<div dir="ltr"><div><div><div>Hi,<br><br></div>I don't know Notetab, but as long as you
 have one system for each zone, this is pretty easy if your editor 
supports Regular Expressions (Regex).<br><br></div>As you might know, 
inp files has what I call a positional input for a few things (space 
> surface > window/door, same for system > zone). Meaning if 
you find something that is a system, everything that's right after 
(which are zones) below to this system until you find another system. As
 opposed to having a keyword linking those two objects.<br><br></div><div>So
 you could use a regex for this job. Especially using positive 
lookaheads to delimit a single system and its zone (singular here, could
 be plural).<br><br></div><div>If you do have only a single zone per system, it's even easier.<br><br><br></div><div>Just look for a system and it's zone below it.<br><br></div><div>If
 you are not familiar with regex and can't manage to build it, let me 
know, I'll try to find a few tomorrow to help you out (send me your file
 or an extract or it so I don't have to create a dummy one to play with 
it).<br><br></div><div>By the way, here's a website I wish existed when I first started playing with regex: <a href="https://regex101.com/" target="_blank">https://regex101.com/</a>. Fyi, Notepad++ uses the prce engine.<br><br></div><div>Cheers,<br></div><div>Julien<br></div><div><br></div></div><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><div>--<br>Julien Marrec, EBCP, BPI MFBA<br>Energy&Sustainability Engineer<br>T: +33 6 95 14 42 13<br><span style="color:rgb(0,0,0)"><br></span><span style="color:rgb(0,0,0)">LinkedIn (en) : <span style="color:rgb(0,0,0)"><a href="http://www.linkedin.com/in/julienmarrec" target="_blank">www.linkedin.com/in/julienmarrec</a><br></span>LinkedIn (fr) : <a href="http://www.linkedin.com/in/julienmarrec/fr" target="_blank">www.linkedin.com/in/julienmarrec/fr</a></span><br><span style="color:rgb(0,0,0)"><a href="http://www.linkedin.com/in/julienmarrec" target="_blank"></a></span></div></div></div></div>
<br><div class="gmail_quote">2015-09-09 22:04 GMT+02:00 Phillips, Jesse <span dir="ltr"><<a href="mailto:jphillips@rdkengineers.com" target="_blank">jphillips@rdkengineers.com</a>></span>:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">





<div link="#0563C1" vlink="#954F72" lang="EN-US">
<div>
<p class="MsoNormal"><span style="color:#1f497d">I don’t think you can create macros in NoteTab.  What would that macro look like in boxer?<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Times New Roman",serif;color:#1f497d">Jesse Phillips<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Times New Roman",serif;color:#1f497d">Energy Engineer<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Times New Roman",serif;color:#1f497d">RDK Engineers<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Times New Roman",serif;color:#1f497d">P: 857-221-5957<u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<div>
<div style="border:none;border-top:solid #e1e1e1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Nathan Miller [mailto:<a href="mailto:nathanm@rushingco.com" target="_blank">nathanm@rushingco.com</a>] <br>
<b>Sent:</b> Wednesday, September 09, 2015 3:38 PM<br>
<b>To:</b> Phillips, Jesse <jphillips@RDKEngineers.com>; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> RE: eQuest & NoteTab Question<u></u><u></u></p>
</div>
</div><div><div class="h5">
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="color:#1f497d">Can you create a macro that searches for each instance of “=ZONE”, copies the text before the “=” to get the zone name, and the pastes in the lines necessary to create a new single zone system, using the zone
 name now stored in the clip-board to paste in the control zone? <u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d">I’m not familiar with NoteTab, but you can do that in boxer.
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal" style="margin-top:1.0pt"><b><span style="font-size:10.0pt;font-family:"Verdana",sans-serif;color:#632423"><u></u> <u></u></span></b></p>
<p class="MsoNormal" style="margin-right:0in;margin-bottom:4.0pt;margin-left:0in">
<b><span style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#6f1200">Nathan Miller, PE, LEED AP BD+C</span></b><b><span style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#632423"> –
</span></b><i><span style="font-size:8.0pt;font-family:"Verdana",sans-serif;color:black">Mechanical Engineer/Senior Energy Analyst</span></i><b><span style="font-size:9.0pt;font-family:"Verdana",sans-serif;color:#632423"><u></u><u></u></span></b></p>
<p class="MsoNormal" style="margin-top:3.0pt;line-height:115%"><b><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6f1200">RUSHING</span></b><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#bfab7f">
</span><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">|
</span><b><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6f1200">D</span></b><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#bfab7f">
</span><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">206-788-4577 |</span><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#bfab7f">
</span><b><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6f1200">O</span></b><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#a50021">
</span><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:black">206-285-7100</span><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#bfab7f"><u></u><u></u></span></p>
<p class="MsoNormal" style="line-height:115%"><b><span style="font-size:8.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6f1200"><a href="http://www.rushingco.com/" target="_blank"><span style="color:#6f1200">www.rushingco.com</span></a></span></b><b><span style="font-size:9.0pt;line-height:115%;font-family:"Verdana",sans-serif;color:#6f1200"><u></u><u></u></span></b></p>
</div>
<p class="MsoNormal"><span style="color:#1f497d"><u></u> <u></u></span></p>
<div>
<div style="border:none;border-top:solid #e1e1e1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Phillips, Jesse<br>
<b>Sent:</b> Wednesday, September 09, 2015 3:23 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] eQuest & NoteTab Question<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Hi,<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">I have a model with 233 zones.  Right now, every zone has a water loop heat pump.  I want to convert these all to packaged single zone systems.  To do this, I am working in the .inp file and doing a “find and replace” in NoteTab.  The replacing
 of the system type is easy.  I simply search for the “type      = HP” line and replace with “type     = PSZ”.  However, the PSZ system requires a control zone.  I would like each control zone to be the zone in which that particular system resides.  Which means,
 for each of my 233 zones, I will have a different control zone (i.e. no longer a simple find and replace search).<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Does anyone know of a way to use “find and replace” (or another method) to set each control zone with the zone name which the system resides?<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">This is what the .inp file should look like for a packaged single zone system:<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="font-size:10.0pt;background:yellow">"EL1 Sys1 (PTAC) (G.SSW1)" = SYSTEM</span><span style="font-size:10.0pt">         
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   TYPE             = PSZ<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   HEAT-SOURCE      = HEAT-PUMP<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   ZONE-HEAT-SOURCE = NONE<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   SIZING-RATIO     = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   COOL-SIZING-RATI = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   MIN-SUPPLY-T     = 58<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   FAN-SCHEDULE     = "S1 Sys1 (PTAC) Fan Sch"<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   CW-LOOP          = "DEFAULT-CW"<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   COOLING-CAPACITY = 15752<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   COOL-SH-CAP      = 11839<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   HP-SUPP-SOURCE   = NONE<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   FURNACE-HIR      = 1.24067<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   <span style="background:yellow">
CONTROL-ZONE     = "EL1 SSW Perim Zn (G.SSW1)"</span><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-EER95          = 8.24<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-COP47          = 0.78<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-AFUE           = 0.78<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-SF-MTR-TYPE    = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-RF-MTR-TYPE    = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-OSA-DMPR-CTRL  = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-HTG-DUCT-LOCN  = *Ceiling Plenum*<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-HTG-DUCT-RVAL  = 7<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-CLG-DUCT-LOCN  = *Ceiling Plenum*<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-CLG-DUCT-RVAL  = 7<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-CLG-CAP-CATEG  = 14<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt"><u></u> <u></u></span></p>
<p class="MsoNormal">For my next system, everything would be exactly the same except the highlighted lines (and so on for all 233 systems):<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="font-size:10.0pt;background:yellow">"EL1 Sys1 (PTAC) (G.W2)" = SYSTEM</span><span style="font-size:10.0pt">         
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   TYPE             = PSZ<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   HEAT-SOURCE      = HEAT-PUMP<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   ZONE-HEAT-SOURCE = NONE<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   SIZING-RATIO     = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   COOL-SIZING-RATI = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   MIN-SUPPLY-T     = 58<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   FAN-SCHEDULE     = "S1 Sys1 (PTAC) Fan Sch"<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   CW-LOOP          = "DEFAULT-CW"<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   COOLING-CAPACITY = 15752<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   COOL-SH-CAP      = 11839<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   HP-SUPP-SOURCE   = NONE<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   FURNACE-HIR      = 1.24067<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   <span style="background:yellow">
CONTROL-ZONE     = "EL1 Sys1 (PTAC) (G.W2)"</span><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-EER95          = 8.24<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-COP47          = 0.78<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-AFUE           = 0.78<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-SF-MTR-TYPE    = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-RF-MTR-TYPE    = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-OSA-DMPR-CTRL  = 1<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-HTG-DUCT-LOCN  = *Ceiling Plenum*<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-HTG-DUCT-RVAL  = 7<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-CLG-DUCT-LOCN  = *Ceiling Plenum*<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-CLG-DUCT-RVAL  = 7<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt">   C-CLG-CAP-CATEG  = 14<u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">thank you,<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal" style="text-autospace:none"><span style="color:#1f497d">Jesse Phillips | Energy Engineer<u></u><u></u></span></p>
<p class="MsoNormal" style="margin-bottom:12.0pt"><span style="font-size:12.0pt;font-family:"Times New Roman",serif"><u></u> <u></u></span></p>
</div></div></div>
<br><br></div>

<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>