<div dir="ltr">One thing to keep in mind is that the value for efficiency in eQUEST is HIR, which is the reciprocal of efficiency. In other words, higher HIR is worse that lower HIR. Is that what you are seeing? <div><br></div><div>Another thing you might be seeing is the that value provided by these curves includes PLR. So at 50% load, the curve value is 0.5 for a boiler with no part-load degradation. </div><div><br></div><div>I've examined the default curves in the past and found they performed correctly, i.e. in the right direction. </div><div><br></div><div>-Erik</div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><b>Erik Kolderup, PE, LEED AP</b><div><a href="mailto:erik@kolderupconsulting.com" target="_blank">erik@kolderupconsulting.com</a><span style="color:rgb(153,153,153)"> | 415.531.5198 | </span><a href="http://www.kolderupconsulting.com" target="_blank">www.kolderupconsulting.com</a><span style="color:rgb(153,153,153)"> </span><br></div></div></div></div>
<br><div class="gmail_quote">On Tue, Sep 22, 2015 at 1:02 PM, Adam Barker <span dir="ltr"><<a href="mailto:ABarker@pemi.com" target="_blank">ABarker@pemi.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Has anyone come across issues with the default condensing boiler curve in eQuest? This curve is a function of part load and return water temperature, and based on how condensing boilers work you would anticipate the part load efficiency to get worse as return water temperature increased (assuming part load is the same).<br>
<br>
I am seeing the opposite in eQuest, where the default 80F RWT is giving me a poor seasonal efficiency, and a temperature like 160 RWT (in the non-condensing spectrum) is giving me a very high seasonal efficiency.<br>
<br>
Any insight into why this might be happening?<br>
<br>
Adam Barker, MBSc, C.E.T., LEED AP BD+C<br>
Energy Project Manager<br>
Provident Energy Management Inc.<br>
T: <a href="tel:416-736-0630%20x%201874" value="+14167360630">416-736-0630 x 1874</a> | <a href="mailto:abarker@pemi.com">abarker@pemi.com</a><mailto:<a href="mailto:abarker@pemi.com">abarker@pemi.com</a>><br>
<br>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>