<div dir="ltr"><div><span style="font-size:12.8000001907349px">Hello All -</span><div style="font-size:12.8000001907349px"><br></div><div style="font-size:12.8000001907349px">I am entering the data for a 60 floor building in equest. I had to return back to the wizard mode after doing a lot of work in the detailed mode since the client wanted lots of changes in the zoning.</div><div style="font-size:12.8000001907349px"><br></div><div style="font-size:12.8000001907349px">It is an exisiting building. My question is:</div><div style="font-size:12.8000001907349px"><br></div><div style="font-size:12.8000001907349px">How do I create different zones for cooling and heating?</div><div style="font-size:12.8000001907349px"><br></div><div style="font-size:12.8000001907349px">The 60 floor building has 15 different floor plans(hence i have 15 different shells entered). I am able to enter all of shell data but am stuck at the zoning. If I have to create different zones for cooling and heating please suggest the best method to do this. I am under tight deadlines, would appreciate some quick advice. Thank you in advance.</div><div style="font-size:12.8000001907349px"><br></div><div style="font-size:12.8000001907349px"><b>I will be able to mail the eQuest file if required for reference.</b><br clear="all"><div><br></div><div>Below are some details on the building system and the zoning required:</div><div><br></div><div><span style="font-size:12.8000001907349px"><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)"><b><br></b></span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)"><b><br></b></span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)"><b>NOTES for Zones:</b></span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">7-18 floor ( 7 zones in total)</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div></span><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">NE and NW and South are perimeter,</span><b><i><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)"> </span></i></b><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)">Steam Radiation </span><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">zones (please verify this information from spreadsheet)</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">4 AHUs from 7-18 floor cool the floors. This is a VAV chilled water</span><b><i><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)"> </span></i></b><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)"> with preheat coil</span><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">. Cooling source is mentioned below.</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">19-</span><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)">2</span><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">4 same 3 perimeter zones as the heating zones of the below floor. </span><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)">For Cooling 3 AHUs for core.<b><i></i></b> <b><i> </i></b>The perimeter zones are Steam Radiators.</span><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)"></span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><span style="font-size:12.8000001907349px"><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">25-34 same 3 perimeter heating zones.</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">For cooling 2 AHUs per floor, hence 2 zones.</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div></span><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">All cooling </span><b><i><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)"> </span></i></b><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)">up to 25<sup>th</sup> Floor is Primary</span><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)"> chilled water from one of the 3 sources:</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><span style="font-size:12.8000001907349px"><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">- 1300 ton chiller</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">-400 ton electric chiller on moderate mode</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div></span><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">-cooling tower and </span><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)">Plate Heat Exchanger</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><span style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">- sensible only cooling on small loads.</span><span style="font-size:9.5pt"><u></u><u></u></span></p></span><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)"></span><b><i><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)"> </span></i></b><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(152,72,7)">All cooling from 25<sup>th</sup> Floor is secondary chilled water via Plate Heat Exchanger supplied from one of the 3 sources above.</span><span style="font-size:9.5pt;color:rgb(152,72,7)"><u></u><u></u></span></p><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><span style="font-size:12.8000001907349px"><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">35- 56 Another heating zone. All perimeter heat is ONE zone. 1 AHU for the CORE zone per floor.</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">57-Roof ONE perimeter heating zone. 1 AHU for the Core zone per floor.</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:10pt;font-family:'Lucida Sans Typewriter';color:rgb(31,73,125)">Hence for HEATING:</span><span style="font-size:9.5pt"><u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">Riser 1: 6-34 NE<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">Riser 2: 6-34 NW<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">Riser3: 6-34 S<u></u><u></u></span></p></div></span><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">Riser 4: <span style="color:rgb(152,72,7)"> <b><i>[Bryan] </i></b>3</span>5-56 entire floor<u></u><u></u></span></p></div><span style="font-size:12.8000001907349px"><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">Riser 5: 57 - Roof Entire Floor.<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">Sum down of heating zones. PERIMETER RADIATION HEATING ZONES:<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">6-34 (3 zones)<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">35-56 (1zone)<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">57-roof (1 zone)<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">AHU FOR CORE ZONES:<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">7-18 (4 AHU)<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">19-24(3 AHU)<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">25-34 (2AHU, chilled water goes through heat exchanger and secondary chilled water.<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">35- above (1 AHU) per floor.<u></u><u></u></span></p></div><div><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div></span><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">Cooling is VAV chilled water preheat coil<span style="color:rgb(31,73,125)"> </span><span style="color:rgb(152,72,7)">and water side economizer with Plenum Return</span><u></u><u></u></span></p></div><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt"><u></u> <u></u></span></p></div><div style="font-size:12.8000001907349px"><p class="MsoNormal" style="margin:0in 0in 0.0001pt;font-size:12pt;font-family:'Times New Roman',serif"><span style="font-size:9.5pt">Below 7th floor floor they are return ducts and return fans. Hot water perimeter induction units.<span style="color:rgb(152,72,7)">Shell and Tube Heat Exchanger on 5<sup>th</sup> floor.<u></u><u></u></span></span></p><div><img src="https://ssl.gstatic.com/ui/v1/icons/mail/images/cleardot.gif" class=""></div></div></div></div></div>-- <br><div class="gmail_signature"><p style="margin:0in 0in 0pt"><b><font size="3"><font color="#006600" face="Calibri">- Pranita </font></font></b></p><br></div>
</div>