<div dir="ltr"><font color="#0000ff">Hi Travis,</font><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">I can understand your problem but the achieved negative cooling load can be due to the less cooling requirement at that time.</font></div><div><font color="#0000ff">The cooling system is deprived of that part by the heat recovery wheel as a result of simulation.</font></div><div><font color="#0000ff">The negative cooling load is being seen at the cooler part of year.</font></div><div><font color="#0000ff">Now the heat recovery can use the hot air from the zone and return it back to the zone and making the cooling system behave like this.</font></div><div><font color="#0000ff">This is happening in only two zones of basement. </font></div><div><font color="#0000ff">So due to the less heating load in those spaces this thing is happening.</font></div><div><font color="#0000ff">Just try to find out those zones in basement and may be believe that basements could have less cooling requirement.</font></div><div><font color="#0000ff">The negative sign is just the opposite to that nature.</font></div><div><font color="#0000ff">So if the cooling load is negative then it is believed that there is heating load.If any more issue then may be there is some incorrect input in the model. like thermostat set-point, heating, cooling or fan schedules.</font></div><div><font color="#0000ff"><br></font></div><div><font color="#0000ff">Thanks,</font></div><div><font color="#0000ff">Sharad.</font><br><div class="gmail_extra"><br><div class="gmail_quote">On Thu, Jul 30, 2015 at 3:57 AM,  <span dir="ltr"><<a href="mailto:equest-users-request@lists.onebuilding.org" target="_blank">equest-users-request@lists.onebuilding.org</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Send Equest-users mailing list submissions to<br>
        <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
<br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:equest-users-request@lists.onebuilding.org" target="_blank">equest-users-request@lists.onebuilding.org</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:equest-users-owner@lists.onebuilding.org" target="_blank">equest-users-owner@lists.onebuilding.org</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of Equest-users digest..."<br>
<br>Today's Topics:<br>
<br>
   1. VRF Heat Recovery Calculations (Travis Miller)<br>
<br><br>---------- Forwarded message ----------<br>From: Travis Miller <<a href="mailto:tmiller@dcengineering.net" target="_blank">tmiller@dcengineering.net</a>><br>To: "<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>" <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>><br>Cc: <br>Date: Wed, 29 Jul 2015 22:21:35 +0000<br>Subject: [Equest-users] VRF Heat Recovery Calculations<br>





<div lang="EN-US" link="#0563C1" vlink="#954F72">
<div>
<p class="MsoNormal">I have created some heat recovery calculations for a VRF system following the Energy Trust of Oregon guidelines and I am getting some underwhelming savings.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">The project is a 4-story office building, one of the floors is a basement, and there is approximately 9000 SF per floor. 1 VRF air cooled unit per floor except for the third, where there are two. There might not be enough load diversity
 between zones to generate much heat recovery. One strange thing is that I am getting negative elec input to heat/cool numbers exported from the CSV hourly reports. Has anybody encountered this before?<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">I have attached my excel file for reference (sorry for the size – not sure how to compress an excel file). Any feedback would be much appreciated. Thanks in advance for your help.
<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><b><span style="font-size:13.5pt;font-family:"Arial Narrow","sans-serif"">Travis Miller, PE<u></u><u></u></span></b></p>
<p class="MsoNormal"><b><span style="font-family:"Arial Narrow","sans-serif"">DC Engineering</span></b><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif"">O: 406-829-8828; x. 209</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif"">123 W. Spruce ST.</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif"">Missoula, MT 59802<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:9.0pt;font-family:"Arial","sans-serif""><a href="http://www.dcengineering.net" target="_blank"><span style="color:blue">www.dcengineering.net</span></a></span><u><span style="font-size:9.0pt;color:blue"><u></u><u></u></span></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>

<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="mailto:Equest-users@lists.onebuilding.org" target="_blank">Equest-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
<br></blockquote></div><br></div></div></div>