<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div>This requirement of adding cooling where it is not designed is an odd one to be sure.  A possible workaround is to recognize that the proposed building will have a cooling "setpoint" that is higher than usual and to model the proposed and baseline cooling systems with an equally high cooling setpoint. </div><div><br></div><div>Dan</div><div><br><div>—</div><div>Sent from my phone</div></div><div><br>On Apr 25, 2014, at 10:32 AM, Steve Jacobs <<a href="mailto:sjacobseng@gmail.com">sjacobseng@gmail.com</a>> wrote:<br><br></div><blockquote type="cite"><div>
  
    <meta content="text/html; charset=ISO-8859-1" http-equiv="Content-Type">
  
  
    <div class="moz-cite-prefix">I'm not aware of anything says we can
      or can't use addendum to Appendix G. It is certainly frustrating
      not having anywhere to take questions. The inability for modelers
      to seek clarifications means that the community is probably taking
      a lot of different approaches to the incentive. <br>
      <br>
      <br>
      <br>
      On 4/25/2014 6:56 AM, Busby, Aaron wrote:<br>
    </div>
    <blockquote cite="mid:8D32E889163A5F4392F349F8034C79DB72B85E@SHANDMBX02.syskamail.syska.net" type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Verdana;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
span.EmailStyle18
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {page:Section1;}
-->
</style><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
      <div class="Section1">
        <p class="MsoNormal"><span style="color:#1F497D">ASHRAE 90.1 has
            several addendums now that have added system types, just for
            warehouse type spaces where they are heated only.  Look for
            Addenda DN, system types 10 and 11.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div style="mso-element:frame;mso-element-frame-hspace:9.0pt;mso-element-wrap:around;mso-element-anchor-vertical:paragraph;mso-element-anchor-horizontal:
page;mso-element-left:15.8pt;mso-element-top:.05pt;mso-height-rule:exactly">
          <table cellpadding="0" cellspacing="0" align="left" hspace="0" vspace="0">
            <tbody>
              <tr>
                <td style="padding-top:0in;padding-right:9.0pt;
                  padding-bottom:0in;padding-left:9.0pt" align="left" valign="top">
                  <div>
                    <p class="MsoNormal" style="line-height:115%;mso-element:frame;mso-element-frame-hspace:
                      9.0pt;mso-element-wrap:around;mso-element-anchor-vertical:paragraph;
                      mso-element-anchor-horizontal:page;mso-element-left:15.8pt;mso-element-top:
                      .05pt;mso-height-rule:exactly">
                      <b><i><span style="font-size:10.0pt;
line-height:115%;font-family:"Verdana","sans-serif";color:#1F497D">Aaron
                            Busby, PE,  LEED AP<o:p></o:p></span></i></b></p>
                    <p class="MsoNormal" style="line-height:115%;mso-element:frame;mso-element-frame-hspace:
                      9.0pt;mso-element-wrap:around;mso-element-anchor-vertical:paragraph;
                      mso-element-anchor-horizontal:page;mso-element-left:15.8pt;mso-element-top:
                      .05pt;mso-height-rule:exactly">
                      <span style="font-size:8.0pt;line-height:115%;
                        font-family:"Verdana","sans-serif";color:#1F497D">Tel: 
                        770.563.1522<br>
                        Cell: 678.642.7549<o:p></o:p></span></p>
                  </div>
                </td>
              </tr>
            </tbody>
          </table>
        </div>
        <p class="MsoNormal"><span style="color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
                <a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
                [<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Tom Mickley<br>
                <b>Sent:</b> Friday, April 25, 2014 8:38 AM<br>
                <b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> [Equest-users] Section 179D Question<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Has anyone run a baseline building for a
          retrofit building to qualify a business owner for the Section
          179D tax deduction?  It seems simple enough to model the
          existing building based on ASHRAE 90.1 standards.  Has anyone
          found any potential “hiccups” along the way that has prevented
          the up to $1.80/sq tax deduction aside from the obvious of not
          meeting the energy upgrade percentage?
          <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Here’s my main concern.  I have a cabinet
          manufacturer customer who has a 100,000sf metal building that
          is roughly 30% wood working or manufacturing, 65% warehouse
          storage and 5% office space.  95% of this facility is heated
          only.  Do I have to include cooling in the baseline from
          ASHRAE 90.1 system 5 on appendix G, table G3.1.1.A?  The only
          upgrades we are proposing are to take out the air rotation
          unit and radiant tube vacuum systems and a few other minor
          items. 
          <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Any advice would help.  Thanks in advance.
          <o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Thanks,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Tom Mickley<o:p></o:p></p>
        <p class="MsoNormal">Mechanical Engineer CEM<o:p></o:p></p>
        <p class="MsoNormal">The K Company<o:p></o:p></p>
        <p class="MsoNormal">Cell 330-760-3994<o:p></o:p></p>
        <p class="MsoNormal">Office 330-773-5125<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  
</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>Equest-users mailing list</span><br><span><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a></span><br><span>To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span><br></div></blockquote></body></html>