<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns="http://www.w3.org/TR/REC-html40">
<head>
<meta http-equiv="Content-Type" content="text/html; charset=iso-8859-1">
<meta name="Generator" content="Microsoft Word 14 (filtered medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]--><style><!--
/* Font Definitions */
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
{font-family:Verdana;
panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
{mso-style-priority:99;
mso-style-link:"Balloon Text Char";
margin:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma","sans-serif";}
span.EmailStyle17
{mso-style-type:personal-compose;
font-family:"Calibri","sans-serif";
color:windowtext;}
span.BalloonTextChar
{mso-style-name:"Balloon Text Char";
mso-style-priority:99;
mso-style-link:"Balloon Text";
font-family:"Tahoma","sans-serif";}
.MsoChpDefault
{mso-style-type:export-only;
font-family:"Calibri","sans-serif";}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
</head>
<body lang="EN-US" link="blue" vlink="purple">
<div class="WordSection1">
<p class="MsoNormal">Hello everyone,<o:p></o:p></p>
<p class="MsoNormal">I got the following comment from a LEED reviewer, and was hoping you guys could help me out.
<o:p></o:p></p>
<p class="MsoNormal"><i><span style="background:silver;mso-highlight:silver">“It is unclear whether the Baseline case fan air flow rates were sized based on a 20 deg. F supply-air-to-room-air temperature difference for each Baseline system because using the
sensible heat equation (Q = 1.08*CFM*deltaT) with the total cooling capacity of 1,103,721 Btuh and total supply airflow of 15,656 CFM reported in Table 1.4.7A, it appears that a temperature difference of 65 deg. F was used. Update the model, provide input
summary reports showing that the Baseline case air flow rates were sized based on a 20 deg. F supply-air-to-room-air temperature difference per G3.1.2.8, update Supplemental Table 1.4 to reflect the total Baseline Case air flow, and update the form to reflect
any changes made.</span></i><i>”<o:p></o:p></i></p>
<p class="MsoNormal"><i><o:p> </o:p></i></p>
<p class="MsoNormal">The zone temperature is set to 75F and the MIN-SUPPLY-T is set to 55F, therefore it should be sized based on the 20 degree difference if I leave the airflow to be estimated automatically, am I correct?<o:p></o:p></p>
<p class="MsoNormal">The other issue is that the reviewer seems to be estimating the temperature difference using the sensible heat equation with the total cooling capacity, which is incorrect, right? If I use the sensible heat capacity, as it should be in
the equation, the temperature difference drops to 30F; which is still high and I intend to correct it, but it is not 65F as mentioned by the reviewer.
<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I really appreciate your help.<o:p></o:p></p>
<p class="MsoNormal"><span lang="ES-CR">Best regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="ES-CR"><o:p> </o:p></span></p>
<table class="MsoNormalTable" border="0" cellspacing="0" cellpadding="0" style="border-collapse:collapse">
<tbody>
<tr>
<td width="271" valign="top" style="width:203.4pt;padding:0in 5.4pt 0in 5.4pt">
<p class="MsoNormal" style="line-height:150%"><b><span lang="ES-CR" style="font-size:10.0pt;line-height:150%;font-family:"Verdana","sans-serif";mso-fareast-language:ES"> Ing. Gastón Michaud F.
</span></b><b><span lang="ES-CR" style="font-size:10.0pt;line-height:150%;font-family:"Verdana","sans-serif";mso-fareast-language:ES"><o:p></o:p></span></b></p>
<p class="MsoNormal"><span lang="ES-CR" style="font-size:10.0pt;font-family:"Verdana","sans-serif""> Tel.: (506) 2222-7529<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="ES-CR" style="font-size:10.0pt;font-family:"Verdana","sans-serif""> Fax: (506) 2256-5608<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="ES-CR" style="font-size:10.0pt;font-family:"Verdana","sans-serif""> From USA: 1-305-433-3668</span><span lang="ES-CR" style="font-size:12.0pt;font-family:"Times New Roman","serif""><o:p></o:p></span></p>
<p class="MsoNormal"><span lang="ES-CR" style="font-size:10.0pt;font-family:"Verdana","sans-serif"">
</span><span lang="ES-CR" style="font-size:7.5pt;font-family:"Verdana","sans-serif"">Calle 30, Avenida 0 y 2.
</span><span style="font-size:7.5pt;font-family:"Verdana","sans-serif"">San José, Costa Rica</span><span style="font-size:7.5pt;font-family:"Verdana","sans-serif""><o:p></o:p></span></p>
</td>
<td width="362" valign="top" style="width:271.6pt;padding:0in 5.4pt 0in 5.4pt">
<p class="MsoNormal" style="line-height:150%"><b><span style="font-size:8.0pt;line-height:150%;font-family:"Verdana","sans-serif""><img width="43" height="48" id="Picture_x0020_1" src="cid:image001.jpg@01D07B8F.F1706880" alt="Description: Description: Description: Description: Description: LEEDAP_BDCbw"></span></b><b><span style="font-size:8.0pt;line-height:150%;font-family:"Verdana","sans-serif";mso-fareast-language:ES"> </span></b><img width="59" height="40" id="Picture_x0020_2" src="cid:image002.jpg@01D07B8F.F1706880" alt="cid:image002.jpg@01CF4517.8D2BB550"><b><span style="font-size:10.0pt;line-height:150%;font-family:"Verdana","sans-serif""><o:p></o:p></span></b></p>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal" style="line-height:150%"><img width="144" height="131" id="Picture_x0020_3" src="cid:image003.jpg@01D07B8F.F1706880" alt="Description: Logo CTS firma"><i><span lang="ES-CR" style="font-size:7.0pt;line-height:150%;font-family:"Verdana","sans-serif";mso-fareast-language:ES"> </span></i><i><span lang="ES-CR" style="font-size:7.0pt;line-height:150%;font-family:"Verdana","sans-serif";mso-fareast-language:ES"><o:p></o:p></span></i></p>
<p class="MsoNormal"><i><span lang="ES-CR" style="font-size:7.0pt;font-family:"Verdana","sans-serif";mso-fareast-language:ES">Este correo puede contener información protegida por el secreto profesional. Si usted no es la persona a quien va dirigido, por favor
tome en cuenta que su divulgación, distribución o reproducción es estrictamente prohibida. Cualquier persona que reciba este mensaje por error debe notificarlo inmediatamente al remitente vía telefónica o correo electrónico y borrarlo permanentemente de su
computador. Los comentarios plasmados en este correo son del remitente solamente y no reflejan necesariamente la posición de CTS S.A.</span></i><span lang="ES-CR" style="mso-fareast-language:ES"><o:p></o:p></span></p>
<p class="MsoNormal"><b><i><span lang="ES-CR" style="font-size:7.5pt;font-family:"Verdana","sans-serif";mso-fareast-language:ES">Por favor considere su responsabilidad con el medio ambiente antes de imprimir este correo electrónico</span></i></b><span lang="ES-CR" style="mso-fareast-language:ES"> <o:p></o:p></span></p>
<p class="MsoNormal"><i><span style="font-size:7.0pt;font-family:"Verdana","sans-serif";mso-fareast-language:ES">----------------------------------------------------------------------------------------------------------------<o:p></o:p></span></i></p>
<p class="MsoNormal"><i><span style="font-size:7.0pt;font-family:"Verdana","sans-serif";mso-fareast-language:ES">This mail may contain information that is legally privileged, confidential or exempt from disclosure. If you are not the intended recipient, please
note that any dissemination, distribution or copying of this message is strictly prohibited. Anyone who receives this message in error should notify the sender immediately by telephone or by e-mail and delete it permanently from their computer. The opinions
above are those of the author and do not necessarily reflect the position of CTS S.A.<o:p></o:p></span></i></p>