<div>FUNCTIONS is a very nice feature, which makes DOE2 more extendability.Hope it will be implemented in future DOE2 version and thanks Joe to do that!!</div><div>PS:If FUNCTIOS were to be implemented, would DOE2.2/2.3 Engineer manual open to public?</div><div><div style="color:#909090;font-family:Arial Narrow;font-size:12px">------------------</div><div style="font-size:14px;font-family:Verdana;color:#000;"><div>
<div><font color="#3366ff" size="2"><strong>Yongqing Zhao</strong></font></div>
<div><font size="2"><strong><font color="#006600">Changsha Green Building & Energy Saving Technology CO.,LTD<br></font></strong><font color="#3366ff">NO.438,Shaoshan Road,Changsha,Hunan,China<br>Telephone:13574805636</font></font></div>
<div><font color="#3366ff" size="2">Email:zhaoyongqing1987@126.com</font></div>
<div><font size="2"> <span>503271081@qq.com</span></font> </div></div></div></div><div> </div><div><div><br></div><div><br></div><div style="font-size: 12px;font-family: Arial Narrow;padding:2px 0 2px 0;">------------------ Original ------------------</div><div style="font-size: 12px;background:#efefef;padding:8px;"><div><b>From: </b> "Joe huang";<yjhuang@whiteboxtechnologies.com>;</div><div><b>Date: </b> Sun, Sep 6, 2015 10:54 AM</div><div><b>To: </b> "equest-users"<equest-users@lists.onebuilding.org>; <wbr></div><div></div><div><b>Subject: </b> Re: [Equest-users] eQUEST wish list</div></div><div><br></div>
I also support re-enabling FUNCTIONS in DOE-2.2, which I've found to
be extremely useful and powerful for adding and testing new features
missing in the standard release. I've actually offered to do that
for Jeff, but have not been able to block out a time to do that.
Maybe sometime soon :-)<br>
<br>
Joe<br>
<pre class="moz-signature" cols="72">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
<a class="moz-txt-link-freetext" href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<div class="moz-cite-prefix">On 9/3/2015 6:32 AM, Jones, Christopher
wrote:<br>
</div>
<blockquote cite="mid:25F861E695EA99478F9790869A57C7D45E08C961@catormsx02" type="cite">
<style></style>
<div class="WordSection1">
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D ">FUNCTIONS<o:p></o:p></span></p>
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D "><o:p> </o:p></span></p>
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D "><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><img id="_x0000_i1029" src="cid:DA67B0B2@AF8AB745.C1AEEB55" height="43" width="108"></span><b><span style="color:#1C467A"><o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span style=" font-size:10.0pt ; ; ; ;;color:#1C467A ">Christopher
Jones,</span></b><b><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D "></span></b><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D ">P.Eng.<i>
<br>
</i></span><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA">Senior Engineer<b><o:p></o:p></b></span></p>
<p class="MsoNormal"><b><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA"><o:p> </o:p></span></b></p>
<p class="MsoNormal"><b><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA">WSP Canada Inc.<o:p></o:p></span></b></p>
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA">2300 Yonge Street, Suite 2300<o:p></o:p></span></p>
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA">Toronto, ON M4P 1E4</span><span style=" font-size:10.0pt ; ; ; ;;color:#595959 " lang="EN-CA"><br>
</span><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA">T +1 416-644-4226<o:p></o:p></span></p>
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA">F +1 416-487-9766<o:p></o:p></span></p>
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA">C +1 416-697-0065<o:p></o:p></span></p>
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D " lang="EN-CA"><a moz-do-not-send="true" href="http://www.wspgroup.com/"><span style="color:blue">www.wspgroup.com</span></a>
</span><i><span style=" font-size:10.0pt ; ; ; ;;color:#565656 " lang="EN-CA"><o:p></o:p></span></i></p>
</div>
<p class="MsoNormal"><span style=" font-size:10.0pt ; ; ; ;;color:#1F497D "><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #B5C4DF
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style=" font-size:10.0pt ; ; ; ; ">From:</span></b><span style=" font-size:10.0pt ; ; ; ; ">
Equest-users
[<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Sami, Vikram<br>
<b>Sent:</b> Wednesday, September 02, 2015 2:07 PM<br>
<b>To:</b> Kathryn Kerns; Lapierre, Patrick; Bishop,
Bill; <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] eQUEST wish list -
DOAS capabilities?<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="color:#1F497D">These are all
good suggestions. I would also expand on Shaun’s point about
transfer air between zones to incorporate energy recovery
capabilities in the DOAS. <o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<table class="MsoNormalTable" border="0" cellpadding="0">
<tbody>
<tr>
<td style="padding:.75pt .75pt .75pt .75pt" valign="top">
<p class="MsoNormal" style="line-height:12.0pt"><b><span style=" font-size:9.0pt ; ;;color:#E33B45 ">Vikram Sami</span></b><span style=" font-size:12.0pt ; ; ; ;;color:#1F497D "><br>
</span><span style=" font-size:7.0pt ; ;;color:#666666 ">AIA, BEMP, LEED BD+C</span><span style=" font-size:9.0pt ; ;;color:black "> </span><span style=" font-size:12.0pt ; ; ; ;;color:#1F497D "><br>
</span><span style=" font-size:9.0pt ; ;;color:#666666 ">Associate Partner</span><span style=" font-size:12.0pt ; ; ; ;;color:#1F497D "><o:p></o:p></span></p>
</td>
<td style="width:12.0pt;padding:.75pt .75pt .75pt .75pt" width="16">
<p class="MsoNormal" style="line-height:12.0pt"><span style=" font-size:12.0pt ; ; ; ;;color:#1F497D "> <o:p></o:p></span></p>
</td>
<td style="padding:.75pt .75pt .75pt .75pt" valign="top">
<p class="MsoNormal" style="line-height:12.0pt"><span style=" font-size:9.0pt ; ;;color:#666666 ">ZGF ARCHITECTS LLP</span><span style=" font-size:12.0pt ; ; ; ;;color:#1F497D "><br>
</span><b><span style=" font-size:7.5pt ; ;;color:#E33B45 ">T
</span></b><span style=" font-size:9.0pt ; ;;color:#666666 ">206.521.3509
</span><b><span style=" font-size:7.5pt ; ;;color:#E33B45 ">E
</span></b><span style=" font-size:9.0pt ; ;;color:#666666 "><a moz-do-not-send="true" href="mailto:vikram.sami@zgf.com"></a><a class="moz-txt-link-abbreviated" href="mailto:vikram.sami@zgf.com">vikram.sami@zgf.com</a></span><span style=" font-size:12.0pt ; ; ; ;;color:#1F497D "><br>
</span><span style=" font-size:9.0pt ; ;;color:#666666 ">925 Fourth Avenue, Suite
2400
<br>
Seattle, WA 98104</span><span style=" font-size:12.0pt ; ; ; ;;color:#1F497D "><o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
</div>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [<a moz-do-not-send="true" href="mailto:equest-users-bounces@lists.onebuilding.org"></a><a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Kathryn Kerns<br>
<b>Sent:</b> Wednesday, September 02, 2015 9:23 AM<br>
<b>To:</b> Lapierre, Patrick <<a moz-do-not-send="true" href="mailto:plapierre@bpa.ca">plapierre@bpa.ca</a>>;
Bishop, Bill <<a moz-do-not-send="true" href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a>>;
<a moz-do-not-send="true" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] eQUEST wish list - DOAS
capabilities?<o:p></o:p></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="color:#1F497D">Great
suggestions. Also it would be nice to have the ability to
modify a heating device downstream of the DOA cooling coil
to simulate hot gas bypass or a supply desiccant system.
There are many white papers regarding the efficiency of an
enthalpy heat wheel located in the DOA supply downstream of
the DX coil. This heat wheel is half exposed to the supply
air and the other half heated by a hot water coil, furnace,
hot gas bypass, heat pipe, etc.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><b><span style=" font-size:12.0pt ; ; ; ;;color:black ">Kathryn
Kerns</span></b><span style=" font-size:12.0pt ; ; ; ;;color:#1F497D "><o:p></o:p></span></p>
<p class="MsoNormal"><b><span style=" ; ; ;;color:#1F497D ">Systems
Specialist</span></b><span style=" font-size:12.0pt ; ; ; ;;color:#1F497D "><o:p></o:p></span></p>
<p class="MsoNormal"><b><span style=" font-size:12.0pt ; ; ; ;;font-variant:small-caps;color:teal ">BCE</span></b><b><span style=" font-size:10.0pt ; ; ; ;;font-variant:small-caps;color:teal ">
</span></b><b><span style=" font-size:12.0pt ; ; ; ;;font-variant:small-caps;color:teal ">Engineers,
Inc.<o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span style=" font-size:9.0pt ; ; ; ;;color:black ">| Ph:
253.922.0446 | Fx: 253.922.0896 |</span></b><span style=" font-size:7.0pt ; ; ; ;;color:black ">
<o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [<a moz-do-not-send="true" href="mailto:equest-users-bounces@lists.onebuilding.org"></a><a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Lapierre, Patrick<br>
<b>Sent:</b> Tuesday, September 01, 2015 9:12 AM<br>
<b>To:</b> Bishop, Bill <<a moz-do-not-send="true" href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a>>;
<a moz-do-not-send="true" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] eQUEST wish list - DOAS
capabilities?<o:p></o:p></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span style="color:#366092" lang="FR-CA">Concerning
DOAS, the following capabilities would be great :<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#366092" lang="FR-CA"><o:p> </o:p></span></p>
<p class="MsoListParagraph" style="text-indent:-.25in"><span style="color:#366092" lang="FR-CA">1-</span><span style=" font-size:7.0pt ; ; ; ;;color:#366092 " lang="FR-CA">
</span><span style="color:#366092" lang="FR-CA">Return air
temperature/humidity is the actual mixed air
temperature/humidity from the return of every system
attached to the DOAS and varies hourly (for heat recovery
purposes);<o:p></o:p></span></p>
<p class="MsoListParagraph" style="text-indent:-.25in"><span style="color:#366092" lang="FR-CA">2-</span><span style=" font-size:7.0pt ; ; ; ;;color:#366092 " lang="FR-CA">
</span><span style="color:#366092" lang="FR-CA">Removing the
need of a dummy-zone;<o:p></o:p></span></p>
<p class="MsoListParagraph" style="text-indent:-.25in"><span style="color:#366092" lang="FR-CA">3-</span><span style=" font-size:7.0pt ; ; ; ;;color:#366092 " lang="FR-CA">
</span><span style="color:#366092" lang="FR-CA">Supply air
temperature setpoint can vary hourly depending on its
attached systems heating/cooling demands. IE : if attached
systems are in cooling mode, supply = 55F, if in heating
mode, supply = 70F. (right now the need of using a dummy
zone limits this).<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#366092" lang="FR-CA"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#366092" lang="FR-CA">Great
to know an update is being worked on. Fixing these would
help out.<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#366092" lang="FR-CA"><o:p> </o:p></span></p>
<p class="MsoNormal"><span style="color:#366092" lang="FR-CA">Thanks,<o:p></o:p></span></p>
<p class="MsoNormal"><span style="color:#366092" lang="FR-CA"><o:p> </o:p></span></p>
<div>
<table class="MsoNormalTable" style="width:100.0%;border-collapse:collapse" border="0" width="100%" cellpadding="0" cellspacing="0">
<tbody>
<tr>
<td style="width:26.25pt;padding:0in 0in 0in 0in" width="35">
<p class="MsoNormal"><span style=" font-size:12.0pt ; ; ; ;;color:#366092 "><img id="_x0000_i1025" src="cid:AD60B3E3@AF8AB745.C1AEEB55" border="0" height="31" width="34"><o:p></o:p></span></p>
</td>
<td style="padding:0in 0in 0in 0in" valign="top">
<p class="MsoNormal"><b><span style=" font-size:10.0pt ; ; ; ;;color:#3F3F3F ">Patrick</span></b><b><span style=" font-size:10.0pt ; ; ; ;;color:#366092 "> </span></b><b><span style=" font-size:10.0pt ; ; ; ;;color:#3F3F3F ">Lapierre</span></b><b><span style=" font-size:10.0pt ; ; ; ;;color:#7D7D7D ">_ing.</span></b><b><span style=" font-size:10.0pt ; ; ; ;;color:#366092 "><o:p></o:p></span></b></p>
<p class="MsoNormal"><span style=" font-size:7.5pt ; ; ; ;;color:#A5A5A5 "><a moz-do-not-send="true" href="mailto:plapierre@bpa.ca"></a><a class="moz-txt-link-abbreviated" href="mailto:plapierre@bpa.ca">plapierre@bpa.ca</a><o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
</div>
<p class="MsoNormal"><span style=" font-size:7.5pt ; ; ; ;;color:#BFBFBF " lang="FR-CA"> </span><span style="color:#366092" lang="FR-CA"><o:p></o:p></span></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span lang="FR">De :</span></b><span lang="FR"> Equest-users [<a moz-do-not-send="true" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>De la part de</b> Bishop, Bill<br>
<b>Envoyé :</b> 1 septembre 2015 11:52<br>
<b>À :</b> <a moz-do-not-send="true" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Objet :</b> [Equest-users] eQUEST wish list - DOAS
capabilities?<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><span lang="FR-CA"><o:p> </o:p></span></p>
<p class="MsoNormal">Hi All,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">DOE-2.3 is coming along slowly and it’s
anybody’s guess as to when it will be ready. That said, Steve
gates is asking for feedback regarding DOAS (dedicated outdoor
air system) capabilities, as he will be implementing that
next. The intent is to allow it to operate with any type of
system.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Please share your ideas for desired DOAS
capabilities in eQUEST, and emphasize what is most important
to you. Limit your suggestions to anything related to
ventilation. I will send a compiled list to Steve next week.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Thanks!<o:p></o:p></p>
<p class="MsoNormal">~Bill<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><b><span style=" font-size:10.0pt ; ; ; ;;color:black ">William
Bishop, PE, BEMP, BEAP, CEM, LEED AP
</span></b><b><span style=" font-size:10.0pt ; ; ; ;;color:#006600 ">|</span></b><b><span style=" font-size:10.0pt ; ; ; ;;color:black ">
Pathfinder Engineers & Architects LLP<o:p></o:p></span></b></p>
<table class="MsoNormalTable" style="width:394.8pt;border-collapse:collapse" border="0" width="526" cellpadding="0" cellspacing="0">
<tbody>
<tr style="height:13.45pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:13.45pt" width="345">
<p class="MsoNormal" style="line-height:105%"><b><span style=" font-size:9.0pt;line-height:105% ; ; ; ;;color:black ">Senior
Energy Engineer<o:p></o:p></span></b></p>
</td>
<td rowspan="6" style="width:136.35pt;padding:0in 5.4pt
0in 5.4pt;height:13.45pt" width="182">
<p class="MsoNormal" style="line-height:105%"><span style=" font-size:9.0pt;line-height:105% ; ; ; ;;color:black "><img id="Picture_x0020_4" src="cid:865C72E8@AF8AB745.C1AEEB55" border="0" height="47" width="70">
<img id="Picture_x0020_2" src="cid:527DAAE1@AF8AB745.C1AEEB55" border="0" height="49" width="57"><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:4.55pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:4.55pt" valign="top" width="345">
<p class="MsoNormal" style="line-height:105%"><span style=" font-size:5.0pt;line-height:105% ; ; ; ;;color:black "><o:p> </o:p></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:9.8pt" nowrap="nowrap" valign="bottom" width="345">
<p class="MsoNormal" style="line-height:105%"><span style=" font-size:9.0pt;line-height:105% ; ; ; ;;color:#1F497D ">134
South Fitzhugh Street</span><span style="font-size:9.0pt;line-color:#1F497D">
</span><span style=" font-size:9.0pt;line-height:105% ; ; ; ;;color:#1F497D ">Rochester,
NY 14608<o:p></o:p></span></p>
</td>
</tr>
<tr style="height:12.4pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:12.4pt" valign="top" width="345">
<p class="MsoNormal" style="line-height:105%"><b><i><span style=" font-size:9.0pt;line-height:105% ; ; ; ;;color:#002060 ">T:
(585) 698-1956</span><span style="color:#002060">
</span></i></b><span style="color:#1F497D"> </span><span style=" font-size:9.0pt;line-height:105% ; ; ; ;;color:#1F497D ">F:
(585) 325-6005</span><span style=" font-size:9.0pt;line-height:105% ; ; ; ;;color:black "><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:9.8pt" valign="top" width="345">
<p class="MsoNormal" style="mso-line-height-alt:9.8pt"><a moz-do-not-send="true" href="mailto:wbishop@pathfinder-ea.com"><span style=" font-size:9.0pt ; ; ; ;;color:blue "></span></a><a class="moz-txt-link-abbreviated" href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a><span style=" font-size:9.0pt ; ; ; ;;color:black ">
</span><a moz-do-not-send="true" href="http://www.pathfinder-ea.com/"><span style=" font-size:9.0pt ; ; ; ;;color:blue ">www.pathfinder-ea.com</span></a><span style="color:#1F497D"><o:p></o:p></span></p>
</td>
</tr>
<tr style="height:24.6pt">
<td style="width:258.45pt;padding:0in 5.4pt 0in
5.4pt;height:24.6pt" valign="top" width="345">
<p class="MsoNormal" style="margin-top:3.0pt;line-height:105%"><img id="Picture_x0020_5" src="cid:5C9B04B1@AF8AB745.C1AEEB55" border="0" height="40" width="42"><span style="font-size:7.5pt;line-color:#00B0F0">Carbon
Fee and Dividend - simple, effective, and
market-based.</span><span style="color:#1F497D"><o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><o:p> </o:p></p>
<table class="MsoNormalTable" border="0" cellpadding="0">
<tbody>
<tr>
<td style="padding:.75pt .75pt .75pt .75pt" valign="top">
<p class="MsoNormal" style="line-height:12.0pt"><span style=" font-size:9.0pt ; ;;color:#666666 "><a moz-do-not-send="true" href="https://www.zgf.com/ZGF_Email_Disclaimer.html">ZGF Email
Disclaimer</a></span><span style=" font-size:12.0pt ; ; ; ; ">
<o:p></o:p></span></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><span style=" font-size:12.0pt ; ; ; ; "><o:p> </o:p></span></p>
</div>
<hr>
<div style="font-size:9pt; color:gray; font-family:Arial,
sans-serif;"><br>
You are receiving this communication because you are listed as a
current WSP contact. Should you have any questions regarding
WSP’s electronic communications policy, please consult our
Anti-Spam Commitment
<a moz-do-not-send="true">www.wspgroup.com/casl</a>.
For any concern or if you believe you should not be receiving
this message, please forward this message to us at
<a moz-do-not-send="true" href="mailto:caslcompliance@wspgroup.com">caslcompliance@wspgroup.com</a>
so that we can promptly address your request. This message is
intended only for the use of the individual or entity to which
it is addressed, and may contain information which is
privileged, confidential, proprietary or exempt from disclosure
under applicable law. If you are not the intended recipient or
the person responsible for delivering the message to the
intended recipient, you are strictly prohibited from disclosing,
distributing, copying or in any way using this message. If you
have received this communication in error, please notify the
sender, and destroy and delete any copies you may have received.
<br>
<br>
WSP provides professional land surveying services through the
following entities: WSP Surveys (AB) Limited Partnership and WSP
Surveys (BC) Limited Partnership
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br></div>