    Julien,<br>
    <br>
    I don't mind at all being quoted or cited, but since I don't read
    everything that's posted, just the ones that intrigue me, you might
    want to cc me via e-mail to get my attention.  It's true that I had
    said in an earlier post that I've found DOE-2 models to be "lighter"
    than measurements, it was not just by a bit, but by a lot.  I didn't
    do any serious investigation into the discrepancy, but I attributed
    it to the models assuming uniform air conditions within a space,
    surface air film coefficients based on smooth planar surfaces, and
    uniform distribution of the internal thermal mass within the space. 
    As scientists or engineers, there's a preference for "getting the
    inputs right", i.e., having the furniture-fraction correspond to the
    actual amount of furniture in the space, but it may be that either
    the algorithm or the inputs need to be tweaked in order to get a
    indoor air temperatures closer to what's actually observed.<br>
    <br>
    Joe<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-freetext" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <div class="moz-cite-prefix">On 6/18/2015 1:04 AM, Julien Marrec
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAEqKKty8W+Gd5K9aZz0b_sah8_QRQYTYcyePQyg7pMYKCbOiqA@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>
          <div>Jeff,<br>
            <br>
            In E+ there's also an "InternalMass" objec. It is listed
            under the group "Thermal Zones and Surfaces". It only asks
            for a construction, a zone name, and its surface (m² / ft²):
            might be easier.<br>
            <br>
            From the I/O reference:<br>
            <i><b>Internal Mass</b><br>
              is used to specify the construction/material parameters
              and area of items within the space that are important to
              heat transfer calculations but not necessarily important
              geometrically. (For example, furniture within the space –
              particularly for large spaces).</i><br>
            <br>
            John,<br>
            <br>
            Both e+ and equest can have internal mass objects, that you
            can add/or customize.<br>
            <br>
            E+ having no defaults on the subject, it won't take any
            internal mass into account unless you tell it to.<br>
            <br>
            eQuest has by default some internal mass: Floor-weight and
            Furniture. For Furniture - default is FURN-WEIGHT = 2 lb/ft²
            of floor area - compare that to what you think you have in
            your garage and you'll see the difference :))<br>
            <br>
            I think an even bigger problem is to use external walls
            (especially in equest where it's so easy...) defined only by
            R-value as opposed to layer-by-layer, thus with no thermal
            mass...<br>
            <br>
            I'm pretty sure as a general rule we tend to underestimate
            the overall thermal mass.<br>
            On the subject, I remembered Joe Huang (Joe, I hope you
            don't mind me quoting you) making a comment about DOE2
            making "lighter" models than real anyway so you have to
            "boost up the internal mass considerably beyond what's there
            to get  the floating temperature profiles to match measured
            temperatures" (see his post <a moz-do-not-send="true"
href="http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2015-January/046078.html">here</a>)<br>
            <br>
          </div>
          Best,<br>
        </div>
        Julien<br>
        <div>
          <div><br>
            <br>
            > Le 17 juin 2015 à 20:20, "Eurek, John S NWO" <<a
              moz-do-not-send="true"
              href="mailto:John.S.Eurek@usace.army.mil">John.S.Eurek@usace.army.mil</a>>
            a écrit :<br>
            ><br>
            > Classification: UNCLASSIFIED<br>
            > Caveats: NONE<br>
            ><br>
            > General question:<br>
            ><br>
            > Do any energy models take into account the thermal mass
            of stuff?<br>
            ><br>
            > Then extreme case I know about is a garage.  When my
            garage was empty and I turned on the heater it heated up
            fairly quickly.  When I brought in my truck, tools, shelves,
            etc. (a few tons of steel) it took a lot lot longer to get
            warm.<br>
            ><br>
            > This is an extreme case, but the same thing would
            happen in every type of building on some level.<br>
            ><br>
            > -----Original Message-----<br>
            > From: Equest-users [mailto:<a moz-do-not-send="true"
              href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>]
            On Behalf Of Jeff Haberl<br>
            > Sent: Wednesday, June 17, 2015 10:39 AM<br>
            > To: Peter Schonherr; <a moz-do-not-send="true"
              href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
            > Subject: [EXTERNAL] Re: [Equest-users] Thermal mass
            effects of interior walls<br>
            ><br>
            > Hello Peter,<br>
            ><br>
            ><br>
            ><br>
            > Create layered walls with the materials you intend to
            simulate and then set the floor weight = 0 to trigger custom
            weighting factors. You may have to fiddle with the interior
            convection/radiation coefficient to get a meaningful
            “connection” to the room air node.<br>
            ><br>
            ><br>
            ><br>
            > Jeff<br>
            ><br>
            ><br>
            ><br>
            > 8=!  8=)  :=)  8=)  ;=)  8=)  8=(  8=)  8=()  8=)  8=|
             8=)  :=')  8=) 8=?<br>
            > Jeff S. Haberl,
            Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......<a
              moz-do-not-send="true" href="mailto:jhaberl@tamu.edu">jhaberl@tamu.edu</a>
            <mailto:........<a moz-do-not-send="true"
              href="mailto:jhaberl@tamu.edu">jhaberl@tamu.edu</a>><br>
            >
            Professor........................................................................Office
            Ph: 979-845-6507<br>
            > Department of
            Architecture............................................Lab
            Ph:979-845-6065<br>
            > Energy Systems
            Laboratory...........................................FAX:
            979-862-2457<br>
            > Texas A&M
            University...................................................77843-3581<br>
            > College Station, Texas, USA,
            77843..............................URL:<a
              moz-do-not-send="true" href="http://www.esl.tamu.edu">www.esl.tamu.edu</a><br>
            > 8=/  8=)  :=)  8=)  ;=)  8=)  8=()  8=)  :=)  8=)  8=!
             8=)  8=? 8=) 8=0<br>
            ><br>
            ><br>
            ><br>
            > From: Equest-users [mailto:<a moz-do-not-send="true"
              href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>]
            On Behalf Of Peter Schonherr<br>
            > Sent: Wednesday, June 17, 2015 10:26 AM<br>
            > To: <a moz-do-not-send="true"
              href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
            > Subject: [Equest-users] Thermal mass effects of
            interior walls<br>
            ><br>
            ><br>
            ><br>
            > Hello,<br>
            ><br>
            ><br>
            ><br>
            >      Is it possible to model the effects of thermal
            mass of interior walls? if so, how is that done?<br>
            ><br>
            ><br>
            ><br>
            > Peter Schonherr<br>
            ><br>
            ><br>
            ><br>
            ><br>
            > Classification: UNCLASSIFIED<br>
            > Caveats: NONE<br>
            ><br>
            ><br>
            > _______________________________________________<br>
            > Equest-users mailing list<br>
            > <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
            > To unsubscribe from this mailing list send  a blank
            message to <a moz-do-not-send="true"
              href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>