<div dir="ltr"><p class="MsoNormal" style="margin-bottom:0.0001pt;background-image:initial;background-repeat:initial"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">Dear Keith,<br><br>
Thank you so much for all the clarifications and recommendations. I will follow your
instruction and coordinate with the mechanical engineer who thinks it is possible
to achieve a considerable energy savings with the WLHP system.<br>  <br>I truly appreciate your help, </span></p>

<span style="font-size:10pt;line-height:115%;font-family:Arial,sans-serif;color:rgb(39,78,19)">Morteza</span><br><div class="gmail_extra"><br clear="all"><div><div class="gmail_signature"><div dir="ltr"><img src="https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no"><br><div><br></div></div></div></div>
<br><div class="gmail_quote">On Thu, May 7, 2015 at 4:02 PM,  <span dir="ltr"><<a href="mailto:equest-users-request@lists.onebuilding.org" target="_blank">equest-users-request@lists.onebuilding.org</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-color:rgb(204,204,204);border-left-style:solid;padding-left:1ex">Send Equest-users mailing list submissions to<br>
        <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
<br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:equest-users-request@lists.onebuilding.org">equest-users-request@lists.onebuilding.org</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:equest-users-owner@lists.onebuilding.org">equest-users-owner@lists.onebuilding.org</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of Equest-users digest..."<br>
<br>Today's Topics:<br>
<br>
   1. Re: Area of the building (Bishop, Bill)<br>
   2. Re: Area of the building (Singhal, Harshul)<br>
   3. Re: PTAC vs WLHP Annual Energy Consumption (Keith Swartz)<br>
   4. Re: eQuest LPD input output disagree (Nicholas Caton)<br>
   5. Re: eQuest LPD input output disagree (Sami, Vikram)<br>
   6. Re: eQuest LPD input output disagree (Nicholas Caton)<br>
   7. What is meant by Zone Min Design Air Flow (Faisal Sharif)<br>
<br><br>---------- Forwarded message ----------<br>From: "Bishop, Bill" <<a href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a>><br>To: "Singhal, Harshul" <<a href="mailto:HSinghal@thorntontomasetti.com">HSinghal@thorntontomasetti.com</a>>, "<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>" <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>Cc: <br>Date: Wed, 6 May 2015 20:06:30 +0000<br>Subject: Re: [Equest-users] Area of the building<br>





<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">Harshul,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">Go to the spreadsheet view for spaces, not zones, via the Building Shell or Internal Loads modules. I believe that is how the conditioned area is determined.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">~Bill<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(225,225,225);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b>From:</b> Singhal, Harshul [mailto:<a href="mailto:HSinghal@ThorntonTomasetti.com" target="_blank">HSinghal@ThorntonTomasetti.com</a>]
<br>
<b>Sent:</b> Wednesday, May 06, 2015 4:01 PM<br>
<b>To:</b> Bishop, Bill; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> RE: Area of the building<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Thanks for reply. Yeah I checked my LSC. Sorry about numbers. My total “conditoned” office area is 35,000 sq ft & “unconditioned” office area is 15,000 for future. For
<u>unconditioned office</u> we cant take credit. But if you see snapshot given below, I have assigned warehouses spaces as conditioned where I have given only heating schedule only (for makeup unit air system as I mentioned in my first email). All warehouses
 are named with “WH”.  Is there any other spot where I need to make necessary changes so that eQuest can report these areas too?<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Thanks!<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><img width="1482" height="222" src="cid:image001.jpg@01D08816.9C097D30"><span style="color:rgb(31,73,125)"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal" style="margin-bottom:12pt"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">Harshul Singhal, LEED AP BD+C</span></b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">
<br>
Project Consultant <br>
Thornton Tomasetti <br>
386 Fore Street, Suite 401 <br>
Portland, ME  04101 <br>
<b>T</b> <a href="tel:%2B1.207.245.6060" value="+12072456060" target="_blank">+1.207.245.6060</a>  <b>F</b> <a href="tel:%2B1.207.245.6061" value="+12072456061" target="_blank">+1.207.245.6061</a>   <br>
<b>D</b> <a href="tel:%2B1.207.245.6074" value="+12072456074" target="_blank">+1.207.245.6074</a>   <br>
<a href="mailto:HSinghal@ThorntonTomasetti.com" target="_blank">HSinghal@ThorntonTomasetti.com</a>
<br>
<a href="http://www.ThorntonTomasetti.com" target="_blank">www.ThorntonTomasetti.com</a> <u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(181,196,223);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Tahoma,sans-serif">From:</span></b><span style="font-size:10pt;font-family:Tahoma,sans-serif"> Bishop, Bill [<a href="mailto:bbishop@pathfinder-ea.com" target="_blank">mailto:bbishop@pathfinder-ea.com</a>]
<br>
<b>Sent:</b> Wednesday, May 06, 2015 3:41 PM<br>
<b>To:</b> Singhal, Harshul; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">
equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> RE: Area of the building<u></u><u></u></span></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">Harshul,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">I didn’t open your model but I suspect you are not modeling the entire warehouse as “conditioned”. The area used in the metrics on BEPS/BEPU are based on conditioned area. See the LS-C report for the conditioned
 area in the model. Based on your numbers below, your modeled conditioned area is only 35,000 ft<sup>2</sup> or so.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">~Bill<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:'Franklin Gothic Medium',sans-serif;color:black">William Bishop, PE, BEMP, BEAP, CEM, LEED AP
</span></b><b><span style="font-size:10pt;font-family:'Franklin Gothic Medium',sans-serif;color:rgb(0,102,0)">|</span></b><b><span style="font-size:10pt;font-family:'Franklin Gothic Medium',sans-serif;color:black"> Pathfinder Engineers & Architects LLP<u></u><u></u></span></b></p>
<table border="0" cellspacing="0" cellpadding="0" width="658" style="width:394.8pt;border-collapse:collapse">
<tbody>
<tr style="height:13.45pt">
<td width="431" style="width:258.45pt;padding:0in 5.4pt;height:13.45pt">
<p class="MsoNormal" style="line-height:105%"><b><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:black">Senior Energy Engineer<u></u><u></u></span></b></p>
</td>
<td width="227" rowspan="6" style="width:136.35pt;padding:0in 5.4pt;height:13.45pt">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:black"><img border="0" width="70" height="47" src="cid:image002.jpg@01D08816.9C097D30"> 
<img border="0" width="57" height="49" src="cid:image003.jpg@01D08816.9C097D30"><u></u><u></u></span></p>
</td>
</tr>
<tr style="height:4.55pt">
<td width="431" valign="top" style="width:258.45pt;padding:0in 5.4pt;height:4.55pt">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:5pt;line-height:105%;font-family:Arial,sans-serif;color:black"><u></u> <u></u></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td width="431" nowrap valign="bottom" style="width:258.45pt;padding:0in 5.4pt;height:9.8pt">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:rgb(31,73,125)">134 South Fitzhugh Street</span><span style="font-size:9pt;line-height:105%;color:rgb(31,73,125)">                
</span><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:rgb(31,73,125)">Rochester, NY 14608<u></u><u></u></span></p>
</td>
</tr>
<tr style="height:12.4pt">
<td width="431" valign="top" style="width:258.45pt;padding:0in 5.4pt;height:12.4pt">
<p class="MsoNormal" style="line-height:105%"><b><i><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:rgb(0,32,96)">T: <a href="tel:%28585%29%20698-1956" value="+15856981956" target="_blank">(585) 698-1956</a></span><span style="color:rgb(0,32,96)">             
</span></i></b><span style="color:rgb(31,73,125)">          </span><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:rgb(31,73,125)">F: <a href="tel:%28585%29%20325-6005" value="+15853256005" target="_blank">(585) 325-6005</a></span><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:black"><u></u><u></u></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td width="431" valign="top" style="width:258.45pt;padding:0in 5.4pt;height:9.8pt">
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><a href="mailto:wbishop@pathfinder-ea.com" target="_blank"><span style="font-size:9pt;font-family:Arial,sans-serif">bbishop@pathfinder-ea.com</span></a></span><span style="font-size:9pt;font-family:Arial,sans-serif;color:black">            
</span><span style="color:rgb(31,73,125)"><a href="http://www.pathfinder-ea.com/" target="_blank"><span style="font-size:9pt;font-family:Arial,sans-serif">www.pathfinder-ea.com</span></a><u></u><u></u></span></p>
</td>
</tr>
<tr style="height:24.6pt">
<td width="431" valign="top" style="width:258.45pt;padding:0in 5.4pt;height:24.6pt">
<p class="MsoNormal" style="margin-top:3pt;line-height:105%"><span style="color:rgb(31,73,125)"><img border="0" width="42" height="40" src="cid:image004.png@01D08816.9C097D30" alt="http://png-5.findicons.com/files/icons/977/rrze/720/globe.png"></span><span style="font-size:7.5pt;line-height:105%;color:rgb(0,176,240)">Carbon
 Fee and Dividend - simple, effective, and market-based.</span><span style="color:rgb(31,73,125)"><u></u><u></u></span></p>
</td>
</tr>
</tbody>
</table>
</div>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(225,225,225);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Singhal, Harshul<br>
<b>Sent:</b> Wednesday, May 06, 2015 3:29 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Area of the building<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Hi everyone, <u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">I am working on this warehouse (distribution center) building with 50,000 sf of office space (VAV system) & 1.5 million sq ft of warehouse (makeup unit of only 13,500 CFM with heating only). When I do calculation on excel sheet for EUI
 (total area 1.5 million + 50,000), it’s around 15 (for design case) but when I look into BEPS report, it shows 395 EUI which doesn’t even make sense. It seems like it’s not reporting the area for distribution center and doing EUI calculation just for office
 space area. Can you please let me know how to make equest report the whole area of the facility? Please find the attachment of eQuest files.
<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Thanks!<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal" style="margin-bottom:12pt"><img border="0" width="997" height="251" src="cid:image005.jpg@01D08816.9C097D30"><span style="font-size:10pt;font-family:Arial,sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Arial,sans-serif">Harshul Singhal, LEED AP BD+C</span></b><span style="font-size:10pt;font-family:Arial,sans-serif">
<br>
Project Consultant <br>
Thornton Tomasetti <br>
386 Fore Street, Suite 401 <br>
Portland, ME  04101 <br>
<b>T</b> <a href="tel:%2B1.207.245.6060" value="+12072456060" target="_blank">+1.207.245.6060</a>  <b>F</b> <a href="tel:%2B1.207.245.6061" value="+12072456061" target="_blank">+1.207.245.6061</a>   <br>
<b>D</b> <a href="tel:%2B1.207.245.6074" value="+12072456074" target="_blank">+1.207.245.6074</a>   <br>
<a href="mailto:HSinghal@ThorntonTomasetti.com" target="_blank">HSinghal@ThorntonTomasetti.com</a>
<br>
<a href="http://www.ThorntonTomasetti.com" target="_blank">www.ThorntonTomasetti.com</a> <u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="font-size:12pt;font-family:'Times New Roman',serif"><u></u> <u></u></span></p>
<pre><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><u></u> <u></u></pre>
<pre><u></u> <u></u></pre>
<pre>The information in this email and any attachments may contain<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>confidential information that is intended solely for the<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>attention and use of the named addressee(s). This message or<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>any part thereof must not be disclosed, copied, distributed<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>or retained by any person without authorization from the<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>addressee. If you are not the intended addressee, please<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>notify the sender immediately, and delete this message.<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><u></u> <u></u></pre>
<pre><u></u> <u></u></pre>
<p class="MsoNormal"><span style="font-size:12pt;font-family:'Times New Roman',serif"><u></u> <u></u></span></p>
</div>
</div>

<br><br>---------- Forwarded message ----------<br>From: "Singhal, Harshul" <<a href="mailto:HSinghal@thorntontomasetti.com">HSinghal@thorntontomasetti.com</a>><br>To: "Bishop, Bill" <<a href="mailto:bbishop@pathfinder-ea.com">bbishop@pathfinder-ea.com</a>>, "<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>" <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>Cc: <br>Date: Wed, 6 May 2015 20:11:50 +0000<br>Subject: Re: [Equest-users] Area of the building<br>





<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">Thanks Bill. It worked out. </span>
<span style="font-family:Wingdings;color:rgb(31,73,125)">J</span><span style="color:rgb(31,73,125)"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">Harshul Singhal, LEED AP BD+C</span></b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">
<br>
Project Consultant <br>
Thornton Tomasetti <br>
386 Fore Street, Suite 401 <br>
Portland, ME  04101 <br>
<b>T</b> <a href="tel:%2B1.207.245.6060" value="+12072456060" target="_blank">+1.207.245.6060</a>  <b>F</b> <a href="tel:%2B1.207.245.6061" value="+12072456061" target="_blank">+1.207.245.6061</a>   <br>
<b>D</b> <a href="tel:%2B1.207.245.6074" value="+12072456074" target="_blank">+1.207.245.6074</a>   <br>
HSinghal@ThorntonTomasetti.com <br>
<a href="http://www.ThorntonTomasetti.com" target="_blank">www.ThorntonTomasetti.com</a> </span><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(181,196,223);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Tahoma,sans-serif">From:</span></b><span style="font-size:10pt;font-family:Tahoma,sans-serif"> Bishop, Bill [mailto:<a href="mailto:bbishop@pathfinder-ea.com" target="_blank">bbishop@pathfinder-ea.com</a>]
<br>
<b>Sent:</b> Wednesday, May 06, 2015 4:06 PM<br>
<b>To:</b> Singhal, Harshul; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> RE: Area of the building<u></u><u></u></span></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">Harshul,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">Go to the spreadsheet view for spaces, not zones, via the Building Shell or Internal Loads modules. I believe that is how the conditioned area is determined.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">~Bill<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(225,225,225);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b>From:</b> Singhal, Harshul [<a href="mailto:HSinghal@ThorntonTomasetti.com" target="_blank">mailto:HSinghal@ThorntonTomasetti.com</a>]
<br>
<b>Sent:</b> Wednesday, May 06, 2015 4:01 PM<br>
<b>To:</b> Bishop, Bill; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> RE: Area of the building<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Thanks for reply. Yeah I checked my LSC. Sorry about numbers. My total “conditoned” office area is 35,000 sq ft & “unconditioned” office area is 15,000 for future. For
<u>unconditioned office</u> we cant take credit. But if you see snapshot given below, I have assigned warehouses spaces as conditioned where I have given only heating schedule only (for makeup unit air system as I mentioned in my first email). All warehouses
 are named with “WH”.  Is there any other spot where I need to make necessary changes so that eQuest can report these areas too?<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Thanks!<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><img border="0" width="1482" height="222" src="cid:image001.jpg@01D08817.5B511450"><span style="color:rgb(31,73,125)"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal" style="margin-bottom:12pt"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">Harshul Singhal, LEED AP BD+C</span></b><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)">
<br>
Project Consultant <br>
Thornton Tomasetti <br>
386 Fore Street, Suite 401 <br>
Portland, ME  04101 <br>
<b>T</b> <a href="tel:%2B1.207.245.6060" value="+12072456060" target="_blank">+1.207.245.6060</a>  <b>F</b> <a href="tel:%2B1.207.245.6061" value="+12072456061" target="_blank">+1.207.245.6061</a>   <br>
<b>D</b> <a href="tel:%2B1.207.245.6074" value="+12072456074" target="_blank">+1.207.245.6074</a>   <br>
<a href="mailto:HSinghal@ThorntonTomasetti.com" target="_blank">HSinghal@ThorntonTomasetti.com</a>
<br>
<a href="http://www.ThorntonTomasetti.com" target="_blank">www.ThorntonTomasetti.com</a> <u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(181,196,223);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Tahoma,sans-serif">From:</span></b><span style="font-size:10pt;font-family:Tahoma,sans-serif"> Bishop, Bill [<a href="mailto:bbishop@pathfinder-ea.com" target="_blank">mailto:bbishop@pathfinder-ea.com</a>]
<br>
<b>Sent:</b> Wednesday, May 06, 2015 3:41 PM<br>
<b>To:</b> Singhal, Harshul; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">
equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> RE: Area of the building<u></u><u></u></span></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">Harshul,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">I didn’t open your model but I suspect you are not modeling the entire warehouse as “conditioned”. The area used in the metrics on BEPS/BEPU are based on conditioned area. See the LS-C report for the conditioned
 area in the model. Based on your numbers below, your modeled conditioned area is only 35,000 ft<sup>2</sup> or so.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)">~Bill<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:'Franklin Gothic Medium',sans-serif;color:black">William Bishop, PE, BEMP, BEAP, CEM, LEED AP
</span></b><b><span style="font-size:10pt;font-family:'Franklin Gothic Medium',sans-serif;color:rgb(0,102,0)">|</span></b><b><span style="font-size:10pt;font-family:'Franklin Gothic Medium',sans-serif;color:black"> Pathfinder Engineers & Architects LLP<u></u><u></u></span></b></p>
<table border="0" cellspacing="0" cellpadding="0" width="526" style="width:394.8pt;border-collapse:collapse">
<tbody>
<tr style="height:13.45pt">
<td width="345" style="width:258.45pt;padding:0in 5.4pt;height:13.45pt">
<p class="MsoNormal" style="line-height:105%"><b><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:black">Senior Energy Engineer<u></u><u></u></span></b></p>
</td>
<td width="182" rowspan="6" style="width:136.35pt;padding:0in 5.4pt;height:13.45pt">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:black"><img border="0" width="70" height="47" src="cid:image002.jpg@01D08817.5B511450"> 
<img border="0" width="57" height="49" src="cid:image003.jpg@01D08817.5B511450"><u></u><u></u></span></p>
</td>
</tr>
<tr style="height:4.55pt">
<td width="345" valign="top" style="width:258.45pt;padding:0in 5.4pt;height:4.55pt">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:5pt;line-height:105%;font-family:Arial,sans-serif;color:black"><u></u> <u></u></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td width="345" nowrap valign="bottom" style="width:258.45pt;padding:0in 5.4pt;height:9.8pt">
<p class="MsoNormal" style="line-height:105%"><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:rgb(31,73,125)">134 South Fitzhugh Street</span><span style="font-size:9pt;line-height:105%;color:rgb(31,73,125)">                
</span><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:rgb(31,73,125)">Rochester, NY 14608<u></u><u></u></span></p>
</td>
</tr>
<tr style="height:12.4pt">
<td width="345" valign="top" style="width:258.45pt;padding:0in 5.4pt;height:12.4pt">
<p class="MsoNormal" style="line-height:105%"><b><i><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:rgb(0,32,96)">T: <a href="tel:%28585%29%20698-1956" value="+15856981956" target="_blank">(585) 698-1956</a></span><span style="color:rgb(0,32,96)">             
</span></i></b><span style="color:rgb(31,73,125)">          </span><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:rgb(31,73,125)">F: <a href="tel:%28585%29%20325-6005" value="+15853256005" target="_blank">(585) 325-6005</a></span><span style="font-size:9pt;line-height:105%;font-family:Arial,sans-serif;color:black"><u></u><u></u></span></p>
</td>
</tr>
<tr style="height:9.8pt">
<td width="345" valign="top" style="width:258.45pt;padding:0in 5.4pt;height:9.8pt">
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><a href="mailto:wbishop@pathfinder-ea.com" target="_blank"><span style="font-size:9pt;font-family:Arial,sans-serif">bbishop@pathfinder-ea.com</span></a></span><span style="font-size:9pt;font-family:Arial,sans-serif;color:black">            
</span><span style="color:rgb(31,73,125)"><a href="http://www.pathfinder-ea.com/" target="_blank"><span style="font-size:9pt;font-family:Arial,sans-serif">www.pathfinder-ea.com</span></a><u></u><u></u></span></p>
</td>
</tr>
<tr style="height:24.6pt">
<td width="345" valign="top" style="width:258.45pt;padding:0in 5.4pt;height:24.6pt">
<p class="MsoNormal" style="margin-top:3pt;line-height:105%"><span style="color:rgb(31,73,125)"><img border="0" width="42" height="40" src="cid:image004.png@01D08817.5B511450" alt="http://png-5.findicons.com/files/icons/977/rrze/720/globe.png"></span><span style="font-size:7.5pt;line-height:105%;color:rgb(0,176,240)">Carbon
 Fee and Dividend - simple, effective, and market-based.</span><span style="color:rgb(31,73,125)"><u></u><u></u></span></p>
</td>
</tr>
</tbody>
</table>
</div>
<p class="MsoNormal"><span style="color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(225,225,225);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b>From:</b> Equest-users [<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Singhal, Harshul<br>
<b>Sent:</b> Wednesday, May 06, 2015 3:29 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Area of the building<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Hi everyone, <u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">I am working on this warehouse (distribution center) building with 50,000 sf of office space (VAV system) & 1.5 million sq ft of warehouse (makeup unit of only 13,500 CFM with heating only). When I do calculation on excel sheet for EUI
 (total area 1.5 million + 50,000), it’s around 15 (for design case) but when I look into BEPS report, it shows 395 EUI which doesn’t even make sense. It seems like it’s not reporting the area for distribution center and doing EUI calculation just for office
 space area. Can you please let me know how to make equest report the whole area of the facility? Please find the attachment of eQuest files.
<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Thanks!<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal" style="margin-bottom:12pt"><img border="0" width="997" height="251" src="cid:image005.jpg@01D08817.5B511450"><span style="font-size:10pt;font-family:Arial,sans-serif"><u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Arial,sans-serif">Harshul Singhal, LEED AP BD+C</span></b><span style="font-size:10pt;font-family:Arial,sans-serif">
<br>
Project Consultant <br>
Thornton Tomasetti <br>
386 Fore Street, Suite 401 <br>
Portland, ME  04101 <br>
<b>T</b> <a href="tel:%2B1.207.245.6060" value="+12072456060" target="_blank">+1.207.245.6060</a>  <b>F</b> <a href="tel:%2B1.207.245.6061" value="+12072456061" target="_blank">+1.207.245.6061</a>   <br>
<b>D</b> <a href="tel:%2B1.207.245.6074" value="+12072456074" target="_blank">+1.207.245.6074</a>   <br>
<a href="mailto:HSinghal@ThorntonTomasetti.com" target="_blank">HSinghal@ThorntonTomasetti.com</a>
<br>
<a href="http://www.ThorntonTomasetti.com" target="_blank">www.ThorntonTomasetti.com</a> <u></u><u></u></span></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="font-size:12pt;font-family:'Times New Roman',serif"><u></u> <u></u></span></p>
<pre><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><u></u> <u></u></pre>
<pre><u></u> <u></u></pre>
<pre>The information in this email and any attachments may contain<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>confidential information that is intended solely for the<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>attention and use of the named addressee(s). This message or<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>any part thereof must not be disclosed, copied, distributed<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>or retained by any person without authorization from the<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>addressee. If you are not the intended addressee, please<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre>notify the sender immediately, and delete this message.<u></u><u></u></pre>
<pre><u></u> <u></u></pre>
<pre><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><u></u> <u></u></pre>
<pre><u></u> <u></u></pre>
<p class="MsoNormal"><span style="font-size:12pt;font-family:'Times New Roman',serif"><u></u> <u></u></span></p>
</div>

<br><pre><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>

The information in this email and any attachments may contain

confidential information that is intended solely for the

attention and use of the named addressee(s). This message or

any part thereof must not be disclosed, copied, distributed

or retained by any person without authorization from the

addressee. If you are not the intended addressee, please

notify the sender immediately, and delete this message.

<><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>

</pre><br></div>

<br><br>---------- Forwarded message ----------<br>From: Keith Swartz <<a href="mailto:KSwartz@seventhwave.org">KSwartz@seventhwave.org</a>><br>To: "<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>" <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>Cc: <br>Date: Wed, 6 May 2015 20:18:09 +0000<br>Subject: Re: [Equest-users] PTAC vs WLHP Annual Energy Consumption<br>





<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Arial,sans-serif">Morteza,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Arial,sans-serif"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Arial,sans-serif">If you are looking for a relatively simple upgrade from PTACs (with electric resistance heat), consider packaged terminal heat pumps.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Arial,sans-serif"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Arial,sans-serif;color:black">Keith Swartz, PE<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Arial,sans-serif;color:black">Senior Energy Engineer |
<b>Seventhwave </b></span><span style="font-size:10pt;font-family:Arial,sans-serif;color:gray">|
<b>Madison.Chicago.Minneapolis<u></u><u></u></b></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Arial,sans-serif;color:black">(formerly Energy Center of Wisconsin)<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Arial,sans-serif;color:black"><a href="tel:608.210.7123" value="+16082107123" target="_blank">608.210.7123</a> |
<a href="http://www.seventhwave.org/" target="_blank">www.seventhwave.org</a><u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Arial,sans-serif"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(225,225,225);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> David Eldridge [mailto:<a href="mailto:DEldridge@grummanbutkus.com" target="_blank">DEldridge@grummanbutkus.com</a>]
<br>
<b>Sent:</b> Wednesday, May 06, 2015 11:45 AM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] PTAC vs WLHP Annual Energy Consumption<u></u><u></u></span></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Some of the advantages of a WLHP system are related to maintenance and service life compared to systems with air-cooled condensers and requiring envelope penetrations.
 These concerns won’t show up in an ASHRAE 90.1 appendix G energy analysis. (Higher infiltration from PTACs?) Also I’d expect some efficiencies of scale from central equipment if your building is large, compared to the PTACs, this may not apply here.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">But regarding your EAP2 questions…WLHP offers an energy savings when parts of the building are in heating while others are in cooling – depending on your building’s
 form and location, as well as modeling assumptions about setpoints, this may not be taking place. For a residential building it might be reasonable to assume that some portion of the residential units are set to different temperature ranges.
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Conversely, if your location is cooling dominated all year, some of the advantages of WLHP go away. One thing to check here is the end-use demand components in
 your model. Is the WLHP using less at full load than the air-cooled system? If so, then you need to investigate the modeling assumptions about the controls of the WLHP system when operating at part load. Make sure that what you gained in peak efficinecy isn’t
 given back when the system is only partially loaded.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Verify that the WLHP control for the condenser loop is variable flow (if the proposed heat pump units have two-way control valves…if not, talk to your engineer
 about that!) and that there is a an adequate temperature range for the loop so that the towers and boilers don’t come on immediately. WLHP condenser loop which should be in the range where a condensing boiler will operate successfully, verify that the proposed
 case takes advantage of this compared to the baseline. Make sure that the condenser loop is operating on call for demand so that the model isn’t assuming continuous operation.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Regarding the DOAS, make sure that the baseline system has the same OA requirements at the PTAC units. Lastly, verify that the fan power for the WLHP units is
 entered based on the design pressure drop and not eQUEST defaults. Double-check that the fan run-times for the equipment are the same…which for LEED would be fans operating continuously. You probably have this in place already.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">I see an interesting paper forwarded by Maria came through while I was typing. Note that the graphics in Figure 1 and Figure 2 are for CO2 emissions, and have
 non-zero axes, so there could be some variance for your specific case depending on the relative cost of utilities.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">It is very interesting – if we take a proposed high-efficiency WLHP system from Figure 2 in Atlanta producing about 625 MTCDE compared to the Figure 1 ASHRAE
 90.1 baseline air-source heat pump it is just under 650 MTCDE. In your case, by adding the DOAS and some other efficiencies and depending on your specific utility rates, it should be possible for a high-tech WLHP system to at least reach equivalency with PTACs
 if not surpass it. Additional savings should result if you are able to add efficiency from upgraded envelope, lighting, and DHW measures in the proposed design. Check the LS reports to verify that building heating and cooling loads are reduced in the proposed
 case compared to the baseline.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">David<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><u><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black">                                                                                               
</span></u><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:8pt;font-family:Calibri,sans-serif;color:black"> </span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP<u></u><u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(36,64,97)">Grumman/Butkus Associates</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></p>
<p class="MsoNormal"><u><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black">                                                                                               
</span></u><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:black"> </span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(225,225,225);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> Equest-users [<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">mailto:equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Tim Johnson<br>
<b>Sent:</b> Wednesday, May 06, 2015 10:26 AM<br>
<b>To:</b> 'Morteza Kasmai'; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">
equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] PTAC vs WLHP Annual Energy Consumption<u></u><u></u></span></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif">Morteza,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif">I took a quick look at your models and the one thing that sticks out to me is your pump energy.  The difference between PTAC and WSHP is huge.  I would expect some difference
 since the WSHP needs to run the pumps in cooling mode as well as heating while the PTAC only needs pumps in heating, but the difference in energy seems too big.  Also keep in mind that the heating and cooling efficiencies of the WSHPs are only for that piece
 of equipment, they don’t include the heat rejection required in cooling mode, the boiler input in heating mode, or the pumps.  For those reasons, I wouldn’t expect the WSHP system to be a lot more efficient than the PTAC.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif">Tim<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u> <u></u></span></p>
<div>
<table cellspacing="0" cellpadding="0" hspace="0" vspace="0" align="left">
<tbody>
<tr>
<td valign="top" align="left" style="padding:0in 2.25pt">
<p class="MsoNormal">
<b><span style="font-size:10pt;font-family:Arial,sans-serif;color:maroon">Tim Johnson</span></b><span style="font-size:10pt;font-family:'Courier New'"><u></u><u></u></span></p>
<p class="MsoNormal">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:gray">Mechanical Engineer</span><span style="font-size:10pt;font-family:'Courier New'"><u></u><u></u></span></p>
<p class="MsoNormal">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:gray">o <a href="tel:208.336.4900" value="+12083364900" target="_blank">208.336.4900</a> | d <a href="tel:208.577.5645" value="+12085775645" target="_blank">208.577.5645</a></span><span style="font-size:10pt;font-family:'Courier New'"><u></u><u></u></span></p>
<p class="MsoNormal">
<span style="font-size:11pt;font-family:Calibri,sans-serif"><img border="0" width="225" height="72" src="cid:image001.png@01D0880F.D9DAB360" alt="CTA_email_graphic"><u></u><u></u></span></p>
<p class="MsoNormal">
<span style="font-size:10pt;font-family:'Courier New'"><u></u> <u></u></span></p>
</td>
</tr>
</tbody>
</table>
</div>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif"><u></u> <u></u></span></p>
<div style="border-style:solid none none;border-top-color:rgb(181,196,223);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Tahoma,sans-serif">From:</span></b><span style="font-size:10pt;font-family:Tahoma,sans-serif"> Equest-users [</span><a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank"><span style="font-size:10pt;font-family:Tahoma,sans-serif">mailto:equest-users-bounces@lists.onebuilding.org</span></a><span style="font-size:10pt;font-family:Tahoma,sans-serif">]
<b>On Behalf Of </b>Morteza Kasmai<br>
<b>Sent:</b> Wednesday, May 06, 2015 7:54 AM<br>
<b>To:</b> </span><a href="mailto:equest-users@lists.onebuilding.org" target="_blank"><span style="font-size:10pt;font-family:Tahoma,sans-serif">equest-users@lists.onebuilding.org</span></a><span style="font-size:10pt;font-family:Tahoma,sans-serif"><br>
<b>Subject:</b> [Equest-users] PTAC vs WLHP Annual Energy Consumption<u></u><u></u></span></p>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal" style="margin-bottom:12pt"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">Dear eQUEST experts,</span><u></u><u></u></p>
<p class="MsoNormal" style="margin-bottom:12pt;background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">I am still struggling to find out the main reason(s) for high-energy consumption of WLHP system comparing to PTAC system and what can be done to make this system more efficient that
 the baseline system. In other words for complying with EAp2 requirements, for a mid rise residential building what types of HVAC systems (other than split system HP) can be selected which consume less annual energy than the PTAC.
</span><br>
<br>
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">I would appreciate it if you would share your experience on this and make some recommendation.</span><br>
<br>
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">Morteza</span><u></u><u></u></p>
<div>
<p class="MsoNormal"><br clear="all">
<u></u><u></u></p>
<div>
<div>
<div>
<p class="MsoNormal"><img border="0" width="147" height="43" src="https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no" alt="https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no"><u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">On Mon, May 4, 2015 at 4:03 PM, <<a href="mailto:equest-users-request@lists.onebuilding.org" target="_blank">equest-users-request@lists.onebuilding.org</a>> wrote:<u></u><u></u></p>
<p class="MsoNormal">Send Equest-users mailing list submissions to<br>
        <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
        <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
<br>
or, via email, send a message with subject or body 'help' to<br>
        <a href="mailto:equest-users-request@lists.onebuilding.org" target="_blank">equest-users-request@lists.onebuilding.org</a><br>
<br>
You can reach the person managing the list at<br>
        <a href="mailto:equest-users-owner@lists.onebuilding.org" target="_blank">equest-users-owner@lists.onebuilding.org</a><br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than "Re: Contents of Equest-users digest..."<br>
<br>
Today's Topics:<br>
<br>
   1. PTAC vs WLHP Annual Energy Consumption (Morteza Kasmai)<br>
   2. Re: PTAC vs WLHP Annual Energy Consumption (David Reddy)<br>
<br>
<br>
---------- Forwarded message ----------<br>
From: Morteza Kasmai <<a href="mailto:morteza.kasmai@gmail.com" target="_blank">morteza.kasmai@gmail.com</a>><br>
To: "<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>" <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>><br>
Cc: <br>
Date: Mon, 4 May 2015 12:04:23 -0400<br>
Subject: [Equest-users] PTAC vs WLHP Annual Energy Consumption<u></u><u></u></p>
<div>
<div>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">Dear all,</span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)"><br>
This is a multifamily mid-rise building, 9 floors above grade. Per ASHRAE Table G3.1.1A the Baseline HVAC system is system 1 (PTAC with hot-water fossil fuel boiler) 9.3 to 11 EER.
<br>
Selected HVAC system for the proposed design is WLHP (3 Ton High efficiency HP by Daikin, 15.9 EER and 4.83 COP) with 2 cell cooling tower, DOAS unit (9.8 EER) and 2 Boilers (0.92 Eff.).</span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)"> </span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">Although the efficiency of the selected HVAC systems is much higher than the efficiency of the baseline model, the simulation results indicate annual energy consumption of the proposed
 design is much higher than the baseline! </span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)"> </span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">Am I missing something or did something wrong in the models? Please see the attached files of the both models</span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">.</span><u></u><u></u></p>
<p class="MsoNormal" style="margin-bottom:12pt"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">I would greatly appreciate it if anyone kindly gives some feedback on this,<br>
<br>
 Morteza</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal"><br clear="all">
<u></u><u></u></p>
<div>
<div>
<div>
<p class="MsoNormal"><img border="0" width="32" height="32" src="https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no" alt="https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no"><u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
<p class="MsoNormal"><br>
<br>
---------- Forwarded message ----------<br>
From: David Reddy <<a href="mailto:david@360-analytics.com" target="_blank">david@360-analytics.com</a>><br>
To: <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
Cc: <br>
Date: Mon, 04 May 2015 09:39:44 -0700<br>
Subject: Re: [Equest-users] PTAC vs WLHP Annual Energy Consumption<u></u><u></u></p>
<div>
<p class="MsoNormal" style="margin-bottom:12pt">Hi Morteza,<br>
I have not reviewed the results or detailed inputs of your model, but one thing to be aware is that depending on the rating conditions of your efficiency data, you may have to adjust the EIRs to be consistent with DOE-2 performance curves.  The default DOE-2
 curves are normalized to the GSHP rating condition, so if using these and if your efficiency data is @ the WSHP rating condition, you will need to apply these adjustments.<br>
<br>
Here is the table from the DOE-2 help provided with eQUEST.  There is a library of DOE-2 WSHP curves available from ClimateMaster that do not need these adjustments.<br>
<br>
<img border="0" width="733" height="162" src="cid:image002.jpg@01D0880F.D9DAB360" alt="cid:image002.jpg@01D087E7.BEE13610"><br>
<br>
- David<u></u><u></u></p>
<div>
<p class="MsoNormal">On 5/4/2015 9:04 AM, Morteza Kasmai wrote:<u></u><u></u></p>
</div>
<blockquote style="margin-top:5pt;margin-bottom:5pt">
<div>
<div>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">Dear all,</span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)"><br>
This is a multifamily mid-rise building, 9 floors above grade. Per ASHRAE Table G3.1.1A the Baseline HVAC system is system 1 (PTAC with hot-water fossil fuel boiler) 9.3 to 11 EER.
<br>
Selected HVAC system for the proposed design is WLHP (3 Ton High efficiency HP by Daikin, 15.9 EER and 4.83 COP) with 2 cell cooling tower, DOAS unit (9.8 EER) and 2 Boilers (0.92 Eff.).</span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)"> </span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">Although the efficiency of the selected HVAC systems is much higher than the efficiency of the baseline model, the simulation results indicate annual energy consumption of the proposed
 design is much higher than the baseline! </span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)"> </span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">Am I missing something or did something wrong in the models? Please see the attached files of the both models</span><u></u><u></u></p>
<p class="MsoNormal" style="background-image:initial;background-repeat:initial">
<span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">.</span><u></u><u></u></p>
<p class="MsoNormal" style="margin-bottom:12pt"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(39,78,19)">I would greatly appreciate it if anyone kindly gives some feedback on this,<br>
<br>
 Morteza</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal"><br clear="all">
<u></u><u></u></p>
<div>
<div>
<div>
<p class="MsoNormal"><img border="0" width="32" height="32" src="https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no" alt="https://lh6.googleusercontent.com/Uuukta80GuFfvKouzA0mdSvUXqml7MtSwSiw-evuGMU=w147-h43-p-no"><u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
<p class="MsoNormal" style="margin-bottom:12pt"><u></u> <u></u></p>
<pre>_______________________________________________<u></u><u></u></pre>
<pre>Equest-users mailing list<u></u><u></u></pre>
<pre><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><u></u><u></u></pre>
<pre>To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><u></u><u></u></pre>
</blockquote>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal" style="margin-bottom:12pt"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="mailto:Equest-users@lists.onebuilding.org" target="_blank">Equest-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><u></u><u></u></p>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>

<br><br>---------- Forwarded message ----------<br>From: Nicholas Caton <<a href="mailto:ncaton@catonenergy.com">ncaton@catonenergy.com</a>><br>To: Dale elegant <<a href="mailto:elegantdale@gmail.com">elegantdale@gmail.com</a>>, <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>Cc: <br>Date: Wed, 6 May 2015 13:50:44 -0700<br>Subject: Re: [Equest-users] eQuest LPD input output disagree<br><div lang="EN-US" link="#0563C1" vlink="#954F72"><div><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">The EUI figures reported on BEPU use the building area entered in the following location (if entered).  You might check here first to see if it reads 700,000 or something else:</span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><img width="462" height="256" src="cid:image001.png@01D08803.A5F3C480"></span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><b><span style="font-size:14pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">NICK CATON, P.E.</span></b><span style="font-size:11pt;font-family:Verdana,sans-serif;color:rgb(31,73,125)"><br></span><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)">Owner</span></b></p><p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"> </span></b></p><p class="MsoNormal"><b><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)">Caton Energy Consulting</span></b><span style="font-size:10pt;font-family:Calibri,sans-serif;color:black"><br></span><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">  1150 N. 192<sup>nd</sup> St., #4-202</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">  Shoreline, WA 98133<br>  office:  <a href="tel:785.410.3317" value="+17854103317" target="_blank">785.410.3317</a></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"><a href="http://www.catonenergy.com" target="_blank"><span style="color:rgb(86,23,130)">www.catonenergy.com</span></a></span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"></span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> Equest-users [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Dale elegant<br><b>Sent:</b> Wednesday, May 06, 2015 10:49 AM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] eQuest LPD input output disagree</span></p><p class="MsoNormal"> </p><div><div><p class="MsoNormal">Dear all:</p></div><div><p class="MsoNormal"> </p></div><div><p class="MsoNormal">I'm modeling a 700000 sqft warehouse, everything works fine, except in BEPU report it shows a <span lang="EN">360.310 KWH /SQFT-YR GROSS-AREA, which doesn't make any sense. The utility rates are correct, under Quality control reports, it indicates errors of the peak lighting load of 67.74 w/sqft and peak miscellaneous equipment load of 40.91 w/sqft. I did input LPD and EPD with around 0.6 w/sqft and 0.5 w/sqft, the corresponding schedules are correct, the building area in each floor and each zone are correct, the total energy demand looks about right for the size of building.</span></p><p><span lang="EN">But at some point the model makes the LPD output 100 times bigger than what I input, <span style="color:rgb(39,78,19)">I would appreciate it if you could provide me with any advices, thanks!</span></span></p><p><span lang="EN" style="color:rgb(39,78,19)">Qing</span><span lang="EN"></span></p><p><span lang="EN"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p></div></div></div></div>
<br><br>---------- Forwarded message ----------<br>From: "Sami, Vikram" <<a href="mailto:vikram.sami@zgf.com">vikram.sami@zgf.com</a>><br>To: Nicholas Caton <<a href="mailto:ncaton@catonenergy.com">ncaton@catonenergy.com</a>>, Dale elegant <<a href="mailto:elegantdale@gmail.com">elegantdale@gmail.com</a>>, "<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>" <<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>Cc: <br>Date: Thu, 7 May 2015 16:39:08 +0000<br>Subject: Re: [Equest-users] eQuest LPD input output disagree<br>





<div lang="EN-US" link="#0563C1" vlink="#954F72">
<div>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Dale,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Curious. Could you attach your inp file?
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<table border="0" cellpadding="0">
<tbody>
<tr>
<td valign="top" style="padding:0.75pt">
<p class="MsoNormal" style="line-height:12pt"><b><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(227,59,69)">Vikram Sami</span></b><span style="color:rgb(31,73,125)"><br>
</span><span style="font-size:7pt;font-family:'Futura LT Book';color:rgb(102,102,102)">AIA, BEMP, LEED BD+C</span><span style="font-size:9pt;font-family:'Futura LT Book';color:black"> </span><span style="color:rgb(31,73,125)"><br>
</span><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)">Associate Partner</span><span style="color:rgb(31,73,125)"><u></u><u></u></span></p>
</td>
<td width="16" style="width:12pt;padding:0.75pt">
<p class="MsoNormal" style="line-height:12pt"><span style="color:rgb(31,73,125)"> <u></u><u></u></span></p>
</td>
<td valign="top" style="padding:0.75pt">
<p class="MsoNormal" style="line-height:12pt"><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)">ZGF ARCHITECTS LLP</span><span style="color:rgb(31,73,125)"><br>
</span><b><span style="font-size:7.5pt;font-family:'Futura LT Book';color:rgb(227,59,69)">T
</span></b><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)"><a href="tel:206.521.3509" value="+12065213509" target="_blank">206.521.3509</a>
</span><b><span style="font-size:7.5pt;font-family:'Futura LT Book';color:rgb(227,59,69)">E
</span></b><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)"><a href="mailto:vikram.sami@zgf.com" target="_blank">vikram.sami@zgf.com</a></span><span style="color:rgb(31,73,125)"><br>
</span><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)">925 Fourth Avenue, Suite 2400
<br>
Seattle, WA 98104</span><span style="color:rgb(31,73,125)"><u></u><u></u></span></p>
</td>
</tr>
</tbody>
</table>
</div>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><u></u> <u></u></span></p>
<div>
<div style="border-style:solid none none;border-top-color:rgb(225,225,225);border-top-width:1pt;padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> Equest-users [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Nicholas Caton<br>
<b>Sent:</b> Wednesday, May 06, 2015 1:51 PM<br>
<b>To:</b> Dale elegant; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] eQuest LPD input output disagree<u></u><u></u></span></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">The EUI figures reported on BEPU use the building area entered in the following location (if entered).  You might check here first to see if it reads 700,000
 or something else:</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><img width="462" height="256" src="cid:image001.png@01D088A9.A9F3C480"></span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span><u></u><u></u></p>
<p class="MsoNormal"><b><span style="font-size:14pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">NICK CATON, P.E.</span></b><span style="font-size:11pt;font-family:Verdana,sans-serif;color:rgb(31,73,125)"><br>
</span><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)">Owner</span></b><u></u><u></u></p>
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"> </span></b><u></u><u></u></p>
<p class="MsoNormal"><b><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)">Caton Energy Consulting</span></b><span style="font-size:10pt;font-family:Calibri,sans-serif;color:black"><br>
</span><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">  1150 N. 192<sup>nd</sup> St., #4-202</span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">  Shoreline, WA 98133<br>
  office:  <a href="tel:785.410.3317" value="+17854103317" target="_blank">785.410.3317</a></span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"><a href="http://www.catonenergy.com" target="_blank"><span style="color:rgb(86,23,130)">www.catonenergy.com</span></a></span><u></u><u></u></p>
<p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span><u></u><u></u></p>
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> Equest-users [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Dale elegant<br>
<b>Sent:</b> Wednesday, May 06, 2015 10:49 AM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] eQuest LPD input output disagree</span><u></u><u></u></p>
<p class="MsoNormal"> <u></u><u></u></p>
<div>
<div>
<p class="MsoNormal">Dear all:<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"> <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">I'm modeling a 700000 sqft warehouse, everything works fine, except in BEPU report it shows a
<span lang="EN">360.310 KWH /SQFT-YR GROSS-AREA, which doesn't make any sense. The utility rates are correct, under Quality control reports, it indicates errors of the peak lighting load of 67.74 w/sqft and peak miscellaneous equipment load of 40.91 w/sqft.
 I did input LPD and EPD with around 0.6 w/sqft and 0.5 w/sqft, the corresponding schedules are correct, the building area in each floor and each zone are correct, the total energy demand looks about right for the size of building.</span><u></u><u></u></p>
<p><span lang="EN">But at some point the model makes the LPD output 100 times bigger than what I input,
<span style="color:rgb(39,78,19)">I would appreciate it if you could provide me with any advices, thanks!</span></span><u></u><u></u></p>
<p><span lang="EN" style="color:rgb(39,78,19)">Qing</span><u></u><u></u></p>
<p><span lang="EN"> </span><u></u><u></u></p>
<p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span><u></u><u></u></p>
<p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span><u></u><u></u></p>
<p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span><u></u><u></u></p>
<p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span><u></u><u></u></p>
<p><span lang="EN"> </span><u></u><u></u></p>
<p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span><u></u><u></u></p>
<p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span><u></u><u></u></p>
<p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span><u></u><u></u></p>
</div>
</div>
</div>
<u></u>

<table border="0" style="line-height:16px">
<tbody>
<tr>
<td valign="top"><span style="color:rgb(102,102,102);font-family:'futura lt book',arial;font-size:12px;line-height:15px"><a href="https://www.zgf.com/ZGF_Email_Disclaimer.html" target="_blank">ZGF Email Disclaimer</a></span>
</td>
</tr>
</tbody>
</table>
</div>

<br><br>---------- Forwarded message ----------<br>From: Nicholas Caton <<a href="mailto:ncaton@catonenergy.com">ncaton@catonenergy.com</a>><br>To: "Sami, Vikram" <<a href="mailto:vikram.sami@zgf.com">vikram.sami@zgf.com</a>>, Dale elegant <<a href="mailto:elegantdale@gmail.com">elegantdale@gmail.com</a>>, <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>Cc: <br>Date: Thu, 7 May 2015 11:18:48 -0700<br>Subject: Re: [Equest-users] eQuest LPD input output disagree<br><div lang="EN-US" link="#0563C1" vlink="#954F72"><div><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Hey Vikram,</span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Qing Dale replied off-list that his issue is resolved.  For his 700,000 ft2 project, only a small fraction was conditioned and therefore used for EUI reporting.  I suspect among other possible solutions, he could have used the input I suggested below to override the area used in determining reported EUI metrics.</span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">~Nick</span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><div><p class="MsoNormal"><b><span style="font-size:14pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">NICK CATON, P.E.</span></b><span style="font-size:11pt;font-family:Verdana,sans-serif;color:rgb(31,73,125)"><br></span><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)">Owner</span></b></p><p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"> </span></b></p><p class="MsoNormal"><b><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)">Caton Energy Consulting</span></b><span style="font-size:10pt;font-family:Calibri,sans-serif;color:black"><br></span><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">  1150 N. 192<sup>nd</sup> St., #4-202</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">  Shoreline, WA 98133<br>  office:  <a href="tel:785.410.3317" value="+17854103317" target="_blank">785.410.3317</a></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"><a href="http://www.catonenergy.com" target="_blank"><span style="color:rgb(86,23,130)">www.catonenergy.com</span></a></span><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"></span></p></div><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><div><div style="border-style:solid none none;border-top-color:rgb(225,225,225);border-top-width:1pt;padding:3pt 0in 0in"><p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> Sami, Vikram [mailto:<a href="mailto:vikram.sami@zgf.com" target="_blank">vikram.sami@zgf.com</a>] <br><b>Sent:</b> Thursday, May 07, 2015 9:39 AM<br><b>To:</b> Nicholas Caton; Dale elegant; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> RE: [Equest-users] eQuest LPD input output disagree</span></p></div></div><p class="MsoNormal"> </p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Dale,</span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">Curious. Could you attach your inp file? </span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><div><table border="0" cellpadding="0"><tbody><tr><td valign="top" style="padding:0.75pt"><p class="MsoNormal" style="line-height:12pt"><b><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(227,59,69)">Vikram Sami</span></b><span style="color:rgb(31,73,125)"><br></span><span style="font-size:7pt;font-family:'Futura LT Book';color:rgb(102,102,102)">AIA, BEMP, LEED BD+C</span><span style="font-size:9pt;font-family:'Futura LT Book';color:black"> </span><span style="color:rgb(31,73,125)"><br></span><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)">Associate Partner</span><span style="color:rgb(31,73,125)"></span></p></td><td width="16" style="width:12pt;padding:0.75pt"><p class="MsoNormal" style="line-height:12pt"><span style="color:rgb(31,73,125)"> </span></p></td><td valign="top" style="padding:0.75pt"><p class="MsoNormal" style="line-height:12pt"><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)">ZGF ARCHITECTS LLP</span><span style="color:rgb(31,73,125)"><br></span><b><span style="font-size:7.5pt;font-family:'Futura LT Book';color:rgb(227,59,69)">T </span></b><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)"><a href="tel:206.521.3509" value="+12065213509" target="_blank">206.521.3509</a> </span><b><span style="font-size:7.5pt;font-family:'Futura LT Book';color:rgb(227,59,69)">E </span></b><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)"><a href="mailto:vikram.sami@zgf.com" target="_blank">vikram.sami@zgf.com</a></span><span style="color:rgb(31,73,125)"><br></span><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)">925 Fourth Avenue, Suite 2400 <br>Seattle, WA 98104</span><span style="color:rgb(31,73,125)"></span></p></td></tr></tbody></table></div><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><div><div style="border-style:solid none none;border-top-color:rgb(225,225,225);border-top-width:1pt;padding:3pt 0in 0in"><p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> Equest-users [<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Nicholas Caton<br><b>Sent:</b> Wednesday, May 06, 2015 1:51 PM<br><b>To:</b> Dale elegant; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> Re: [Equest-users] eQuest LPD input output disagree</span></p></div></div><p class="MsoNormal"> </p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">The EUI figures reported on BEPU use the building area entered in the following location (if entered).  You might check here first to see if it reads 700,000 or something else:</span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"><img border="0" width="462" height="256" src="cid:image001.png@01D088B7.96E81810"></span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><b><span style="font-size:14pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">NICK CATON, P.E.</span></b><span style="font-size:11pt;font-family:Verdana,sans-serif;color:rgb(31,73,125)"><br></span><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)">Owner</span></b></p><p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"> </span></b></p><p class="MsoNormal"><b><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)">Caton Energy Consulting</span></b><span style="font-size:10pt;font-family:Calibri,sans-serif;color:black"><br></span><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">  1150 N. 192<sup>nd</sup> St., #4-202</span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)">  Shoreline, WA 98133<br>  office:  <a href="tel:785.410.3317" value="+17854103317" target="_blank">785.410.3317</a></span></p><p class="MsoNormal"><span style="font-size:10pt;font-family:Calibri,sans-serif;color:rgb(86,23,130)"><a href="http://www.catonenergy.com" target="_blank"><span style="color:rgb(86,23,130)">www.catonenergy.com</span></a></span></p><p class="MsoNormal"><span style="font-size:11pt;font-family:Calibri,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> Equest-users [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Dale elegant<br><b>Sent:</b> Wednesday, May 06, 2015 10:49 AM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] eQuest LPD input output disagree</span></p><p class="MsoNormal"> </p><div><div><p class="MsoNormal">Dear all:</p></div><div><p class="MsoNormal"> </p></div><div><p class="MsoNormal">I'm modeling a 700000 sqft warehouse, everything works fine, except in BEPU report it shows a <span lang="EN">360.310 KWH /SQFT-YR GROSS-AREA, which doesn't make any sense. The utility rates are correct, under Quality control reports, it indicates errors of the peak lighting load of 67.74 w/sqft and peak miscellaneous equipment load of 40.91 w/sqft. I did input LPD and EPD with around 0.6 w/sqft and 0.5 w/sqft, the corresponding schedules are correct, the building area in each floor and each zone are correct, the total energy demand looks about right for the size of building.</span></p><p><span lang="EN">But at some point the model makes the LPD output 100 times bigger than what I input, <span style="color:rgb(39,78,19)">I would appreciate it if you could provide me with any advices, thanks!</span></span></p><p><span lang="EN" style="color:rgb(39,78,19)">Qing</span></p><p><span lang="EN"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p><p><span lang="EN" style="font-size:7.5pt;font-family:Verdana,sans-serif"> </span></p></div></div><table border="0" cellpadding="0"><tbody><tr><td valign="top" style="padding:0.75pt"><p class="MsoNormal" style="line-height:12pt"><span style="font-size:9pt;font-family:'Futura LT Book';color:rgb(102,102,102)"><a href="https://www.zgf.com/ZGF_Email_Disclaimer.html" target="_blank">ZGF Email Disclaimer</a></span> </p></td></tr></tbody></table><p class="MsoNormal"> </p></div></div>
<br><br>---------- Forwarded message ----------<br>From: Faisal Sharif <<a href="mailto:fisharif@gmail.com">fisharif@gmail.com</a>><br>To: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>Cc: <br>Date: Thu, 7 May 2015 15:36:00 -0400<br>Subject: [Equest-users] What is meant by Zone Min Design Air Flow<br><div dir="ltr"><div style="font-family:'comic sans ms',sans-serif;font-size:small;color:rgb(11,83,148)"><div>Dear Equest Users </div><div><br></div><div>Can you please advice what is meant by Zone Min Design Air Flow?..  dose that refer to the min Vent. fresh air required for a specific zone (all zone here were considered as office)</div><div>As per the below Schematic design wizard .. this is  a 3 story building; each level has core and perimeter zones </div><div>The wizard had generated the green data as default ... it looks for me that 2.54 l/s m2 is too high for an office min. vent air , if that is meant by Zone Min Design Air Flow</div><div>Or it could be something else</div><div><br></div><div><img src="https://mail.google.com/mail/u/0/?ui=2&ik=df94f8f765&view=fimg&th=14d2fd0d6297e547&attid=0.1&disp=emb&realattid=ii_14d2fbe94aca9f9b&attbid=ANGjdJ8RL62GDUc2z0158blTGPvxTZlK91Hjgx2Kk-9ljVjMwmGnbPmaRMwNezppDInmtAIyfMGFCdLa2cHKX13hYtXS2ei8nAGvz8pgFNW-3-yUy1qbWaVEg9Yq9Gs&sz=s0-l75&ats=1431026326307&rm=14d2fd0d6297e547&zw" alt="Inline image 1" width="472" height="379" style="margin-right: 0px;"></div></div><div><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><p><font size="2" color="#0b5394" face="trebuchet ms, sans-serif">Regards,</font></p></div><div><p><font size="2" color="#0b5394" face="trebuchet ms, sans-serif">Faisal Ibrahim Sharif </font></p>

<p><br></p></div></div></div></div></div></div></div></div>
</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="mailto:Equest-users@lists.onebuilding.org">Equest-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
<br></blockquote></div><br></div></div>