infiltration method... I am
                            currently trying to do this with a small
                            bathroom with 50cfm exhaust.  This is a core
                            zone.  Adjusting the design day values as
                            described in the write-up does not appear to
                            be doing anything.  Any thoughts?<br>
                            <br>
                          </div>
                          Thanks,<br>
                        </div>
                        Mike<br>
                      </div>
                      <div class="gmail_extra"><br>
                        <div class="gmail_quote">On Thu, Oct 15, 2015 at
                          11:45 AM, Julien Marrec <span dir="ltr"><<a
                              moz-do-not-send="true"
                              href="mailto:julien.marrec@gmail.com"
                              target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:julien.marrec@gmail.com">julien.marrec@gmail.com</a></a>></span>
                          wrote:<br>
                          <blockquote class="gmail_quote"
                            style="margin:0 0 0 .8ex;border-left:1px
                            #ccc solid;padding-left:1ex">
                            <div dir="ltr">
                              <div>Michael,<br>
                                <br>
                              </div>
                              <div>First, you're under 300 hours so
                                indeed it's a minor problem.<br>
                                <br>
                              </div>
                              <div>I've only looked at your model very
                                briefly but:<br>
                                <ul>
                                  <li>HW loop operation is set to "SNAP"
                                    at OA of 60°F. This is causing some
                                    minor underheating in shoulder
                                    season.<br>
                                  </li>
                                </ul>
                                <ul>
                                  <li>You have local exhaust fan with
                                    makeup = infiltration. Basically
                                    equest ignores this added
                                    infiltration during the sizing, so
                                    you have to trick it to take it into
                                    account by having a different
                                    schedule for sizing (heating AND
                                    cooling design days). I've put
                                    together my findings on the subject
                                    on Unmet Hours <a
                                      moz-do-not-send="true"
href="https://unmethours.com/question/3102/how-do-you-model-exhaust-fans-in-equest/"
                                      target="_blank">here</a> in some
                                    kind of tutorial that I hope is
                                    helpful. <br>
                                  </li>
                                </ul>
                                <p><br>
                                </p>
                                <p>Do the above and your unmet hours
                                  disappear.</p>
                                <p><br>
                                </p>
                                <p>Additionally:<br>
                                </p>
                                <ul>
                                  <li>Throttle range of 0.3°R seems
                                    pretty aggressive to me.<br>
                                  </li>
                                  <li>when you use baseboards and want
                                    to oversize, use the system's sizing
                                    ratio</li>
                                </ul>
                                <br>
                              </div>
                              <div>Hope this helps,<br>
                              </div>
                              <div>Julien<br>
                              </div>
                              <div><br>
                              </div>
                            </div>
                            <div class="gmail_extra"><br clear="all">
                              <div>
                                <div>
                                  <div dir="ltr">
                                    <div>--<br>
                                      Julien Marrec, EBCP, BPI MFBA<br>
                                      Energy&Sustainability Engineer<br>
                                      T: <a moz-do-not-send="true"
                                        href="tel:%2B33%206%2095%2014%2042%2013"
                                        value="+33695144213"
                                        target="_blank">+33 6 95 14 42
                                        13</a><br>
                                      <span style="color:rgb(0,0,0)"><br>
                                      </span><span
                                        style="color:rgb(0,0,0)">LinkedIn
                                        (en) : <span
                                          style="color:rgb(0,0,0)"><a
                                            moz-do-not-send="true"
                                            href="http://www.linkedin.com/in/julienmarrec"
                                            target="_blank"><a class="moz-txt-link-abbreviated" href="http://www.linkedin.com/in/julienmarrec">www.linkedin.com/in/julienmarrec</a></a><br>
                                        </span>LinkedIn (fr) : <a
                                          moz-do-not-send="true"
                                          href="http://www.linkedin.com/in/julienmarrec/fr"
                                          target="_blank"><a class="moz-txt-link-abbreviated" href="http://www.linkedin.com/in/julienmarrec/fr">www.linkedin.com/in/julienmarrec/fr</a></a></span><br>
                                      <span style="color:rgb(0,0,0)"></span></div>
                                  </div>
                                </div>
                              </div>
                              <br>
                              <div class="gmail_quote"><span>2015-10-15
                                  16:30 GMT+02:00 Michael Campbell <span
                                    dir="ltr"><<a
                                      moz-do-not-send="true"
                                      href="mailto:mcamp1206@gmail.com"
                                      target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:mcamp1206@gmail.com">mcamp1206@gmail.com</a></a>></span>:<br>
                                </span>
                                <blockquote class="gmail_quote"
                                  style="margin:0 0 0
                                  .8ex;border-left:1px #ccc
                                  solid;padding-left:1ex"><span>
                                    <div dir="ltr">I mistakenly attached
                                      the PRD file instead of PD2. 
                                      Correct files are attached.</div>
                                    <div>
                                      <div>
                                        <div class="gmail_extra"><br>
                                          <div class="gmail_quote">On
                                            Thu, Oct 15, 2015 at 10:16
                                            AM, Michael Campbell <span
                                              dir="ltr"><<a
                                                moz-do-not-send="true"
                                                href="mailto:mcamp1206@gmail.com"
                                                target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:mcamp1206@gmail.com">mcamp1206@gmail.com</a></a>></span>
                                            wrote:<br>
                                            <blockquote
                                              class="gmail_quote"
                                              style="margin:0 0 0
                                              .8ex;border-left:1px #ccc
                                              solid;padding-left:1ex">
                                              <div dir="ltr">
                                                <div>
                                                  <div>
                                                    <div>Hello,<br>
                                                      <br>
                                                    </div>
                                                    I'm having what
                                                    appears to be a
                                                    minor issue with
                                                    unmet hours in a
                                                    model that I've
                                                    inherited.  My INP
                                                    and PD2 files are
                                                    attached.  I've
                                                    tried adjusting the
                                                    cool sizing ratio
                                                    and and adjusted
                                                    infiltration rates
                                                    and equipment loads
                                                    with no real
                                                    effects.  Anybody
                                                    have any ideas?<br>
                                                    <br>
                                                  </div>
                                                  Thanks,<br>
                                                </div>
                                                Mike Campbell<br>
                                              </div>
                                            </blockquote>
                                          </div>
                                          <br>
                                        </div>
                                      </div>
                                    </div>
                                    <br>
                                  </span>_______________________________________________<br>
                                  Equest-users mailing list<br>
                                  <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
                                    rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                                  To unsubscribe from this mailing list
                                  send  a blank message to <a
                                    moz-do-not-send="true"
                                    href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG"
                                    target="_blank"><a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></a><br>
                                  <br>
                                </blockquote>
                              </div>
                              <br>
                            </div>
                          </blockquote>
                        </div>
                        <br>
                      </div>
                    </div>
                  </blockquote>
                </div>
              </div>
            </div>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <p class="" avgcert""="" color="#000000" align="left">No virus
        found in this message.<br>
        Checked by AVG - <a moz-do-not-send="true"
          href="http://www.avg.com">www.avg.com</a><br>
        Version: 2015.0.6173 / Virus Database: 4455/10903 - Release
        Date: 10/28/15</p>
    </blockquote>
    <br>
  </body>
</html>