<div dir="ltr"><div><div>Hi,<br><br></div>Just wanted to clarify something in the above. I made a crude simplification that your 'percent loading column' was actually the PLR (equivalent to assuming you have a constant available capacity), when the PLR should be the capacity at which it's currently running divided by the capacity available at the current condition.<br><br></div><div>The capacity available at the current condition is missing from your table, and should be obtained from the manufacturer, or as Bill mentioned, you could estimate it based on a default eQuest curve. This will have some impact. I've checked with a default eQuest curve and the calculated PLR is then 4-8% lower than what I used.<br><br></div><div>If you do use the equest CAPFT curve to estimate the available capacity, you'll have to change it as well to match your non-AHRI rating condition, or the other way around...<br></div><div><br></div><div>Please bear that in mind!<br><br><br></div><div><br><br></div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div>--<br>Julien Marrec, EBCP, BPI MFBA<br>Energy&Sustainability Engineer<br>T: +33 6 95 14 42 13<br><span style="color:rgb(0,0,0)"><br></span><span style="color:rgb(0,0,0)">LinkedIn (en) : <span style="color:rgb(0,0,0)"><a href="http://www.linkedin.com/in/julienmarrec" target="_blank">www.linkedin.com/in/julienmarrec</a><br></span>LinkedIn (fr) : <a href="http://www.linkedin.com/in/julienmarrec/fr" target="_blank">www.linkedin.com/in/julienmarrec/fr</a></span><br><span style="color:rgb(0,0,0)"><a href="http://www.linkedin.com/in/julienmarrec" target="_blank"></a></span></div></div></div></div>
<br><div class="gmail_quote">2015-10-20 18:13 GMT+02:00 Julien Marrec <span dir="ltr"><<a href="mailto:julien.marrec@gmail.com" target="_blank">julien.marrec@gmail.com</a>></span>:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="ltr"><div><div><div><div>Hi,<br><br></div><div>Bill made great points on the rated v design as well as "Capacity" being mislabeled.<br><br></div>I'll try to get slightly more directive regarding how to create the curve from the data you have (per my understanding at least... correct me if I'm wrong) as well as trying to highlight that one needs to be real careful when fitting a biquadratic curve...<br></div><div><br></div><div><b><font size="4">Normalized curves<br><br></font></b></div>First, you have to remember that this curve is "normalized" at the rated/design conditions, meaning the dependent variable Z is 1.0 when independent variables (X, Y) are at rated conditions.<br><br></div>In your case, you need two independent variables: the PLR, the evaporated/condenser dT (in your case air-cooled chiller it's dT between outdoor air temperature and leaving chilled water) and one dependent variable EIRFPLR.<br><br>For the EIRFPLR value, my understanding is that you should calculate as InputkW_i / InputkW_n (where 'i' is at the specific operating point and 'n' is the rated value).<br><u><br></u></div><div><u>See attached spreadsheet for how I understand you should fit this curve (red columns)</u><br></div><div><br></div><div><b>It's critical that you set the RATED conditions properly because of this normalization.</b><br><br><br></div><div><b><font size="4">Curve fitting with 10 points...<br><br></font></b></div><div><b>Please also note that fitting a biquadratic curve (essentially a 3D surface) with only 10 points will result in <i>not so great </i>results... </b><br>If you want to get any accurate, you need to get a broader range of conditions, when outside temperature is 90F but the PLR is 50% for example (which can happen quite often if you have temperature setbacks for example, or simply an oversized cooling plant for that matter...).<br><br></div><div><b>If you try fitting with those 10 points, by entering them as a curve fit with "raw data points" in eQuest </b>(or doing the curve fit by yourself...) <b>you'll get some coefficients, no problems here, but do they <i>actually </i>represent something physical?</b> The mathematical fit is actually really good, but that's not quite enough. (a biquadratic curve has 6 coefficients, for 10 points, overfitting is bound to occur...)<br><br></div><div>Try and plot that and you'll see that:<br><br></div><div>1. It is SIGNIFICANTLY different than any curve already in eQuest<br></div><div>2. Some quite non-physical things can actually happen. Like if you have 80°F outside, and a PLR of ~30%, you get a resulting EIR that's negative...<br></div><div>(3. In your case this isn't such a problem because "thankfully" you have three datapoints at the same dT but with different PLR, which makes it a little bit more robust, but the rest of them can almost be described as a line rather than a surface. Often you can find radically different surfaces that will produce the same almost perfect R²...) <br></div><div>4. I'd bet that if you get 2 more datapoints at different conditions you'll get a completely different curve (overfitting)<br></div><div><br><br></div><div><a href="https://plot.ly/~jmarrec/214/zfx-y-biquadratic-curve-fitting/" target="_blank">Here is an interactive 3d graph</a> (orbit holding left click, and zoom with your mouse wheel) on which you will find:<br><br></div><div>- A 3d surface for the fitted curve, based on your data entered in eQuest as a curve fit with "raw data points" and getting the coefficients from there<br></div><div>- A 3d surface (grey colorscale) that is one of the curve from eQuest's library ('RecipAir-EIR-fPLR-3Comp/Ckt') for reference<br></div><div>- A 3d scatter plot (the crosshairs are the datapoints from your manufacturers)<br></div><div>- A translucent neutral plane (EIRFPLR=0): anything below that plane is unphysical<br><br></div><div>See what I mean?<br><br><br></div><div><br></div><div>Hope this was somewhat informative and not just too long to read...<br><br></div><div>Best,<br></div><div>Julien<br></div><div><div><br></div></div></div><div class="gmail_extra"><br clear="all"><div><div><div dir="ltr"><div>--<br>Julien Marrec, EBCP, BPI MFBA<br>Energy&Sustainability Engineer<br>T: <a href="tel:%2B33%206%2095%2014%2042%2013" value="+33695144213" target="_blank">+33 6 95 14 42 13</a><br><span style="color:rgb(0,0,0)"><br></span><span style="color:rgb(0,0,0)">LinkedIn (en) : <span style="color:rgb(0,0,0)"><a href="http://www.linkedin.com/in/julienmarrec" target="_blank">www.linkedin.com/in/julienmarrec</a><br></span>LinkedIn (fr) : <a href="http://www.linkedin.com/in/julienmarrec/fr" target="_blank">www.linkedin.com/in/julienmarrec/fr</a></span><br><span style="color:rgb(0,0,0)"><a href="http://www.linkedin.com/in/julienmarrec" target="_blank"></a></span></div></div></div></div><div><div class="h5">
<br><div class="gmail_quote">2015-10-19 20:58 GMT+02:00 Bishop, Bill <span dir="ltr"><<a href="mailto:bbishop@pathfinder-ea.com" target="_blank">bbishop@pathfinder-ea.com</a>></span>:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">





<div link="blue" vlink="purple" lang="EN-US">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Kusum,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">The entry for “Chiller Energy Consumption” in the DOE-2 help files is a good place to start. It explains how hourly chiller energy is determined.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">The three curves that determine hourly chiller energy are EIR-FT, EIR-FPLR and CAPACITY-FT. I believe the data in your attachment could help you create a custom
 curve for any one of these inputs, given the other two. I would create a custom EIR-FT curve based on the default eQUEST curves for EIR-FPLR and CAPACITY-FT for an air-cooled chiller, but you could create a custom EIR-FPLR curve using default curves for the
 other two as well.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">The independent variables (knowns) that you have based on your manufacturer’s data are CHW-T, DBT, (or t1, t2 per the help menu description), Load, rated Capacity
 and EIR. (More correctly, you have <i>design capacity</i> at 105F since the eQUEST
<i>rated capacity</i> is based on 95F outdoor drybulb.)<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">The dependent variables are hourly capacity as a function of temperature Cap<sub>hour</sub>, and PLR which is a function of load and Cap<sub>hour</sub>.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">The manufacturer’s data column for “Capacity” is mislabeled. It is actually load, as seen by multiplying the “Percent Loading” column by the design capacity.
 Actual chiller capacity should <i>increase</i> slightly with decreasing ambient temperature. So the table doesn’t actually show you the part load ratio PLR, which is the load divided by the hourly capacity.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">Regards,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d">~Bill<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium",sans-serif;color:black">William Bishop, PE, BEMP, BEAP, CEM, LEED AP
</span></b><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium",sans-serif;color:#006600">|</span></b><b><span style="font-size:10.0pt;font-family:"Franklin Gothic Medium",sans-serif;color:black"> Pathfinder Engineers & Architects LLP<u></u><u></u></span></b></p>
<table style="width:394.8pt;border-collapse:collapse" border="0" cellpadding="0" cellspacing="0" width="658">
<tbody>
<tr style="height:13.45pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:13.45pt" width="431">
<p class="MsoNormal" style="line-height:105%"><b><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black">Senior Energy Engineer<u></u><u></u></span></b></p>
</td>
<td rowspan="6" style="width:136.35pt;padding:0in 5.4pt 0in 5.4pt;height:13.45pt" width="227">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><img src="cid:image002.jpg@01D10A7E.94C599B0" height="47" width="70"> 
<img src="cid:image004.jpg@01D10A7E.94C599B0" height="49" width="57"><u></u><u></u></span></p>
</td>
</tr>
<tr style="height:4.55pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:4.55pt" valign="top" width="431">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:5.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><u></u> <u></u></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:9.8pt" nowrap valign="bottom" width="431">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1f497d">134 South Fitzhugh Street</span><span style="font-size:9.0pt;line-height:105%;font-family:"Calibri",sans-serif;color:#1f497d">                
</span><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1f497d">Rochester, NY 14608<u></u><u></u></span></p>
</td>
</tr>
<tr style="height:12.4pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:12.4pt" valign="top" width="431">
<p class="MsoNormal" style="line-height:105%"><b><i><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#002060">T: (585) 698-1956</span></i></b><b><i><span style="font-size:11.0pt;line-height:105%;font-family:"Calibri",sans-serif;color:#002060">             
</span></i></b><span style="font-size:11.0pt;line-height:105%;font-family:"Calibri",sans-serif;color:#1f497d">          </span><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1f497d">F: (585) 325-6005</span><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><u></u><u></u></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:9.8pt" valign="top" width="431">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:11.0pt;line-height:105%;font-family:"Calibri",sans-serif;color:#1f497d"><a href="mailto:wbishop@pathfinder-ea.com" target="_blank"><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif">bbishop@pathfinder-ea.com</span></a></span><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black">            
</span><span style="font-size:11.0pt;line-height:105%;font-family:"Calibri",sans-serif;color:#1f497d"><a href="http://www.pathfinder-ea.com/" target="_blank"><span style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif">www.pathfinder-ea.com</span></a><u></u><u></u></span></p>
</td>
</tr>
<tr style="height:24.6pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in 5.4pt;height:24.6pt" valign="top" width="431">
<p class="MsoNormal" style="margin-top:3.0pt;line-height:105%"><span style="font-size:11.0pt;line-height:105%;font-family:"Calibri",sans-serif;color:#1f497d"><img src="cid:image006.png@01D10A7E.94C599B0" alt="http://png-5.findicons.com/files/icons/977/rrze/720/globe.png" border="0" height="40" width="42"></span><span style="font-size:7.5pt;line-height:105%;font-family:"Calibri",sans-serif;color:#00b0f0">Carbon
 Fee and Dividend - simple, effective, and market-based.</span><span style="font-size:11.0pt;line-height:105%;font-family:"Calibri",sans-serif;color:#1f497d"><u></u><u></u></span></p>
</td>
</tr>
</tbody>
</table>
</div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri",sans-serif;color:#1f497d"><u></u> <u></u></span></p>
<div>
<div style="border:none;border-top:solid #e1e1e1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:11.0pt;font-family:"Calibri",sans-serif">From:</span></b><span style="font-size:11.0pt;font-family:"Calibri",sans-serif"> Equest-users [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>John Aulbach<br>
<b>Sent:</b> Monday, October 19, 2015 12:26 PM<br>
<b>To:</b> Kusum Sekhalia <<a href="mailto:skusum3@gmail.com" target="_blank">skusum3@gmail.com</a>>; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Air-cooled Chiller EIRFPLR curve in eQUEST<u></u><u></u></span></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Verdana",sans-serif;color:black">Hi Kusem:<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Verdana",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Verdana",sans-serif;color:black">I don't have too much time, but if you are holding a 44 DegF CHW temp and varying the outdoor temp (essentially your condenser), aren't you simply changing
 the capacity of the chiller based on outdoor temp. I believe you need to leaving the outdoor temp at a fixed temp, then apply your part load  and the equivalent kW. <u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Verdana",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Verdana",sans-serif;color:black">eQuest will vary the chiller peak based on outdoor loadwith onwe of the other chiller curves (guys, help me).<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Verdana",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Verdana",sans-serif;color:black">John Aulbach<u></u><u></u></span></p>
</div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Verdana",sans-serif;color:black"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal" style="margin-bottom:12.0pt;background:white"><span style="font-family:"Verdana",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<div>
<div><div><div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">On Monday, October 19, 2015 9:05 AM, Kusum Sekhalia <<a href="mailto:skusum3@gmail.com" target="_blank">skusum3@gmail.com</a>> wrote:</span><span style="font-family:"Helvetica",sans-serif;color:black"><u></u><u></u></span></p>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt;background:white"><span style="font-family:"Helvetica",sans-serif;color:black"><u></u> <u></u></span></p>
</div></div><div><div><div>
<div>
<div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Helvetica",sans-serif;color:black">Hi all,<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Helvetica",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Helvetica",sans-serif;color:black">I am trying to create an air-cooled chiller EIRFPLR curve but am getting errors. I am not able to figure out what am I doing wrong? I have attached the
 part load data from the manufacturer. Can someone help me or provide me some information which shows step by step on how to create the curve. I am using the Design guidelines HVAC simulation pdf to create the curve but not successful so far. Please help.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Helvetica",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Helvetica",sans-serif;color:black">Thank you in advance.
<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Helvetica",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal" style="background:white"><span style="font-family:"Helvetica",sans-serif;color:black">Kusum Shekhlia<u></u><u></u></span></p>
</div>
</div>
</div>
</div></div><p class="MsoNormal" style="margin-bottom:12.0pt;background:white"><span style="font-family:"Helvetica",sans-serif;color:black"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>
<u></u><u></u></span></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>

<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div></div></div>
</blockquote></div><br></div>