<html>
  <head>
    <meta content="text/html; charset=utf-8" http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <font face="Times New Roman, Times, serif">One other thing about
      envelope insulation is it is not all equal in effect.  Most times
      an extra R-10 is more effective in the roof than on the wall or
      under a floor.  The type of insulation and what you do to place it
      can have a large effect as well.  I'm currently coming in late on
      a super insulated house.  R-30 EPS under the slab on grade, R-60
      walls using wood I joists and cellulose and an R-60 cathedral roof
      of the same.  I haven't modeled it yet but I can pretty much guess
      about R-15 was wasted under the floor and about R-20 on the wall.</font> 
    The floor sees a constant 45F delta T year round, the roof +60F to
    -110F delta T and the walls +20F to -100F.  The economics of the
    build outs could be adjusted as well.  On the walls a 2x3 parallel
    cord truss would be in the range of 80% cheaper than a wood I.  A
    2x4 truss on the roof about 65% cheaper than a wood I.  I know the
    insulation companies claim their blown in insulation doesn't settle
    but I have never found any of this magic insulation in real life. 
    If you have a 17' high column of blown in insulation I will
    guarantee in 5 years you have a cavity at the top with zero
    insulation.  The design has a nice 14" wall overhang of the
    foundation with minimal protection.  Sooner or later a raccoon will
    be turning a wall cavity into an apartment.<br>
    There is always a trade-off and it is very climate dependent.  Super
    or platinum can mean many different things depending on where the
    building is situated.  Spending an extra $1000 to save $100 over 20
    years doesn't make much sense either.  Even less if the building has
    a life span of 40 years.  Also, a 2000 SF main floor slab of 50F
    concrete can come in pretty handy when your 3 week heat wave hits,
    depending on where it is of course.<br>
    I suppose what I'm really railing against is everyone blindly
    following "the prescription".  Do this and everything is perfect,
    get your star and everything is beautiful.  LOL, fat chance!  Most
    "official" building codes are 60 to 70 years old and are still
    evolving.  This green, energy conservation and sustainability is
    barely a decade old.  Just don't forget common sense and being
    practical.  It is as much of the "art" as excellent modeling is.<br>
    Bruce Easterbrook P.Eng.<br>
    Abode Engineering. <br>
    <br>
    <div class="moz-cite-prefix">On 28/04/2015 04:29 PM, Chris Baker
      wrote:<br>
    </div>
    <blockquote
cite="mid:DFB335DD1FE55A418B15D44AB708D8D5162EE0@CCIEX1.corp.ccieast.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <meta name="Generator" content="Microsoft Word 14 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
@font-face
        {font-family:Verdana;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";
        color:black;}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:Consolas;
        color:black;}
span.EmailStyle19
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.EmailStyle20
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";
        color:black;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">After
            seeing Nick’s comment I thought I would add my 2 cents just
            being in Alaska and constantly dealing with insulation
            issues.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">The
            winter obviously puts high demands for heating and
            ventilation and I think every building we’ve upgraded for
            energy efficiency has seen substantial improvements in
            energy savings.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">But
            many of our clients insist on “more insulation is better” in
            arctic conditions without really understanding the effects
            over an entire year.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">On
            some projects I’ve seen R-80+ systems with 18” wall
            buildups.  Not to mention R80-90+  roof buildups (14”-16”
            thick) which obviously improve the overall heating
            performance – especially given our heating systems are
            typically operating more than 6 months out of the year.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">But
            there is a tradeoff.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">We
            typically get around 4-1/2 months of 60-90 degree weather up
            here.  This puts a high demand on cooling systems during
            this period.  You can easily end up with a building so
            heavily insulated that even in the mid 60’s outside temp
            range the cooling system may need to operate unless all the
            doors and windows were opened up– which isn’t always
            possible because of security reasons.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">The
            buildings become too efficient at retaining heat to the
            degree that the cooling demand is higher to basically fight
            the building during summer months to maintain temp
            setpoints.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Also,
            Many buildings in Alaska do not have cooling systems so when
            you increase R-value and U-value to a certain threshold you
            are in some ways “biting the bullet” with regard to adding
            appropriate ventilation and cooling systems capable of
            cancelling out the heat buildup in warmer weather (which
            offsets X dollar amount of energy savings provided during
            the winter months).<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Fortunately,
            the end result in Alaska is usually a net cost savings just
            because heating costs in Alaska are so ridiculously high
            given most buildings use fuel-oil.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">However,
            in theory, if you were to cut the cost of heating up here to
            a certain threshold the cost of cooling the building would
            eventually be higher than the cost of heating it in the
            winter months.  At which point I imagine someone doing the
            classic face-palm.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">-Chris<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
                Equest-users [<a class="moz-txt-link-freetext"
                  href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Nicholas Caton<br>
                <b>Sent:</b> Tuesday, April 28, 2015 11:40 AM<br>
                <b>To:</b> Joe Huang; Daniel Knapp; Mayank Bhatnagar<br>
                <b>Cc:</b> eQUEST Users List<br>
                <b>Subject:</b> Re: [Equest-users] [Bldg-sim] Expert
                advice on Wall Insulation study in eQuest<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Great
            discussion!</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Since
            this thread has clearly gathered attentions of the right
            individuals, I’d like to layer on a query which may further
            inform Mayank’s efforts:</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Is
            the “law of diminishing returns” as you improve envelope
            insulation universal to ALL climates, in practice or in
            theory?  While I have reliably observed such behavior
            exploring comparable ECM’s in temperate climates, I am
            curious whether tropical or arctic climates should expect
            (all else being equal) a relatively “flatter” curve when
            plotting R-value against annual energy savings?  </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">My
            gut tells me the reduced opportunity to leverage airside
            economizer function or operable windows would make
            incremental insulation increases more attractive for annual
            energy consumption, but experience has taught me to question
            my gut on such matters (…Thanks Joe!).</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Regards,</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">~Nick</span><o:p></o:p></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
        <div>
          <p class="MsoNormal"><b><span
style="font-size:14.0pt;font-family:"Calibri","sans-serif";color:#1F497D">NICK
                CATON, P.E.</span></b><span
style="font-size:11.0pt;font-family:"Verdana","sans-serif";color:#1F497D"><br>
            </span><b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#561782">Owner</span></b><o:p></o:p></p>
          <p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#561782"> </span></b><o:p></o:p></p>
          <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#561782">Caton
                Energy Consulting</span></b><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif""><br>
            </span><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> 
              1150 N. 192<sup>nd</sup> St., #4-202</span><o:p></o:p></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> 
              Shoreline, WA 98133<br>
                office:  785.410.3317</span><o:p></o:p></p>
          <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#561782"><a
                moz-do-not-send="true" href="www.catonenergy.com"><span
                  style="color:#561782">www.catonenergy.com</span></a></span><o:p></o:p></p>
        </div>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"> </span><o:p></o:p></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:windowtext">From:</span></b><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:windowtext">
                Equest-users [mailto:<a moz-do-not-send="true"
                  href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Joe Huang<br>
                <b>Sent:</b> Tuesday, April 28, 2015 11:56 AM<br>
                <b>To:</b> Daniel Knapp; Mayank Bhatnagar<br>
                <b>Cc:</b> eQUEST Users List<br>
                <b>Subject:</b> Re: [Equest-users] [Bldg-sim] Expert
                advice on Wall Insulation study in eQuest</span><o:p></o:p></p>
          </div>
        </div>
        <p class="MsoNormal"> <o:p></o:p></p>
        <p class="MsoNormal" style="margin-bottom:12.0pt">Dan,<br>
          <br>
          Very good point!   I didn't even think about this, i.e., that
          the plot was against conductance and not resistance. <br>
          Therefore, I would conclude that eQUEST is behaving properly.<br>
          <br>
          Joe<o:p></o:p></p>
        <pre>Joe Huang<o:p></o:p></pre>
        <pre>White Box Technologies, Inc.<o:p></o:p></pre>
        <pre>346 Rheem Blvd., Suite 205A<o:p></o:p></pre>
        <pre>Moraga CA 94556<o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a><o:p></o:p></pre>
        <pre><a moz-do-not-send="true" href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for simulation-ready weather data<o:p></o:p></pre>
        <pre>(o) (925)388-0265<o:p></o:p></pre>
        <pre>(c) (510)928-2683<o:p></o:p></pre>
        <pre>"building energy simulations at your fingertips"<o:p></o:p></pre>
        <div>
          <p class="MsoNormal">On 4/27/2015 11:12 AM, Daniel Knapp
            wrote:<o:p></o:p></p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <p class="MsoNormal">Hi Mayank, <o:p></o:p></p>
          <div>
            <p class="MsoNormal"> <o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal">I think on further reflection you are
              seeing exactly what you should be seeing. The energy
              consumption should go down linearly with the U-value. What
              does saturate is the energy savings compared to insulation
              thickness or R-value which is plotted as 1/U. Here is a
              graph of energy vs. U and energy vs R for your building:<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"> <o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal">All the best,<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal">Dan<o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"> <o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"> <o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"><img
                id="BF92CB2A-C210-4A66-AC36-237F522B1795"
                src="cid:part6.04010808.06030501@bellnet.ca" border="0"
                height="244" width="663"><o:p></o:p></p>
          </div>
          <div>
            <p class="MsoNormal"> <o:p></o:p></p>
            <div>
              <p class="MsoNormal" style="margin-bottom:12.0pt">—<br>
                Daniel Knapp, PhD, PPhys, LEED® AP O+M<br>
                <a moz-do-not-send="true"
                  href="mailto:danielk@arborus.ca">danielk@arborus.ca</a><br>
                <br>
                Arborus Consulting<br>
                Energy Strategies for the Built Environment<br>
                <a moz-do-not-send="true" href="http://www.arborus.ca">www.arborus.ca</a><br>
                76 Chamberlain Avenue <br>
                Ottawa, ON, K1S 1V9 <br>
                Phone: (613) 234-7178 ext. 113<br>
                Fax: (613) 234-0740<br>
                <br>
                <o:p></o:p></p>
            </div>
            <p class="MsoNormal" style="margin-bottom:12.0pt"><o:p> </o:p></p>
            <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
              <p class="MsoNormal">On Apr 27, 2015, at 6:15 AM, Mayank
                Bhatnagar <<a moz-do-not-send="true"
                  href="mailto:mayank.23aug@gmail.com">mayank.23aug@gmail.com</a>>
                wrote:<br>
                <br>
                Thank you Joe and Daniel for your response.<br>
                <br>
                As you suggested, I checked LS-C report for wall
                conduction variation w.r.t. U-value. It is also giving
                linear trend for wall conduction. Additionally, I have
                done same analysis for without internal loads
                (occupancy, lighting and equipment load) as Joe
                indicated about the compounding effect. I still get
                linear trend between the energy consumption and
                U-value. <br>
                <br>
                For your reference, I am attaching inp, pd2 and weather
                file.<br>
                <br>
                <br>
                <br>
                On Thu, Apr 23, 2015 at 8:10 PM, Joe Huang <<a
                  moz-do-not-send="true"
                  href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>> wrote:<br>
                Mayank, Daniel,<br>
                <br>
                I think it's a good idea to look at the component loads
                in the LS-C reports, but I want to add some words of
                caution.<br>
                The loads (actually heat flows) shown in those reports
                are calculated at the constant Reference Temperature,
                and categorized as either heating or cooling if the
                total load of the building that hour is negative or
                positive. These loads are corrected when DOE-2 solves
                for the actual room temperature based on simple
                UA-deltaT principles.  If you want the corrected wall
                loads, you need to get an hourly report of the wall
                loads and then correct for the temperature difference
                Troom - Treference.<br>
                <br>
                I'm not sure if this level of detail is warranted,
                though.  I also suspect there's some other compounding
                effect that's giving you the results that you report.<br>
                <br>
                Joe<br>
                <br>
                Joe Huang       <br>
                White Box Technologies, Inc.<br>
                346 Rheem Blvd., Suite 205A<br>
                Moraga CA 94556<br>
                <a moz-do-not-send="true"
                  href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a><br>
                <a moz-do-not-send="true"
                  href="http://weather.whiteboxtechnologies.com">http://weather.whiteboxtechnologies.com</a> for
                simulation-ready weather data<br>
                <a moz-do-not-send="true"
                  href="http://www.whiteboxtechnologies.com">http://www.whiteboxtechnologies.com</a><br>
                (o) (925)388-0265<br>
                (c) (510)928-2683<br>
                "building energy simulations at your fingertips"<br>
                <br>
                <br>
                On 4/23/2015 6:18 AM, Daniel Knapp wrote:<br>
                Hi Mayank,<br>
                <br>
                I recommend opening up the SIM file (you can do this by
                going to Tools -> View Simulation Output) and looking
                at the LS-C and LV-D reports. In the LS-C report you can
                find the contribution to the peak heating and cooling
                loads that come from the walls. From this you should be
                able to figure out how the wall conduction is changing
                as a fraction of the peak loads as you decrease the wall
                U-value. In the LV-D report (scroll to the very end of
                it) there is a summary of the U-values for each exterior
                surface. This might be a good place to look to make sure
                that the effective U-values that eQUEST is simulating
                are matching up with your expectations of what the
                U-values should be.<br>
                <br>
                I would agree that the energy savings should saturate at
                some point.<br>
                <br>
                All the best,<br>
                Dan<br>
                <br>
                <br>
                —<br>
                Daniel Knapp, PhD, PPhys, LEED® AP O+M<br>
                <a moz-do-not-send="true"
                  href="mailto:danielk@arborus.ca">danielk@arborus.ca</a><br>
                <br>
                Arborus Consulting<br>
                Energy Strategies for the Built Environment<br>
                <a moz-do-not-send="true" href="http://www.arborus.ca">www.arborus.ca</a><br>
                76 Chamberlain Avenue<br>
                Ottawa, ON, K1S 1V9<br>
                Phone: (613) 234-7178 ext. 113<br>
                Fax: (613) 234-0740<br>
                <br>
                <br>
                <br>
                <br>
                On Apr 23, 2015, at 5:00 AM, Mayank Bhatnagar <a
                  moz-do-not-send="true"
                  href="mailto:mayank.23aug@gmail.com">
                  <mayank.23aug@gmail.com></a> wrote:<br>
                <br>
                Hi Claire,<br>
                <br>
                Thanks for your response.<br>
                <br>
                The analysis has been done on an 8 hour operating office
                building in New Delhi. The mechanical system is packaged
                single zone system with electric resistance heating.<br>
                <br>
                Please let me know if you need more information.<br>
                <br>
                Thanks<br>
                <br>
                Regards,<br>
                Mayank<br>
                <br>
                On Thu, Apr 23, 2015 at 2:25 PM, Claire Das Bhaumik <a
                  moz-do-not-send="true"
                  href="mailto:claire@inklingllp.com">
                  <claire@inklingllp.com></a> wrote:<br>
                Mayank,<br>
                <br>
                I think we need to know a bit more about the building:<br>
                - Location (some parts of India are cool, others hot!)<br>
                - Building usage - office, domestic, retail? Hours of
                use?<br>
                - Servicing - heating and cooling? Mechanical or natural
                vent?<br>
                <br>
                Regards,<br>
                <br>
                Dr Claire Das Bhaumik CEng FCIBSE<br>
                <br>
                Partner - Inkling LLP<br>
                <br>
                  <br>
                e: <a moz-do-not-send="true"
                  href="mailto:claire@inklingllp.com">claire@inklingllp.com</a><br>
                <br>
                t:  07950 282800<br>
                <br>
                w: <a moz-do-not-send="true"
                  href="http://www.inklingllp.com">www.inklingllp.com</a><br>
                <br>
                Follow us on Twitter: @DasInkling<br>
                <br>
                Partnership No. OC367619<br>
                <br>
                <br>
                On Thu, Apr 23, 2015 at 9:51 AM, Mayank Bhatnagar <a
                  moz-do-not-send="true"
                  href="mailto:mayank.23aug@gmail.com">
                  <mayank.23aug@gmail.com></a> wrote:<br>
                Dear All,<br>
                <br>
                We are working on a national level research project in
                India. A building envelope analysis is a part of this
                project. By doing analysis, we have found a vague
                results in trend (linearly downward) of reduction in
                energy consumption with reducing wall U-value in eQUEST.<br>
                <br>
                Theoretically, the energy consumption should approach to
                stagnant with reduction in wall U-value.<br>
                <br>
                Please refer figure.<br>
                <br>
                Appreciate if anyone put light on this.<br>
                <br>
                Thank you.<br>
                <br>
                Regards,<br>
                <br>
                Mayank Bhatnagar<br>
                <br>
                Theoretical should come like this.<br>
                <image.png><br>
                <br>
                In eQuest the trend is-<br>
                <image.png><br>
                <br>
                _______________________________________________<br>
                Bldg-sim mailing list<br>
                <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
                To unsubscribe from this mailing list send  a blank
                message to <a moz-do-not-send="true"
                  href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                <br>
                <br>
                <br>
                _______________________________________________<br>
                Equest-users mailing list<br>
                <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                To unsubscribe from this mailing list send  a blank
                message to <a moz-do-not-send="true"
                  href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                _______________________________________________<br>
                Equest-users mailing list<br>
                <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                To unsubscribe from this mailing list send  a blank
                message to <a moz-do-not-send="true"
                  href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                <br>
                <br>
                <br>
                _______________________________________________<br>
                Equest-users mailing list<br>
                <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                To unsubscribe from this mailing list send  a blank
                message to <a moz-do-not-send="true"
                  href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
                <br>
                <Small Office Bldg_v5_4.pd2><Small Office
                Bldg_v5_4.inp><IND_New.Delhi.421820_ISHRAE.BIN><o:p></o:p></p>
            </blockquote>
            <p class="MsoNormal"> <o:p></o:p></p>
          </div>
        </blockquote>
        <p class="MsoNormal"> <o:p></o:p></p>
      </div>
      <br>
      <hr> <font color="Gray" face="Courier New" size="2"><br>
        CCI-Alliance Confidentiality notice: This message is intended
        only for the person to whom addressed in the text above and may
        contain privileged or confidential information. If you are not
        that person, any use of this message is prohibited. We request
        that you notify us by reply to this message, and then delete all
        copies of this message including any contained in your reply.
        Thank you.<br>
      </font> <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>