<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Russell,<br>
    This issue was also posted to Unmet Hours, and Matt L. posted what I
    thought was a viable workaround, though I never took the time to go
    back and check.  <br>
<a class="moz-txt-link-freetext" href="https://unmethours.com/question/626/extraneuous-piu-system-central-heat-coil-output/">https://unmethours.com/question/626/extraneuous-piu-system-central-heat-coil-output/</a><br>
    -David<br>
    <br>
    <div class="moz-cite-prefix">On 10/26/2015 2:14 PM, Knudson, Russell
      wrote:<br>
    </div>
    <blockquote
cite="mid:BY2PR12MB0145D33AF789E05C12CD206EC2230@BY2PR12MB0145.namprd12.prod.outlook.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:"Segoe UI";
        panose-1:2 11 5 2 4 2 4 2 2 3;}
@font-face
        {font-family:Rockwell;
        panose-1:2 6 6 3 2 2 5 2 4 3;}
@font-face
        {font-family:"Arial Narrow";
        panose-1:2 11 6 6 2 2 2 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:"Courier New";}
span.EmailStyle19
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle20
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span style="color:#1F497D">Follow-up
            thought:<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">I am just going
            to ignore the hourly report column “Total central heat coil
            output (Btu/hr)” – not sure how that data is actually used.
            I made a dummy model with no SYSTEM/ZONE heating coils, no
            baseboards, no heating source at all. The “Total central
            heat…” hourly report column sums to a substantial heating
            load, but the summary energy consumption reports show zero
            energy spent on space heating, just as one would expect with
            no heating coils in the building.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><b><span style="font-family:"Arial
              Narrow",sans-serif;color:#38197A">Russell Knudson
            </span></b><b><span
              style="font-size:10.0pt;font-family:"Arial
              Narrow",sans-serif;color:#7F7F7F">EIT</span></b><span
            style="font-size:13.5pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D"><o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial
            Narrow",sans-serif;color:#7F7F7F">desk:404.946.2158 |
          </span><b><span
              style="font-family:"Rockwell",serif;color:#38197A">HEERY</span></b><span
            style="font-size:13.5pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D"><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> Knudson, Russell <br>
              <b>Sent:</b> Monday, October 26, 2015 5:05 PM<br>
              <b>To:</b> '<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>'
              <a class="moz-txt-link-rfc2396E" href="mailto:equest-users@lists.onebuilding.org"><equest-users@lists.onebuilding.org></a><br>
              <b>Subject:</b> [Equest-users] PIU system central heat
              coil ouput<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <pre>All,<o:p></o:p></pre>
        <pre>I see similar behavior. Without a heating coil installed, I see heat coil outputs sporadic and interspersed between hours with cooling coil outputs, but never for two or more hours in a row. Taking the before coil and after coil air temperatures, I can confirm that the heat rate values jive. The best I can figure, in the intermittent hours where cooling is not needed (DX in my case), the return air temp is warming the air within the SYSTEM. Feeling shaky on that theory though. Thoughts?<o:p></o:p></pre>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><b><span style="font-family:"Arial
              Narrow",sans-serif;color:#38197A">Russell Knudson
            </span></b><b><span
              style="font-size:10.0pt;font-family:"Arial
              Narrow",sans-serif;color:#7F7F7F">EIT</span></b><span
            style="font-size:13.5pt;font-family:"Segoe
            UI",sans-serif"><o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial
            Narrow",sans-serif;color:#7F7F7F">desk:404.946.2158 |
          </span><b><span
              style="font-family:"Rockwell",serif;color:#38197A">HEERY</span></b><span
            style="font-size:13.5pt;font-family:"Segoe
            UI",sans-serif"><o:p></o:p></span></p>
        <pre><o:p> </o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre>Hi Erik,<o:p></o:p></pre>
        <pre>Yes, I should have mentioned that I tried that too.  That is typically <o:p></o:p></pre>
        <pre>what I do, but I thought perhaps defining a heat source with a small <o:p></o:p></pre>
        <pre>amount of capacity would be a reasonable way to alleviate the "free" <o:p></o:p></pre>
        <pre>heat energy I appear to be getting...<o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre>Attached is a quick and dirty wizard model that illustrates the issue <o:p></o:p></pre>
        <pre>(you will need to download .bin file or change to something <o:p></o:p></pre>
        <pre>comparable).  This is representative of the configuration I was going <o:p></o:p></pre>
        <pre>for except air-cooled DX.<o:p></o:p></pre>
        <pre>David<o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre>On 10/17/2014 2:00 PM, Erik Kolderup wrote:<o:p></o:p></pre>
        <pre>><i> David,<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i> Have you tried setting the HEAT-SET-T (Hot Deck Max Leaving Temp) to <o:p></o:p></i></pre>
        <pre>><i> no value (i.e. Restore Default)?  I think that any value for that <o:p></o:p></i></pre>
        <pre>><i> keyword enables heating at the AHU level.<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i> -Erik<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i> *Erik Kolderup, PE, LEED AP*<o:p></o:p></i></pre>
        <pre>><i> <a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">erik at kolderupconsulting.com</a> <mailto:<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">erik at kolderupconsulting.com</a>>| <o:p></o:p></i></pre>
        <pre>><i> 415.531.5198 | <a moz-do-not-send="true" href="http://www.kolderupconsulting.com">www.kolderupconsulting.com</a> <o:p></o:p></i></pre>
        <pre>><i> <<a moz-do-not-send="true" href="http://www.kolderupconsulting.com">http://www.kolderupconsulting.com</a>><o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i> On Fri, Oct 17, 2014 at 1:29 PM, David Reddy <<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">david at 360-analytics.com</a> <o:p></o:p></i></pre>
        <pre>><i> <mailto:<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">david at 360-analytics.com</a>>> wrote:<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     Hi all,<o:p></o:p></i></pre>
        <pre>><i>     I am modeling a PIU system w/ a water-cooled DX coil and series<o:p></o:p></i></pre>
        <pre>><i>     electric FPBs; no central or preheat heating coils.  Using eQ v3.64<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     SV-A report indicates heating capacity for system is 0.<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     Despite this configuration, hourly reports of for SYSTEM, 'Total<o:p></o:p></i></pre>
        <pre>><i>     central heat coil output (Btu/hr)' indicates there is varying<o:p></o:p></i></pre>
        <pre>><i>     amount of central heat energy output in the first 1-2 and in some<o:p></o:p></i></pre>
        <pre>><i>     cases, the last 2-3 hours of many days in heating months (location<o:p></o:p></i></pre>
        <pre>><i>     Seattle, WA).  This is also confirmed by looking at the difference<o:p></o:p></i></pre>
        <pre>><i>     in energy reported between SS-A Heating and SS-B Zone Heating.  It<o:p></o:p></i></pre>
        <pre>><i>     is not necessarily a trivial amount of energy, ~25% of total.<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     Have others observed this before, and if so, found a way to fix this?<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     Can't say I've tried everything I can think of, but this is what I<o:p></o:p></i></pre>
        <pre>><i>     have tried:<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     A) Set HEAT-SOURCE = "ELECTRIC" and use a very small capacity both<o:p></o:p></i></pre>
        <pre>><i>     -1 or -1000<o:p></o:p></i></pre>
        <pre>><i>     B) A + setting HEAT-CONTROL = "CONSTANT"<o:p></o:p></i></pre>
        <pre>><i>     C) B + set HEAT-SET-T various values, including minimum (50F)<o:p></o:p></i></pre>
        <pre>><i>     D) Setting HEATING-SCHEDULE to something that locks out heating. <o:p></o:p></i></pre>
        <pre>><i>     This works, but also locks out zone heating, so not a viable solution<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     Thanks in advance for any input.<o:p></o:p></i></pre>
        <pre>><i>     -David<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     -- <o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     David Reddy<o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     *360 Analytics*<o:p></o:p></i></pre>
        <pre>><i>     Building Energy Analysis Consultants<o:p></o:p></i></pre>
        <pre>><i>     mail:     9750 3rd Ave NE, Suite 405, Seattle, WA 98115<o:p></o:p></i></pre>
        <pre>><i>     office: 206.557.4732 x 201 <<a moz-do-not-send="true" href="tel:206.557.4732%20x%20201">tel:206.557.4732%20x%20201</a>><o:p></o:p></i></pre>
        <pre>><i>     cell: 206.406.9856 <<a moz-do-not-send="true" href="tel:206.406.9856">tel:206.406.9856</a>><o:p></o:p></i></pre>
        <pre>><i>     web: <a moz-do-not-send="true" href="http://www.360-Analytics.com">www.360-Analytics.com</a> <<a moz-do-not-send="true" href="http://www.360-Analytics.com">http://www.360-Analytics.com</a>><o:p></o:p></i></pre>
        <pre>><i><o:p> </o:p></i></pre>
        <pre>><i>     _______________________________________________<o:p></o:p></i></pre>
        <pre>><i>     Equest-users mailing list<o:p></o:p></i></pre>
        <pre>><i>     <a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><o:p></o:p></i></pre>
        <pre>><i>     To unsubscribe from this mailing list send  a blank message to<o:p></o:p></i></pre>
        <pre>><i>     <a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG</a><o:p></o:p></i></pre>
        <pre>><i>     <mailto:<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG</a>></i><o:p></o:p></pre>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>