<div dir="ltr"><p class="MsoNormal" style="margin-bottom:0.0001pt;text-align:justify"><b><font face="arial, helvetica, sans-serif" color="#000000">Dear all,</font></b></p><p class="MsoNormal" style="margin-bottom:0.0001pt;text-align:justify"><b><font face="arial, helvetica, sans-serif" color="#000000"> I've got the following reply for a psz system in the baseline case during preliminary LEED design submittal:</font></b></p><p class="MsoNormal" style="margin-bottom:0.0001pt;text-align:justify"><b><font face="arial, helvetica, sans-serif" color="#000000"><br></font></b></p><p class="MsoNormal" style="margin-bottom:0.0001pt;text-align:justify"><font face="arial, helvetica, sans-serif"><b><font color="#000000">"</font><font color="#38761d">N</font></b><font color="#38761d">ote that
section G3.1.2.1 requires that where efficiency ratings, such as EER and COP, include
fan energy, the descriptor shall be broken down into its components so that
supply fan energy can be modeled separately. Because the efficiency ratings are
calculated at ARI-rated conditions, the fans should also be broken out at
ARI-rated conditions. Most simulation software programs have the capability to
perform this step automatically. Provide documentation showing that this
calculation has been performed by the software automatically or provide
calculations consistent with the ASHRAE 90.1-2007 User’s Manual showing that
the calculation has been performed at ARI-rated conditions</font></font><font face="arial, helvetica, sans-serif" color="#000000">."</font></p><p class="MsoNormal" style="margin-bottom:0.0001pt;text-align:justify"><font face="arial, helvetica, sans-serif" color="#000000"><br></font></p><p style="margin:0px;padding:0px 0px 10px;border:0px;outline:0px;vertical-align:baseline;line-height:1.5;background-image:initial;background-repeat:initial"><font face="arial, helvetica, sans-serif" color="#000000">What I did is that I referred to eQuest library, and documented the following paragraph to the reviewer:</font></p><p style="margin:0px;padding:0px 0px 10px;border:0px;outline:0px;vertical-align:baseline;line-height:1.5;background-image:initial;background-repeat:initial"><font face="arial, helvetica, sans-serif" color="#000000">"</font><font face="arial, helvetica, sans-serif" color="#783f04">COOLING-EIR:<br>The Electric Input Ratio (EIR), or 1/(Coefficient of Performance), for the cooling unit at ARI rated conditions..... This EIR is at ARI rated conditions, i.e., without correction for different temperature or part load. Note: If you include fan electric energy consumption in your value of COOLING-EIR, then you should set SUPPLY-KW/FLOW to zero. Otherwise, the supply fan electrical energy will be double counted........ Imbedding the fan energy into the COOLING-EIR is valid only if the fan is constant volume and INDOOR-FAN-MODE = INTERMITTENT; i.e. the fan cycles on/off with the compressor. If the fan runs continuously during occupied hours, or the fan is variable volume, then the fan energy cannot be included in the COOLING-EIR (or HEATING-EIR).</font><font face="arial, helvetica, sans-serif" color="#000000">"</font></p><p style="margin:0px;padding:0px 0px 10px;border:0px;outline:0px;vertical-align:baseline;line-height:1.5;background-image:initial;background-repeat:initial"><font face="arial, helvetica, sans-serif" color="#000000">And I did set fan kw/cfm to zero, intermittent, and constant volume, but I've got the SV-A report reporting zero kw power demand, and zero fan (kw) for the system and its zones.</font></p><p style="margin:0px;padding:0px 0px 10px;border:0px;outline:0px;vertical-align:baseline;line-height:1.5;background-image:initial;background-repeat:initial"><font color="#000000" face="arial, helvetica, sans-serif"><u>Then I got an advice stating that:</u></font></p><p style="margin:0px;padding:0px 0px 10px;border:0px;outline:0px;vertical-align:baseline;line-height:1.5;background-image:initial;background-repeat:initial"><font color="#000000" face="arial, helvetica, sans-serif">"<span style="line-height:19.2000007629395px">You should do what the reviewer mentions, divide the indoor fan from the efficiency rating at ARI-rated conditions and model it separately; this way you will be able to report the appropriate fan power"</span></font></p><p style="margin:0px;padding:0px 0px 10px;border:0px;outline:0px;vertical-align:baseline;line-height:1.5;background-image:initial;background-repeat:initial"><font color="#000000" face="arial, helvetica, sans-serif">My question is:<b><span style="line-height:19.2000007629395px"> </span><span style="line-height:19.2000007629395px">where do I separately input the indoor fan power (kw), and what value should it be?, knowing that this is a baseline case that do not refer to an actual design.</span></b></font></p><p style="margin:0px;padding:0px 0px 10px;border:0px;outline:0px;vertical-align:baseline;background-image:initial;background-repeat:initial"><font color="#000000" face="arial, helvetica, sans-serif"><span style="line-height:19.2000007629395px">Thanks,</span></font></p><div><div class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><blockquote style="padding:0px;color:rgb(0,0,0);font-family:Calibri,sans-serif;font-size:16px;border:none;margin-top:0px!important;margin-bottom:0px!important"><b style="color:rgb(34,34,34);font-family:arial,sans-serif;font-size:12.8000001907349px">Omar ElRawy, LEED AP BD+C</b><div style="color:rgb(34,34,34);font-family:arial,sans-serif;font-size:12.8000001907349px">LEED Project Manager</div><div style="color:rgb(34,34,34);font-family:arial,sans-serif;font-size:12.8000001907349px">EA Sustainable Building Consultants</div><div style="color:rgb(34,34,34);font-family:arial,sans-serif;font-size:12.8000001907349px"><a href="http://www.ea-buildingconsultants.com/" target="_blank">http://www.ea-buildingconsultants.com</a></div></blockquote></div></div></div></div></div>
</div>