    There are so many differences between what's reported in the LS-D
    and SS-D that I would not use this method for anything more than an
    extremely crude look at the load attributable to OA.  In Loads,  all
    the heat flows are calculated at the reference temperature (TLOADS)
    and counted as Cooling if the net space load that hour is positive
    or Heating if it's negative.  In Systems, these loads are corrected
    to the actual zone temperature and the load from OA and interzone
    heat transfer added, while solving for the zone temperature. If the
    zone temperature is outside the thermostat deadband, a deficit would
    be considered a heating load and an excess as a cooling  load on the
    HVAC system.<br>
    <br>
    There's a much better way to get the OA load, but it would take some
    work, either with a User-Function, which unfortunately is not
    available in DOE-2.2 (although I've heard that Expressions could do
    much the same thing...), or by post-processing hourly outputs. 
    Print out an Hourly Report with the following parameters: Outdoor
    Air Temp (To), Room Air Temperature (Trm), Outside Air CFM, and the
    Zone Load.  Then, use Excel or awk ( my favorite :-) :-) ) to
    calculate the load due to the OA as (Trm-To)*CFM*Cp of air .  This
    can then be compared to the Zone Load, but you'll notice some
    anomalies  such as during the swing season when the OA Load is
    actually "free cooling".   You'll then have to decide how to
    attribute the OA heat flows to the HVAC loads, which can be tricky. 
    <br>
    <br>
    Various people, including me, Dan Fisher, Jason Glazer, etc., have
    wandered into this area of deriving component loads, and have found
    that it ultimately raises philosophical questions.  :-) :-)<br>
    <br>
    Joe
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 10/13/2015 9:02 AM, Keith Swartz
      wrote:<br>
    </div>
    <blockquote
cite="mid:DM3PR1201MB09920A5BD1B955817105D713AE300@DM3PR1201MB0992.namprd12.prod.outlook.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:"Segoe UI";
        panose-1:2 11 5 2 4 2 4 2 2 3;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:"Franklin Gothic Medium";
        panose-1:2 11 6 3 2 1 2 2 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma",sans-serif;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma",sans-serif;}
span.EmailStyle19
        {mso-style-type:personal;
        font-family:"Segoe UI",sans-serif;
        color:windowtext;}
span.EmailStyle20
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle21
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle22
        {mso-style-type:personal;
        font-family:"Segoe UI",sans-serif;
        color:#1F497D;}
span.EmailStyle23
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle24
        {mso-style-type:personal;
        font-family:"Arial",sans-serif;
        color:windowtext;
        font-weight:normal;
        font-style:normal;
        text-decoration:none none;}
span.EmailStyle25
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle26
        {mso-style-type:personal;
        font-family:"Arial",sans-serif;
        color:windowtext;}
span.EmailStyle27
        {mso-style-type:personal-compose;
        font-family:"Arial",sans-serif;
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif">Good
            point, David. The system report adds more than just
            ventilation load to the space load.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Keith
              Swartz, PE
            </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:gray">|
            </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Senior
              Energy Engineer<o:p></o:p></span></p>
          <p class="MsoNormal" style="line-height:110%"><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">Seventhwave</span></b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:gray">
              |
            </span><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:#5F5F5F">Madison.Chicago.Minneapolis</span></b><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:gray"><o:p></o:p></span></b></p>
          <p class="MsoNormal" style="line-height:110%"><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">608.210.7123
              seventhwave.org<o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> David Eldridge
              [<a class="moz-txt-link-freetext" href="mailto:DEldridge@grummanbutkus.com">mailto:DEldridge@grummanbutkus.com</a>]
              <br>
              <b>Sent:</b> Tuesday, October 13, 2015 10:47 AM<br>
              <b>To:</b> Keith Swartz <a class="moz-txt-link-rfc2396E" href="mailto:KSwartz@seventhwave.org"><KSwartz@seventhwave.org></a>;
              <a class="moz-txt-link-abbreviated" href="mailto:Mark.Hallman@rwdi.com">Mark.Hallman@rwdi.com</a><br>
              <b>Subject:</b> RE: [Equest-users] % LOAD ATTRIBUTED TO OA
              DELIVERY<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span style="color:#1F497D">I’m not sure if
            that will exactly give the ventilation loads – the “L”
            reports are the building space loads, but the “S” reports
            will include other system effects such as fan heat, reheat,
            heat gain to the return air, so that the difference might
            not exactly be a ventilation load, and might be pretty far
            from an OA-only load.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">If there is a
            preheat coil, you can set up a report to trend that coil’s
            load if you are after the heating loads. You could trend the
            cooling coil load as well, but this is a function of
            economizer operation and outside air temperature as well.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">David<o:p></o:p></span></p>
        <div>
          <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
          <p class="MsoNormal"><u><span style="color:black">                                                                                               
              </span></u><span style="color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><span style="font-size:8.0pt;color:black"> </span><span
              style="color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:#1F497D">David S.
              Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP<o:p></o:p></span></p>
          <p class="MsoNormal"><b><span style="color:#244061">Grumman/Butkus
                Associates</span></b><span style="color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><u><span style="color:black">                                                                                               
              </span></u><span style="color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><span style="color:black"> </span><span
              style="color:#1F497D"><o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> Equest-users [<a
                moz-do-not-send="true"
                href="mailto:equest-users-bounces@lists.onebuilding.org"><a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a></a>]
              <b>On Behalf Of </b>Keith Swartz<br>
              <b>Sent:</b> Monday, October 12, 2015 8:55 AM<br>
              <b>To:</b> <a moz-do-not-send="true"
                href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
              <b>Subject:</b> Re: [Equest-users] % LOAD ATTRIBUTED TO OA
              DELIVERY<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif">Mark,<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif">Look
            at the differences between values in reports LS-D and SS-D.
            SS-D includes ventilation. LS-D does not. (The first letter
            “S” stands for “system.” “L” is for “load,” the load in the
            space.)<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Keith
              Swartz, PE
            </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:gray">|
            </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Senior
              Energy Engineer<o:p></o:p></span></p>
          <p class="MsoNormal" style="line-height:110%"><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">Seventhwave</span></b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:gray">
              |
            </span><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:#5F5F5F">Madison.Chicago.Minneapolis</span></b><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:gray"><o:p></o:p></span></b></p>
          <p class="MsoNormal" style="line-height:110%"><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">608.210.7123
              seventhwave.org<o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> Shaun Martin [<a
                moz-do-not-send="true"
                href="mailto:smartin@shaunmartinconsulting.com"><a class="moz-txt-link-freetext" href="mailto:smartin@shaunmartinconsulting.com">mailto:smartin@shaunmartinconsulting.com</a></a>]
              <br>
              <b>Sent:</b> Friday, October 09, 2015 12:13 PM<br>
              <b>To:</b> 'Mark Hallman' <<a moz-do-not-send="true"
                href="mailto:Mark.Hallman@rwdi.com">Mark.Hallman@rwdi.com</a>>;
              'Bishop, Bill' <<a moz-do-not-send="true"
                href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a>>;
              <a moz-do-not-send="true"
                href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
              <b>Subject:</b> Re: [Equest-users] % LOAD ATTRIBUTED TO OA
              DELIVERY<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span style="color:#1F497D">Hi Mark,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><a moz-do-not-send="true"
            name="_MailEndCompose"><span style="color:#1F497D">You can
              use hourly reports to pull out the outside air volume
              (variable PO) plus the supply and return volumes and
              temperatures. Then off to a spreadsheet.</span></a><span
            style="color:#1F497D"><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Or, if you’re
            feeling ambitious, you could write an input function (see
            Topics).<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Shaun<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Shaun Martin
            LEED-AP, BEMP<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Principal<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Shaun Martin
            Consulting<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">#90 – 425
            Carrall Street<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Vancouver, BC 
            V6B 6E3<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">p. 604-789-1095<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> Equest-users [<a
                moz-do-not-send="true"
                href="mailto:equest-users-bounces@lists.onebuilding.org"><a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a></a>]
              <b>On Behalf Of </b>Mark Hallman<br>
              <b>Sent:</b> Wednesday, October 7, 2015 7:59 PM<br>
              <b>To:</b> 'Bishop, Bill' <<a moz-do-not-send="true"
                href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a>>;
              '<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>' <<a
                moz-do-not-send="true"
                href="mailto:equest-users@lists.onebuilding.org"><a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a></a>><br>
              <b>Subject:</b> Re: [Equest-users] % LOAD ATTRIBUTED TO OA
              DELIVERY<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D">Thanks Bill, nice tip. 
            Any way of parsing it out without running two simulations?<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D">Tx!<br>
            Mark.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><b><span
                style="font-size:7.5pt;font-family:"Segoe
                UI",sans-serif;color:#1F497D">mark hallman<o:p></o:p></span></b></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D">p.eng. leed ap bd&c<o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D">project engineer<o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
          <p class="MsoNormal"><a moz-do-not-send="true"
              href="mailto:mdh@rwdi.com"><span
                style="font-size:7.5pt;font-family:"Segoe
                UI",sans-serif">mdh@rwdi.com</span></a><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D"><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D">519 823 1311 x2494<o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D">RWDI:  the science of
              buildings, structures & the environment.  See what we
              do
            </span><a moz-do-not-send="true"
              href="http://www.rwdi.com/#%21services3/c1h0m"><span
                style="font-size:7.5pt;font-family:"Segoe
                UI",sans-serif">HERE</span></a><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D">.<o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:10.0pt;font-family:"Tahoma",sans-serif">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma",sans-serif">
                Bishop, Bill [</span><a moz-do-not-send="true"
                href="mailto:bbishop@pathfinder-ea.com"><span
                  style="font-size:10.0pt;font-family:"Tahoma",sans-serif">mailto:bbishop@pathfinder-ea.com</span></a><span
style="font-size:10.0pt;font-family:"Tahoma",sans-serif">]
                <br>
                <b>Sent:</b> Wednesday, October 07, 2015 11:12<br>
                <b>To:</b> Mark Hallman;
                '<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>'<br>
                <b>Subject:</b> RE: % LOAD ATTRIBUTED TO OA DELIVERY<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span style="color:#1F497D">One way would
            be to create a MIN-AIR-SCH with all hourly values set to 0
            (or 0.001 to activate economizer), apply it to all SYSTEMs
            and use the difference in the outputs.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Regards,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">~Bill<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><b><span
                style="font-size:10.0pt;font-family:"Franklin
                Gothic Medium",sans-serif;color:black">William
                Bishop, PE, BEMP, BEAP, CEM, LEED AP
              </span></b><b><span
                style="font-size:10.0pt;font-family:"Franklin
                Gothic Medium",sans-serif;color:#006600">|</span></b><b><span
                style="font-size:10.0pt;font-family:"Franklin
                Gothic Medium",sans-serif;color:black"> Pathfinder
                Engineers & Architects LLP<o:p></o:p></span></b></p>
          <table class="MsoNormalTable"
            style="width:394.8pt;border-collapse:collapse" border="0"
            cellpadding="0" cellspacing="0" width="658">
            <tbody>
              <tr style="height:13.45pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:13.45pt" width="431">
                  <p class="MsoNormal" style="line-height:105%"><b><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black">Senior
                        Energy Engineer<o:p></o:p></span></b></p>
                </td>
                <td rowspan="6" style="width:136.35pt;padding:0in 5.4pt
                  0in 5.4pt;height:13.45pt" width="227">
                  <p class="MsoNormal" style="line-height:105%"><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><img
                        id="Picture_x0020_4"
                        src="cid:part14.05010902.09090206@whiteboxtechnologies.com"
                        alt="cid:image001.jpg@01D104F5.971C54D0"
                        border="0" height="47" width="70"> 
                      <img id="Picture_x0020_2"
                        src="cid:part15.02060405.07030100@whiteboxtechnologies.com"
                        alt="cid:image002.jpg@01D104F5.971C54D0"
                        border="0" height="49" width="57"><o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:4.55pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:4.55pt" valign="top" width="431">
                  <p class="MsoNormal" style="line-height:105%"><span
style="font-size:5.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><o:p> </o:p></span></p>
                </td>
              </tr>
              <tr style="height:9.8pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:9.8pt" nowrap="nowrap" valign="bottom"
                  width="431">
                  <p class="MsoNormal" style="line-height:105%"><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">134
                      South Fitzhugh Street</span><span
                      style="font-size:9.0pt;line-height:105%;color:#1F497D">                
                    </span><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">Rochester,
                      NY 14608<o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:12.4pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:12.4pt" valign="top" width="431">
                  <p class="MsoNormal" style="line-height:105%"><b><i><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#002060">T:
                          (585) 698-1956</span><span
                          style="color:#002060">             
                        </span></i></b><span style="color:#1F497D">          </span><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">F:
                      (585) 325-6005</span><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:9.8pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:9.8pt" valign="top" width="431">
                  <p class="MsoNormal" style="mso-line-height-alt:9.8pt"><a
                      moz-do-not-send="true"
                      href="mailto:wbishop@pathfinder-ea.com"><span
                        style="font-size:9.0pt;font-family:"Arial",sans-serif"><a class="moz-txt-link-abbreviated" href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a></span></a><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">            
                    </span><a moz-do-not-send="true"
                      href="http://www.pathfinder-ea.com/"><span
                        style="font-size:9.0pt;font-family:"Arial",sans-serif">www.pathfinder-ea.com</span></a><span
                      style="color:#1F497D"><o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:24.6pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:24.6pt" valign="top" width="431">
                  <p class="MsoNormal"
                    style="margin-top:3.0pt;line-height:105%"><span
                      style="color:#1F497D"><img id="Picture_x0020_5"
                        src="cid:part18.08030508.03080108@whiteboxtechnologies.com"
alt="http://png-5.findicons.com/files/icons/977/rrze/720/globe.png"
                        border="0" height="40" width="42"></span><span
                      style="font-size:7.5pt;line-height:105%;color:#00B0F0">Carbon

                      Fee and Dividend - simple, effective, and
                      market-based.</span><span style="color:#1F497D"><o:p></o:p></span></p>
                </td>
              </tr>
            </tbody>
          </table>
          <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        </div>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> Equest-users [<a
                moz-do-not-send="true"
                href="mailto:equest-users-bounces@lists.onebuilding.org"><a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a></a>]
              <b>On Behalf Of </b>Mark Hallman<br>
              <b>Sent:</b> Wednesday, October 07, 2015 10:59 AM<br>
              <b>To:</b> '<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>' <<a
                moz-do-not-send="true"
                href="mailto:equest-users@lists.onebuilding.org"><a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a></a>><br>
              <b>Subject:</b> [Equest-users] % LOAD ATTRIBUTED TO OA
              DELIVERY<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif">Hi there,<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif">Is there a way to accurately parse out
            from the eQUEST output file the percentage of the cooling
            and heating load that is attributed to OA delivery?   Any
            advice would be appreciated.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif">Thanks in advance!<br>
            Mark Hallman.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><b><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif">mark hallman<o:p></o:p></span></b></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif">p.eng. leed ap bd&c<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif">project engineer<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><a moz-do-not-send="true"
            href="mailto:mdh@rwdi.com"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif">mdh@rwdi.com</span></a><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif"><o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif">519 823 1311 x2494<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif">RWDI:  the science of buildings,
            structures & the environment.  See what we do
          </span><a moz-do-not-send="true"
            href="http://www.rwdi.com/#%21services3/c1h0m"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif">HERE</span></a><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif">.<o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>