This is a good tip and I often use the difference between LS-C and
SS-D to give me a quick assessment of the impact of heating (or
cooling) ventilation air. However, it is good to understand the
other contributors to the differences between the peak heating (or
cooling) loads in LS-C and SS-D. Key differences that come to mind:<br>
- LS-C only reports the peak loads in conditioned spaces. That
means that if you have plenums defined in your model, the roof heat
loss is likely not reported in LS-C.<br>
- Loads use the space keyword TEMPERATURE to determine the peak load
whereas in SS-D it is the heating and cooling setpoint value at the
time of peak load occurrence that is used.<br>
<br>
<br>
<br>
<div class="moz-cite-prefix">On 12/10/2015 9:55 AM, Keith Swartz
wrote:<br>
</div>
<blockquote
cite="mid:DM3PR1201MB0992B2EFF94D61F936CCF755AE310@DM3PR1201MB0992.namprd12.prod.outlook.com"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=windows-1252">
<meta name="Generator" content="Microsoft Word 15 (filtered
medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
<style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:"Segoe UI";
panose-1:2 11 5 2 4 2 4 2 2 3;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:"Franklin Gothic Medium";
panose-1:2 11 6 3 2 1 2 2 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Balloon Text Char";
margin:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma",sans-serif;}
span.BalloonTextChar
{mso-style-name:"Balloon Text Char";
mso-style-priority:99;
mso-style-link:"Balloon Text";
font-family:"Tahoma",sans-serif;}
span.EmailStyle19
{mso-style-type:personal;
font-family:"Segoe UI",sans-serif;
color:windowtext;}
span.EmailStyle20
{mso-style-type:personal;
font-family:"Calibri",sans-serif;
color:#1F497D;}
span.EmailStyle21
{mso-style-type:personal;
font-family:"Calibri",sans-serif;
color:windowtext;}
span.EmailStyle22
{mso-style-type:personal;
font-family:"Segoe UI",sans-serif;
color:#1F497D;}
span.EmailStyle23
{mso-style-type:personal;
font-family:"Calibri",sans-serif;
color:#1F497D;}
span.EmailStyle24
{mso-style-type:personal-reply;
font-family:"Arial",sans-serif;
color:windowtext;
font-weight:normal;
font-style:normal;
text-decoration:none none;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif">Mark,<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif">Look
at the differences between values in reports LS-D and SS-D.
SS-D includes ventilation. LS-D does not. (The first letter
“S” stands for “system.” “L” is for “load,” the load in the
space.)<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Keith
Swartz, PE</span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black"></span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:gray">|
</span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Senior
Energy Engineer<o:p></o:p></span></p>
<p class="MsoNormal" style="line-height:110%"><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">Seventhwave</span></b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:gray">
|
</span><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:#5F5F5F">Madison.Chicago.Minneapolis</span></b><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:gray"><o:p></o:p></span></b></p>
<p class="MsoNormal" style="line-height:110%"><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">608.210.7123
seventhwave.org<o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Shaun Martin
[<a class="moz-txt-link-freetext" href="mailto:smartin@shaunmartinconsulting.com">mailto:smartin@shaunmartinconsulting.com</a>]
<br>
<b>Sent:</b> Friday, October 09, 2015 12:13 PM<br>
<b>To:</b> 'Mark Hallman' <a class="moz-txt-link-rfc2396E" href="mailto:Mark.Hallman@rwdi.com"><Mark.Hallman@rwdi.com></a>;
'Bishop, Bill' <a class="moz-txt-link-rfc2396E" href="mailto:bbishop@pathfinder-ea.com"><bbishop@pathfinder-ea.com></a>;
<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] % LOAD ATTRIBUTED TO OA
DELIVERY<o:p></o:p></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="color:#1F497D">Hi Mark,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><a moz-do-not-send="true"
name="_MailEndCompose"><span style="color:#1F497D">You can
use hourly reports to pull out the outside air volume
(variable PO) plus the supply and return volumes and
temperatures. Then off to a spreadsheet.</span></a><span
style="color:#1F497D"><o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">Or, if you’re
feeling ambitious, you could write an input function (see
Topics).<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">Shaun<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">Shaun Martin
LEED-AP, BEMP<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">Principal<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">Shaun Martin
Consulting<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">#90 – 425
Carrall Street<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">Vancouver, BC
V6B 6E3<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">p. 604-789-1095<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [<a
moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org"><a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a></a>]
<b>On Behalf Of </b>Mark Hallman<br>
<b>Sent:</b> Wednesday, October 7, 2015 7:59 PM<br>
<b>To:</b> 'Bishop, Bill' <<a moz-do-not-send="true"
href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a>>;
'<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>' <<a
moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org"><a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a></a>><br>
<b>Subject:</b> Re: [Equest-users] % LOAD ATTRIBUTED TO OA
DELIVERY<o:p></o:p></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif;color:#1F497D">Thanks Bill, nice tip.
Any way of parsing it out without running two simulations?<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif;color:#1F497D">Tx!<br>
Mark.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><b><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif;color:#1F497D">mark hallman<o:p></o:p></span></b></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif;color:#1F497D">p.eng. leed ap bd&c<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif;color:#1F497D">project engineer<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif;color:#1F497D"><a
moz-do-not-send="true" href="mailto:mdh@rwdi.com"><a class="moz-txt-link-abbreviated" href="mailto:mdh@rwdi.com">mdh@rwdi.com</a></a><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif;color:#1F497D">519 823 1311 x2494<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif;color:#1F497D">RWDI: the science of
buildings, structures & the environment. See what we
do
<a moz-do-not-send="true"
href="http://www.rwdi.com/#%21services3/c1h0m">HERE</a>.<o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma",sans-serif">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma",sans-serif">
Bishop, Bill [<a moz-do-not-send="true"
href="mailto:bbishop@pathfinder-ea.com">mailto:bbishop@pathfinder-ea.com</a>]
<br>
<b>Sent:</b> Wednesday, October 07, 2015 11:12<br>
<b>To:</b> Mark Hallman;
'<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>'<br>
<b>Subject:</b> RE: % LOAD ATTRIBUTED TO OA DELIVERY<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="color:#1F497D">One way would
be to create a MIN-AIR-SCH with all hourly values set to 0
(or 0.001 to activate economizer), apply it to all SYSTEMs
and use the difference in the outputs.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">Regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D">~Bill<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Franklin
Gothic Medium",sans-serif;color:black">William
Bishop, PE, BEMP, BEAP, CEM, LEED AP
</span></b><b><span
style="font-size:10.0pt;font-family:"Franklin
Gothic Medium",sans-serif;color:#006600">|</span></b><b><span
style="font-size:10.0pt;font-family:"Franklin
Gothic Medium",sans-serif;color:black"> Pathfinder
Engineers & Architects LLP<o:p></o:p></span></b></p>
<table class="MsoNormalTable"
style="width:394.8pt;border-collapse:collapse" border="0"
width="658" cellpadding="0" cellspacing="0">
<tbody>
<tr style="height:13.45pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:13.45pt" width="431">
<p class="MsoNormal" style="line-height:105%"><b><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black">Senior
Energy Engineer<o:p></o:p></span></b></p>
</td>
<td rowspan="6" style="width:136.35pt;padding:0in 5.4pt
0in 5.4pt;height:13.45pt" width="227">
<p class="MsoNormal" style="line-height:105%"><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><img
id="Picture_x0020_4"
src="cid:part8.00090504.05080103@greensim.com"
border="0" height="47" width="70">
<img id="Picture_x0020_2"
src="cid:part9.08080007.09030609@greensim.com"
border="0" height="49" width="57"><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:4.55pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:4.55pt" valign="top" width="431">
<p class="MsoNormal" style="line-height:105%"><span
style="font-size:5.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><o:p> </o:p></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:9.8pt" nowrap="nowrap" valign="bottom"
width="431">
<p class="MsoNormal" style="line-height:105%"><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">134
South Fitzhugh Street</span><span
style="font-size:9.0pt;line-height:105%;color:#1F497D">
</span><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">Rochester,
NY 14608<o:p></o:p></span></p>
</td>
</tr>
<tr style="height:12.4pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:12.4pt" valign="top" width="431">
<p class="MsoNormal" style="line-height:105%"><b><i><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#002060">T:
(585) 698-1956</span><span
style="color:#002060">
</span></i></b><span style="color:#1F497D"> </span><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">F:
(585) 325-6005</span><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:9.8pt" valign="top" width="431">
<p class="MsoNormal" style="mso-line-height-alt:9.8pt"><span
style="color:#1F497D"><a moz-do-not-send="true"
href="mailto:wbishop@pathfinder-ea.com"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif">bbishop@pathfinder-ea.com</span></a></span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">
</span><span style="color:#1F497D"><a
moz-do-not-send="true"
href="http://www.pathfinder-ea.com/"><span
style="font-size:9.0pt;font-family:"Arial",sans-serif"><a class="moz-txt-link-abbreviated" href="http://www.pathfinder-ea.com">www.pathfinder-ea.com</a></span></a><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:24.6pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:24.6pt" valign="top" width="431">
<p class="MsoNormal"
style="margin-top:3.0pt;line-height:105%"><span
style="color:#1F497D"><img id="Picture_x0020_5"
src="cid:part12.00010106.05060305@greensim.com"
alt="http://png-5.findicons.com/files/icons/977/rrze/720/globe.png"
border="0" height="40" width="42"></span><span
style="font-size:7.5pt;line-height:105%;color:#00B0F0">Carbon
Fee and Dividend - simple, effective, and
market-based.</span><span style="color:#1F497D"><o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
</div>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [<a
moz-do-not-send="true"
href="mailto:equest-users-bounces@lists.onebuilding.org"><a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a></a>]
<b>On Behalf Of </b>Mark Hallman<br>
<b>Sent:</b> Wednesday, October 07, 2015 10:59 AM<br>
<b>To:</b> '<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>' <<a
moz-do-not-send="true"
href="mailto:equest-users@lists.onebuilding.org"><a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a></a>><br>
<b>Subject:</b> [Equest-users] % LOAD ATTRIBUTED TO OA
DELIVERY<o:p></o:p></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif">Hi there,<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif">Is there a way to accurately parse out
from the eQUEST output file the percentage of the cooling
and heating load that is attributed to OA delivery? Any
advice would be appreciated.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif">Thanks in advance!<br>
Mark Hallman.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:9.0pt;font-family:"Segoe
UI",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><b><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif">mark hallman<o:p></o:p></span></b></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif">p.eng. leed ap bd&c<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif">project engineer<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif"><a moz-do-not-send="true"
href="mailto:mdh@rwdi.com">mdh@rwdi.com</a><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif">519 823 1311 x2494<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Segoe
UI",sans-serif">RWDI: the science of buildings,
structures & the environment. See what we do
<a moz-do-not-send="true"
href="http://www.rwdi.com/#%21services3/c1h0m">HERE</a>.<o:p></o:p></span></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
</body>
</html>