    This is a good tip and I often use the difference between LS-C and
    SS-D to give me a quick assessment of the impact of heating (or
    cooling) ventilation air.  However, it is good to understand the
    other contributors to the differences between the peak heating (or
    cooling) loads in LS-C and SS-D. Key differences that come to mind:<br>
    - LS-C only reports the peak loads in conditioned spaces.  That
    means that if you have plenums defined in your model, the roof heat
    loss is likely not reported in LS-C.<br>
    - Loads use the space keyword TEMPERATURE to determine the peak load
    whereas in SS-D it is the heating and cooling setpoint value at the
    time of peak load occurrence that is used.<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 12/10/2015 9:55 AM, Keith Swartz
      wrote:<br>
    </div>
    <blockquote
cite="mid:DM3PR1201MB0992B2EFF94D61F936CCF755AE310@DM3PR1201MB0992.namprd12.prod.outlook.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:"Segoe UI";
        panose-1:2 11 5 2 4 2 4 2 2 3;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:"Franklin Gothic Medium";
        panose-1:2 11 6 3 2 1 2 2 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma",sans-serif;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma",sans-serif;}
span.EmailStyle19
        {mso-style-type:personal;
        font-family:"Segoe UI",sans-serif;
        color:windowtext;}
span.EmailStyle20
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle21
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:windowtext;}
span.EmailStyle22
        {mso-style-type:personal;
        font-family:"Segoe UI",sans-serif;
        color:#1F497D;}
span.EmailStyle23
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:#1F497D;}
span.EmailStyle24
        {mso-style-type:personal-reply;
        font-family:"Arial",sans-serif;
        color:windowtext;
        font-weight:normal;
        font-style:normal;
        text-decoration:none none;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif">Mark,<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif">Look
            at the differences between values in reports LS-D and SS-D.
            SS-D includes ventilation. LS-D does not. (The first letter
            “S” stands for “system.” “L” is for “load,” the load in the
            space.)<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Keith
              Swartz, PE</span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black"></span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:gray">|
            </span><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black">Senior
              Energy Engineer<o:p></o:p></span></p>
          <p class="MsoNormal" style="line-height:110%"><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">Seventhwave</span></b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:gray">
              |
            </span><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:#5F5F5F">Madison.Chicago.Minneapolis</span></b><b><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:gray"><o:p></o:p></span></b></p>
          <p class="MsoNormal" style="line-height:110%"><span
style="font-size:10.0pt;line-height:110%;font-family:"Arial",sans-serif;color:black">608.210.7123
              seventhwave.org<o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:10.0pt;font-family:"Arial",sans-serif"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> Shaun Martin
              [<a class="moz-txt-link-freetext" href="mailto:smartin@shaunmartinconsulting.com">mailto:smartin@shaunmartinconsulting.com</a>]
              <br>
              <b>Sent:</b> Friday, October 09, 2015 12:13 PM<br>
              <b>To:</b> 'Mark Hallman' <a class="moz-txt-link-rfc2396E" href="mailto:Mark.Hallman@rwdi.com"><Mark.Hallman@rwdi.com></a>;
              'Bishop, Bill' <a class="moz-txt-link-rfc2396E" href="mailto:bbishop@pathfinder-ea.com"><bbishop@pathfinder-ea.com></a>;
              <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
              <b>Subject:</b> Re: [Equest-users] % LOAD ATTRIBUTED TO OA
              DELIVERY<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span style="color:#1F497D">Hi Mark,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><a moz-do-not-send="true"
            name="_MailEndCompose"><span style="color:#1F497D">You can
              use hourly reports to pull out the outside air volume
              (variable PO) plus the supply and return volumes and
              temperatures. Then off to a spreadsheet.</span></a><span
            style="color:#1F497D"><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Or, if you’re
            feeling ambitious, you could write an input function (see
            Topics).<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Shaun<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Shaun Martin
            LEED-AP, BEMP<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Principal<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Shaun Martin
            Consulting<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">#90 – 425
            Carrall Street<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Vancouver, BC 
            V6B 6E3<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">p. 604-789-1095<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> Equest-users [<a
                moz-do-not-send="true"
                href="mailto:equest-users-bounces@lists.onebuilding.org"><a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a></a>]
              <b>On Behalf Of </b>Mark Hallman<br>
              <b>Sent:</b> Wednesday, October 7, 2015 7:59 PM<br>
              <b>To:</b> 'Bishop, Bill' <<a moz-do-not-send="true"
                href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a>>;
              '<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>' <<a
                moz-do-not-send="true"
                href="mailto:equest-users@lists.onebuilding.org"><a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a></a>><br>
              <b>Subject:</b> Re: [Equest-users] % LOAD ATTRIBUTED TO OA
              DELIVERY<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D">Thanks Bill, nice tip. 
            Any way of parsing it out without running two simulations?<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D">Tx!<br>
            Mark.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><b><span
                style="font-size:7.5pt;font-family:"Segoe
                UI",sans-serif;color:#1F497D">mark hallman<o:p></o:p></span></b></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D">p.eng. leed ap bd&c<o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D">project engineer<o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D"><a
                moz-do-not-send="true" href="mailto:mdh@rwdi.com"><a class="moz-txt-link-abbreviated" href="mailto:mdh@rwdi.com">mdh@rwdi.com</a></a><o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D">519 823 1311 x2494<o:p></o:p></span></p>
          <p class="MsoNormal"><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif;color:#1F497D">RWDI:  the science of
              buildings, structures & the environment.  See what we
              do
              <a moz-do-not-send="true"
                href="http://www.rwdi.com/#%21services3/c1h0m">HERE</a>.<o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif;color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
                  style="font-size:10.0pt;font-family:"Tahoma",sans-serif">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma",sans-serif">
                Bishop, Bill [<a moz-do-not-send="true"
                  href="mailto:bbishop@pathfinder-ea.com">mailto:bbishop@pathfinder-ea.com</a>]
                <br>
                <b>Sent:</b> Wednesday, October 07, 2015 11:12<br>
                <b>To:</b> Mark Hallman;
                '<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>'<br>
                <b>Subject:</b> RE: % LOAD ATTRIBUTED TO OA DELIVERY<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span style="color:#1F497D">One way would
            be to create a MIN-AIR-SCH with all hourly values set to 0
            (or 0.001 to activate economizer), apply it to all SYSTEMs
            and use the difference in the outputs.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">Regards,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D">~Bill<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><b><span
                style="font-size:10.0pt;font-family:"Franklin
                Gothic Medium",sans-serif;color:black">William
                Bishop, PE, BEMP, BEAP, CEM, LEED AP
              </span></b><b><span
                style="font-size:10.0pt;font-family:"Franklin
                Gothic Medium",sans-serif;color:#006600">|</span></b><b><span
                style="font-size:10.0pt;font-family:"Franklin
                Gothic Medium",sans-serif;color:black"> Pathfinder
                Engineers & Architects LLP<o:p></o:p></span></b></p>
          <table class="MsoNormalTable"
            style="width:394.8pt;border-collapse:collapse" border="0"
            width="658" cellpadding="0" cellspacing="0">
            <tbody>
              <tr style="height:13.45pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:13.45pt" width="431">
                  <p class="MsoNormal" style="line-height:105%"><b><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black">Senior
                        Energy Engineer<o:p></o:p></span></b></p>
                </td>
                <td rowspan="6" style="width:136.35pt;padding:0in 5.4pt
                  0in 5.4pt;height:13.45pt" width="227">
                  <p class="MsoNormal" style="line-height:105%"><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><img
                        id="Picture_x0020_4"
                        src="cid:part8.00090504.05080103@greensim.com"
                        border="0" height="47" width="70"> 
                      <img id="Picture_x0020_2"
                        src="cid:part9.08080007.09030609@greensim.com"
                        border="0" height="49" width="57"><o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:4.55pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:4.55pt" valign="top" width="431">
                  <p class="MsoNormal" style="line-height:105%"><span
style="font-size:5.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><o:p> </o:p></span></p>
                </td>
              </tr>
              <tr style="height:9.8pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:9.8pt" nowrap="nowrap" valign="bottom"
                  width="431">
                  <p class="MsoNormal" style="line-height:105%"><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">134
                      South Fitzhugh Street</span><span
                      style="font-size:9.0pt;line-height:105%;color:#1F497D">                
                    </span><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">Rochester,
                      NY 14608<o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:12.4pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:12.4pt" valign="top" width="431">
                  <p class="MsoNormal" style="line-height:105%"><b><i><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#002060">T:
                          (585) 698-1956</span><span
                          style="color:#002060">             
                        </span></i></b><span style="color:#1F497D">          </span><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:#1F497D">F:
                      (585) 325-6005</span><span
style="font-size:9.0pt;line-height:105%;font-family:"Arial",sans-serif;color:black"><o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:9.8pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:9.8pt" valign="top" width="431">
                  <p class="MsoNormal" style="mso-line-height-alt:9.8pt"><span
                      style="color:#1F497D"><a moz-do-not-send="true"
                        href="mailto:wbishop@pathfinder-ea.com"><span
                          style="font-size:9.0pt;font-family:"Arial",sans-serif">bbishop@pathfinder-ea.com</span></a></span><span
style="font-size:9.0pt;font-family:"Arial",sans-serif;color:black">            
                    </span><span style="color:#1F497D"><a
                        moz-do-not-send="true"
                        href="http://www.pathfinder-ea.com/"><span
                          style="font-size:9.0pt;font-family:"Arial",sans-serif"><a class="moz-txt-link-abbreviated" href="http://www.pathfinder-ea.com">www.pathfinder-ea.com</a></span></a><o:p></o:p></span></p>
                </td>
              </tr>
              <tr style="height:24.6pt">
                <td style="width:258.45pt;padding:0in 5.4pt 0in
                  5.4pt;height:24.6pt" valign="top" width="431">
                  <p class="MsoNormal"
                    style="margin-top:3.0pt;line-height:105%"><span
                      style="color:#1F497D"><img id="Picture_x0020_5"
                        src="cid:part12.00010106.05060305@greensim.com"
alt="http://png-5.findicons.com/files/icons/977/rrze/720/globe.png"
                        border="0" height="40" width="42"></span><span
                      style="font-size:7.5pt;line-height:105%;color:#00B0F0">Carbon

                      Fee and Dividend - simple, effective, and
                      market-based.</span><span style="color:#1F497D"><o:p></o:p></span></p>
                </td>
              </tr>
            </tbody>
          </table>
          <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        </div>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b>From:</b> Equest-users [<a
                moz-do-not-send="true"
                href="mailto:equest-users-bounces@lists.onebuilding.org"><a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a></a>]
              <b>On Behalf Of </b>Mark Hallman<br>
              <b>Sent:</b> Wednesday, October 07, 2015 10:59 AM<br>
              <b>To:</b> '<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>' <<a
                moz-do-not-send="true"
                href="mailto:equest-users@lists.onebuilding.org"><a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a></a>><br>
              <b>Subject:</b> [Equest-users] % LOAD ATTRIBUTED TO OA
              DELIVERY<o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif">Hi there,<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif">Is there a way to accurately parse out
            from the eQUEST output file the percentage of the cooling
            and heating load that is attributed to OA delivery?   Any
            advice would be appreciated.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif">Thanks in advance!<br>
            Mark Hallman.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:9.0pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><b><span
              style="font-size:7.5pt;font-family:"Segoe
              UI",sans-serif">mark hallman<o:p></o:p></span></b></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif">p.eng. leed ap bd&c<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif">project engineer<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif"><a moz-do-not-send="true"
              href="mailto:mdh@rwdi.com">mdh@rwdi.com</a><o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif">519 823 1311 x2494<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:7.5pt;font-family:"Segoe
            UI",sans-serif">RWDI:  the science of buildings,
            structures & the environment.  See what we do
            <a moz-do-not-send="true"
              href="http://www.rwdi.com/#%21services3/c1h0m">HERE</a>.<o:p></o:p></span></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>