<div dir="ltr"><div><div>Thank you for valuable suggestions.<br><br></div>However, the model with thermal storage still have unmet hours. I checked peak building load annually and monthly (LS-C and LS-D report) and found no change in peak load.<br>
<br></div>Please guide me to overcome this problem.<br></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Fri, Apr 25, 2014 at 6:37 AM, Tan, Kevin Zong-Neng <span dir="ltr"><<a href="mailto:tan.kevin@pbworld.com" target="_blank">tan.kevin@pbworld.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div link="blue" vlink="purple" lang="ZH-CN"><div><p class="MsoNormal"><span lang="EN-US">Mayank,<u></u><u></u></span></p>
<p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><span lang="EN-US">Pls check your charging sch & discharging sch, this may help.<u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p>
<p class="MsoNormal"><span lang="EN-US">Kevin<u></u><u></u></span></p><p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><p class="MsoNormal"><b><span style="font-size:10.0pt">发件人<span lang="EN-US">:</span></span></b><span style="font-size:10.0pt" lang="EN-US"> Mayank Bhatnagar [mailto:<a href="mailto:mayank.23aug@gmail.com" target="_blank">mayank.23aug@gmail.com</a>] <br>
</span><b><span style="font-size:10.0pt">发送时间<span lang="EN-US">:</span></span></b><span style="font-size:10.0pt" lang="EN-US"> 2014</span><span style="font-size:10.0pt">年<span lang="EN-US">4</span>月<span lang="EN-US">24</span>日<span lang="EN-US"> 13:29<br>
</span><b>收件人<span lang="EN-US">:</span></b><span lang="EN-US"> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br></span><b>主题<span lang="EN-US">:</span></b><span lang="EN-US"> [Equest-users] Thermal storage modeling issues: high cooling capacity and unmet hours<u></u><u></u></span></span></p>
<div><div class="h5"><p class="MsoNormal"><span lang="EN-US"><u></u> <u></u></span></p><div><p class="MsoNormal"><span lang="EN-US">Dear eQuest users,<u></u><u></u></span></p><div><p class="MsoNormal"><span lang="EN-US"><br>
I need help in thermal storage modelling. The issue which I have faced is: <br> <br>The project have 4 chiller (2200 TR each). To reduce peak load in day time, I have modeled thermal storage of 8000 TR-h (95 MBTU) with charging and discharging rate at 11.9 MBTU/h and 12 MBTU/h. To size each chiller capacity, I modeled chillers as autosize in both case (with and without thermal storage).<br>
<br>When there is no thermal storage the chiller sizing is 2386 TR each (4 chiller) with zero unmet hours and When I modeled thermal storage and a chiller dedicated to thermal storage and other three are working as supporting to thermal storage. The chiller size in this case are 3 chillers of 3496 TR and one chiller of 1026 TR and 5467 unmet hours.<br>
<br><br>I am following procedure as mentioned in tutorial (attached). However, I got unmet hours and higher cooling tonnage than without thermal storage case.<br><br>Please help me to sort out this problem. <br><br>Regards,<br>
Mayank Bhatnagar<br>Energy Analyst<u></u><u></u></span></p></div></div></div></div></div><br clear="all">
______________________________________________________________________<br>
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.<br>
</div>
</blockquote></div><br></div>