    <div class="moz-cite-prefix">Simge, <br>
      <br>
      I feel compelled to respond since you mentioned me so prominently
      in your post :-)<br>
      <br>
      I think you're bringing up a very germaine question, and indeed
      it's one that in my opinion needs further study, i.e., <br>
      how does EnergyPlus compare with eQUEST or other building energy
      simulation programs in their modeling results?<br>
      <br>
      The LBNL paper you cited is a summary paper from a SimBuild
      Conference in 2008 that only skimmed the findings from a<br>
      year-long effort supported by the California Energy Commission. 
      I've put the full report on the Web, along with a later study<br>
      I did last year as part of an EnergyPlus Feasibility Study by
      AutoDesk done for Southern California Edison that you might find<br>
      equally interesting:<br>
      <br>
<a class="moz-txt-link-freetext" href="http://www.whiteboxtechnologies.com/download_AutoDesk_EP_feasib_rpt.htm">http://www.whiteboxtechnologies.com/download_AutoDesk_EP_feasib_rpt.htm</a><br>
      <br>
      The second study was under wraps for a long time, but I received
      clearance from SCE to release it two months ago.<br>
      My part of the study is strictly the EnergyPlus to DOE-2.2
      comparison pp. 57 -98, and I have no opinions one way or <br>
      the other in respect to the rest of the study. My task was to take
      several DEER prototypes (office, residential, and retail)<br>
      modeled in eQUEST/DOE-2.2 and convert them to EP 7.X.  Compared to
      what I saw in the 2007 study, the discrepancies<br>
      in heating energy consumption were even more striking, probably
      because all the buildings were modeled in southern <br>
      California climates.   I was getting consistently from a 5:1 to a
      20:1 difference in heating energies (DOE-2 high, EP low).<br>
      <br>
      Following up on Jeff's earlier comment, diagnosing the differences
      between two simulation programs requires a lot of <br>
      time, experimentation, and often in-depth study of the source
      codes. In the 2007 paper,  I mentioned somewhere between<br>
      15 and 20 areas of modeling differences with significant effects
      on the results. <br>
      <br>
      It's been 7 years since the first study, and I've been
      disappointed by the lack of progress. Some of it is
      understandable, since <br>
      speaking frankly, there are a very limited number of people with
      sufficient knowledge and interest across two programs to make
      heads or tails out of these comparisons. But it is a very
      important issue, not just from technical curiosity, but because a
      lot of<br>
      money have been invested based on what these programs say, so if
      they give significantly different results, policy makers would <br>
      like to know what's going on and ideally, what is the ground
      truth? <br>
      <br>
      I don't want to sound like a modern-day Cassandra, and I don't
      have enough resources or time to pursue this as a private<br>
      adventure. However, I hope that public institutions will see the
      need and benefit, and support some serious work in this area.<br>
      <br>
      I know that you (Simge) or I are not the only people who've
      wrestled with this problem.  I would like to hear the experiences
      of<br>
      others (not you, Jeff,  I already know what you would say :-) ). 
      Since all the efforts I've heard of are going from eQUEST<br>
      to EnergyPlus, not the other way around, the domain knowledge is
      probably higher on the eQUEST/DOE-2 side. Therefore,<br>
      it would be most valuable to get the EnergyPlus experts to chime
      in on the nuances of EnergyPlus modeling of which we<br>
      may be lacking.  For the same reason, you might consider posting
      your message to the EnergyPlus_Support bulletin board<br>
      as well. <br>
      <br>
      See, Simge, now you got me wasting a couple of hours on a Friday
      afternoon! <br>
      <br>
      I'm not sure when I would have time to look at your input files,
      but if I see anything I'll let you know.<br>
      <br>
      Joe<br>
      <br>
      <br>
      <br>
      <br>
      On 5/1/2014 1:35 PM, Simge Andolsun wrote:<br>
    </div>
    <blockquote
cite="mid:CAHm8iRMJeJ6bkYh5uD5sYKeTcE-G5Q-gVsEN-pt79hDEr4uc1A@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>Dear eQUEST users (Particularly Dear Joe Huang),</div>
        <div><br>
        </div>
        <div>Please find the attached eQUEST and EnergyPlus files. They
          represent identical cases for comparison of the two programs.
          The runs are conducted for Los Angeles. The heating and
          cooling consumption of EnergyPlus file are, however,
          unreasonably higher than that of EQUEST. It is particularly
          strange that heating occurs in early morning time during the
          summer in EnergyPlus whereas no heating occurs in eQUEST
          during these hours.</div>
        <div><br>
        </div>
        <div>We need our results not to deviate extremely from eQUEST
          when we start using EnergyPlus. That is why, I am conducting
          this comparative analyses for cases representing identical
          conditions. I would appreciate it very much if you could
          examine these files and let me know whether there is anything
          I can do to make the results of these cases in the two
          programs as close as possible to each other.</div>
        <div><br>
        </div>
        <div>Dear Joe Huang,</div>
        <div><br>
        </div>
        <div>Please see the attached charts that show the hourly
          variation of temperatures in the system nodes and hourly
          energy consumption. There is definitely something weird going
          on in the early morning hours when the system just starts
          working. I have read your paper in the link below. Below is a
          section from your paper that I have paid particular attention
          to. Might I be having a similar issue in my case? </div>
        <div><a moz-do-not-send="true"
            href="http://gundog.lbl.gov/dirpubs/SB06/huang.pdf"
            target="_blank">http://gundog.lbl.gov/dirpubs/SB06/huang.pdf</a>.
        </div>
        <div>
          <p align="LEFT"> <font face="Times New Roman"><font
                face="Times New Roman"><i>"Heating to the cooling
                  setpoint</i></font></font><font face="Times New Roman"><font
                face="Times New Roman">. Temperature plots revealed that
                at times during the shoulder seasons, <em>EnergyPlus </em><font
                  face="Times New Roman"><font face="Times New Roman">had
                    difficulty in picking between the heating or cooling
                    season control logic. This resulted in the supply
                    air being heated to the cooling, rather than the
                    heating, setpoint during the morning hours. This
                    problem was corrected by improving the setpoint
                    manager in <i><font face="Times New Roman"><font
                          face="Times New Roman">EnergyPlus</font></font></i><font
                      face="Times New Roman"><font face="Times New
                        Roman">."</font></font></font></font></font></font></p>
          <font face="Times New Roman"><font face="Times New Roman">
              <p>Looking forward to hearing from you,</p>
              <div>Best Regards,</div>
              <div>Simge Andolsun, PhD.</div>
            </font></font></div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>